Typical ceiling demand - no reductio fro in-racks
Yes on balancing the in-rack design
There is an option not to balance the in-rack with the ceiling IF you increase
the number of in-racks to include face sprinklers AND double the flow for the
in-racks to 60 gpm/sprinkler
Roland Huggins, PE -
NFPA 13 (16ed) sections 16.1.6.6 and 16.1.6.8
I have a customer that installed solid shelve racks in part of a warehouse
protected with ESFR sprinklers. NFPA 2016 allows this provided we follow
section 16.1.6. What overhead density would I use for the ESFR
sprinklers? Is 16.1.6.8 saying that