RE: mixing EC sprinks with SC sprinks

2021-10-12 Thread bill.brooks brooksfpe.com via Sprinklerforum
And this seems to be the difference between the Classification of the Occupancy/Commodity (hard part performed by EOR) and figuring out what sprinkler and spacing to use in a particular compartment with clouds, soffits, skylights, beams, joists, hidden spaces, piping configuration, hanger

Open Grate Flooring - Calculations

2020-12-31 Thread bill.brooks brooksfpe.com via Sprinklerforum
A multilevel industrial facility is using extensive open grate flooring systems. Is it feasible to use a density/area calculation when the fire plume does not stop at the open grate? Does a building have to have a "ceiling" (2016 3.3.5) to perform a hydraulic calculation? Just questioning

RE: NFPA 13D

2020-03-31 Thread bill.brooks brooksfpe.com via Sprinklerforum
To address the initial concern, 2015 IRC M1601.4.4 regulates support for ducts and refers to two SMACNA standards for fibrous glass and metal ducts. For reference, the 2012 edition requires nonmetallic ducts to be hung in accordance with manufacturers’ instructions. I’d bet neither recommends

RE: Sprinklers in lieu of fire rated assemblies

2019-09-24 Thread bill.brooks brooksfpe.com via Sprinklerforum
Some of the EOR brainstorms we see on this forum are pretty farfetched. This one seems to be based on precedent in current codes and standards. The EOR appears to have created a performance objective which says the heat absorption rate of the water curtain exceeds the likely rate of heat flow