If anyone has designed a grou
AM
To: sprinklerforum@firesprinkler.org
Subject: Aicraft Hangar Group III
If anyone has designed a group III hangar lately, (or within
recollection
limits), what is the most common fire protection system? (foam-water
deluge
system, ceiling sprinklers and low level low expansion foam, etc...)
The followi
IF you have to provide protection for Group III, you do it in
accordance with the requirements for Group II if I remember correctly.
Most popular Group II option is usually automatic sprinkler system
above with low level low expansion foam system.
Justin Reid
Sent from my iPhone
On Feb 2
If anyone has designed a group III hangar lately, (or within recollection
limits), what is the most common fire protection system? (foam-water deluge
system, ceiling sprinklers and low level low expansion foam, etc...)
The following is from NFPA 409, 2001
"8.9 Fire Protection for Group III Hang