Thanks guys!
Brian Harris, CET
BVS Systems Inc.
bvssytemsinc.com
-Original Message-
From: John Denhardt
Sent: Tuesday, May 04, 2021 4:17 PM
To: sprinklerforum@lists.firesprinkler.org
Cc: Steve Leyton ; Brian Harris
; Henry Fontana
Subject: Re: Manual Dry Standpipe
Fully agree.
Fully agree. Interconnection is required. A control valve is required at each
stairway riser.
Thanks,
John
>
> The foregoing is my opinion only and does not represent NFPA or the NFPA 14
> Technical Committee, nor intended to serve as an interpretation of the
> standard.
>
John August
Agreed. Four separate FDC's - in a building with no sprinklers and likely
without any annunciation of where in the building a fire is working - would be
extremely challenging for the first responding company. The intent is for
each FDC, including multiple FDCs that pump into a single
Yes. There is no exception for dry manual standpipes. Also, I tap the cap
at the bottom and add ball drips to remove any moisture after testing.
On Tue, May 4, 2021 at 3:25 PM Brian Harris via Sprinklerforum <
sprinklerforum@lists.firesprinkler.org> wrote:
> A parking garage is being supplied
I would just say if they were not interconnected then it would be very
confusing when the fire department showed up on where to pump the water
Henry Fontana
Operations Manager (NYC)
Johnson Controls Fire Protection
100 Lighting Way Secaucus, NJ 07094
-Original Message-
From:
A parking garage is being supplied by a Manual Dry Standpipe in each exit
stairwell, 4 total. Per NFPA-14 (2013) 7.5 would these need to be
interconnected? There are no sprinklers in the garage, only standpipes in the
stairwells.
Brian Harris, CET
BVS Systems Inc.
Design Manager