From: Brian Harris
Sent: Thursday, June 8, 2023 1:33 PM
To: Discussion list on issues relating to automatic fire sprinklers
Subject: [Sprinklerforum] Re: Manual Wet Standpipe & Pump
Anthony-
Thanks. I was asking more about sizing the pump based on sprinkler demand only.
Brian Harris,
mail mmo...@shambaugh.com
[cid:image001.png@01D99A0F.8797F4D0]
From: matthew.will...@ferguson.com
Sent: Thursday, June 8, 2023 1:42 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: [Sprinklerforum] Re: Manual Wet Standpipe & Pump
Would it be an Automatic Wet connected to the pum
Bingo!
Brian Harris, CET
BVS Systems Inc.
bvssytemsinc.com<http://bvssystemsinc.com/>
From: matthew.will...@ferguson.com
Sent: Thursday, June 08, 2023 1:42 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: [Sprinklerforum] Re: Manual Wet Standpipe & Pump
Would it be an Aut
ist on issues relating to automatic fire sprinklers
Subject: [Sprinklerforum] Re: Manual Wet Standpipe & Pump
Anthony-
Thanks. I was asking more about sizing the pump based on sprinkler demand only.
Brian Harris, CET
BVS Systems Inc.
bvssytemsinc.com<http://bvssystemsinc.
c fire sprinklers
Subject: [Sprinklerforum] Re: Manual Wet Standpipe & Pump
Yes, the answer is in your question since a manual wet standpipe requires a
fire truck. If you were to connect the standpipe to the pump it would no longer
be a manual wet standpipe - it would be an automatic wet standpip
Thank you.
Brian Harris, CET
BVS Systems Inc.
bvssytemsinc.com<http://bvssystemsinc.com/>
From: Steve Leyton
Sent: Thursday, June 08, 2023 11:59 AM
To: Discussion list on issues relating to automatic fire sprinklers
Subject: [Sprinklerforum] Re: Manual Wet Standpipe & Pump
I
In combined standpipe/sprinkler systems utilizing a manual-wet standpipe, the
sizing of any attached water supply for sprinklers is not required to meet the
standpipe demand. This is explicitly codified in §7.7.3 of the 2019 edition
and conveniently, so numbered in preceding editions as well.
Yes, the answer is in your question since a manual wet standpipe requires a
fire truck. If you were to connect the standpipe to the pump it would no
longer be a manual wet standpipe - it would be an automatic wet standpipe.
023 10:48 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: [Sprinklerforum] Re: Manual Wet Standpipe & Pump
Brian,
Sure you could size the fire pump to meet that demand. Speaking only as one
who is pretty frugal I have to ask - should you do so? Why size the pump for
standpipe dema
Thank you sir!
Brian Harris, CET
BVS Systems Inc.
bvssytemsinc.com<http://bvssystemsinc.com/>
From: cl...@fire-design.com
Sent: Thursday, June 08, 2023 10:21 AM
To: 'Discussion list on issues relating to automatic fire sprinklers'
Subject: [Sprinklerforum] Re: Manual Wet Standpipe
Brian,
Sure you could size the fire pump to meet that demand. Speaking only as
one who is pretty frugal I have to ask - should you do so? Why size the
pump for standpipe demand instead of sprinkler system demand?
If it's a manual-wet, the first responders aren't going to rely on a
Yes
Cliff Whitfield, SET
President
Fire Design, Inc.
940 Summerbrooke Dr
Tallahassee, FL 32312
Ph: 828-284-4772
From: Brian Harris
Sent: Thursday, June 8, 2023 10:18 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: [Sprinklerforum] Manual Wet Standpipe & Pump
If a