RE: Is there test information that shows whether or notobstructing lycra fabric ceiling elements are an issue?

2009-04-16 Thread George Church
Yes, sometimes boiling it down to one logical question is enough. Ok, u want to suspend flammable fabric that drips hot burning debris down atop kids in a daycare? What were u thinking? In this case, if no obvious, dependable method of protection is available, remark it's a nice idea but no, you

RE: Is there test information that shows whether or not obstructing lycrafabric ceiling elements are an issue?

2009-04-16 Thread Chris Cahill
Create your own test. Light a controlled fire like a pan of heptane or alcohol in the space with the lycra installed and see what happens with just overhead sprinklers. Find some local FPE's or arson investigators to help they'd love it. Could find a warehouse with an 18' ceiling if they don't

rated wall opening

2009-04-16 Thread Dewayne Martinez
Is there any testing or criteria in regards to equivalent rating for a water curtain or deluge curtain when protecting an opening in a rated wall? I have a 3' opening in a 3 hour wall and the architect is trying to see if this can be accomplished with a water or deluge curtain. Thanks, Dewayne

RE: rated wall opening

2009-04-16 Thread Craig.Prahl
We've discussed this before and the answer is no there is no published data of an equivalency. Fire shutter is your best bet. What is the opening for? Craig L. Prahl, CET Fire Protection Specialist Mechanical Department CH2MHILL Lockwood Greene 1500 International Drive PO Box 491,

RE: rated wall opening

2009-04-16 Thread Dewayne Martinez
Not sure, one of my PM's came to me with the question. -Original Message- From: sprinklerforum-boun...@firesprinkler.org [mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of craig.pr...@ch2m.com Sent: Thursday, April 16, 2009 10:04 AM To: sprinklerforum@firesprinkler.org

RE: rated wall opening

2009-04-16 Thread Travis Mack, SET
We have the same thing in a 2 hr wall. However, this opening is for a conveyor to pass through. I don't think I can get a shutter there. Any ideas? -Original Message- From: sprinklerforum-boun...@firesprinkler.org [mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Dewayne

RE: rated wall opening

2009-04-16 Thread Chris Cahill
And a water curtain allows radiant heat energy to pass but not convective. So fires could start on the other side theoretically. True it's really hard to start a fire at distance with radiant heat alone. It's especially hard with a sprinkler controlled fire. Local AHJ may be sympathetic

Re: Is there test information that shows whether or not obstructing lycrafabric ceiling elements are an issue?

2009-04-16 Thread Allan Seidel
What I have learned so far is that Lycra is strong polyurethane fiber segments joined with stretchy (soft) polyester or polyether fiber segments. The amounts of each varies with the blend. The polyurethane provides the mechanical body to the fiber while the other stuff provides the elasticity. The

RE: rated wall opening

2009-04-16 Thread Steve Leyton
unsubscribe in the subject field) __ Information from ESET NOD32 Antivirus, version of virus signature database 4013 (20090416) __ The message was checked by ESET NOD32 Antivirus. http://www.eset.com __ Information from ESET NOD32 Antivirus, version of virus

RE: Is there test information that shows whether or not obstructinglycra fabric ceiling elements are an issue?

2009-04-16 Thread Thom McMahon
Our local school auditorium has 3x8 ft acoustic panels suspended above the stage with 135'F links and 200'F sprinklers. The panels release on one side to hang perpendicular between the overhead sprinklers. I believe the links used were the same ones used on automatic roof vents. Yes Lycra will

RE: Is there test information that shows whether or notobstructing lycra fabric ceiling elements are an issue?

2009-04-16 Thread Thom McMahon
Or just get a different material. Thom McMahon, SET Firetech, Inc. 2560 Copper Ridge Dr P.O. Box 882136 Steamboat Springs, CO 80488 Tel: 970-879-7952 Fax: 970-879-7926 -Original Message- From: sprinklerforum-boun...@firesprinkler.org [mailto:sprinklerforum-boun...@firesprinkler.org]

RE: rated wall opening

2009-04-16 Thread Craig.Prahl
Typically conveyors will have a break at a rated wall to allow for a shutter, often they will also have interlocks to stop the conveyor if a fire signal is sent from a sprinkler system or if a shutter closes (when the shutters have closure switches on them, not all do). I've seen some where

Re: rated wall opening

2009-04-16 Thread Roland Huggins
It's done all the time in fire partitions but a 3 hr wall is starting to sound like a fire wall (which presents a much greater concern regarding integrity etc.). I'd proceed carefully. Roland On Apr 16, 2009, at 7:50 AM, Dewayne Martinez wrote: Is there any testing or criteria in regards

RE: Is there test information that shows whether or not obstructing lycrafabric ceiling elements are an issue?

2009-04-16 Thread Chris Cahill
I can almost guarantee wet lycra will not go anywhere in the early stages of a fire. Ever put a paper cup or plastic bag full of water in a fire? Let's assume the first heads goes off without any delay. Let's even assume the lycra below the fire is gone. These are reasonable assumptions

RE: rated wall opening

2009-04-16 Thread Thom McMahon
http://www.mmdoor.com.cn/e_index.htm Try these guys the make custom fire doors as well. Any door that reduces the opening, and then having sprinklers on both side may be the most effective. Thom McMahon, SET Firetech, Inc. 2560 Copper Ridge Dr P.O. Box 882136 Steamboat Springs, CO 80488 Tel:

Re: Is there test information that shows whether or not obstructing lycrafabric ceiling elements are an issue?

2009-04-16 Thread Todd Williams
Allan, There are way too many question on this stuff. What is really going to happen with that arrangement in a fire situation? Will the fabric more likely start to deteriorate directly above the fire or along the ceiling jet? If one area starts to go, how will the rest of the panel react?

RE: rated wall opening

2009-04-16 Thread Craig.Prahl
Rated partition and rated wall assemblies are different in construction, but in either case has anyone seen any calcs proving equivalency of a sprinkler or sprinklers to a UL listed rated assembly? Craig L. Prahl, CET Fire Protection Specialist Mechanical Department CH2MHILL Lockwood Greene

RE: rated wall opening

2009-04-16 Thread Thom McMahon
Only the window sprinklers. Thom McMahon, SET Firetech, Inc. 2560 Copper Ridge Dr P.O. Box 882136 Steamboat Springs, CO 80488 Tel: 970-879-7952 Fax: 970-879-7926 -Original Message- From: sprinklerforum-boun...@firesprinkler.org [mailto:sprinklerforum-boun...@firesprinkler.org] On

CPVC in Ord Hazard

2009-04-16 Thread Thom McMahon
If an AHJ accepts CPVC pipe for an Ord. Group II warehouse installation, is it ok to do a LH alteration to that system for office space? Or is it better to just Run and make sure there is no connection to you for any part in this system? I'm thinking Don't Touch It! Any other thoughts?

RE: rated wall opening

2009-04-16 Thread George Church
I've also seen the conveyor be enclosed for 10' +/- on either side with either QR heads or with something like a gem thermal control valve on each side, each TCV feeding spkrs on BOTH sides of the wall. Learn from history, if you have any aerosols present, Kmart (1981) Falls twp, PA; just over a

RE: CPVC in Ord Hazard

2009-04-16 Thread Jim Johnston
I personally wouldn't touch it, if something bad happens in any area of the system I'm sure the legal system would try to tie you to it since you were aware of the problems even though you didn't originally cause it. Jim Johnston, P.E. Fire Protection Engineer Inland Fire Protection, Inc 1100

RE: CPVC in Ord Hazard

2009-04-16 Thread George Church
Noreen can omit almost anything in contract :) I assume its over 400 SF warehouse and not in a light hazard building? I'd scan the horizon for what could bite you later, tho- is return worth risk? glc -Original Message- From: sprinklerforum-boun...@firesprinkler.org

RE: CPVC in Ord Hazard

2009-04-16 Thread Paul Johnson
The classic contractor's dilemma - Risk versus Reward. A few humble-opinion thoughts on each: From a Risk standpoint, if something (anything) goes wrong later down the road, what can you rely on that will prove you installed in accordance with applicable standards, manufacturers' instructions,

Re: CPVC in Ord Hazard

2009-04-16 Thread Todd Williams
Sounds like a great project for your competition. Many moons ago (my previous employer), we did a partial system in a manufacturing area that was so caustic that galvanized pipe would rot in less than a year. We got permission to use CPVC and it held up fine. Other than that, stay away At

RE: CPVC in Ord Hazard

2009-04-16 Thread Craig.Prahl
What did you hang the pipe with? Just because someone gave permission to install a product in a system outside of it's listing doesn't absolve a contractor of potential negligence if the system fails or does not perform as a listed component would. That could be kind of shaky ground. Was

RE: CPVC in Ord Hazard

2009-04-16 Thread Thom McMahon
The way I see it, If you have a situation Outside of the scope of the code/standard like a corrosive environment, and the EOR says use this product in this manner. Both you and the owner are protected from liability to the best of your ability, by the EOR knowing the extent of his design

RE: CPVC in Ord Hazard

2009-04-16 Thread Todd Williams
I don't recall what they used for hangers. The job was done 22 years ago +/-, so I don't remember all the details. My boss at the time handled the negotiations and everybody signed off on it (Ins co, AHJ, etc.). As I recall there was an issue with stainless but I really don't remember what. It

RE: CPVC in Ord Hazard

2009-04-16 Thread George Church
LOL- while that's a tribute to the longevity of CPVC in acid bath proximity, NOW we have a storage area protected by CPVC lines :) Give ya a similar recent experience: Those darn balcony heads in IBC- owner strictly enforces No BBQ in apts. We're doing Bldg 2, enforcement obvious in adjacent

RE: Re: Is there test information that shows whether or not obstructinglycra fabric ceiling elements are an issue?

2009-04-16 Thread fire...@eoni.com
Fusible links have tension rating of 1# to #50# for metal links. I do not know the tension rating of the glass bulb links made by Job. Temperature ratings are from 135*F to 500*F Douglas Hicks General Fire Equipment Co of Eastern Oregon, Inc --- Original Message --- The last

Cause Analysis of Accidental Discharge of Fire Sprinklers

2009-04-16 Thread Aydın ÖZKAYA
We are reported an accidental discharge of ESFR in a roll paper warehouse. I have two questions: Q1 : Apart from the technical papers, does any one has a, - flow chart - check list for a systematic and analytical analysis of (root) cause(s)? Q2 : Is there a database where I can both report to