Re: Aicraft Hangar Group III

2009-02-27 Thread Roland Huggins
85024 -Original Message- From: sprinklerforum-boun...@firesprinkler.org [mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of A.P.Silva Sent: Friday, February 27, 2009 12:23 AM To: sprinklerforum@firesprinkler.org Subject: Aicraft Hangar Group III If anyone has designed a grou

RE: Aicraft Hangar Group III

2009-02-27 Thread Fletcher, Ron
AM To: sprinklerforum@firesprinkler.org Subject: Aicraft Hangar Group III If anyone has designed a group III hangar lately, (or within recollection limits), what is the most common fire protection system? (foam-water deluge system, ceiling sprinklers and low level low expansion foam, etc...) The followi

Re: Aicraft Hangar Group III

2009-02-27 Thread Justin Reid
IF you have to provide protection for Group III, you do it in accordance with the requirements for Group II if I remember correctly. Most popular Group II option is usually automatic sprinkler system above with low level low expansion foam system. Justin Reid Sent from my iPhone On Feb 2

Aicraft Hangar Group III

2009-02-26 Thread A.P.Silva
If anyone has designed a group III hangar lately, (or within recollection limits), what is the most common fire protection system? (foam-water deluge system, ceiling sprinklers and low level low expansion foam, etc...) The following is from NFPA 409, 2001 "8.9 Fire Protection for Group III Hang