Re: 4 1/2" FDC

2021-03-18 Thread BRUCE VERHEI via Sprinklerforum
Before you spend your cash I’d make sure you have the correct thread standard. Best. Bruce. > On 03/18/2021 2:55 PM Skyler Bilbo via Sprinklerforum > wrote: > > > Sorry, the one I sent was NST on the 4" side. This should be the correct > one. > >

Re: NFPA 13 2016 25.2.1.4.2

2021-03-18 Thread BRUCE VERHEI via Sprinklerforum
I wish we used two terms. I used to call the 13-D test a ‘leak test’, instead of hydrostatic test. That’s what we really mean here. We want to see the pipe charged, and see if it leaks. A hydrostatic and a leak test aren’t really the same thing. Best. Bruce Verhei > On 03/18/2021 8:21 PM

RE: Different Levels of protection open to each other in the same hazard

2021-03-18 Thread BRUCE VERHEI via Sprinklerforum
I’d ask why. Is the fire sprinkler system acting as detection system for a smoke exhaust system? Best. Bruce Verhei > On 03/18/2021 8:05 PM Travis Mack via Sprinklerforum > wrote: > > > We've had cases where the 2 story volume area is required to be protected > from the 1st floor

Re: NFPA 13 2016 25.2.1.4.2

2021-03-18 Thread John Denhardt via Sprinklerforum
If you think it would help, I can always have a personal conversation with her. Let';s discuss tomorrow. For future use with AHJs, AFSA will make the informal interpretation available to all members. Thanks, John John August Denhardt, PE *Vice President, Engineering and Technical Services*

Re: NFPA 13 2016 25.2.1.4.2

2021-03-18 Thread John Irwin via Sprinklerforum
I'd like that. The last time I went a couple rounds with her we did have a few AFSA interpretations but none exactly fit the 'identical' situation so she wasn't satisfied. John Irwin Director Of Construction Quick Response Fire Protection 727-282-9243 Typed on tiny keys, just for you. Please

Re: NFPA 13 2016 25.2.1.4.2

2021-03-18 Thread John Denhardt via Sprinklerforum
John - Let's talk tomorrow. I think we can prepare an informal interpretation for you describing the intent of this section. AFSA will be covering Acceptance Testing is some upcoming AHJ webinars. Thanks, John John August Denhardt, PE *Vice President, Engineering and Technical Services*

Re: Cleveland Automatic Sprinkler

2021-03-18 Thread Ron Greenman via Sprinklerforum
I believe Automatics came out with the first Standard Spray Sprinklers in 1953. The SS had the U (upright) of P (pendant) designation and defined their orientation. The "old-style" sprinklers or conventional sprinklers manufactured before then could be installed in the upright or the pendant

Re: Cleveland Automatic Sprinkler

2021-03-18 Thread Vince Sabolik via Sprinklerforum
CLEVELAND and 'conventional' head that could be installed as a pendent or upright. On Mar 18, 2021, Vince Sabolik via Sprinklerforum wrote: >"Automatic" Sprinkler used to be IN Clevelar. >Did you run into one of the old style heads that was installed in the >upright or pendent position? > >On

NFPA 13 2016 25.2.1.4.2

2021-03-18 Thread John Irwin via Sprinklerforum
NFPA 13 2016 25.2.1.4.2, Modifications that cannot be isolated, such as relocated drops, shall require testing at system working pressure. We have a local AHJ that always requires us to pump up tenant improvement projects to 200 psi if they are over 20 sprinklers. We have a waiver/release form

Re: Cleveland Automatic Sprinkler

2021-03-18 Thread Vince Sabolik via Sprinklerforum
"Automatic" Sprinkler used to be IN Clevelar. Did you run into one of the old style heads that was installed in the upright or pendent position? On Mar 18, 2021, jaycs7919--- via Sprinklerforum wrote: >Just wondering if anyone is familiar with these sprinklers.  I am >hoping some of the more

RE: Different Levels of protection open to each other in the same hazard

2021-03-18 Thread Jerry Van Kolken via Sprinklerforum
I ask because this time it will require a 40'-0" drop and seismic assembly for each sprinkler Jerry Van Kolken Millennium Fire Protection Corp. 2950 San Luis Rey Rd. Oceanside, CA 92058 (760) 722-2722 FX 722-2730 -Original Message- From: Sprinklerforum On Behalf Of Jerry Van Kolken

RE: Different Levels of protection open to each other in the same hazard

2021-03-18 Thread Matthew J Willis via Sprinklerforum
I believe there was a change somewhere, or just good practice, but responders like the ability to shut the system off from the floor they are standing on. In other words, if you can see it, then the control valve should be on the level you are standing. I have been meaning to research this

RE: Different Levels of protection open to each other in the same hazard

2021-03-18 Thread Travis Mack via Sprinklerforum
We've had cases where the 2 story volume area is required to be protected from the 1st floor system, but not the entire building just off of one system because of that. Travis Mack, CFPS, CWBSP, RME-G, COC, SET Engineering Manager MFP Design 3356 E Vallejo Ct Gilbert, AZ 85298 480-505-9271 ext.

Different Levels of protection open to each other in the same hazard

2021-03-18 Thread Jerry Van Kolken via Sprinklerforum
I've had this review comment come up and want to know if there was any way to argue it. I have a project where each level of the building has its own system. There are areas where the lower level opens into the upper level. Because these 2 level are not complete separate the reviewer is asking

Cleveland Automatic Sprinkler

2021-03-18 Thread jaycs7919--- via Sprinklerforum
Just wondering if anyone is familiar with these sprinklers.  I am hoping some of the more experienced guys like Ron or Richard dealt with them.  They are installed in two configurations and trying to verify which is correct. Jay Stough Tilley Fire Solutions

RE: Section 9.5.6 versus Section 20.6.6 of the 2019 Edition

2021-03-18 Thread Mike Morey via Sprinklerforum
https://www.nfpa.org/assets/files/AboutTheCodes/13/Errata_13_19_2.pdf Mike Morey CFPS 3229 * NICET S.E.T. 123677 Project Manager * Fire Protection Group Shambaugh & Son, LP an EMCOR Company 7614 Opportunity Drive * Fort Wayne, IN * 46825 direct 260.487.7824 / cell 260.417.0625 / fax

Section 9.5.6 versus Section 20.6.6 of the 2019 Edition

2021-03-18 Thread Larrimer, Peter A (HEFP\19HEF) via Sprinklerforum
Can someone tell me if Section 9.5.6 was truly supposed to be deleted from the 2019 edition of NFPA 13 and replaced with Section 20.6.6? Looking at the free access online, Section 9.5.6 still exists. However, if you view the standard as a committee member, Section 9.5.6 is not there. I have

Re: 4 1/2" FDC

2021-03-18 Thread Skyler Bilbo via Sprinklerforum
Sorry, the one I sent was NST on the 4" side. This should be the correct one. https://www.firehosedirect.com/aluminum-4-1-2-nh-to-4-npt-double-female - Skyler Bilbo On Thu, Mar 18, 2021 at 1:52 PM Skyler Bilbo wrote: > Same site offers a 4" NPT to 4-1/2" NST female-female adapter.

Re: 4 1/2" FDC

2021-03-18 Thread Skyler Bilbo via Sprinklerforum
Same site offers a 4" NPT to 4-1/2" NST female-female adapter. Probably need to get AHJ approval, since it is not listed/approved. https://www.firehosedirect.com/aluminum-4-1-2-nh-to-4-nh-double-female https://www.firehosedirect.com/aluminum-4-1-2-nh-rocker-lug-plug - Skyler Bilbo On Thu,

RE: 4 1/2" FDC

2021-03-18 Thread Henry Fontana via Sprinklerforum
Hello sir. Check out this site. https://www.firehosedirect.com/aluminum-4-storz-x-4-1-2-male-nh-thread Henry Fontana Operations Manager (NYC) Johnson Controls Fire Protection 100 Lighting Way Secaucus, NJ 07094 Cell: 201-210-9873 henry.font...@jci.com -Original Message- From:

Re: 4 1/2" FDC

2021-03-18 Thread Kevin Hall via Sprinklerforum
Local authorities can require threadless couplings (storz) or other inlet requirements if not in conformance with NFPA 1963: 16.12.3.1.1 Where local fire department connections do not conform to NFPA 1963, the authority having jurisdiction shall be permitted to designate the connection to be

RE: 4 1/2" FDC

2021-03-18 Thread Michael Hill via Sprinklerforum
You may have to put an adapter on a standard Storz connection. Mike Hill -Original Message- From: Sprinklerforum On Behalf Of BOB AKINS via Sprinklerforum Sent: Thursday, March 18, 2021 2:41 PM To: sprinklerforum@lists.firesprinkler.org Cc: BOB AKINS Subject: 4 1/2" FDC I have a city

Re: 4 1/2" FDC

2021-03-18 Thread Craig Leadbetter via Sprinklerforum
Storz connection? > On Mar 18, 2021, at 1:40 PM, BOB AKINS via Sprinklerforum > wrote: > > I have a city requiring 4 1/2" FDC and I am having difficulty finding a > source > SincerelyBob > ___ > Sprinklerforum mailing list >

4 1/2" FDC

2021-03-18 Thread BOB AKINS via Sprinklerforum
I have a city requiring 4 1/2" FDC and I am having difficulty finding a source SincerelyBob ___ Sprinklerforum mailing list Sprinklerforum@lists.firesprinkler.org http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Listed Horizontal Load Adjusted

2021-03-18 Thread Jerry Van Kolken via Sprinklerforum
I was updating my Tolco product sheet for seismic bracing and was noticing a lot of changes to these sheets and updated values on the loading. The UL listed sheets don't have values for specific angles, but the FM listed sheets do. These sheets also are now marked with an "OPM" next to the UL

RE: Smoke Detectors

2021-03-18 Thread Brian Harris via Sprinklerforum
Ron- Seems like it's the "I've always done it that way rule..." Thanks. Brian Harris, CET BVS Systems Inc. bvssytemsinc.com -Original Message- From: Sprinklerforum On Behalf Of Ron Greenman via Sprinklerforum Sent: Thursday, March 18, 2021 11:10 AM To:

Re: Smoke Detectors

2021-03-18 Thread Ron Greenman via Sprinklerforum
I remember something about keeping the detector 12" out and down from the intersection of a wall and ceiling but that had nothing to do with sprinklers and may have been an industry practice, or a "Sven and Ollie we've always done it this way, right-or-wrong" rule. On Thu, Mar 18, 2021 at 7:40 AM

RE: Smoke Detectors

2021-03-18 Thread Prahl, Craig/GVL via Sprinklerforum
That was for heat detectors. 2019 NFPA 72, 21.4.2 related to the shunt-trip operation of elevators. Craig Prahl | Jacobs | Group Lead/SME - Fire Protection | craig.pr...@jacobs.com | www.jacobs.com 1041 East Butler Road Greenville, South Carolina 29606 CONTACT BY: email or MS TEAMS

Re: Question about a drop pipe size

2021-03-18 Thread Bob Caputo via Sprinklerforum
Henry, I’m not sure why the forum site would have disallowed your question but I will inquire with our IT people. To your specific question, NFPA 13, 2019 edition was reorganized (as you know) and all existing system modification requirements were moved to Chapter 29. The use of a 4”

RE: Smoke Detectors

2021-03-18 Thread Brian Harris via Sprinklerforum
Matt- Thank you. Brian Harris, CET BVS Systems Inc. bvssytemsinc.com -Original Message- From: Sprinklerforum On Behalf Of Matthew J Willis via Sprinklerforum Sent: Thursday, March 18, 2021 10:07 AM To: sprinklerforum@lists.firesprinkler.org Cc: Matthew J Willis ; Richard Carr Subject:

RE: Smoke Detectors

2021-03-18 Thread Matthew J Willis via Sprinklerforum
The last time I remember, it was Chapter 6 of NFPA 72. (Not sure which chapter it is in the current edition) It was a requirements for the detector to be located within 24" of the sprinkler. That was for like in an elevator situation where you want the detector going before the sprinkler.

RE: Smoke Detectors

2021-03-18 Thread Brian Harris via Sprinklerforum
It's not for the sprinkler, wasn't sure if it was for the detector. Thanks. Brian Harris, CET BVS Systems Inc. bvssytemsinc.com -Original Message- From: Sprinklerforum On Behalf Of Richard Carr via Sprinklerforum Sent: Thursday, March 18, 2021 9:12 AM To:

RE: Smoke Detectors

2021-03-18 Thread Brian Harris via Sprinklerforum
Craig- Thank you. Brian Harris, CET BVS Systems Inc. bvssytemsinc.com -Original Message- From: Sprinklerforum On Behalf Of Craig Leadbetter via Sprinklerforum Sent: Thursday, March 18, 2021 9:11 AM To: sprinklerforum@lists.firesprinkler.org Cc: Craig Leadbetter Subject: Re: Smoke

RE: Smoke Detectors

2021-03-18 Thread Richard Carr via Sprinklerforum
Could be an obstruction issue. Richard M. Carr, SET Project Manager/Design Diboco Fire Sprinklers, Inc. 325 Jackson Loop Road Flat Rock, NC  28731 rich...@diboco.com 828-696-3400 828-696-2288 Fax 828-708-9118 Mobile -Original Message- From: Sprinklerforum On Behalf Of Prahl,

Re: Smoke Detectors

2021-03-18 Thread Craig Leadbetter via Sprinklerforum
I don't believe there is anything other than when the smoke is close enough to cause an obstruction to the spray pattern. Craig Leadbetter (C) 906-362-5393 craigleadbet...@gmail.com On Thu, Mar 18, 2021 at 7:38 AM Brian Harris via Sprinklerforum < sprinklerforum@lists.firesprinkler.org>

RE: Smoke Detectors

2021-03-18 Thread Prahl, Craig/GVL via Sprinklerforum
I searched NFPA 13, 15 and 72 and couldn't find anything referring to a separation between a detector and a sprinkler. Craig Prahl | Jacobs | Group Lead/SME - Fire Protection | craig.pr...@jacobs.com | www.jacobs.com 1041 East Butler Road Greenville, South Carolina 29606 CONTACT BY: email or

Smoke Detectors

2021-03-18 Thread Brian Harris via Sprinklerforum
Has anyone heard of a minimum distance of 12" required between a smoke detector and a sprinkler head? I don't see anything in NFPA-13 and I'm admittedly not very familiar with alarm/electrical codes. Thank You, Brian Harris, CET BVS Systems Inc. Design Manager