Column Sprinklers in rubber tire storage

2010-04-13 Thread Fletcher, Ron
We have an AHJ that is using the 2002 NFPA 13 and doesn't care what is in the 07. We have 25 ft. high tire storage in portable racks in a 35 ft bldg. They want column sprinklers installed with the ESFR's because there is no specific exception (that I can find) for column sprinklers as there is in

RE: Column Sprinklers in rubber tire storage

2010-04-13 Thread Pielow, Robert
: Column Sprinklers in rubber tire storage We have an AHJ that is using the 2002 NFPA 13 and doesn't care what is in the 07. We have 25 ft. high tire storage in portable racks in a 35 ft bldg. They want column sprinklers installed with the ESFR's because there is no specific exception (that I can find

RE: Column Sprinklers in rubber tire storage

2010-04-13 Thread Craig.Prahl
@firesprinkler.org Subject: RE: Column Sprinklers in rubber tire storage The ESFR exception is in 2002 Section 12.3.1.7.1(3) but not carried to 12.4.1.1.1. You could check the code change documentation to see if the change was viewed as a change in requirements or only a clarification