Dear Forum members, I am investigating a case where 10 out of 45 sprinklers were found open causing total loss of food raw material . No fire traces were found. Normal static pressure is 75 PSI. There is a report that the municipality shutoff water supply and reopened the supply during the

Sprinklers under platforms

2012-11-30 Thread Craig.Prahl
Got an elevated non-combustible equipment access platform that is 8 off the floor. The contractor is informing the GC that because the platform is over 48 wide there needs to be sprinklers below. Trying to put this fire out and it appears the NFPA 13-2007, 8.15.6.2 would cover it. However

RE: Sprinklers under platforms

2012-11-30 Thread Cahill, Christopher
Is it enclosed concealed space under the platform except for the perforated deck? Guess I haven't seen any equipment platform that is enclosed underneath making them all need heads. But if it meets #1 and the only question is tight yeah I think so. I think the requirement is to keep trash

RE: heat trace

2012-11-30 Thread Ice, Chris
The day I stop learning, I'm dead. :) I'm interested in knowing why the NFPA 13 Committee has such issues with heat trace if it offers no other sufficient alternatives (other than antifreeze which has enough challenges of its own). Regards, Chris Ice Fire Protection Industrial Sales Hajoca

RE: Sprinklers under platforms

2012-11-30 Thread RFletcher
8.15.6.1 refers to combustible platforms. I think 8.16.5.2 #3 is there in case the platform is made of grating. The handbook says 8.16.5.2 is there as an exception to the rule that all combustible spaces be sprinklered. Ron Fletcher Aero Phoenix -Original Message- From:

RE: Sprinklers under platforms

2012-11-30 Thread bcasterline
does anybody else find the fact that the floor itself is an obstuction to pattern development a bit disturbing? at 6 feet between sprinklers with 7 inch max deflector above the floor, the 'dry spots' are going to be 2 or 3 feet long! Quoting rfletc...@aerofire.com: 8.15.6.1 refers to

RE: Sprinklers under platforms

2012-11-30 Thread Rod DiBona
Craig, We just had a similar case yesterday where we successfully used this section to eliminate coverage. This platform was not grated however. I think the heart of the question is does this meet the 8.15.2 (3) requirement of tight construction? I had it in my mind that this was to slow fire

RE: Sprinklers under platforms

2012-11-30 Thread Craig.Prahl
Let's review the conditions: This is indoors so trash accumulation is a non-issue. It is 8 off the floor and the space between the deck and the floor is enclosed with sheet metal. The platform is movable by fork truck for equipment maintenance access, it is not permanent. One small section

RE: Sprinklers under platforms

2012-11-30 Thread Todd Williams
Since it is a moveable object, sprinkler protection is impractical. However, if the hydraulic fluid is combustible and there is a leak, fluid could end up under the platform and the potential does exist for a shielded fire. What is the surrounding occupancy and what is there for sprinkler

Re: Sprinklers under platforms

2012-11-30 Thread Ron Greenman
. -Francis Bacon, essayist, philosopher, and statesman (1561-1626) -- next part -- An HTML attachment was scrubbed... URL: http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachments/20121130/995a9693/attachment.html

RE: Sprinklers under platforms

2012-11-30 Thread Law, Kevin W
with their vocations. -Francis Bacon, essayist, philosopher, and statesman (1561-1626) -- next part -- An HTML attachment was scrubbed... URL: http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attach ments/20121130/995a9693/attachment.html

Re: Sprinklers under platforms

2012-11-30 Thread Ron Greenman
/20121130/995a9693/attachment.html ___ Sprinklerforum mailing list Sprinklerforum@firesprinkler.org http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum ___ Sprinklerforum mailing list

Re: Sprinklers under platforms

2012-11-30 Thread tcf...@bellsouth.net
, philosopher, and statesman (1561-1626) -- next part -- An HTML attachment was scrubbed... URL: http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attach ments/20121130/995a9693/attachment.html ___ Sprinklerforum

RE: Sprinklers under platforms

2012-11-30 Thread Craig.Prahl
This is a piece of equipment in a large open industrial processing building. Overhead sprinklers at .15/3000, Non-combustible processes. Craig L. Prahl, CET Fire Protection CH2MHILL Lockwood Greene 1500 International Drive Spartanburg, SC  29304-0491 Direct - 864.599.4102 Fax -

RE: Sprinklers under platforms

2012-11-30 Thread bcasterline
-- An HTML attachment was scrubbed... URL: http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attach ments/20121130/995a9693/attachment.html ___ Sprinklerforum mailing list Sprinklerforum@firesprinkler.org http://fireball.firesprinkler.org

RE: Sprinklers under platforms

2012-11-30 Thread Cahill, Christopher
) -- next part -- An HTML attachment was scrubbed... URL: http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attach ments/20121130/995a9693/attachment.html ___ Sprinklerforum mailing list Sprinklerforum@firesprinkler.org http

RE: Sprinklers under platforms

2012-11-30 Thread bcasterline
part -- An HTML attachment was scrubbed... URL: http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attach ments/20121130/995a9693/attachment.html ___ Sprinklerforum mailing list Sprinklerforum@firesprinkler.org http

RE: Sprinklers under platforms

2012-11-30 Thread Todd Williams
If we have sprinklers adjacent to an unprotected combustible concealed space, the design area has to be increased to 3000 sqft. However, since you already have the 3000 sqft, you would be good on that score. Being that it is a n/c space, I think you can claim (to whomever) that you are good and

RE: Water damage from multiple opened sprinklers

2012-11-30 Thread Matt Grise
Has the relief valve been tested to see if it works? Matt Grisé PE*, LEED AP, NICET II Sales Engineer Alliance Fire Protection 130 w 9th Ave. North Kansas City, MO 64116 *Licensed in KS MO 913.888.0647 ph 913.888.0618 f 913.927.0222 cell www. AFPsprink.com -Original Message-

RE: Sprinklers under platforms

2012-11-30 Thread Cahill, Christopher
://fireball.firesprinkler.org/mailman/private/sprinklerforum/atta ch ments/20121130/995a9693/attachment.html ___ Sprinklerforum mailing list Sprinklerforum@firesprinkler.org http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

RE: Water damage from multiple opened sprinklers

2012-11-30 Thread bcasterline
Dear @riskmanage, there is no similar experience: this is a clear case of present/former drinking buddy vandalism. the report from the municipality is superfulous (a worker there noticed a spike in usage, shut it down, drove around town, saw no prob., brought it back up). By this time the

RE: Water damage from multiple opened sprinklers

2012-11-30 Thread Bruce Verhei
/mailman/listinfo/sprinklerforum -- next part -- An HTML attachment was scrubbed... URL: http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachments/20121130/f68d09c7/attachment.html ___ Sprinklerforum mailing list

Re: single row rack sprinkler location

2012-11-30 Thread Roland Huggins
That's it. It should be noted though that a single rack against the wall is treated as a double row rack with the gap between it and the wall being the longitudinal flue. That's why it shows up in Figures 16.3.4.1.1.1 (a) through (j). Ain't that a kick in the head? Roland On Nov 27, 2012,