RE: Limited Area sprinkler systems

2009-04-01 Thread John Drucker
Ed, My thought exactly! Perhaps this will help; Limited Area Sprinkler Systems are provided for at IBC 903.3.5.1.1. The commentary provides; Use of limited area sprinkler systems is primarily limited to fire areas or other areas where the number of sprinklers does not exceed 20. The use

RE: Limited Area sprinkler systems

2009-04-01 Thread John Drucker
: RE: Limited Area sprinkler systems Ed, My thought exactly! Perhaps this will help; Limited Area Sprinkler Systems are provided for at IBC 903.3.5.1.1. The commentary provides; Use of limited area sprinkler systems is primarily limited to fire areas or other areas where the number of sprinklers

Limited Area sprinkler systems

2009-03-31 Thread Todd Williams
The IBC mentions Limited Area sprinkler systems with a veiled reference being 20 sprinklers or less. However, there is no formal definition or description as to what they are or where they are allowed. Any thoughts or experience with this? I have a proposal on my desk for a partial system

RE: Limited Area sprinkler systems

2009-03-31 Thread Karen Purvis
-Original Message- From: sprinklerforum-boun...@firesprinkler.org [mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Todd Williams Sent: Tuesday, March 31, 2009 7:44 AM To: sprinklerforum@firesprinkler.org Subject: Limited Area sprinkler systems The IBC mentions Limited Area

RE: Limited Area sprinkler systems

2009-03-31 Thread Todd Williams
- From: sprinklerforum-boun...@firesprinkler.org [mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Todd Williams Sent: Tuesday, March 31, 2009 7:44 AM To: sprinklerforum@firesprinkler.org Subject: Limited Area sprinkler systems The IBC mentions Limited Area sprinkler systems with a veiled

RE: Limited Area sprinkler systems

2009-03-31 Thread Eric Shelton
Actually, the IBC section on limited area sprinkler systems goes up to 19 heads (fewer than 20). It also requires a hydraulic calc with a simultaneous plumbing demand. Eric J. Shelton, PE Senior Fire Protection Engineer Hankins and Anderson Consulting Engineers 4880 Sadler Road Suite 300

Re: Limited Area sprinkler systems

2009-03-31 Thread Roland Huggins
of the building needs protection from it? More backwards thinking from a very qualified source. Wear your pointed boots when you talk to them. Roland On Mar 31, 2009, at 4:43 AM, Todd Williams wrote: The IBC mentions Limited Area sprinkler systems with a veiled reference being 20 sprinklers or less

RE: Limited Area sprinkler systems

2009-03-31 Thread Thom McMahon
...@firesprinkler.org] On Behalf Of Roland Huggins Sent: Tuesday, March 31, 2009 10:07 AM To: sprinklerforum@firesprinkler.org Subject: Re: Limited Area sprinkler systems As identified by Karen, the IBC allows some locations (such as furnace rooms) to be individually protected (or a higher degree of separation

Re: Limited Area sprinkler systems

2009-03-31 Thread Todd Williams
boots when you talk to them. Roland On Mar 31, 2009, at 4:43 AM, Todd Williams wrote: The IBC mentions Limited Area sprinkler systems with a veiled reference being 20 sprinklers or less. However, there is no formal definition or description as to what they are or where they are allowed. Any

Re: Limited Area sprinkler systems

2009-03-31 Thread Ed Vining
mentions Limited Area sprinkler systems with a veiled reference being 20 sprinklers or less. However, there is no formal definition or description as to what they are or where they are allowed. Any thoughts or experience with this? I have a proposal on my desk for a partial system covering some