Excellent, thank you.
Thank you,
Brian Harris, CET
BVS Systems Inc.
From: Steve Leyton
Sent: Wednesday, November 29, 2023 4:23 PM
To: Discussion list on issues relating to automatic fire sprinklers
Subject: [Sprinklerforum] Re: 2 Most Remote Hose Valves For Standpipe Calc
The letter
The letter and intent of the standard is to calculate 500 GPM from the 2 most
demanding hose connections on the hydraulically remote standpipe, then add 250
GPM at the connection point to the feed main serving the additional standpipes,
up to the required maximum flow rate for the building.