I think he is making a cloud clg. per NFPA because of the openings
*Glen Bue**low*
*Glen W. Buelow, Inc.*
*Fire Protection Design and Consulting216-469-7390** <330.665.4439>*
On Fri, Mar 22, 2024 at 1:26 PM Ed Kramer wrote:
> In order to provide maintenance access to HVAC devices above a
See NFPA 2022 9.5.2.1.1 (2) It states that the coverage area is defined by
determining the perpendicular distance to the branch lines on either side, then
using the larger of twice the distance to calculate the coverage area. So the
14' dimension is the one that must be used.
Sarah FifiOasis
I think Todd is right too. No different than finding the spacing of a head
next to the wall. Use the greater distance of either 2x the distance of the
head off the wall or the spacing between that head and the next head in the
line.
Thank you,
Dewayne Martinez
Fire Protection Design Manager
>From the Tyco BlazeMaster handbook
[cid:image001.png@01DA7C2B.3D04E5A0]
I know this isn't a system riser but the concept is the same. Maybe reach out
to BlazeMaster and see what they say.
Thank you,
Dewayne Martinez
Fire Protection Design Manager
TOTAL Mechanical