RE: Hotels

2017-06-06 Thread Steve Leyton
If there are separations that satisfy the building official, different areas within a single “building” can be protected with the two different standards. But I can’t use one standard in the dwelling units and one outside of them. But universally, I think there’s a pretty wide-span

Re: Hotels

2017-06-06 Thread Design Dept
Travis, Didn't they just change the IBC to allow that? Design Mgr *Living Water Fire Protection, LLC* 1160 McKenzie Rd. Cantonment, FL 32533 (850) 937-1850 On Tue, Jun 6, 2017 at 10:04 AM, Travis Mack wrote: > You can not have a 13 system with 13R in the units. The

RE: Hotels

2017-06-06 Thread Richard Carr
If it is combustible construction you may need the attic and interstitial spaces protected. Richard Carr, SET Branch Manager Cox Fire Protection, Inc 6555 Grace Lane. Jacksonville, Fl. 32205 rc...@coxfire.com 904-781-8227 From: Sprinklerforum

RE: Hotels

2017-06-06 Thread Brian Harris
Hey Micah, things are good, how's Florida? This just happens to be a Marriot project, I'll definitely ask about Module 14. Thanks! Brian Harris, CET BVS Systems Inc. bvssytemsinc.com From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On

Re: Hotels

2017-06-06 Thread Travis Mack
You can not have a 13 system with 13R in the units. The system is either designed per 13 or 13R, not a hybrid. Travis Mack, SET MFP Design, LLC "Follow" us on Facebook: https://www.facebook.com/pages/MFP-Design-LLC/92218417692 Send large files to MFP Design via:

Re: Hotels

2017-06-06 Thread John Irwin
Marriott is 13 regardless. Additionally if any area increase was taken for fire sprinklers it may be 13. John Irwin Division Manager - Fire Sprinklers Critical System Solutions jir...@criticalsystemsolutions.com 813-618-2781 Sent from a mobile device. Please forgive brevity, spelling errors

RE: Hotels

2017-06-06 Thread Brian Harris
It's (4) stories, the notes on the FP drawings call for a 13 system with 13R coverage in the guest room. Brian Harris, CET BVS Systems Inc. bvssytemsinc.com From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of Trillium Fire

RE: Hotels

2017-06-06 Thread Matt Grise
Hilton Family of hotels also has their own standards. Matt From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of Micah Davis, SET Sent: Tuesday, June 06, 2017 9:49 AM To: sprinklerforum@lists.firesprinkler.org Subject: Re: Hotels Hey Brian! I hope all is

Re: Hotels

2017-06-06 Thread Micah Davis, SET
Hey Brian! I hope all is well! If it is in the Marriott family, be sure to get a copy of Marriott Module 14. They have specific requirements above and beyond NFPA. Mostly it has to do with the standpipes. Also, I have run into local amendments that effected design specifically related to

RE: Hotels

2017-06-06 Thread Trillium Fire Sprinkler Design Inc.
Send me your email and I can shoot you over a recent project I did so you have something to look at. From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of Brian Harris Sent: June-06-17 10:37 AM To: sprinklerforum@lists.firesprinkler.org Subject: Hotels

RE: Hotels

2017-06-06 Thread Trillium Fire Sprinkler Design Inc.
I do several of these every year. How tall are you talking. Are they wanting 13 or 13R? This determines a few starting factors From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of Brian Harris Sent: June-06-17 10:37 AM To:

Hotels

2017-06-06 Thread Brian Harris
Been doing this sprinkler stuff for just over 11 years now and finally ran into my first hotel project. Any tips/pointers from you guys that do a lot of these ? Brian Harris, CET BVS Systems Inc. Design Manager bvssystemsinc.com Phone: 704.896.9989 Fax: 704.896.1935