RE: [EXTERNAL] Re: Captive Aire Systems

2019-08-16 Thread Phil Stoehr via Sprinklerforum
Every few months we get a GC asking us to hook up to these systems, we 
“politely” refuse.

The manufacturer’s literature is vague, installation requirements can be 
expensive (reduced pressure backflow, low maximum pressure limit, pipe sizing?, 
inspection/testing requirements?), and we’ve had Captive Aire submit these for 
permit under our contractor number without permission.  After trying to 
facilitate installation on a couple projects, we’ve determined it’s not worth 
the hassle.

Phil Stoehr
Design Manager
Smith Fire Systems
Direct: (253) 248-2057
Cell:  (253) 380-1623
psto...@smithfire.com<mailto:psto...@smithfire.com>

From: Kyle.Montgomery 
Sent: Thursday, August 15, 2019 1:22 PM
To: sprinklerforum@lists.firesprinkler.org
Cc: Travis Mack ; Ron Greenman 
Subject: RE: [EXTERNAL] Re: Captive Aire Systems

Travis,

In a roundabout way, that sort of answers your question. If they aren’t allowed 
to connect to domestic fixtures that may be operating at the same time, then it 
stands to reason that they shouldn’t connect to sprinkler systems that are 
operating at the same time. Ergo, if they are allowed to be connected to the 
sprinkler system, then it stands to reason that the sprinklers should not be 
operating simultaneously with this system.

Case closed. ☺

-Kyle M


From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of Travis Mack via Sprinklerforum
Sent: Thursday, August 15, 2019 12:49 PM
To: 
sprinklerforum@lists.firesprinkler.org<mailto:sprinklerforum@lists.firesprinkler.org>
Cc: Travis Mack mailto:tm...@mfpdesign.com>>; Ron Greenman 
mailto:rongreen...@gmail.com>>
Subject: [EXTERNAL] Re: Captive Aire Systems

I’ve run into these on multiple projects. They go by the name Captive Aire, 
Core and Pirhana.

They have a pressure demand of 32-70 psi and a flow rate of about 40 gpm 
depending on the number of nozzles. We see these in Marriott properties often.

They can be off domestic or fire as I see it. They are supposed to be direct 
line as was described to me yesterday. So they can’t have sinks or other 
fixture coming off the line supplying them. Doesn’t make sense why it can 
attach to sprinkler then. But none of the suppliers will state if we have to 
flow this simultaneously with sprinklers.

This job is always fun. Get to see lots of crazy things.
Travis Mack, CFPS, CWBSP, RME-G, SET
480-505-9271
MFP Design, LLC
www.mfpdesign,com<http://www.mfpdesign,com>
Send large files to MFP Design via:
https://www.hightail.com/u/MFPDesign<https://urldefense.proofpoint.com/v2/url?u=https-3A__www.hightail.com_u_MFPDesign=DwMFaQ=wn3mZQLIuInh2ClcJ0_DIA=Z_2A85VL7AQzoqudh6uOyS3bn8etxB7nLN8OBJwQd9A=P9cL1oBlMFsJR9PkQUpPBhDWLqRBCWXfiCfaqcJDrso=9xvLfQ6AqIL4u1QdnX9fyYjt0D0CraEfbnfamwDCjHU=>

Sent from my iPhone

On Aug 15, 2019, at 11:36 AM, Ron Greenman via Sprinklerforum 
mailto:sprinklerforum@lists.firesprinkler.org>>
 wrote:
Travis,

Like Bruce, I may be a few years out of date also but I've never seen one of 
these connected to a sprinkler system. They are for a special hazard and so 
independent of the life safety and building protection definition for a 
sprinkler system. These are designed to smother the fire with the saponifying 
agent and then use the water to cool down the appliances to avoid reflash. Way 
back in the nineties, this system was a way that Ansul came up with to meet the 
new requirements of UL 300. requirements that commercial cooking operations had 
to comply with even in unsprinklered buildings (think stand-alone McDonald's, 
Red Robins, etc, under 5000 or 6000 sqft that weren't required to be 
sprinklered then). Note that NFPA 13 isn't even referenced as an applicable 
code/standard.

CODES AND STANDARDS
The PIRANHA hybrid wet agent system and its components meet the following 
codes, standards and recommended practices:

1. Underwriters Laboratories, Inc. (UL): Standard 300 – Fire Testing of Fire 
Extinguishing Systems for Protection of Restaurant Cooking Areas.

2. Underwriters Laboratories, Inc. (UL): Standard 2092 – Pre-Engineered Wet 
Chemical Extinguishing Units.

3. Underwriters Laboratory of Canada (ULC): Standard ORD-C1254.6 – 
Pre-Engineered Wet Chemical Extinguishing System Units.

4. National Fire Protection Association (NFPA): Standard 17A – Wet Chemical 
Extinguishing Systems.

5. National Fire Protection Association (NFPA): Standard 96 – Ventilation 
Control and Fire Protection of Commercial Cooking Operations.

6. American Society of Sanitary Engineers (ASSE): Standard 1001 – Cross 
Connection Protection Devices: Guidelines for Selection of the Proper Type of 
Backflow Preventor – Piped Applied Atmospheric Vacuum Breakers.

7. International Association of Plumbing and Mechanical Officials (IAPMO): 
Installation, Material and Property Standard PS 108-98 – Grease Fire 
Suppression Systems.


Ron Greenman

rongreen...@gmail.com<mailto:rongreen...@gmail.com>

253.576.9700

The Uni

Re: [EXTERNAL] Re: Captive Aire Systems

2019-08-16 Thread AKS-Gmail-IMAP via Sprinklerforum
It is definitely a challenge to get down to the details for these systems to 
determine the implications for “supply its water from the automatic sprinkler 
system”. I don’t think the system nuts and bolts details are easily available 
online for inquiry. I have seen the installation and controls diagrams for such 
an existing system, which probably was tucked into the control cabinet or 
pasted to its access door. It had two water supply connections. One was for 
cold water and one was for hot water. 

These hot and cold supplies connected to electrically operated valves. The 
control panel switched the water supply between cold and hot as needed for the 
suppression mode and the wash down mode. In this part of the country connecting 
the cold supply to the automatic sprinkler system meant there are two possible 
water supply cross contamination avenues. One is the automatic sprinkler system 
crossing into the kitchen hot water system which may not have had an RPZ back 
flow preventer on its supply line. The other avenue is the wet chemical 
suppression agent somehow backing into the sprinkler system, thus requiring an 
RPZ back flow preventer between the sprinkler system and its water supply. 

New Zealand sounds like it may be sophisticated in its rules regarding these 
systems so that the question regarding supply from the automatic sprinkler 
system is not one that opens a can of worms.

Allan Seidel
St.Louis, MO

> On Aug 15, 2019, at 7:26 PM, Russell Gregory via Sprinklerforum 
>  wrote:
> 
> Further to Nicky’s comments I would add that the systems installed as tail 
> end to fire sprinklers do not have the hood washing feature that the Captive 
> Air appear to have.
> Pressure reducing is needed in some cases.
>  
> Russell Gregory
> Christchurch; New Zealand
>  
> From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] 
> On Behalf Of Nicky Marshall via Sprinklerforum
> Sent: Friday, 16 August 2019 11:43 AM
> To: sprinklerforum@lists.firesprinkler.org
> Cc: Nicky Marshall; Travis Mack
> Subject: RE: [EXTERNAL] Re: Captive Aire Systems
>  
> In New Zealand, we frequently connect them to a sprinkler system as the 
> installation of an approved ‘restaurant system’ permits sprinklers to be 
> omitted from ducts and hoods in our standard.
> We do not allow a cumulative demand.  Although our standard does not 
> explicitly state what you should do.
> When connected to a sprinkler system they are treated much like a ‘tail-end’ 
> pre-action or dry system.  Because sprinkler system compliance is dependent 
> on that system, they are connected with a supervised/monitored valve to warn 
> if closed and they also usually have a flow or operation switch on them that 
> indicates on a fire alarm panel.
> Our suppliers also do the calculations.
>  
>  
> Nicky Marshall <>
> Southern Regional Manager
> PROTECH DESIGN LIMITED
> Specialist Fire Protection Consultants
> Phone: +64 (0)3 579 5577 extn 1  Mobile: +64 (0)21 433 488  Email: 
> ni...@protechdesign.co.nz <mailto:ni...@protechdesign.co.nz>  Web 
> :www.protechdesign.co.nz
> Address:105A Alabama Rd, Redwoodtown, Blenheim 7201, NZ Skype for Business: 
> ni...@protechdesign.co.nz <mailto:ni...@protechdesign.co.nz>
> 
> “I always wondered why somebody doesn't do something about that. Then I 
> realised I was somebody” Lily Tomlin
>  
>>>  
>>> From: Sprinklerforum >> <mailto:sprinklerforum-boun...@lists.firesprinkler.org>> On Behalf Of 
>>> Travis Mack, SET, CFPS, CWBSP, RME-G via Sprinklerforum
>>> Sent: Wednesday, August 14, 2019 6:32 PM
>>> To: sprinklerforum@lists.firesprinkler.org 
>>> <mailto:sprinklerforum@lists.firesprinkler.org>
>>> Cc: Travis Mack, SET, CFPS, CWBSP, RME-G >> <mailto:tm...@mfpdesign.com>>; 'Bruce Verhei' >> <mailto:bver...@comcast.net>>
>>> Subject: RE: Captive Aire Systems
>>>  
>>> Get this.  They are concerned of the domestic system robbing the hood of 
>>> the water.  So this is why they are pushing it to the sprinkler system.  
>>> We’ve seen these attached to both domestic and fire.  I always push for 
>>> domestic because I don’t want to deal with them.  I find it funny that the 
>>> hood supplier will say it has to connect to the sprinkler system but they 
>>> won’t do anything to prove it will work.  They throw that all back to the 
>>> sprinkler guys.  Just been one of those days.
>>>  
>>>  
>>> <https://urldefense.proofpoint.com/v2/url?u=http-3A__www.mfpdesign.com_=DwMFaQ=wn3mZQLIuInh2ClcJ0_DIA=Z_2A85VL7AQzoqudh6uOyS3bn8etxB7nLN8OBJwQd9A=P9cL1oBlMFsJR9PkQUpPBhDWLqRBCWXfiCfaqcJDrso=Acxe8iKYA32DZOYelVqiEbnMyMuAFqfl5EZoKkQ

RE: [EXTERNAL] Re: Captive Aire Systems

2019-08-15 Thread Russell Gregory via Sprinklerforum
Further to Nicky’s comments I would add that the systems installed as tail end 
to fire sprinklers do not have the hood washing feature that the Captive Air 
appear to have. 

Pressure reducing is needed in some cases.

 

Russell Gregory

Christchurch; New Zealand 

 

From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of Nicky Marshall via Sprinklerforum
Sent: Friday, 16 August 2019 11:43 AM
To: sprinklerforum@lists.firesprinkler.org
Cc: Nicky Marshall; Travis Mack
Subject: RE: [EXTERNAL] Re: Captive Aire Systems

 

In New Zealand, we frequently connect them to a sprinkler system as the 
installation of an approved ‘restaurant system’ permits sprinklers to be 
omitted from ducts and hoods in our standard.

We do not allow a cumulative demand.  Although our standard does not explicitly 
state what you should do.

When connected to a sprinkler system they are treated much like a ‘tail-end’ 
pre-action or dry system.  Because sprinkler system compliance is dependent on 
that system, they are connected with a supervised/monitored valve to warn if 
closed and they also usually have a flow or operation switch on them that 
indicates on a fire alarm panel.

Our suppliers also do the calculations. 

 

 

Nicky Marshall

Southern Regional Manager

PROTECH DESIGN LIMITED

Specialist Fire Protection Consultants

Phone: +64 (0)3 579 5577 extn 1  Mobile: +64 (0)21 433 488  Email:  
<mailto:ni...@protechdesign.co.nz> ni...@protechdesign.co.nz  Web 
:www.protechdesign.co.nz 

Address:105A Alabama Rd, Redwoodtown, Blenheim 7201, NZ Skype for Business:  
<mailto:ni...@protechdesign.co.nz> ni...@protechdesign.co.nz

A close up of a signDescription automatically generated

“I always wondered why somebody doesn't do something about that. Then I 
realised I was somebody” Lily Tomlin

 

 

From: Sprinklerforum  On Behalf 
Of Travis Mack, SET, CFPS, CWBSP, RME-G via Sprinklerforum
Sent: Wednesday, August 14, 2019 6:32 PM
To: sprinklerforum@lists.firesprinkler.org
Cc: Travis Mack, SET, CFPS, CWBSP, RME-G ; 'Bruce Verhei' 

Subject: RE: Captive Aire Systems

 

Get this.  They are concerned of the domestic system robbing the hood of the 
water.  So this is why they are pushing it to the sprinkler system.  We’ve seen 
these attached to both domestic and fire.  I always push for domestic because I 
don’t want to deal with them.  I find it funny that the hood supplier will say 
it has to connect to the sprinkler system but they won’t do anything to prove 
it will work.  They throw that all back to the sprinkler guys.  Just been one 
of those days.

 

 
<https://urldefense.proofpoint.com/v2/url?u=http-3A__www.mfpdesign.com_=DwMFaQ=wn3mZQLIuInh2ClcJ0_DIA=Z_2A85VL7AQzoqudh6uOyS3bn8etxB7nLN8OBJwQd9A=P9cL1oBlMFsJR9PkQUpPBhDWLqRBCWXfiCfaqcJDrso=Acxe8iKYA32DZOYelVqiEbnMyMuAFqfl5EZoKkQ2Avg=>
 

Travis Mack, CFPS, CWBSP, RME-G, SET

MFP Design, LLC

3356 E Vallejo Ct

Gilbert, AZ 85298

480-505-9271

fax: 866-430-6107

 <mailto:tm...@mfpdesign.com> tm...@mfpdesign.com

www.mfpdesign.com 
<https://urldefense.proofpoint.com/v2/url?u=http-3A__www.mfpdesign.com=DwMFaQ=wn3mZQLIuInh2ClcJ0_DIA=Z_2A85VL7AQzoqudh6uOyS3bn8etxB7nLN8OBJwQd9A=P9cL1oBlMFsJR9PkQUpPBhDWLqRBCWXfiCfaqcJDrso=Gltsm1BrBL21AQMy8Nvo33FoaCPDBK_xhLt7P67dJR8=>
 

 

Send large files to us via: https://www.hightail.com/u/MFPDesign 

LinkedIn: https://www.linkedin.com/in/travismack

 

“The bitterness of poor quality remains long after the sweetness of low price 
is forgotten.”

 

 

From: Sprinklerforum  On Behalf 
Of Bruce Verhei via Sprinklerforum
Sent: Wednesday, August 14, 2019 3:28 PM
To: sprinklerforum@lists.firesprinkler.org
Cc: Bruce Verhei 
Subject: Re: Captive Aire Systems

 

I might be a couple years out of date. I think the ones we saw were off 
domestic water, with a small backflow device. You can’t run a restaurant 
without water, so there is no concern about water system not being monitored.  

Best.


On Aug 14, 2019, at 15:19, Travis Mack, SET, CFPS, CWBSP, RME-G via 
Sprinklerforum  wrote:

I’m sure some of you have dealt with these Captive Aire / Piranha systems.  
Basically they are hood systems that connect to the sprinkler system.  The one 
I have a data sheet for has an operating pressure of 32-70 psi and flows vary 
depending on # of nozzles.  How do those of you dealing with these handle them? 
 The supplier will not do any calculations for the system.  My question is, do 
we treat these like a “rack” system and balance the hood systems to the 
overhead?  If I have a kitchen with 3 of these, do I figure 0, 1, 2 or 3 
flowing simultaneously with the overhead.  As you can imagine, a standard 
sprinkler in the kitchen is ±10 psi.  Now, if we have to treat this like a rack 
system and balance at the junction point, this 30 psi for the Piranha system 
will significantly over-discharge the sprinklers leading to a much larger 
kitchen demand.  These often seem to be brought up toward t

RE: [EXTERNAL] Re: Captive Aire Systems

2019-08-15 Thread Nicky Marshall via Sprinklerforum
In New Zealand, we frequently connect them to a sprinkler system as the 
installation of an approved ‘restaurant system’ permits sprinklers to be 
omitted from ducts and hoods in our standard.
We do not allow a cumulative demand.  Although our standard does not explicitly 
state what you should do.
When connected to a sprinkler system they are treated much like a ‘tail-end’ 
pre-action or dry system.  Because sprinkler system compliance is dependent on 
that system, they are connected with a supervised/monitored valve to warn if 
closed and they also usually have a flow or operation switch on them that 
indicates on a fire alarm panel.
Our suppliers also do the calculations.


[cid:image002.jpg@01D55427.AE70BF60]Nicky Marshall
Southern Regional Manager
PROTECH DESIGN LIMITED
Specialist Fire Protection Consultants
Phone: +64 (0)3 579 5577 extn 1  Mobile: +64 (0)21 433 488  Email: 
ni...@protechdesign.co.nz  Web 
:www.protechdesign.co.nz
Address:105A Alabama Rd, Redwoodtown, Blenheim 7201, NZ Skype for Business: 
ni...@protechdesign.co.nz
[A close up of a signDescription automatically generated]
“I always wondered why somebody doesn't do something about that. Then I 
realised I was somebody” Lily Tomlin


From: Sprinklerforum 
mailto:sprinklerforum-boun...@lists.firesprinkler.org>>
 On Behalf Of Travis Mack, SET, CFPS, CWBSP, RME-G via Sprinklerforum
Sent: Wednesday, August 14, 2019 6:32 PM
To: 
sprinklerforum@lists.firesprinkler.org
Cc: Travis Mack, SET, CFPS, CWBSP, RME-G 
mailto:tm...@mfpdesign.com>>; 'Bruce Verhei' 
mailto:bver...@comcast.net>>
Subject: RE: Captive Aire Systems

Get this.  They are concerned of the domestic system robbing the hood of the 
water.  So this is why they are pushing it to the sprinkler system.  We’ve seen 
these attached to both domestic and fire.  I always push for domestic because I 
don’t want to deal with them.  I find it funny that the hood supplier will say 
it has to connect to the sprinkler system but they won’t do anything to prove 
it will work.  They throw that all back to the sprinkler guys.  Just been one 
of those days.


Travis Mack, CFPS, CWBSP, RME-G, SET
MFP Design, LLC
3356 E Vallejo Ct
Gilbert, AZ 85298
480-505-9271
fax: 866-430-6107
tm...@mfpdesign.com
www.mfpdesign.com

Send large files to us via: 
https://www.hightail.com/u/MFPDesign
LinkedIn: 
https://www.linkedin.com/in/travismack

“The bitterness of poor quality remains long after the sweetness of low price 
is forgotten.”


From: Sprinklerforum 
mailto:sprinklerforum-boun...@lists.firesprinkler.org>>
 On Behalf Of Bruce Verhei via Sprinklerforum
Sent: Wednesday, August 14, 2019 3:28 PM
To: 
sprinklerforum@lists.firesprinkler.org
Cc: Bruce Verhei mailto:bver...@comcast.net>>
Subject: Re: Captive Aire Systems

I might be a couple years out of date. I think the ones we saw were off 
domestic water, with a small backflow device. You can’t run a restaurant 
without water, so there is no concern about water system not being monitored.
Best.

On Aug 14, 2019, at 15:19, Travis Mack, SET, CFPS, CWBSP, RME-G via 
Sprinklerforum 
mailto:sprinklerforum@lists.firesprinkler.org>>
 wrote:
I’m sure some of you have dealt with these Captive Aire / Piranha systems.  
Basically they are hood systems that connect to 

RE: [EXTERNAL] Re: Captive Aire Systems

2019-08-15 Thread Travis Mack, SET, CFPS, CWBSP, RME-G via Sprinklerforum
I was told that they can’t have the connections to toilets or sinks upstream 
because it could take water away from the system when needed.  But, in this 
case they finally came back and just took it from the domestic.  So I won’t 
worry about it until the next one comes up.

 

 <http://www.mfpdesign.com/> 

Travis Mack, CFPS, CWBSP, RME-G, SET

MFP Design, LLC

3356 E Vallejo Ct

Gilbert, AZ 85298

480-505-9271

fax: 866-430-6107

 <mailto:tm...@mfpdesign.com> tm...@mfpdesign.com

www.mfpdesign.com

 

Send large files to us via:  
<https://na01.safelinks.protection.outlook.com/?url=https%3A%2F%2Fwww.hightail.com%2Fu%2FMFPDesign=02%7C01%7C%7C1121d49f9e6b4cf248f108d4df580e77%7C14e5497c16da42e69ffa77d19bafe511%7C0%7C0%7C636379016677342180=eGdMZGu2wXhUupGwgGTrqF3b54OP5%2BAZvlHhABSexWY%3D=0>
 https://www.hightail.com/u/MFPDesign 

LinkedIn:  
<https://na01.safelinks.protection.outlook.com/?url=https%3A%2F%2Fwww.linkedin.com%2Fin%2Ftravismack=02%7C01%7C%7C1121d49f9e6b4cf248f108d4df580e77%7C14e5497c16da42e69ffa77d19bafe511%7C0%7C0%7C636379016677342180=tT5E7LsZjSmyreKi4gDCa70EWN%2BZodi%2FhbeCbHNRijI%3D=0>
 https://www.linkedin.com/in/travismack

 

“The bitterness of poor quality remains long after the sweetness of low price 
is forgotten.”

 

 

From: Kyle.Montgomery  
Sent: Thursday, August 15, 2019 1:22 PM
To: sprinklerforum@lists.firesprinkler.org
Cc: Travis Mack ; Ron Greenman 
Subject: RE: [EXTERNAL] Re: Captive Aire Systems

 

Travis,

 

In a roundabout way, that sort of answers your question. If they aren’t allowed 
to connect to domestic fixtures that may be operating at the same time, then it 
stands to reason that they shouldn’t connect to sprinkler systems that are 
operating at the same time. Ergo, if they are allowed to be connected to the 
sprinkler system, then it stands to reason that the sprinklers should not be 
operating simultaneously with this system.

 

Case closed. :)

 

-Kyle M

 

 

From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of Travis Mack via Sprinklerforum
Sent: Thursday, August 15, 2019 12:49 PM
To: sprinklerforum@lists.firesprinkler.org 
<mailto:sprinklerforum@lists.firesprinkler.org> 
Cc: Travis Mack mailto:tm...@mfpdesign.com> >; Ron 
Greenman mailto:rongreen...@gmail.com> >
Subject: [EXTERNAL] Re: Captive Aire Systems

 

I’ve run into these on multiple projects. They go by the name Captive Aire, 
Core and Pirhana. 

 

They have a pressure demand of 32-70 psi and a flow rate of about 40 gpm 
depending on the number of nozzles. We see these in Marriott properties often. 

 

They can be off domestic or fire as I see it. They are supposed to be direct 
line as was described to me yesterday. So they can’t have sinks or other 
fixture coming off the line supplying them. Doesn’t make sense why it can 
attach to sprinkler then. But none of the suppliers will state if we have to 
flow this simultaneously with sprinklers. 

 

This job is always fun. Get to see lots of crazy things. 

Travis Mack, CFPS, CWBSP, RME-G, SET

480-505-9271

MFP Design, LLC

www.mfpdesign,com <http://www.mfpdesign,com> 

Send large files to MFP Design via:

https://www.hightail.com/u/MFPDesign 
<https://urldefense.proofpoint.com/v2/url?u=https-3A__www.hightail.com_u_MFPDesign=DwMFaQ=wn3mZQLIuInh2ClcJ0_DIA=Z_2A85VL7AQzoqudh6uOyS3bn8etxB7nLN8OBJwQd9A=P9cL1oBlMFsJR9PkQUpPBhDWLqRBCWXfiCfaqcJDrso=9xvLfQ6AqIL4u1QdnX9fyYjt0D0CraEfbnfamwDCjHU=>
 

 

Sent from my iPhone


On Aug 15, 2019, at 11:36 AM, Ron Greenman via Sprinklerforum 
mailto:sprinklerforum@lists.firesprinkler.org> > wrote:

Travis,

 

Like Bruce, I may be a few years out of date also but I've never seen one of 
these connected to a sprinkler system. They are for a special hazard and so 
independent of the life safety and building protection definition for a 
sprinkler system. These are designed to smother the fire with the saponifying 
agent and then use the water to cool down the appliances to avoid reflash. Way 
back in the nineties, this system was a way that Ansul came up with to meet the 
new requirements of UL 300. requirements that commercial cooking operations had 
to comply with even in unsprinklered buildings (think stand-alone McDonald's, 
Red Robins, etc, under 5000 or 6000 sqft that weren't required to be 
sprinklered then). Note that NFPA 13 isn't even referenced as an applicable 
code/standard.

 

CODES AND STANDARDS 

The PIRANHA hybrid wet agent system and its components meet the following 
codes, standards and recommended practices: 

 

1. Underwriters Laboratories, Inc. (UL): Standard 300 – Fire Testing of Fire 
Extinguishing Systems for Protection of Restaurant Cooking Areas. 

 

2. Underwriters Laboratories, Inc. (UL): Standard 2092 – Pre-Engineered Wet 
Chemical Extinguishing Units. 

 

3. Underwriters Laboratory of Canada (ULC): Standard ORD-C1254.6 – 
Pre-Engineered Wet Chemical Extinguishing System Units. 

 


RE: [EXTERNAL] Re: Captive Aire Systems

2019-08-15 Thread Kyle.Montgomery via Sprinklerforum
Travis,

In a roundabout way, that sort of answers your question. If they aren’t allowed 
to connect to domestic fixtures that may be operating at the same time, then it 
stands to reason that they shouldn’t connect to sprinkler systems that are 
operating at the same time. Ergo, if they are allowed to be connected to the 
sprinkler system, then it stands to reason that the sprinklers should not be 
operating simultaneously with this system.

Case closed. ☺

-Kyle M


From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of Travis Mack via Sprinklerforum
Sent: Thursday, August 15, 2019 12:49 PM
To: sprinklerforum@lists.firesprinkler.org
Cc: Travis Mack ; Ron Greenman 
Subject: [EXTERNAL] Re: Captive Aire Systems

I’ve run into these on multiple projects. They go by the name Captive Aire, 
Core and Pirhana.

They have a pressure demand of 32-70 psi and a flow rate of about 40 gpm 
depending on the number of nozzles. We see these in Marriott properties often.

They can be off domestic or fire as I see it. They are supposed to be direct 
line as was described to me yesterday. So they can’t have sinks or other 
fixture coming off the line supplying them. Doesn’t make sense why it can 
attach to sprinkler then. But none of the suppliers will state if we have to 
flow this simultaneously with sprinklers.

This job is always fun. Get to see lots of crazy things.
Travis Mack, CFPS, CWBSP, RME-G, SET
480-505-9271
MFP Design, LLC
www.mfpdesign,com
Send large files to MFP Design via:
https://www.hightail.com/u/MFPDesign

Sent from my iPhone

On Aug 15, 2019, at 11:36 AM, Ron Greenman via Sprinklerforum 
mailto:sprinklerforum@lists.firesprinkler.org>>
 wrote:
Travis,

Like Bruce, I may be a few years out of date also but I've never seen one of 
these connected to a sprinkler system. They are for a special hazard and so 
independent of the life safety and building protection definition for a 
sprinkler system. These are designed to smother the fire with the saponifying 
agent and then use the water to cool down the appliances to avoid reflash. Way 
back in the nineties, this system was a way that Ansul came up with to meet the 
new requirements of UL 300. requirements that commercial cooking operations had 
to comply with even in unsprinklered buildings (think stand-alone McDonald's, 
Red Robins, etc, under 5000 or 6000 sqft that weren't required to be 
sprinklered then). Note that NFPA 13 isn't even referenced as an applicable 
code/standard.

CODES AND STANDARDS
The PIRANHA hybrid wet agent system and its components meet the following 
codes, standards and recommended practices:

1. Underwriters Laboratories, Inc. (UL): Standard 300 – Fire Testing of Fire 
Extinguishing Systems for Protection of Restaurant Cooking Areas.

2. Underwriters Laboratories, Inc. (UL): Standard 2092 – Pre-Engineered Wet 
Chemical Extinguishing Units.

3. Underwriters Laboratory of Canada (ULC): Standard ORD-C1254.6 – 
Pre-Engineered Wet Chemical Extinguishing System Units.

4. National Fire Protection Association (NFPA): Standard 17A – Wet Chemical 
Extinguishing Systems.

5. National Fire Protection Association (NFPA): Standard 96 – Ventilation 
Control and Fire Protection of Commercial Cooking Operations.

6. American Society of Sanitary Engineers (ASSE): Standard 1001 – Cross 
Connection Protection Devices: Guidelines for Selection of the Proper Type of 
Backflow Preventor – Piped Applied Atmospheric Vacuum Breakers.

7. International Association of Plumbing and Mechanical Officials (IAPMO): 
Installation, Material and Property Standard PS 108-98 – Grease Fire 
Suppression Systems.


Ron Greenman

rongreen...@gmail.com

253.576.9700

The Universe is monstrously indifferent to the presence of man. -Werner Herzog, 
screenwriter, film director, author, actor and opera director (1942-)


On Thu, Aug 15, 2019 at 8:21 AM Matthew J Willis via Sprinklerforum 
mailto:sprinklerforum@lists.firesprinkler.org>>
 wrote:
The purpose of a “hood” in this application is to direct and capture grease 
laden stuff…

Re: NFPA 96.

R/
Matt

Matthew J. Willis, CWBSP
Design Manager /3-D Specialist
Rapid Fire Protection 
Inc.
1530 Samco Road
Rapid City, SD 57702
Office-605.348.2342
Direct Line-605.593.5063
Cell-605.391.2733
Fax:-605.348.0108



From: Sprinklerforum 
mailto:sprinklerforum-boun...@lists.firesprinkler.org>>
 On Behalf Of Jonathan Mote via Sprinklerforum
Sent: Thursday, August 15, 2019 9:15