BIM anyone?

2021-01-20 Thread Vince Sabolik via Sprinklerforum
Good evening, Forum - Can someone email or post a set of instruction on how to transfer clashes out of Navis Manage to an Autocad drawing? I was familiar in 2019 - has something changed? Both programs are 2021 versions out of the box. Thanks!! Vince *Vince Sabolik* *West Tech Fire

Re: schedule 7 pipe?

2021-01-20 Thread John Denhardt via Sprinklerforum
Matt - fully understand the position you have. To answer your initial question specifically, I have heard of *no* push to change NFPA 13 with regard to piping material. Thanks, John John August Denhardt, PE *Vice President, Engineering and Technical Services* *American Fire Sprinkler

RE: schedule 7 pipe?

2021-01-20 Thread Matt Grise via Sprinklerforum
There is no doubt that thicker pipe lasts longer. However, when the owner of a warehouse specifies schedule 7 piping for the sprinkler system in a hard bid, the installing contractor will be using schedule 7. Matt -Original Message- From: Lucas Kirn Sent: Wednesday, January 20,

RE: schedule 7 pipe?

2021-01-20 Thread Lucas Kirn via Sprinklerforum
Matt, Having seen many cases of failed sch. 7 pipe over the past 10+ years I would tell anyone willing to listen to stay far, far away from it. Pipe schedule is the most basic form of corrosion/leak protection. The thinner the pipe, the shorter the lifespan. I have also seen several instances

RE: schedule 7 pipe?

2021-01-20 Thread Steve Leyton via Sprinklerforum
Jeff: As a 3rd party consultant, we've been offering remediation and claims management services as well as technical consulting to the legal, property ownership and property management communities on MIC-related issues for about 15 years. 2 years ago, we spun off a subsidiary business to

Re: schedule 7 pipe?

2021-01-20 Thread Bob Caputo via Sprinklerforum
Jeff Normand is correct in terms of the 1st exposed thread at the fitting having less depth of material than a schedule 10 roll groove, however most corrosion we see is related to oxidation as opposed to MIC. The problem with roll grooves tends to be water trapped between the grooves sitting

Re: schedule 7 pipe?

2021-01-20 Thread John Denhardt via Sprinklerforum
That is what I missed. Correct - if you *do not *comply with 16.3.1 for the pipe or tube you are using, Listed pipe or tube is required. Thanks, John John August Denhardt, PE *Vice President, Engineering and Technical Services* *American Fire Sprinkler Association* m: p: 301-343-1457

RE: schedule 7 pipe?

2021-01-20 Thread Matt Grise via Sprinklerforum
I was looking at NFPA 13 - 2019 16.3.2 "when steel pipe referenced in 7.3.1.1 is used... ...minimum nominal wall thickness for pressures up to 300psi shall be in accordance with Schedule 10..." Does this require that thinner pipe be listed? I was curious if the listed s7/s5 products are any

Re: schedule 7 pipe?

2021-01-20 Thread John Denhardt via Sprinklerforum
Keep in mind, NFPA 13 states piping or tubing that meets Table 7.3.1.1 is acceptable. Listing is NOT required. *NFPA 13 - 2019: 7.3.1.1 Pipe or tube shall meet or exceed one of the standards in Table 7.3.1.1 or be in accordance with 7.3.3.* Thus, as long as any piping or tubing material

Re: schedule 7 pipe?

2021-01-20 Thread Jeff Normand via Sprinklerforum
I have been designing with sch 7 pipe for over 25 years. Not sure about longevity. But you mentioned A53 unlisted pipe. Possibly getting listed? I would really like to see comparisons of sch 7, 10 and 40 for corrosion and MIC. Specially treated pipe some manufacturers claim. Always heard that sch

RE: schedule 7 pipe?

2021-01-20 Thread Scott Futrell via Sprinklerforum
Considering how much corrosion I've observed and documented in wet and dry systems in schedule 10 in 8-15 years - not MIC - we only specify schedule 40. Scott   Office: (763) 425-1001 x 2 Cell: (612) 759-5556 -Original Message- From: Sprinklerforum On Behalf Of Steve Leyton via

schedule 7 pipe?

2021-01-20 Thread Matt Grise via Sprinklerforum
Has there been any push/interest in allowing unlisted (standard ASTM A53) schedule 7 steel pipe to be allowed by code in place of the listed "flow" piping options? Matt ___ Sprinklerforum mailing list Sprinklerforum@lists.firesprinkler.org