RE: potential freezing in ESFR system

2020-12-22 Thread Scott Futrell via Sprinklerforum
Great comments. Great information. 1" pipe with cast iron fittings filled with water explodes the side out of the cast iron ell in 52 minutes at 17⁰F and that piece flies 65 feet when not confined. I’ve done these experiments outside in winter. Scott Office: (763) 425-1001 x 2 Cell:

Re: potential freezing in ESFR system

2020-12-22 Thread AKS-Gmail-IMAP via Sprinklerforum
It is and has been surprising to me when fire protection contractors ask the pipe freezing question or when they ask piping support questions in context with approval by local AHJ of any kind. The reason for the surprise is because contractors have ready access to materials, labor and space to

RE: potential freezing in ESFR system

2020-12-22 Thread Hinson, Ryan via Sprinklerforum
Hopefully, your sprinklers are not already installed. Ryan L. Hinson, PE*, SET**  \  Burns & McDonnell Senior Fire Protection Engineer O 612-900-3755 NEW \ M 763-688-4045 \  F 952-229-2923 rhin...@burnsmcd.com  \  burnsmcd.com 8201 Norman Center Drive, Suite 500  \  Minneapolis-St. Paul, MN

Re: potential freezing in ESFR system

2020-12-22 Thread John Denhardt via Sprinklerforum
Currently - NFPA 13-2019 allows pulling plugs and installing sprinklers without another hydrostatic test. 28.2.1.8* When systems are being hydrostatically tested, tests shall be permitted to be conducted with pendent or horizontal sidewall sprinklers or plugs installed in fittings. Any plugs

RE: [EXTERNAL] Re: potential freezing in ESFR system

2020-12-22 Thread Kyle.Montgomery via Sprinklerforum
Matt, I think I agree with all of Bob's points. Likelihood of freeze damage in a drained system should be lower, but in the event of damage the manufacturer would probably use that as an excuse to not be held liable. So there is some probably some risk there. What are they hoping to

Re: potential freezing in ESFR system

2020-12-22 Thread Richard Mote via Sprinklerforum
Just wondering, what would be the point of doing a hydrostatic test and then replacing all the sprinklers. In a 40,000 sq. ft. system at 100 sq. ft. per, that a potential for 400 new leaks.  -Original Message- From: John Denhardt via Sprinklerforum To:

Re: potential freezing in ESFR system

2020-12-22 Thread John Denhardt via Sprinklerforum
Again personally, I would never knowingly put water in a wet piping system unless the "client" can ensure or take responsibility" for any damage due to freezing. Pulling the pendent sprinklers is not a viable option. As a contractor, in almost all cases, our client backed down. In the case when

Re: potential freezing in ESFR system

2020-12-22 Thread Bob Caputo via Sprinklerforum
Matt, Not sure many people are lurking around the forum this week, so I’ll offer my 2 cents worth…. 1st and foremost, I would get the GC to sign off on a letter stating that you are not responsible for any freeze damage resulting from their request to perform the hydro prior to having heat in

potential freezing in ESFR system

2020-12-22 Thread Matt Grise via Sprinklerforum
we have a GC who wants to hydro test a pendant ESFR system before they have heat in the building. They want to fill and test during the day while temperatures are over 40F, and then drain the system before it gets cold again. I thought it did not sound like a great idea, but I can't