Re: [EXTERNAL] RE: On/Off Switch in the Electric supply to a Dry Pipe System Air Compressor

2020-09-25 Thread John Denhardt via Sprinklerforum
Before we state UL does not have a specific listing for fire protection air compressors, look at the SCope of UL 1450 and not just the title. UL 1450 1 Scope 1.1 These requirements cover household and commercial air compressors, vacuum pumps, inflators (both compressor-type and blower-type

RE: [EXTERNAL] RE: On/Off Switch in the Electric supply to a Dry Pipe System Air Compressor

2020-09-25 Thread BRUCE VERHEI via Sprinklerforum
Yes, I would be against such a listing, also. Best. Bruce. > On 09/25/2020 3:34 PM Kyle.Montgomery via Sprinklerforum > wrote: > > > Bruce, > > That's kind of what I'm concerned about. If the code changes to say that > compressors must be listed for fire protection use, then at first

RE: [EXTERNAL] RE: On/Off Switch in the Electric supply to a Dry Pipe System Air Compressor

2020-09-25 Thread Kyle.Montgomery via Sprinklerforum
Bruce, That's kind of what I'm concerned about. If the code changes to say that compressors must be listed for fire protection use, then at first there is going to be a lag because such a listing doesn’t even exist. Then, if a listing standard gets developed and the manufacturers get some