The IBC mentions Limited Area sprinkler systems with a veiled
reference being 20 sprinklers or less. However, there is no formal
definition or description as to what they are or where they are
allowed. Any thoughts or experience with this? I have a proposal on
my desk for a partial system
I have done a few of these type systems. Usually the ones I have done
involve a mechanical room with a gas furnace or an elevator equipment room.
Karen Purvis
Senior Designer
Facility Systems Consultants
713 South Central Street,
Suite 101
Knoxville, TN 37902
ph.865-246-0164
fax 865-246-1084
Not an issue. In a birdcage the riser is not serving and area greater than
5000 sq.ft. (usually). There may be dozens or dozens of dozens of risers.
And it's not exactly clear in the definitions but in a birdcage the vertical
piping more closely matches the definition of a branch line.
Chris
I've done a few of the partial systems according to NFPA 101, but as
you say, it is just a couple of heads in a space. That tops out a 6
sprinklers. However, the IBC one appears to go to 20. The one I have
been asked to look at is 18.
At 08:32 AM 3/31/2009, you wrote:
I have done a few of
Travis,
This product commodity falls within the same parameters as boat storage - there
is no prescriptive requirement to follow.
In fact, NFPA has issued a statement this particular type of storage
arrangement is outside the scope of NFPA-13.
That being said, I have done a fair amount of
Actually, the IBC section on limited area sprinkler systems goes up to 19 heads
(fewer than 20). It also requires a hydraulic calc with a simultaneous
plumbing demand.
Eric J. Shelton, PE
Senior Fire Protection Engineer
Hankins and Anderson
Consulting Engineers
4880 Sadler Road Suite 300
The only hole in the thinking of the experts is their opinions are based
on WAG not SWAG to my knowledge. I'm not suggesting they are wrong. I'd
trust their knowledge a bit more if they had some test data (which doesn't
exist) or at least some examples of fires and the outcome. Sure would be
As identified by Karen, the IBC allows some locations (such as furnace
rooms) to be individually protected (or a higher degree of
separation). This is providing protection from this room to the rest
of the building. So I guess the sleeping room is such a hazard that
the rest of the
While true initially the HPR then is replaced next year by Billy Bob Joe's
Insurance and they sue the contractor when it fails. HPR didn't legally
engineer it as they are not the EOR usually even though they often drive a
design, Codes don't cover it. You are out on your own at that point.
This requirement for 15 Sec. delivery in residential dry systems already
exists in NFPA 13 2007, Table 7.2.3.6.1
Thom McMahon, SET
Firetech, Inc.
2560 Copper Ridge Dr
P.O. Box 882136
Steamboat Springs, CO 80488
Tel: 970-879-7952
Fax: 970-879-7926
-Original Message-
From:
1. If you can get the insurer to spec the design, good.
2. If the EOR spec's the design, protect yourself as best you can. Refer all
questions of changes to them so they assume responsibility for every
decision.
3. If you as a contractor are asked to make the design decisions, Walk, Run,
take a
true but the text is weakly worded. The section that references the
Table says based on the hazard not the type of sprinkler (as does
the Table). I believe the intent was for residential sprinklers (for
which a 15 sec requirement exists as part of the listing test
standard) but writing
This is similar to the requirement for Basements over a certain area.
903.2.10.1 Stories and basements without openings.
An automatic sprinkler system shall be installed in every
story or basement of all buildings where the floor area
exceeds 1,500 square feet (139.4 m2) and where there is
not
This is me we're talking about. I'll wear hip waiters and carry a
bazooka. I got a proposal a few years back for a 58 head system fed
from 10 separate risers from the 3/4 public connection (6 heads off
a domestic system times 10 systems, right?). Same town; I hope not
the same guy.
I have no
This sounds like something as ridiculous as I saw once. A dorm above a
restaurant
Surely someone is trying to protect the sleeping rooms from a fire in the
restaurant.
And by sprinklering the rooms??
Ed Vining
On Tue, Mar 31, 2009 at 4:43 AM, Todd Williams t...@fpdc.com wrote:
The IBC
I wish that existed many editions ago. One of our clients have 20+ group
residences built in the 70's and 80's, more like large ranch houses, they
house severely mentally retarded adults. Most have 3 or 4 DPV's and sch40
systems throughout the attics feeding uprights and dry pendents. Some of
FYI
John Drucker
Sent: Monday, March 30, 2009 10:34 PM
Subject: [NJFireSafety] Upstate NY Group Home Fire - Sprinkler System
Failure?
An important fire that should be studied
Here is he local newspaper's accounts of the fire. A 13D system?
4 die as plan 'impractical'
State:
Does anyone have any information regarding the request below? Thanks in
advance.
Carl Chappell
From: Chris Brown [mailto:cbr...@certifiedlifesafety.com]
Sent: Tuesday, March 31, 2009 3:45 PM
To: Chappell, Carl
Subject: CPVC
Carl,
Can you
I would contact the manufacturers and lunizol.
Sent from my Verizon Wireless BlackBerry
-Original Message-
From: Chappell, Carl cchapp...@rjagroup.com
Date: Tue, 31 Mar 2009 18:57:55
To: sprinklerforum@firesprinkler.org
Subject: FW: CPVC
Does anyone have any information regarding
Absolutely - some anti-MIC 1st generation coatings were identified as
potentially incompatible, but I heard that has been reconciled in current
products.
Steve L.
Sent from my Verizon Wireless BlackBerry
-Original Message-
From: Forest Wilson cherokeefire...@aol.com
Date: Tue,
Carl,
While I am not aware of any published case studies per-se, I do know you can
go to manufacturers' websites for good information. For Spears, check out
www.spearsmfg.com and click the link for Flameguard information. Scroll to
the bottom for their document on this topic. For Blazemaster
Contact Blazemaster. They have a publication that lists compatible
products. I recently picked up a hand out at a trade show.
At 07:57 PM 3/31/2009, you wrote:
Does anyone have any information regarding the request below? Thanks in
advance.
Carl Chappell
John,
Please keep us informed of how this develops. I have done several
similar type homes; the last one being for 6 multiple handicapped
children that are not self rescuing. All have been full 13 systems
(wet). If there is a problem, I want to know about it. Fortunately,
CT allows the