RE: 13R ATTIC Protection

2009-02-09 Thread Thom McMahon
Actually Areas Outside of the dwelling unit In 13R Refer to Occupied
areas, and do NOT require areas, not otherwise required to be protected in a
13R system, to be protected. Similarly because you have to protect an area
per 13 in a 13R building, does NOT require it comply with all of 13, such as
Hose or concealed combustible space protection.

I understand how in So. Cal, a LH attic is No big Deal that's not always
the case in the rest of the country, where Dry, Antifreeze or pre-action
systems would be required. We find in cold country that the drywall is
always cheaper, and that doesn't even take into account the cost of on-going
maint. Testing and inspection of another entire system.

Thom McMahon, SET
Firetech, Inc.
2560 Copper Ridge Dr
P.O. Box 882136
Steamboat Springs, CO 80488
Tel:  970-879-7952
Fax: 970-879-7926


-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Steve Leyton
Sent: Saturday, February 07, 2009 5:14 PM
To: sprinklerforum@firesprinkler.org
Subject: RE: 13R ATTIC Protection

Haven't seen an unprotected attic with a 13R system absent draft-stopping
before, but have done at least 3 or 4 projects with 13R
and the attic sprinklered in lieu of draft-stopping.   It's no big deal
- light hazard, same as it ever was.   It's one of those areas outside
the dwelling units that gets protected per 13.

Steve Leyton
Protection Design  Consulting
San Diego, CA




-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Thom McMahon
Sent: Saturday, February 07, 2009 11:57 AM
To: sprinklerforum@firesprinkler.org
Subject: RE: 13R ATTIC Protection

This is just part of an ongoing discussion with a AHJ for a Hampton INN, but
how many of you have seen 13R used with no draft stopping of the attics, or
only every 3000 SF, but the concealed combustible spaces unprotected?

You're talking about Chapter 7, section 717 Draft stopping in IBC right?
They are installing draft stopping in the attic's, so then a 13R system is
OK. It's only if you want to eliminate the draft stopping that a
903.3.1.1
(13) system is required(717.4.2 Exception 3) or a 903.3.1.2 (13R) with
concealed combustible spaces protected. (717.4.2 exception 4)

Those of you that work under the IBC may want to get familiar with section
717 especially if you bid 13R work.

Thom McMahon, SET
Firetech, Inc.
2560 Copper Ridge Dr
P.O. Box 882136
Steamboat Springs, CO 80488
Tel:  970-879-7952
Fax: 970-879-7926




___
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to:
techsupp...@firesprinkler.org

To Unsubscribe, send an email
to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)
 

__ Information from ESET NOD32 Antivirus, version of virus signature
database 3836 (20090207) __

The message was checked by ESET NOD32 Antivirus.

http://www.eset.com
 
 

__ Information from ESET NOD32 Antivirus, version of virus signature
database 3836 (20090207) __

The message was checked by ESET NOD32 Antivirus.

http://www.eset.com
 
___
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: techsupp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)

___
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: techsupp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)


RE: 13R ATTIC Protection

2009-02-09 Thread Steve Leyton
Right - I mean to say that if you VOLUNTARILY sprinkler the attic, as
you might to satisfy the draft-stopping and compartmentalization
provisions of the building code, THEN it becomes an area outside the
dwelling unit and you protect per 13.  It's consistent with the language
and intent of the 13R standard.  

WRT to the big deal, I understand it's potentially WAY more expensive
in areas subject to freezing.   I meant no big deal in terms of it not
being a complicated code formula and that the determination of what's
required is straightforward.  Obviously, cost and logistics might make
draft=stopping a much more attractive alternative if you had to use
anti-freeze or dry pipe, or if it meant the difference between pump/no
pump.

Steve Leyton
Protection Design  Consulting
San Diego, CA




-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Thom
McMahon
Sent: Monday, February 09, 2009 8:33 AM
To: sprinklerforum@firesprinkler.org
Subject: RE: 13R ATTIC Protection

Actually Areas Outside of the dwelling unit In 13R Refer to Occupied
areas, and do NOT require areas, not otherwise required to be protected
in a
13R system, to be protected. Similarly because you have to protect an
area
per 13 in a 13R building, does NOT require it comply with all of 13,
such as
Hose or concealed combustible space protection.

I understand how in So. Cal, a LH attic is No big Deal that's not
always
the case in the rest of the country, where Dry, Antifreeze or pre-action
systems would be required. We find in cold country that the drywall is
always cheaper, and that doesn't even take into account the cost of
on-going
maint. Testing and inspection of another entire system.

Thom McMahon, SET
Firetech, Inc.
2560 Copper Ridge Dr
P.O. Box 882136
Steamboat Springs, CO 80488
Tel:  970-879-7952
Fax: 970-879-7926


-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Steve
Leyton
Sent: Saturday, February 07, 2009 5:14 PM
To: sprinklerforum@firesprinkler.org
Subject: RE: 13R ATTIC Protection

Haven't seen an unprotected attic with a 13R system absent
draft-stopping
before, but have done at least 3 or 4 projects with 13R
and the attic sprinklered in lieu of draft-stopping.   It's no big deal
- light hazard, same as it ever was.   It's one of those areas outside
the dwelling units that gets protected per 13.

Steve Leyton
Protection Design  Consulting
San Diego, CA




-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Thom
McMahon
Sent: Saturday, February 07, 2009 11:57 AM
To: sprinklerforum@firesprinkler.org
Subject: RE: 13R ATTIC Protection

This is just part of an ongoing discussion with a AHJ for a Hampton INN,
but
how many of you have seen 13R used with no draft stopping of the attics,
or
only every 3000 SF, but the concealed combustible spaces unprotected?

You're talking about Chapter 7, section 717 Draft stopping in IBC
right?
They are installing draft stopping in the attic's, so then a 13R system
is
OK. It's only if you want to eliminate the draft stopping that a
903.3.1.1
(13) system is required(717.4.2 Exception 3) or a 903.3.1.2 (13R) with
concealed combustible spaces protected. (717.4.2 exception 4)

Those of you that work under the IBC may want to get familiar with
section
717 especially if you bid 13R work.

Thom McMahon, SET
Firetech, Inc.
2560 Copper Ridge Dr
P.O. Box 882136
Steamboat Springs, CO 80488
Tel:  970-879-7952
Fax: 970-879-7926




___
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to:
techsupp...@firesprinkler.org

To Unsubscribe, send an email
to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)
 

__ Information from ESET NOD32 Antivirus, version of virus
signature
database 3836 (20090207) __

The message was checked by ESET NOD32 Antivirus.

http://www.eset.com
 
 

__ Information from ESET NOD32 Antivirus, version of virus
signature
database 3836 (20090207) __

The message was checked by ESET NOD32 Antivirus.

http://www.eset.com
 
___
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to:
techsupp...@firesprinkler.org

To Unsubscribe, send an email
to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)

___
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to:
techsupp...@firesprinkler.org

To Unsubscribe, send an email
to:sprinklerforum-requ...@firesprinkler.org
(Put the word

RE: 13R ATTIC Protection

2009-02-09 Thread Todd Williams

Steve,

Sprinklering the attic is not always voluntary. Some jurisdictions 
are requiring it




At 11:49 AM 2/9/2009, you wrote:

Right - I mean to say that if you VOLUNTARILY sprinkler the attic, as
you might to satisfy the draft-stopping and compartmentalization
provisions of the building code, THEN it becomes an area outside the
dwelling unit and you protect per 13.  It's consistent with the language
and intent of the 13R standard.

WRT to the big deal, I understand it's potentially WAY more expensive
in areas subject to freezing.   I meant no big deal in terms of it not
being a complicated code formula and that the determination of what's
required is straightforward.  Obviously, cost and logistics might make
draft=stopping a much more attractive alternative if you had to use
anti-freeze or dry pipe, or if it meant the difference between pump/no
pump.

Steve Leyton
Protection Design  Consulting
San Diego, CA




-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Thom
McMahon
Sent: Monday, February 09, 2009 8:33 AM
To: sprinklerforum@firesprinkler.org
Subject: RE: 13R ATTIC Protection

Actually Areas Outside of the dwelling unit In 13R Refer to Occupied
areas, and do NOT require areas, not otherwise required to be protected
in a
13R system, to be protected. Similarly because you have to protect an
area
per 13 in a 13R building, does NOT require it comply with all of 13,
such as
Hose or concealed combustible space protection.

I understand how in So. Cal, a LH attic is No big Deal that's not
always
the case in the rest of the country, where Dry, Antifreeze or pre-action
systems would be required. We find in cold country that the drywall is
always cheaper, and that doesn't even take into account the cost of
on-going
maint. Testing and inspection of another entire system.

Thom McMahon, SET
Firetech, Inc.
2560 Copper Ridge Dr
P.O. Box 882136
Steamboat Springs, CO 80488
Tel:  970-879-7952
Fax: 970-879-7926


-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Steve
Leyton
Sent: Saturday, February 07, 2009 5:14 PM
To: sprinklerforum@firesprinkler.org
Subject: RE: 13R ATTIC Protection

Haven't seen an unprotected attic with a 13R system absent
draft-stopping
before, but have done at least 3 or 4 projects with 13R
and the attic sprinklered in lieu of draft-stopping.   It's no big deal
- light hazard, same as it ever was.   It's one of those areas outside
the dwelling units that gets protected per 13.

Steve Leyton
Protection Design  Consulting
San Diego, CA




-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Thom
McMahon
Sent: Saturday, February 07, 2009 11:57 AM
To: sprinklerforum@firesprinkler.org
Subject: RE: 13R ATTIC Protection

This is just part of an ongoing discussion with a AHJ for a Hampton INN,
but
how many of you have seen 13R used with no draft stopping of the attics,
or
only every 3000 SF, but the concealed combustible spaces unprotected?

You're talking about Chapter 7, section 717 Draft stopping in IBC
right?
They are installing draft stopping in the attic's, so then a 13R system
is
OK. It's only if you want to eliminate the draft stopping that a
903.3.1.1
(13) system is required(717.4.2 Exception 3) or a 903.3.1.2 (13R) with
concealed combustible spaces protected. (717.4.2 exception 4)

Those of you that work under the IBC may want to get familiar with
section
717 especially if you bid 13R work.

Thom McMahon, SET
Firetech, Inc.
2560 Copper Ridge Dr
P.O. Box 882136
Steamboat Springs, CO 80488
Tel:  970-879-7952
Fax: 970-879-7926




___
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to:
techsupp...@firesprinkler.org

To Unsubscribe, send an email
to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)


__ Information from ESET NOD32 Antivirus, version of virus
signature
database 3836 (20090207) __

The message was checked by ESET NOD32 Antivirus.

http://www.eset.com



__ Information from ESET NOD32 Antivirus, version of virus
signature
database 3836 (20090207) __

The message was checked by ESET NOD32 Antivirus.

http://www.eset.com

___
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to:
techsupp...@firesprinkler.org

To Unsubscribe, send an email
to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)

___
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email

RE: 13R ATTIC Protection

2009-02-07 Thread Thom McMahon
This is just part of an ongoing discussion with a AHJ for a Hampton INN, but
how many of you have seen 13R used with no draft stopping of the attics, or
only every 3000 SF, but the concealed combustible spaces unprotected?

You're talking about Chapter 7, section 717 Draft stopping in IBC right?
They are installing draft stopping in the attic's, so then a 13R system is
OK. It's only if you want to eliminate the draft stopping that a 903.3.1.1
(13) system is required(717.4.2 Exception 3) or a 903.3.1.2 (13R) with
concealed combustible spaces protected. (717.4.2 exception 4)

Those of you that work under the IBC may want to get familiar with section
717 especially if you bid 13R work.

Thom McMahon, SET
Firetech, Inc.
2560 Copper Ridge Dr
P.O. Box 882136
Steamboat Springs, CO 80488
Tel:  970-879-7952
Fax: 970-879-7926




___
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: techsupp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)


RE: 13R ATTIC Protection

2009-02-07 Thread Steve Leyton
Haven't seen an unprotected attic with a 13R system absent
draft-stopping before, but have done at least 3 or 4 projects with 13R
and the attic sprinklered in lieu of draft-stopping.   It's no big deal
- light hazard, same as it ever was.   It's one of those areas outside
the dwelling units that gets protected per 13.

Steve Leyton
Protection Design  Consulting
San Diego, CA




-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Thom
McMahon
Sent: Saturday, February 07, 2009 11:57 AM
To: sprinklerforum@firesprinkler.org
Subject: RE: 13R ATTIC Protection

This is just part of an ongoing discussion with a AHJ for a Hampton INN,
but
how many of you have seen 13R used with no draft stopping of the attics,
or
only every 3000 SF, but the concealed combustible spaces unprotected?

You're talking about Chapter 7, section 717 Draft stopping in IBC
right?
They are installing draft stopping in the attic's, so then a 13R system
is
OK. It's only if you want to eliminate the draft stopping that a
903.3.1.1
(13) system is required(717.4.2 Exception 3) or a 903.3.1.2 (13R) with
concealed combustible spaces protected. (717.4.2 exception 4)

Those of you that work under the IBC may want to get familiar with
section
717 especially if you bid 13R work.

Thom McMahon, SET
Firetech, Inc.
2560 Copper Ridge Dr
P.O. Box 882136
Steamboat Springs, CO 80488
Tel:  970-879-7952
Fax: 970-879-7926




___
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to:
techsupp...@firesprinkler.org

To Unsubscribe, send an email
to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)
 

__ Information from ESET NOD32 Antivirus, version of virus
signature database 3836 (20090207) __

The message was checked by ESET NOD32 Antivirus.

http://www.eset.com
 
 

__ Information from ESET NOD32 Antivirus, version of virus
signature database 3836 (20090207) __

The message was checked by ESET NOD32 Antivirus.

http://www.eset.com
 
___
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: techsupp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)