RE: Mixed use Bldg. Question

2010-06-01 Thread Thom McMahon
that this is a committee intent, that the 3000 Sf be required when CC spaces, no matter what design type was used. Major change from previous editions. Roland some help here Please! Thom McMahon, SET Firetech, Inc. 2560 Copper Ridge Dr P.O. Box 882136 Steamboat Springs, CO 80488 Tel: 970-879-7952 Fax: 970-879-7926

RE: seismic seminar

2010-06-01 Thread Thom McMahon
Yes! The AFSA convention has had Seismic Seminars for the past 6 years. RI is close enough to you that not attending is a real loss. SIGN UP NOW!!! Thom McMahon, SET Firetech, Inc. 2560 Copper Ridge Dr P.O. Box 882136 Steamboat Springs, CO 80488 Tel: 970-879-7952 Fax: 970-879-7926

RE: Mist Systems Considered Option for Inside Homes

2010-05-29 Thread Thom McMahon
is volunteering their community to be a Guinea Pig for this mist system, I don't see its application as a option in 13D or R very soon. Of course you could always do it a Equivalent engineered design. Thom McMahon, SET Firetech, Inc. 2560 Copper Ridge Dr P.O. Box 882136 Steamboat Springs, CO 80488

RE: Beam obstructions

2010-05-27 Thread Thom McMahon
. Hence the 3000 SF design area when you have concealed comb spaces. Could a fire burn at the bottom of these boxes? Yes. Does that present a serious threat to the ability of the system to contain it to the crawl space? I don't think so. Thom McMahon, SET Firetech, Inc. 2560 Copper Ridge Dr P.O. Box

RE: Size considerations

2010-05-26 Thread Thom McMahon
of Rolland's favorite phrases, which to me means Call in the FPE's! (Like they are some kind of Light Brigade Onward Rode the 300 or some such.) Thom McMahon, SET Firetech, Inc. 2560 Copper Ridge Dr P.O. Box 882136 Steamboat Springs, CO 80488 Tel: 970-879-7952 Fax: 970-879-7926

RE: Size considerations

2010-05-26 Thread Thom McMahon
? Colorado Div. of Fire Prevention requires the Contractor to verify the registration of the Inspector? I thought that would be the div. job, but even when I was on the advisory board I couldn't win that one. I know Life isn't always fair. Live with it. Thom McMahon, SET Firetech, Inc. 2560 Copper Ridge

RE: Size considerations

2010-05-26 Thread Thom McMahon
Thom McMahon, SET Firetech, Inc. 2560 Copper Ridge Dr P.O. Box 882136 Steamboat Springs, CO 80488 Tel: 970-879-7952 Fax: 970-879-7926 -Original Message- From: sprinklerforum-boun...@firesprinkler.org [mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Chris Cahill In MN

RE: Occupancy vs Hazard

2010-05-26 Thread Thom McMahon
If they are an FM customer, you might just ask FM for what's appropriate. Thom McMahon, SET Firetech, Inc. 2560 Copper Ridge Dr P.O. Box 882136 Steamboat Springs, CO 80488 Tel: 970-879-7952 Fax: 970-879-7926 ___ Sprinklerforum mailing list

RE: Occupancy vs Hazard

2010-05-26 Thread Thom McMahon
wouldn't do any good. Just send flowers to the widow. Thom McMahon, SET Firetech, Inc. 2560 Copper Ridge Dr P.O. Box 882136 Steamboat Springs, CO 80488 Tel: 970-879-7952 Fax: 970-879-7926 Fletcher, Ron Sent: Wednesday, May 26, 2010 5:30 PM To: sprinklerforum@firesprinkler.org Subject: RE

RE: Size considerations

2010-05-25 Thread Thom McMahon
or money to up-date anything. Like I said, it's expensive to write or re-write a spec. See my new book out in paperback soon. These Spec's Suck! Thom McMahon, SET Firetech, Inc. 2560 Copper Ridge Dr P.O. Box 882136 Steamboat Springs, CO 80488 Tel: 970-879-7952 Fax: 970-879-7926

RE: Salary/Project cost

2010-05-24 Thread Thom McMahon
we do are not like the average jobs in Means. Thom McMahon, SET Firetech, Inc. 2560 Copper Ridge Dr P.O. Box 882136 Steamboat Springs, CO 80488 Tel: 970-879-7952 Fax: 970-879-7926 ___ Sprinklerforum mailing list Sprinklerforum@firesprinkler.org http

RE: Salary/Bim

2010-05-24 Thread Thom McMahon
Thom McMahon, SET Firetech, Inc. 2560 Copper Ridge Dr P.O. Box 882136 Steamboat Springs, CO 80488 Tel: 970-879-7952 Fax: 970-879-7926 While many projects now Require BIM, our industry is slow off the mark in reguards to supplying us with BIM Blocks. That is if you click on the alarm valve

RE: Elevator Equipment Rooms

2010-05-24 Thread Thom McMahon
Change order is going to be a tough sell, since NFPA 13, 2007 8-15.5 references ASME A17.1 so often, that it could be easy to say, you should have known what it requires. Thom McMahon, SET Firetech, Inc. 2560 Copper Ridge Dr P.O. Box 882136 Steamboat Springs, CO 80488 Tel: 970-879-7952 Fax: 970

RE: Elevator Equipment Rooms

2010-05-24 Thread Thom McMahon
Yes one could! And you might prevail, at least for a while just like the argument that the Earth is Flat. With limited information it sure seemed so for a while, but my what a beautiful blue round planet we live on. Thom McMahon, SET Firetech, Inc. 2560 Copper Ridge Dr P.O. Box 882136 Steamboat

RE: Elevator Equipment Rooms

2010-05-24 Thread Thom McMahon
I just go with what I'm good at! Sorry if you couldn't enjoy the humor. Thom McMahon, SET Firetech, Inc. 2560 Copper Ridge Dr P.O. Box 882136 Steamboat Springs, CO 80488 Tel: 970-879-7952 Fax: 970-879-7926 -Original Message- From: sprinklerforum-boun...@firesprinkler.org

RE: Salary

2010-05-22 Thread Thom McMahon
I think the AutoCAD co-ordination they are speaking of is the BIM required design on many major projects. (AutoCAD 3D) Co-ordinated drawings is the only way anything works. Thom McMahon, SET Firetech, Inc. 2560 Copper Ridge Dr P.O. Box 882136 Steamboat Springs, CO 80488 Tel: 970-879-7952 Fax

RE: Galv fittings?

2010-05-21 Thread Thom McMahon
. Applied after fab. Thom McMahon, SET Firetech, Inc. 2560 Copper Ridge Dr P.O. Box 882136 Steamboat Springs, CO 80488 Tel: 970-879-7952 Fax: 970-879-7926 -Original Message- From: sprinklerforum-boun...@firesprinkler.org [mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of George

RE: Pipe and fitting cost data

2010-05-21 Thread Thom McMahon
Funny! I live in a town of 8 to 18 thousand depending on if you count beds or bodies and what time of year, and our library has the 2010 issue, I'm sorry S.C. is so out of touch. Thom McMahon, SET Firetech, Inc. 2560 Copper Ridge Dr P.O. Box 882136 Steamboat Springs, CO 80488 Tel: 970-879-7952

RE: Something new

2010-05-21 Thread Thom McMahon
Besides, W.C. is Cheap, cheap, cheap! For Office workers. (Designers) Thom McMahon, SET Firetech, Inc. 2560 Copper Ridge Dr P.O. Box 882136 Steamboat Springs, CO 80488 Tel: 970-879-7952 Fax: 970-879-7926 -Original Message- From: sprinklerforum-boun...@firesprinkler.org

RE: Galv fittings?

2010-05-21 Thread Thom McMahon
I was thinking of cut to length pieces and holes for MT's. So how big a wrench did it take to get the plugs out? Thom McMahon, SET Firetech, Inc. 2560 Copper Ridge Dr P.O. Box 882136 Steamboat Springs, CO 80488 Tel: 970-879-7952 Fax: 970-879-7926 -Original Message- From

RE: Something new

2010-05-21 Thread Thom McMahon
We're allowed 15% of time out of office. Thom McMahon, SET Firetech, Inc. 2560 Copper Ridge Dr P.O. Box 882136 Steamboat Springs, CO 80488 Tel: 970-879-7952 Fax: 970-879-7926 -Original Message- From: sprinklerforum-boun...@firesprinkler.org [mailto:sprinklerforum-boun

RE: Ceiling Tiles or Lack thereof...

2010-05-20 Thread Thom McMahon
of existing 13 is enforced. How far exactly, behind, should we get before you'd be satisfied? Thom McMahon, SET Firetech, Inc. 2560 Copper Ridge Dr P.O. Box 882136 Steamboat Springs, CO 80488 Tel: 970-879-7952 Fax: 970-879-7926 Subject: Re: Ceiling Tiles or Lack thereof... It doesn't need carried over

RE: Ceiling Tiles or Lack thereof...

2010-05-20 Thread Thom McMahon
Insurance Vulnerability is a Complete OpeN Disclosure of Un-specified Matters. Practice Strategic Exclusion eXposure! Thom McMahon, SET Firetech, Inc. 2560 Copper Ridge Dr P.O. Box 882136 Steamboat Springs, CO 80488 Tel: 970-879-7952 Fax: 970-879-7926 -Original Message- From: sprinklerforum

RE: Ceiling Tiles or Lack thereof...

2010-05-20 Thread Thom McMahon
You can write and mail anything you want too. Just having that piece of paper in the file could save you and your insurance co. everything, including your kids college fund. Thom McMahon, SET Firetech, Inc. 2560 Copper Ridge Dr P.O. Box 882136 Steamboat Springs, CO 80488 Tel: 970-879-7952 Fax

RE: Ceiling Tiles or Lack thereof...

2010-05-20 Thread Thom McMahon
Read Roland's article in Sprinkler age NFPA 25 Upcoming 2011 Edition, especially the part about Hazard Evaluation. Thom McMahon, SET Firetech, Inc. 2560 Copper Ridge Dr P.O. Box 882136 Steamboat Springs, CO 80488 Tel: 970-879-7952 Fax: 970-879-7926 -Original Message- From

RE: 13R sprinklers

2010-05-19 Thread Thom McMahon
(and Spec. if that applies). Now you're ready when he forwards your C.O. to the Arch. With a recommendation to Deny it. Thom McMahon, SET Firetech, Inc. 2560 Copper Ridge Dr P.O. Box 882136 Steamboat Springs, CO 80488 Tel: 970-879-7952 Fax: 970-879-7926

RE: Stairways

2010-05-18 Thread Thom McMahon
You'll still need to remember to protect any penetrations with fire stopping details equal to the rating of the stairwell shaft rating. Thom McMahon, SET Firetech, Inc. 2560 Copper Ridge Dr P.O. Box 882136 Steamboat Springs, CO 80488 Tel: 970-879-7952 Fax: 970-879-7926 -Original Message

RE: 1500 sqft vs 900 sqft

2010-05-13 Thread Thom McMahon
for QR. The increased area for Dry, concealed combustible construction or slope ceilings are requirements. Thom McMahon, SET Firetech, Inc. 2560 Copper Ridge Dr P.O. Box 882136 Steamboat Springs, CO 80488 Tel: 970-879-7952 Fax: 970-879-7926 -Original Message- From: sprinklerforum-boun

RE: Warehouse Commodity

2010-05-13 Thread Thom McMahon
5% certainly, but most likely more than 15% too. My CYA? Group A Plastics. Thom McMahon, SET Firetech, Inc. 2560 Copper Ridge Dr P.O. Box 882136 Steamboat Springs, CO 80488 Tel: 970-879-7952 Fax: 970-879-7926 -Original Message- From: sprinklerforum-boun...@firesprinkler.org

RE: 13R vs. 13D (Attics)

2010-05-13 Thread Thom McMahon
with the attic system. Thom McMahon, SET Firetech, Inc. 2560 Copper Ridge Dr P.O. Box 882136 Steamboat Springs, CO 80488 Tel: 970-879-7952 Fax: 970-879-7926 -Original Message- From: sprinklerforum-boun...@firesprinkler.org [mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Brian Harris

RE: water heaters above ceiling

2010-05-12 Thread Thom McMahon
-combustible platform for the WH, there are some really simple metal drain pans with outlets that support the WH as well. http://www.aamag.com/heaterpan.htm Thom McMahon, SET Firetech, Inc. 2560 Copper Ridge Dr P.O. Box 882136 Steamboat Springs, CO 80488 Tel: 970-879-7952 Fax: 970-879-7926 -Original

RE: Pipe Size

2010-05-12 Thread Thom McMahon
Actually K8.0 could be a very good choice for LH if you use 14x14 spacing. Thom McMahon, SET Firetech, Inc. 2560 Copper Ridge Dr P.O. Box 882136 Steamboat Springs, CO 80488 Tel: 970-879-7952 Fax: 970-879-7926 -Original Message- From: sprinklerforum-boun...@firesprinkler.org

RE: Are Seismic Braces considered hangers?

2010-05-11 Thread Thom McMahon
Please take the time to locate it for yourself. Memories are full of non-factoid's and strange abstractions. When next you have a senior moment, please don't share it with us. Fact finding services are also available in the yellow pages. Thom McMahon, SET Firetech, Inc. 2560 Copper Ridge Dr P.O

RE: Are Seismic Braces considered hangers?

2010-05-11 Thread Thom McMahon
if you're working. Thom McMahon, SET Firetech, Inc. 2560 Copper Ridge Dr P.O. Box 882136 Steamboat Springs, CO 80488 Tel: 970-879-7952 Fax: 970-879-7926 -Original Message- From: Brad [mailto:bcasterl...@fsc-inc.com] I was not asking anything of you-- this is your 2nd attack

RE: 13R Question

2010-05-11 Thread Thom McMahon
If your under NFPA 101, you need the # of occupants, and their ability to evacuate under their own power. I think it's like 33.2.3.5.2.1 or .2 and some allow 13D or R, generally read chapter 33. Thom McMahon, SET Firetech, Inc. 2560 Copper Ridge Dr P.O. Box 882136 Steamboat Springs, CO 80488 Tel

RE: DCVA test connetion

2010-05-10 Thread Thom McMahon
and testing. Thom McMahon, SET Firetech, Inc. 2560 Copper Ridge Dr P.O. Box 882136 Steamboat Springs, CO 80488 Tel: 970-879-7952 Fax: 970-879-7926 -Original Message- From: sprinklerforum-boun...@firesprinkler.org [mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Chris Cahill Sent

RE: DCVA test connetion

2010-05-10 Thread Thom McMahon
I forgot to add that on exposed risers we have also used Roof Fire Dept. Connections that work well too. Potter-Roemer 5871 - 5892 series. Thom McMahon, SET Firetech, Inc. 2560 Copper Ridge Dr P.O. Box 882136 Steamboat Springs, CO 80488 Tel: 970-879-7952 Fax: 970-879-7926 -Original

RE: Pre-action in same space as wet pipe system

2010-05-07 Thread Thom McMahon
Has anyone considered just putting the wall back between these systems. I know that something that simple will leave out all the various engineering, and pondering of possible and probable's. No fire modeling, advanced detection systems or inflated fees, but hey I'm just a simple guy. Thom

RE: FDC on Limited Area Sprinklers

2010-05-07 Thread Thom McMahon
Use EC heads and you'll still be under the 20 by a long way. Thom McMahon, SET Firetech, Inc. 2560 Copper Ridge Dr P.O. Box 882136 Steamboat Springs, CO 80488 Tel: 970-879-7952 Fax: 970-879-7926 -Original Message- From: sprinklerforum-boun...@firesprinkler.org [mailto:sprinklerforum

RE: Pre-action in same space as wet pipe system

2010-05-06 Thread Thom McMahon
What do you do in that 800,000 Sf warehouse? It's one room but may have twenty systems. Thom McMahon, SET Firetech, Inc. 2560 Copper Ridge Dr P.O. Box 882136 Steamboat Springs, CO 80488 Tel: 970-879-7952 Fax: 970-879-7926 IMHO never a good idea to have two different systems of any type

RE: Sprinkler Save. Water Damage.

2010-05-05 Thread Thom McMahon
Oh you say that now! Just wait until the EPA requires Containment Booms around the fire property before you can apply the water to a blaze. All that run off is Pollution Thom McMahon, SET Firetech, Inc. 2560 Copper Ridge Dr P.O. Box 882136 Steamboat Springs, CO 80488 Tel: 970-879-7952 Fax: 970

RE: boat storage

2010-05-04 Thread Thom McMahon
direct you to do for a layout. Otherwise just head to the bar, and stay there until you forget all about this project. No need to run, but you should call a taxi, as we cannot endorse unsafe behavior. Thom McMahon, SET Firetech, Inc. 2560 Copper Ridge Dr P.O. Box 882136 Steamboat Springs, CO 80488

RE: Fire Pump

2010-05-04 Thread Thom McMahon
system leak, generally from the Hi-pressure side to the low pressure side. That seems to be thru your check valve. Thom McMahon, SET Firetech, Inc. 2560 Copper Ridge Dr P.O. Box 882136 Steamboat Springs, CO 80488 Tel: 970-879-7952 Fax: 970-879-7926 -Original Message- From

RE: boat storage

2010-05-04 Thread Thom McMahon
on it. I'd love to know what you all would end up doing. Now there would be some fodder for the forum. Thom McMahon, SET Firetech, Inc. 2560 Copper Ridge Dr P.O. Box 882136 Steamboat Springs, CO 80488 Tel: 970-879-7952 Fax: 970-879-7926 ___ Sprinklerforum

RE: boat storage

2010-05-04 Thread Thom McMahon
While I may not have been fastest on the track, due as we have discussed, to the lack of weight based handicapping. You'll never forget the ride to the track! Anyone for RI boat racing? George is right, you'll never know what you've missed, if you don't attend. Thom McMahon, SET Firetech, Inc

RE: Fire Pump

2010-05-04 Thread Thom McMahon
ARrrrgg! It's a pirate thing. Thom McMahon, SET Firetech, Inc. 2560 Copper Ridge Dr P.O. Box 882136 Steamboat Springs, CO 80488 Tel: 970-879-7952 Fax: 970-879-7926 ___ Sprinklerforum mailing list Sprinklerforum@firesprinkler.org http

RE: Fire Pump

2010-05-03 Thread Thom McMahon
Sam B (1psi = .0689 Bar) conversely 1 Bar + 14.5 psi so if he's losing 2 Bar to start pump, he's lost 29 Psi. Thom McMahon, SET Firetech, Inc. 2560 Copper Ridge Dr P.O. Box 882136 Steamboat Springs, CO 80488 Tel: 970-879-7952 Fax: 970-879-7926 -Original Message- From: sprinklerforum

RE: NFPA #13 changes/additions

2010-04-29 Thread Thom McMahon
. A shame as they could be a guiding light for the industry and engineering in general if they didn't prostitute their ethic's in the name of profits. We've seen far too much of that lately, and are all suffering because of it, and now our children will be paying for it, for years to come. Thom

RE: Research Question - Group A Plastic Protection

2010-04-28 Thread Thom McMahon
they will store above that, so then your 8'-0 storage is actually 10 or 11'-0 and your required design goes to .45/2500 All of this is based upon the Fire Protection Research Foundation study of Evaluation of sprinkler performance in protecting Gondola type shelf storage Thom McMahon, SET Firetech

RE: Water stats

2010-04-16 Thread Thom McMahon
This info was also in the 1986 Scottsdale report. Thom McMahon, SET Firetech, Inc. 2560 Copper Ridge Dr P.O. Box 882136 Steamboat Springs, CO 80488 Tel: 970-879-7952 Fax: 970-879-7926 -Original Message- From: sprinklerforum-boun...@firesprinkler.org [mailto:sprinklerforum-boun

RE: Pipe Wrapping

2010-04-16 Thread Thom McMahon
Actually per 13, we care if it goes below 40'F. Thom McMahon, SET Firetech, Inc. 2560 Copper Ridge Dr P.O. Box 882136 Steamboat Springs, CO 80488 Tel: 970-879-7952 Fax: 970-879-7926 Chris Cahill Subject: RE: Pipe Wrapping It won't get to 20 but we really don't care because it will fall

RE: Wood Pellet Production Facility

2010-04-16 Thread Thom McMahon
Matt if you contact Dwon Lewis at Extreme Fire Protection in Denver. I now he did one of these about 2 years ago, and yes they have issues! Daily fires in the dryers ect. Small pre-action system in the area of daily fires to re-set on short turn around. Thom McMahon, SET Firetech, Inc. 2560

RE: Pipe Wrapping

2010-04-15 Thread Thom McMahon
Not Mark Twain, but just as true: The three main causes of fires are Men, Women and Children. Bob Caputo We hold these truths to be self evident- Thom McMahon, SET Firetech, Inc. 2560 Copper Ridge Dr P.O. Box 882136 Steamboat Springs

RE: NFPA

2010-04-15 Thread Thom McMahon
Tell Matt he still Owes Thom at Firetech an E-mail reply to the fire pump supply issue 4.27 NFPA 20 2010. Thom McMahon, SET Firetech, Inc. 2560 Copper Ridge Dr P.O. Box 882136 Steamboat Springs, CO 80488 Tel: 970-879-7952 Fax: 970-879-7926 -Original Message- From: sprinklerforum-boun

RE: Foam

2010-04-15 Thread Thom McMahon
David be aware that many contractors will charge LIST price or higher for the products we supply. Just because we can buy it for 1/3 or 1/2 of list doesn't mean we can sell it for that to a customer. At least not if we want to stay in business. Thom McMahon, SET Firetech, Inc. 2560 Copper Ridge

RE: Foam

2010-04-15 Thread Thom McMahon
...@firesprinkler.org [mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Thom McMahon Sent: Thursday, April 15, 2010 11:26 AM To: sprinklerforum@firesprinkler.org Subject: RE: Foam David be aware that many contractors will charge LIST price or higher for the products we supply. Just because we can buy

RE: Wells as a water source

2010-04-14 Thread Thom McMahon
, and lower density in reactor areas, because they go BOOM before they burn. Thom McMahon, SET Firetech, Inc. 2560 Copper Ridge Dr P.O. Box 882136 Steamboat Springs, CO 80488 Tel: 970-879-7952 Fax: 970-879-7926 -Original Message- From: sprinklerforum-boun...@firesprinkler.org

RE: Wells as a water source

2010-04-14 Thread Thom McMahon
a min. storage requirement, that looks at supplying the Fire Dept. requirements. Thom McMahon, SET Firetech, Inc. 2560 Copper Ridge Dr P.O. Box 882136 Steamboat Springs, CO 80488 Tel: 970-879-7952 Fax: 970-879-7926 -Original Message- From: sprinklerforum-boun...@firesprinkler.org

RE: Wells as a water source

2010-04-14 Thread Thom McMahon
The Age old Show me where it says I can't? Thom McMahon, SET Firetech, Inc. 2560 Copper Ridge Dr P.O. Box 882136 Steamboat Springs, CO 80488 Tel: 970-879-7952 Fax: 970-879-7926 Subject: RE: Wells as a water source Since 23.2.5 lists other natural water resources and no specific exclusion

RE: Steam for Fire Suppression

2010-04-12 Thread Thom McMahon
in Court. One of the great beauties of using water is its ability to convert/absorb so many btu's when it changes to steam. If your using steam there is no ability to absorb BTU's, only to displace the Ox. (There's probably a good reason that you don't see Steam duct suppression systems any more.) Thom

RE: Unfinished basements in 4-family NFPA 13R occupancy

2010-04-09 Thread Thom McMahon
Not only that, but if you install a ceiling lid, enclose any HVAC or mech. equip. in its own 130SF room, you'll have one head @ OH, and by calling the room Rec. Room it becomes part of the living unit. (Worst case 4 rooms, labeled personal office or Time Out room. Thom McMahon, SET Firetech, Inc

RE: OHIII

2010-04-09 Thread Thom McMahon
If Scott gets his way Fire Protection will be part of an HVAC system for reducing the Oxygen level. There won't be any sprinklers! Thom McMahon, SET Firetech, Inc. 2560 Copper Ridge Dr P.O. Box 882136 Steamboat Springs, CO 80488 Tel: 970-879-7952 Fax: 970-879-7926 -Original Message

RE: Water Supply

2010-04-08 Thread Thom McMahon
at 500Gpm, that still more than the 450Gpm the sprinkler system will require for 3000 SF. (If you overflow the sprinklers by more than 10% they may become the more demanding.) Thom McMahon, SET Firetech, Inc. 2560 Copper Ridge Dr P.O. Box 882136 Steamboat Springs, CO 80488 Tel: 970-879-7952 Fax: 970

RE: FM Small Room Rule?

2010-04-08 Thread Thom McMahon
Tyco RSV-1 (1) size, they used to make a 2 and you may still find one on somebody's storage shelf. Be careful the lit says for use in 13D systems. You may need to look at a solenoid valve on the domestic operated from the flow sw. Thom McMahon, SET Firetech, Inc. 2560 Copper Ridge Dr P.O. Box

RE: OSHA and WORKING ON FIRE PUMP

2010-04-07 Thread Thom McMahon
have the right clothes on. Kind of like Best Practices even if it's not required, it may still be the best thing to do. Thom McMahon, SET Firetech, Inc. 2560 Copper Ridge Dr P.O. Box 882136 Steamboat Springs, CO 80488 Tel: 970-879-7952 Fax: 970-879-7926

RE: Underground flushing velocities

2010-04-05 Thread Thom McMahon
they are not, often they don't know anything about 24 and guess who the owner blames. Thom McMahon, SET Firetech, Inc. 2560 Copper Ridge Dr P.O. Box 882136 Steamboat Springs, CO 80488 Tel: 970-879-7952 Fax: 970-879-7926 George Church Subject: RE: Underground flushing velocities We put it on a U

RE: WINDOW SPRINKLERS

2010-04-02 Thread Thom McMahon
Who else has a listing? Thom McMahon, SET Firetech, Inc. 2560 Copper Ridge Dr P.O. Box 882136 Steamboat Springs, CO 80488 Tel: 970-879-7952 Fax: 970-879-7926 Subject: RE: WINDOW SPRINKLERS You know there are window sprinklers other than Tyco's. Greg McGahan

RE: Connecting to Public Water Supply

2010-04-02 Thread Thom McMahon
protection. Thom McMahon, SET Firetech, Inc. 2560 Copper Ridge Dr P.O. Box 882136 Steamboat Springs, CO 80488 Tel: 970-879-7952 Fax: 970-879-7926 -Original Message- From: sprinklerforum-boun...@firesprinkler.org [mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of G. Tim Stone Sent

RE: WINDOW SPRINKLERS

2010-04-02 Thread Thom McMahon
The NRC Canada's IRC has an interesting article on the use of SSP QR heads to protect tempered glass windows, but I don't believe ICC has adopted any of these yet. http://www.nrc-cnrc.gc.ca/eng/ibp/irc/ctus/ctus-n12.html Thom McMahon, SET Firetech, Inc. 2560 Copper Ridge Dr P.O. Box 882136

RE: Underground flushing velocities

2010-04-02 Thread Thom McMahon
flow for the first 200 gallons may exceed 10 FPS, but then the average would drop off as pressure built.(Keep in mind that 200 Gallons is less than the volume of 150 LF of 6 pipe) Thom McMahon, SET Firetech, Inc. 2560 Copper Ridge Dr P.O. Box 882136 Steamboat Springs, CO 80488 Tel: 970-879-7952 Fax

RE: WINDOW SPRINKLERS

2010-04-01 Thread Thom McMahon
See TYCO data Sheet TFP 620. Thom McMahon, SET Firetech, Inc. 2560 Copper Ridge Dr P.O. Box 882136 Steamboat Springs, CO 80488 Tel: 970-879-7952 Fax: 970-879-7926 -Original Message- From: sprinklerforum-boun...@firesprinkler.org [mailto:sprinklerforum-boun...@firesprinkler.org

RE: Underground flushing velocities

2010-03-31 Thread Thom McMahon
by improving the protection we give that small part we call our customers. Thom McMahon, SET Firetech, Inc. 2560 Copper Ridge Dr P.O. Box 882136 Steamboat Springs, CO 80488 Tel: 970-879-7952 Fax: 970-879-7926 Subject: Re: Underground flushing velocities Scott, From Wikipedia. Pigging can just

RE: Underground flushing velocities

2010-03-31 Thread Thom McMahon
Yeah! It's the lizard that blows out of the open end of the pipe when you open the the supply valve! And Craig they do have a rule and it has three different ways to be applied, that's all. There's no minimum for (3) because you've used the maximum available. Thom McMahon, SET Firetech, Inc

RE: Underground flushing velocities

2010-03-31 Thread Thom McMahon
. No gauges! No Pito! No Calculation's! Anybody can do it! Thom McMahon, SET Firetech, Inc. 2560 Copper Ridge Dr P.O. Box 882136 Steamboat Springs, CO 80488 Tel: 970-879-7952 Fax: 970-879-7926 ___ Sprinklerforum mailing list Sprinklerforum

RE: Underground flushing velocities

2010-03-30 Thread Thom McMahon
conditions. It will create the maximum velocity in the underground pipe that that pipe will ever see, unless it breaks while it's still 6 or the system is altered and the riser increased in size. Thom McMahon, SET Firetech, Inc. 2560 Copper Ridge Dr P.O. Box 882136 Steamboat Springs, CO 80488 Tel

RE: 2'x4' Light Obstruction

2010-03-29 Thread Thom McMahon
the protected hazard shall comply with 8.5.5.3. 8.5.5.3.1 Sprinklers shall be installed under fixed obstructions over 4 ft (1.2 m) wide such as ducts, decks, open grate flooring, cutting tables, and overhead doors. Thom McMahon, SET Firetech, Inc. 2560 Copper Ridge Dr P.O. Box 882136 Steamboat Springs, CO

RE: 1/2 inch nipple in sprinkler outlet

2010-03-27 Thread Thom McMahon
The use of pipe nipples less than 1 in. (25 mm) in diameter is not permitted in areas subject to earthquakes. If I remove all bushings (If there are any.) and the outlet is less than 1 then I can use the outlet, 1/2 or 3/4 as is with up to a 4 nipple of the outlet size, if the cal. Proves out. Thom

RE: 13D Question

2010-03-26 Thread Thom McMahon
occupancies as required in Sections 907.2.9.1 and 907.9.2 907.2.9.1 Manual Fire Alarm System Thom McMahon, SET Firetech, Inc. 2560 Copper Ridge Dr P.O. Box 882136 Steamboat Springs, CO 80488 Tel: 970-879-7952 Fax: 970-879-7926 -Original Message- From: sprinklerforum-boun...@firesprinkler.org

RE: Grooved Underground, Thrust Blocks Required?

2010-03-26 Thread Thom McMahon
unless you are connecting to a pipe, fitting or joint type that can come apart under increased pressure, lack of compaction or some type of movement, you don't need thrust blocks. Thom McMahon, SET Firetech, Inc. 2560 Copper Ridge Dr P.O. Box 882136 Steamboat Springs, CO 80488 Tel: 970-879-7952 Fax

RE: Grooved Underground, Thrust Blocks Required?

2010-03-26 Thread Thom McMahon
restraint. Grooved joints is another, Roding between fittings is another, and mega lugs are yet another. Are there other means and methods? Sure! And an engineer can create even more. Thom McMahon, SET Firetech, Inc. 2560 Copper Ridge Dr P.O. Box 882136 Steamboat Springs, CO 80488 Tel: 970-879-7952

RE: 13D Question

2010-03-26 Thread Thom McMahon
Does the Name Jethro Gibbs ring any bells for ya? Thom McMahon, SET I guarantee my hobby wood shop in the basement is far more of a problem than a psychologist office. Can you say flammable liquids, dust and piles of cutoffs? No one would question 13D in my house. It's hazard and intent

RE: crumble zone

2010-03-25 Thread Thom McMahon
even fire that took out the windows, just some swirly winds. Thom McMahon, SET Firetech, Inc. 2560 Copper Ridge Dr P.O. Box 882136 Steamboat Springs, CO 80488 Tel: 970-879-7952 Fax: 970-879-7926 -Original Message- From: sprinklerforum-boun...@firesprinkler.org [mailto:sprinklerforum

RE: Grooved Underground, Thrust Blocks Required?

2010-03-25 Thread Thom McMahon
Good luck with that! It's like trying to find a listing for ductile Iron Pipe above ground for fire protection. The most often listed reason not to use PVC (C900) above ground is it's not listed. Well try and find a DIP that's listed for Fire Above ground. Thom McMahon, SET Firetech, Inc. 2560

RE: Victaulic OK'ed for underground service

2010-03-25 Thread Thom McMahon
in Iron Pipe Sizes doesn't mean that 24 thinks of them in IPS and not AWWA Ductile Iron Pipe sizes. A groove fitting is a Groove fitting until it's not quite all grooved fittings. Thom McMahon, SET Firetech, Inc. 2560 Copper Ridge Dr P.O. Box 882136 Steamboat Springs, CO 80488 Tel: 970-879-7952 Fax

RE: FM-200 System

2010-03-24 Thread Thom McMahon
those exceptions and reductions, you will almost always be forced to provide both sprinkler and FM200 in those areas. Thom McMahon, SET Firetech, Inc. 2560 Copper Ridge Dr P.O. Box 882136 Steamboat Springs, CO 80488 Tel: 970-879-7952 Fax: 970-879-7926 2006 IBC/IFC [F] 904.2 Where required

RE: Groove depth

2010-03-24 Thread Thom McMahon
countries. Thom McMahon, SET Firetech, Inc. 2560 Copper Ridge Dr P.O. Box 882136 Steamboat Springs, CO 80488 Tel: 970-879-7952 Fax: 970-879-7926 -Original Message- From: sprinklerforum-boun...@firesprinkler.org [mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Chris Cahill

RE: Groove depth

2010-03-24 Thread Thom McMahon
be dimensionally compatible with the fittings. I've been interested in the Groove standards ever since I started to fabricate a patentable device which included a groove. How to protect it so the simply by changing the groove dimension or tolerance, someone else's device couldn't be called unique. Thom

RE: Room Design vs. Adjacent Hazards

2010-03-22 Thread Thom McMahon
Rich: How does your 600 Sf OH space not meet the requirements of 11.1.2(2)? And still qualify for room design? Thom McMahon, SET Firetech, Inc. 2560 Copper Ridge Dr P.O. Box 882136 Steamboat Springs, CO 80488 Tel: 970-879-7952 Fax: 970-879-7926 -Original Message- From: sprinklerforum

RE: Room Design vs. Adjacent Hazards

2010-03-22 Thread Thom McMahon
the sprinklers in the adj. area, then what we expect to happen is for the fire to be contained to the room of origin if that room is properly protected. Thom McMahon, SET Firetech, Inc. 2560 Copper Ridge Dr P.O. Box 882136 Steamboat Springs, CO 80488 Tel: 970-879-7952 Fax: 970-879-7926

RE: Room Design vs. Adjacent Hazards

2010-03-22 Thread Thom McMahon
will be available. Not to replace the appropriate use of room design but to give the 'Designer'/Layout Tech. alternatives. Thom McMahon, SET Firetech, Inc. 2560 Copper Ridge Dr P.O. Box 882136 Steamboat Springs, CO 80488 Tel: 970-879-7952 Fax: 970-879-7926 -Original Message- From: sprinklerforum-boun

RE: dry system air leak

2010-03-19 Thread Thom McMahon
as some form of leak detector without the fluorocarbons. http://www.labino.com/appl-leak.html Thom McMahon, SET Firetech, Inc. 2560 Copper Ridge Dr P.O. Box 882136 Steamboat Springs, CO 80488 Tel: 970-879-7952 Fax: 970-879-7926 -Original Message- From: sprinklerforum-boun

RE: Cla-Val # 581

2010-03-19 Thread Thom McMahon
the valve. Thom McMahon, SET Firetech, Inc. 2560 Copper Ridge Dr P.O. Box 882136 Steamboat Springs, CO 80488 Tel: 970-879-7952 Fax: 970-879-7926 -Original Message- From: sprinklerforum-boun...@firesprinkler.org [mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Doug Hicks Sent

RE: Over sized escutcheon for seismic clearances

2010-03-19 Thread Thom McMahon
I don't know of any Over sized listed Escutcheons, but the ARGCO OOpps ring at 5 dia is what we've seen used for this. http://www.argco.com/store/main.aspx?p=itemdetailitem=4515499 Thom McMahon, SET Firetech, Inc. 2560 Copper Ridge Dr P.O. Box 882136 Steamboat Springs, CO 80488 Tel: 970-879

RE: Hard wired air compressors

2010-03-18 Thread Thom McMahon
a plugged in compressor. Thom McMahon, SET Firetech, Inc. 2560 Copper Ridge Dr P.O. Box 882136 Steamboat Springs, CO 80488 Tel: 970-879-7952 Fax: 970-879-7926 A disconnect and breaker will also disable the power to the A/C unless locked in ON position. Low air alarm will provide the backup

RE: Hard wired air compressors

2010-03-18 Thread Thom McMahon
serving those devices. Thom McMahon, SET Firetech, Inc. 2560 Copper Ridge Dr P.O. Box 882136 Steamboat Springs, CO 80488 Tel: 970-879-7952 Fax: 970-879-7926 -Original Message- From: sprinklerforum-boun...@firesprinkler.org [mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf

RE: dry pendent's on flex drops

2010-03-17 Thread Thom McMahon
It's been a while since I looked at ALL MFG.'s literature for Dry Pend. But I don't recall any that were OK to screw into a coupling. What brand are you using bobby? Thom McMahon, SET Firetech, Inc. 2560 Copper Ridge Dr P.O. Box 882136 Steamboat Springs, CO 80488 Tel: 970-879-7952 Fax: 970-879

RE: Through wall penetration with sprinkler heads

2010-03-17 Thread Thom McMahon
by the penetration of a fire sprinkler, provided it is covered by a metal escutcheon plate. Thom McMahon, SET Firetech, Inc. 2560 Copper Ridge Dr P.O. Box 882136 Steamboat Springs, CO 80488 Tel: 970-879-7952 Fax: 970-879-7926 -Original Message- From: sprinklerforum-boun

RE: dry pendent's on flex drops

2010-03-17 Thread Thom McMahon
Bobby, you may want to look at that again, the DS-1 only allows you to use a 1CPVC x 1FM adapter by Tyco in wet systems, and suggests the use of Fig. 12 for wet systems, nowhere does it allow the use of a coupling. Wet or Dry. Thom McMahon, SET Firetech, Inc. 2560 Copper Ridge Dr P.O. Box 882136

RE: Through wall penetration with sprinkler heads

2010-03-17 Thread Thom McMahon
True if the heads are truly Back to Back, we have overcome this with Bld. Official approval by offsetting the heads one joist space so the stud forms the fire blocking. Thom McMahon, SET Firetech, Inc. 2560 Copper Ridge Dr P.O. Box 882136 Steamboat Springs, CO 80488 Tel: 970-879-7952 Fax: 970

RE: dry pendent's on flex drops

2010-03-17 Thread Thom McMahon
there, carry on all. Thom McMahon, SET Firetech, Inc. 2560 Copper Ridge Dr P.O. Box 882136 Steamboat Springs, CO 80488 Tel: 970-879-7952 Fax: 970-879-7926 -Original Message- From: sprinklerforum-boun...@firesprinkler.org [mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Bobby