[Sprinklerforum] Re: Openings in ceilings

2024-03-22 Thread Glen Buelow, Inc.
I think he is making a cloud clg. per NFPA because of the openings *Glen Bue**low* *Glen W. Buelow, Inc.* *Fire Protection Design and Consulting216-469-7390** <330.665.4439>* On Fri, Mar 22, 2024 at 1:26 PM Ed Kramer wrote: > In order to provide maintenance access to HVAC devices above a

[Sprinklerforum] Re: Multiple sprinkler spacings

2024-03-22 Thread s.f...@yahoo.com
See NFPA 2022 9.5.2.1.1 (2)  It states that the coverage area is defined by determining the perpendicular distance to the branch lines on either side, then using the larger of twice the distance to calculate the coverage area.  So the 14' dimension is the one that must be used. Sarah FifiOasis

[Sprinklerforum] Re: Multiple sprinkler spacings

2024-03-22 Thread Dewayne Martinez
I think Todd is right too. No different than finding the spacing of a head next to the wall. Use the greater distance of either 2x the distance of the head off the wall or the spacing between that head and the next head in the line. Thank you, Dewayne Martinez Fire Protection Design Manager

[Sprinklerforum] Re: Exposed BlazeMaster

2024-03-22 Thread Dewayne Martinez
>From the Tyco BlazeMaster handbook [cid:image001.png@01DA7C2B.3D04E5A0] I know this isn't a system riser but the concept is the same. Maybe reach out to BlazeMaster and see what they say. Thank you, Dewayne Martinez Fire Protection Design Manager TOTAL Mechanical Building Integrity W234