Do hang the HVAC from the CPVC. Not just taking it off. Ever wonder how codes
get thicker and thicker. One way is more pre-approved design options. The
other. Needing to write this kind of into code.
Simple question. Will HVAC firm post photo on their homepage as example work
their proud
>From the Lubrizol website:
Fiberglass Duct insulation with aluminum, paper, metalized polyester,
polypropylene and polyethylene facing may come into contact with CPVC.
On Sat, Mar 28, 2020 at 9:09 PM Tom Noble via Sprinklerforum <
sprinklerforum@lists.firesprinkler.org> wrote:
> What about
Tom,
I did not see this post until today, so I apologize for the delayed
response. I'll share my thoughts on what you've observed.
No, there is nothing in NFPA 13D regarding hangers for sprinkler system
piping not being allowed to be used for non-system components, as there
is in -13. As