[Sprinklerforum] Re: 2 Most Remote Hose Valves For Standpipe Calc

2023-11-29 Thread Brian Harris
Excellent, thank you. Thank you, Brian Harris, CET BVS Systems Inc. From: Steve Leyton Sent: Wednesday, November 29, 2023 4:23 PM To: Discussion list on issues relating to automatic fire sprinklers Subject: [Sprinklerforum] Re: 2 Most Remote Hose Valves For Standpipe Calc The letter

[Sprinklerforum] Re: 2 Most Remote Hose Valves For Standpipe Calc

2023-11-29 Thread Steve Leyton
The letter and intent of the standard is to calculate 500 GPM from the 2 most demanding hose connections on the hydraulically remote standpipe, then add 250 GPM at the connection point to the feed main serving the additional standpipes, up to the required maximum flow rate for the building.