[Sprinklerforum] Re: [EXTERNAL] Re: Plastics in Bin Box storage

2023-05-22 Thread Steve Leyton
Thank you Craig – yes, considered alternative design options. Building is brand new, fitted with ESFR K25. I am going to pursue the “plastics to 9’-6” is an EH2 and I can use ESFR for EH2” approach. The standard is a little confusing and one could say it’s even self-contradictory to a

[Sprinklerforum] Re: [EXTERNAL] Re: Plastics in Bin Box storage

2023-05-22 Thread Prahl, Craig
I’ll also add to Ken’s comment in that much of what FM produces has dependencies on other requirements as well. Building construction, ventilation, etc. can also be part of the specific requirements related to a fire protection data sheet. Read the whole data sheet to be sure there aren’t