Subject: RE: NFPA 14 / Remote FDC / Manual Stand-pipes
Unfortunately, I am under 2010 Code.
John Irwin
Sprinkler Construction Manager
Critical System Solutions, LLC
Cell: 813.618.2781
Email:
jir...@criticalsystemsolutions.com
er.org] On
Behalf Of Larry Keeping
Sent: Monday, June 06, 2016 1:04 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: NFPA 14 / Remote FDC / Manual Stand-pipes
I think the guidance you are looking for is in Section 5.9 of NFPA 24-2016:
Section 5.9.1 General states that: "Where the A
inklerforum [mailto:
> sprinklerforum-boun...@lists.firesprinkler.org] *On Behalf Of *rongreenman
> .
> *Sent:* Monday, June 06, 2016 9:16 AM
> *To:* sprinklerforum@lists.firesprinkler.org
> *Subject:* Re: NFPA 14 / Remote FDC / Manual Stand-pipes
>
>
>
> Leyton will probably say I
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On
Behalf Of John Irwin
Sent: June-06-16 11:32 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: NFPA 14 / Remote FDC / Manual Stand-pipes
When using a remote FDC on the underground line or the backflow device, how do
w
@lists.firesprinkler.org
Subject: Re: NFPA 14 / Remote FDC / Manual Stand-pipes
Leyton will probably say I'm an idiot but you cannot have any valving between
the FDC and the house connections on the standpipe. Attach after the back flow,
or pump, or what have you, but make sure it's after the last va
alf Of Mike Stossel
Sent: Monday, June 06, 2016 12:27 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: NFPA 14 / Remote FDC / Manual Stand-pipes
To the best of my knowledge, no exception exists for valves located on an FDC.
The FDC will need to take connection to the standpipe and s
erforum-boun...@lists.firesprinkler.org] On
Behalf Of John Irwin
Sent: Monday, June 06, 2016 11:32 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: NFPA 14 / Remote FDC / Manual Stand-pipes
When using a remote FDC on the underground line or the backflow device, how do
we get around NFPA 14 2010 6.4.1 "Exc
Leyton will probably say I'm an idiot but you cannot have any valving
between the FDC and the house connections on the standpipe. Attach after
the back flow, or pump, or what have you, but make sure it's after the last
valve on the municipal line.
On Mon, Jun 6, 2016 at 8:32 AM, John Irwin <
jir..
When using a remote FDC on the underground line or the backflow device, how do
we get around NFPA 14 2010 6.4.1 "Except for the valve required by 6.3.2,
shutoff valves shall not be installed between the FDC and the system"?
I have done many yard FDCs on four story hotels over the years and have