Re: NFPA 13 2016 25.2.1.4.2

2021-03-19 Thread Ron Greenman via Sprinklerforum
dt < > jdenha...@firesprinkler.org> > Subject: Re: NFPA 13 2016 25.2.1.4.2 > > I'd like that. The last time I went a couple rounds with her we did have a > few AFSA interpretations but none exactly fit the 'identical' situation so > she wasn't satisfied. > > John Ir

RE: NFPA 13 2016 25.2.1.4.2

2021-03-19 Thread Matthew J Willis via Sprinklerforum
Subject: Re: NFPA 13 2016 25.2.1.4.2 John - Let's talk tomorrow. I think we can prepare an informal interpretation for you describing the intent of this section. AFSA will be covering Acceptance Testing is some upcoming AHJ webinars. Thanks, John John August Denhardt, PE *Vice President

Re: NFPA 13 2016 25.2.1.4.2

2021-03-18 Thread BRUCE VERHEI via Sprinklerforum
PM John Irwin via Sprinklerforum > wrote: > > > NFPA 13 2016 25.2.1.4.2, Modifications that cannot be isolated, such as > relocated drops, shall require testing at system working pressure. > > We have a local AHJ that always requires us to pump up tenant improvemen

Re: NFPA 13 2016 25.2.1.4.2

2021-03-18 Thread John Denhardt via Sprinklerforum
rch 18, 2021 10:22:20 PM > *To:* sprinklerforum@lists.firesprinkler.org < > sprinklerforum@lists.firesprinkler.org> > *Cc:* John Denhardt > *Subject:* Re: NFPA 13 2016 25.2.1.4.2 > > John - Let's talk tomorrow. I think we can prepare an informal > interpretation for you describing the i

Re: NFPA 13 2016 25.2.1.4.2

2021-03-18 Thread John Irwin via Sprinklerforum
: NFPA 13 2016 25.2.1.4.2 John - Let's talk tomorrow. I think we can prepare an informal interpretation for you describing the intent of this section. AFSA will be covering Acceptance Testing is some upcoming AHJ webinars. Thanks, John John August Denhardt, PE *Vice President, Engineering

Re: NFPA 13 2016 25.2.1.4.2

2021-03-18 Thread John Denhardt via Sprinklerforum
nment teamed with robust curriculum created by top industry leaders. Plus, the first six-months of instruction is online. Now enrolling for Spring 2021 <https://www.firesprinkler.org/itm>. On Thu, Mar 18, 2021 at 8:21 PM John Irwin via Sprinklerforum < sprinklerforum@lists.firespri

NFPA 13 2016 25.2.1.4.2

2021-03-18 Thread John Irwin via Sprinklerforum
NFPA 13 2016 25.2.1.4.2, Modifications that cannot be isolated, such as relocated drops, shall require testing at system working pressure. We have a local AHJ that always requires us to pump up tenant improvement projects to 200 psi if they are over 20 sprinklers. We have a waiver/release form