RE: Vertical Wet Pipes in Dry Attic

2022-03-02 Thread Scott Futrell via Sprinklerforum
I would not recommend this. It is a sure-fire failure event. The tent has to remain intact for the life of the structure and if it can fail it will. If any part of that tent isn't properly sealed or falls apart you have a failure. Exposed inside. Concealed in the heated space with an insulated

RE: [EXTERNAL] 8 inch sprinkler pipe fall from factory ceiling

2022-02-25 Thread Scott Futrell via Sprinklerforum
Interesting discussion on this forum. Steve is utilizing the scientific method that needs to be used to avoid a Daubert challenge and ensure the proper conclusion, if there is one. Scott   Office: (763) 425-1001 x 2 Cell: (612) 759-5556 -Original Message- From: Sprinklerforum On Behalf

RE: question about Storage height

2022-01-26 Thread Scott Futrell via Sprinklerforum
- From: Sprinklerforum On Behalf Of Scott Futrell via Sprinklerforum Sent: Wednesday, January 26, 2022 9:32 AM To: sprinklerforum@lists.firesprinkler.org Cc: Scott Futrell ; Mike Hairfield Subject: RE: question about Storage height You didn't mention what the liquid is. If it is a hazardous

RE: question about Storage height

2022-01-26 Thread Scott Futrell via Sprinklerforum
You didn't mention what the liquid is. If it is a hazardous material as recognized by the International Fire Code then the 'empty' container is still considered full unless completely cleaned. Scott   Office: (763) 425-1001 x 2 Cell: (612) 759-5556 -Original Message- From:

RE: CPVC Fitting

2021-11-09 Thread Scott Futrell via Sprinklerforum
: Taylor Schumacher Subject: RE: CPVC Fitting Seems silly that a threaded female x threaded female fitting in CPVC would even exist? Taylor Schumacher -Original Message- From: Sprinklerforum On Behalf Of Scott Futrell via Sprinklerforum Sent: Tuesday, November 09, 2021 2:18 PM

RE: Dry System Size

2021-11-01 Thread Scott Futrell via Sprinklerforum
Just ONE of the reasons this forum is so valuable to the fire protection industry. Scott   Office: (763) 425-1001 x 2 Cell: (612) 759-5556 -Original Message- From: Sprinklerforum On Behalf Of Tom Prymak via Sprinklerforum Sent: Monday, November 01, 2021 10:05 AM To:

RE: Attic protection over a storage occupancy

2021-10-06 Thread Scott Futrell via Sprinklerforum
Mike, That is an interesting situation and thought. I would defer to Messer's Hall and Denhardt. For CMDA sprinklers there are requirements in light and ordinary hazard, but I don't see specific reference to combustible roof materials for storage and CMDA. The are limitations for spacing of CMSA

RE: NFPA 13 8.15.7.2 / 8.15.7.5 - Temporary Parking

2021-08-05 Thread Scott Futrell via Sprinklerforum
Appreciate that John. I don't see that information in the original post. Sorry I missed the key information and I wouldn't have been a smart*** if I read it correctly and thoroughly. I write, and am governed by, state law as well as professional engineer rules and ethics and sprinkler

RE: NFPA 13 8.15.7.2 / 8.15.7.5 - Temporary Parking

2021-08-05 Thread Scott Futrell via Sprinklerforum
I can't wait to hear what John and Kevin have to say. It seems that if the sprinkler system understands the vehicle parked under the canopy is only there temporarily then it isn't a problem. However, if the sprinkler system doesn't understand the vehicle is parked temporarily and a fire starts

RE: Dry System Couplings

2021-04-30 Thread Scott Futrell via Sprinklerforum
and repair mechanic when I was doing hands-on work, has been that I can't recall ever seeing a leaky tri-seal fitting in a heated, unheated, or cold storage facility whether part of a dry or a preaction system. On Fri, Apr 30, 2021 at 10:47 AM Scott Futrell via Sprinklerforum < sprinklerfo

RE: Dry System Couplings

2021-04-30 Thread Scott Futrell via Sprinklerforum
I'd sure be interested in hearing more on this subject. "Listing" only partially answers the question. Roll groove v. cut groove makes a difference. If the bottom line is as cheap as possible then you go one route. If the bottom line is an effective fire sprinkler system for the life of the

RE: Activity

2021-02-15 Thread Scott Futrell via Sprinklerforum
There really should be a "Like" button for emails, for this thread on George. Scott   Office: (763) 425-1001 x 2 Cell: (612) 759-5556 -Original Message- From: Sprinklerforum On Behalf Of Richard Mote via Sprinklerforum Sent: Monday, February 15, 2021 11:52 AM To:

RE: Tyco LFP - antifreeze

2021-02-10 Thread Scott Futrell via Sprinklerforum
Good morning. I've looked at the flyer briefly and it certainly is moving in the right direction. With record lows in Minneapolis and many other locations that are colder than -25°F in the northern tier of states I wouldn't do it unless it was a loading dock or somewhere where water damage

RE: schedule 7 pipe?

2021-01-20 Thread Scott Futrell via Sprinklerforum
Considering how much corrosion I've observed and documented in wet and dry systems in schedule 10 in 8-15 years - not MIC - we only specify schedule 40. Scott   Office: (763) 425-1001 x 2 Cell: (612) 759-5556 -Original Message- From: Sprinklerforum On Behalf Of Steve Leyton via

RE: CPVC EQ Bracing - 2 hole straps and another question

2020-12-30 Thread Scott Futrell via Sprinklerforum
Just remember to allow for thermal expansion and contraction. It can get very ugly if the CPVC is restrained and thermal expansion and contraction has not been appropriately allowed for. This applies when a building is warm in the summer during construction and then air conditioning is turned

RE: potential freezing in ESFR system

2020-12-22 Thread Scott Futrell via Sprinklerforum
Great comments. Great information. 1" pipe with cast iron fittings filled with water explodes the side out of the cast iron ell in 52 minutes at 17⁰F and that piece flies 65 feet when not confined. I’ve done these experiments outside in winter. Scott Office: (763) 425-1001 x 2 Cell:

RE: [EXTERNAL] 23.4.4.2.5: What is the purpose and how does it apply?

2020-12-10 Thread Scott Futrell via Sprinklerforum
Many more times than you may have heard about, Craig. For a variety of reasons, there are more fires that exceed the full design area than you are told about. I recently spent four days at a fire scene where part of a sprinklered, light hazard building burned to the ground. That fire exceeded

RE: Event Center Floors

2020-12-01 Thread Scott Futrell via Sprinklerforum
Yes that is more relevant than 404.3 exception 2. Scott   Office: (763) 425-1001 x 2 Cell: (612) 759-5556 -Original Message- From: Sprinklerforum On Behalf Of Travis Mack via Sprinklerforum Sent: Tuesday, December 01, 2020 1:10 PM To: sprinklerforum@lists.firesprinkler.org Cc:

RE: Event Center Floors

2020-12-01 Thread Scott Futrell via Sprinklerforum
Travis, It would help to know what edition of the IBC is adopted in the community to narrow the search. Or do you just want to know in general? Scott   Office: (763) 425-1001 x 2 Cell: (612) 759-5556 -Original Message- From: Sprinklerforum On Behalf Of Travis Mack via Sprinklerforum

RE: Class IIIB Liquids

2020-11-30 Thread Scott Futrell via Sprinklerforum
Don't forget, NFPA 30 and International Fire Code sprinkler/foam system criteria are not in sync. Fire code rules. Also, you have to look to the fire code to know what edition of NFPA 30 is enforceable. Scott   Office: (763) 425-1001 x 2 Cell: (612) 759-5556 -Original Message- From:

RE: Class IIIB Liquids

2020-11-28 Thread Scott Futrell via Sprinklerforum
As I stated in a previous, related thread, you start with the fire code and work from there. IIIB's are easier to work with from a fire protection standpoint, but it may take an engineering solution. Scott Office: (763) 425-1001 x2 Cell: (612) 759-5556 -Original Message- From:

RE: [EXTERNAL] Re: Class IA Flammable Liquids

2020-11-05 Thread Scott Futrell via Sprinklerforum
You first start with the Fire Code adopted in the community. The fire code has requirements for flammable and combustible liquids and also includes fire protection requirements. You have to start there. The IFC varies from NFPA 30 in some sections. There are maximum allowable quantities (MAQ's)

RE: On/Off Switch in the Electric supply to a Dry Pipe System Air Compressor

2020-09-25 Thread Scott Futrell via Sprinklerforum
resprinkler.org/ondemand to learn more. On Thu, Sep 24, 2020 at 10:07 PM Scott Futrell via Sprinklerforum < sprinklerforum@lists.firesprinkler.org> wrote: > 2019: > 8.2.6.6.5.1 > The disconnecting means for an automatic air compressor shall not be a > general-use light switch or

RE: On/Off Switch in the Electric supply to a Dry Pipe System Air Compressor

2020-09-24 Thread Scott Futrell via Sprinklerforum
2019: 8.2.6.6.5.1 The disconnecting means for an automatic air compressor shall not be a general-use light switch or a cord-and-plug connected motor. Scott   Office: (763) 425-1001 x 2 Cell: (612) 759-5556 -Original Message- From: Sprinklerforum On Behalf Of Ron Greenman via

RE: Dust Collection

2020-05-22 Thread Scott Futrell via Sprinklerforum
NFPA 91: Standard for Exhaust Systems for Air Conveying of Vapors, Gases, Mists, and Particulate Solids NFPA 654: Standard for the Prevention of Fire and Dust Explosions from the Manufacturing, Processing, and Handling of Combustible Particulate Solids Does that help? Scott Office: (763)

RE: ICC 905.4.2 Handbook Figure

2019-10-01 Thread Scott Futrell via Sprinklerforum
What edition? Scott Office: (763) 425-1001 x 2 Cell: (612) 759-5556 From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of Steve Leyton via Sprinklerforum Sent: Tuesday, October 01, 2019 12:52 PM To: sprinklerforum@lists.firesprinkler.org Cc: Steve Leyton

RE: N1.85 graph paper

2019-08-28 Thread Scott Futrell via Sprinklerforum
Thank you. Not what I need for PowerPoint slides, but thanks! Scott Office: (763) 425-1001 x 2 Cell: (612) 759-5556 From: Travis Allen- Allen Engineering [mailto:tra...@allenfpe.com] Sent: Wednesday, August 28, 2019 4:33 PM To: sprinklerforum@lists.firesprinkler.org Cc: Scott Futrell Subject:

RE: N1.85 graph paper

2019-08-27 Thread Scott Futrell via Sprinklerforum
cns.doe.gov>>; Scott Futrell mailto:sco...@ffcdi.com>> Subject: RE: N1.85 graph paper Me too please Thank you, J. Scott Mitchell, PE Senior Fire Protection Engineer Mission Engineering CNS PTX / Y-12 | 865-576-5258 From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.fire

N1.85 graph paper

2019-08-27 Thread Scott Futrell via Sprinklerforum
Does anyone have an electronic metric/imperial N1.85 graph that they would be willing to share with me offline? I need it for hydraulics seminars and all I have are jpegs with one or the other. Thanks in advance. Scott Futrell Office: (763) 425-1001 x 2 Cell: (612) 759-5556

RE: Attic/Concealed space access to sprinkler heads

2019-08-18 Thread Scott Futrell via Sprinklerforum
See below. Scott Office: (763) 425-1001 x 2 Cell: (612) 759-5556 From: David Williams Sent: Thursday, August 15, 2019 2:39 PM To: Scott Futrell ; sprinklerforum@lists.firesprinkler.org Subject: RE: Attic/Concealed space access to sprinkler heads Language camp facility. Rural area. Installing

RE: Attic/Concealed space access to sprinkler heads

2019-08-15 Thread Scott Futrell via Sprinklerforum
David, Interesting question. You haven't provided enough information for a thorough answer. How big of an attic area? So you intend to mark the location of every upright sprinkler in the concealed space on the ceiling below? No one will ever paint that gypsum? Then cut access for NFPA 25