This fitting (Michigan fitting) was used prior to or alternative to VMTs
in the early eighties
to provide a cheap outlet in the middle of a full stick of pipe. FIT
tees were installed on the up and
downstream ends.
If I remember, the fitting consisted of three parts; a fat rubber
gasket, a
?.
Bruce.
> On Nov 2, 2017, at 13:00, Vince Sabolik wrote:
>
>
> ___
> Sprinklerforum mailing list
> Sprinklerforum@lists.firesprinkler.org
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
Even designers with many years of experience have trouble with this
Carlo- it is rather subtle.
My understanding is (and I don't mean to shout, upper case is meant
for distinction):
Where seismic protection is required-
All MAINS have to be BRACED.
All LINES 2.5" or bigger have to be BRACED.
NFPA 13 2016 9.3.5.5.1 and this only refers to branch-lines. If it’s a main its
required to be braced regardless of size
Rocci Cetani III, CET
Senior Designer
Water-Based Fire Protections Systems Layout, Nicet Level III
Northern California Fire Protection Services Inc.
16840 Joleen Way
I am a newly fire sprinkler designer now and I have been doing it for 2 years.
Well yesterday I was doing a punch list for this sprinkler installation job and
noticed that they were not any seismic bracing attached to the sprinkler
system. So I went back to check the shop drawings and
This is a new installation. The manufacturer is AC and they get their
motors from US motors. Where does the exemption come from?
Best regards,
*Joe Burtell, SET, CFPS*
[image: Burtell Fire_Small]
Phone | Fax | Mobile| Text *406-545-0784 <++1-406-545-0784>*
116 N. 11th Street | Billings, MT
Are you trying to buy a replacement motor for an existing pump? Fire
pumps are exempt from the Premium requirement, however if the manufacturer
sells the motors mostly to other industries they may have made changes
that give up the required Design type B to make it meet the premium
I am being told this by the motor manufacturer. They say they have to do
this by DOE requirements.
Best regards,
*Joe Burtell, SET, CFPS*
[image: Burtell Fire_Small]
Phone | Fax | Mobile| Text *406-545-0784 <++1-406-545-0784>*
116 N. 11th Street | Billings, MT 59101
Email:
Is there an issue as long as the pump unit is UL Listed?
Regards,
G. Tim Stone
G. Tim Stone Consulting, LLC
NICET Level III Engineering Technician
Fire Protection Sprinkler Design
and Consulting Services
117 Old Stage Rd. - Essex Jct., VT. 05452
CELL: (802) 373-0638 TEL:
Has anyone heard of this or know what the schedule is or what states it
applies to?
"the Department of Energy forced the motor manufacturers to move to Premium
Efficient over a certain schedule.
The standard motor that was used on this pump was changed to an A design
code when they moved it to