RE: Attic/Concealed space access to sprinkler heads

2019-08-18 Thread Scott Futrell via Sprinklerforum
See below. Scott Office: (763) 425-1001 x 2 Cell: (612) 759-5556 From: David Williams Sent: Thursday, August 15, 2019 2:39 PM To: Scott Futrell ; sprinklerforum@lists.firesprinkler.org Subject: RE: Attic/Concealed space access to sprinkler heads Language camp facility. Rural area. Installing

RE: Attic/Concealed space access to sprinkler heads

2019-08-15 Thread David Williams via Sprinklerforum
To: sprinklerforum@lists.firesprinkler.org Cc: Ron Greenman Subject: Re: Attic/Concealed space access to sprinkler heads I didn't mean to suggest that you didn't need access to low points. You do, and you need to put the sign on them or next to them, but you also need to note where

Re: Attic/Concealed space access to sprinkler heads

2019-08-15 Thread Bruce Verhei via Sprinklerforum
>> >> LHB, Inc. | PERFORMANCE DRIVEN DESIGN. >> >> >> >> From: Travis Mack >> Sent: Thursday, August 15, 2019 2:40 PM >> To: sprinklerforum@lists.firesprinkler.org >> Cc: b...@firebyknight.com; David Williams >> Subject: Re: Atti

Re: Attic/Concealed space access to sprinkler heads

2019-08-15 Thread Ron Greenman via Sprinklerforum
ngineer* > > > > *LHB, Inc. | PERFORMANCE DRIVEN DESIGN.* > > > > *From:* Travis Mack > *Sent:* Thursday, August 15, 2019 2:40 PM > *To:* sprinklerforum@lists.firesprinkler.org > *Cc:* b...@firebyknight.com; David Williams > *Subject:* Re: Attic/Concealed space a

RE: Attic/Concealed space access to sprinkler heads

2019-08-15 Thread David Williams via Sprinklerforum
.firesprinkler.org> Cc: Bob Knight mailto:b...@firebyknight.com>> Subject: RE: Attic/Concealed space access to sprinkler heads NFPA 25 does not require the inspection of sprinklers in concealed spaces, so that should not be an issue. Thank you, Bob Knight, CET III Fire by Knight, LL

Re: Attic/Concealed space access to sprinkler heads

2019-08-15 Thread Travis Mack via Sprinklerforum
om: Sprinklerforum On > Behalf Of Bob Knight via Sprinklerforum > Sent: Thursday, August 15, 2019 1:59 PM > To: sprinklerforum@lists.firesprinkler.org > Cc: Bob Knight > Subject: RE: Attic/Concealed space access to sprinkler heads > > NFPA 25 does not require the ins

RE: Attic/Concealed space access to sprinkler heads

2019-08-15 Thread David Williams via Sprinklerforum
lliams - Lead MEP/FP Engineer LHB, Inc. | PERFORMANCE DRIVEN DESIGN. From: Scott Futrell Sent: Thursday, August 15, 2019 2:08 PM To: sprinklerforum@lists.firesprinkler.org Cc: David Williams Subject: RE: Attic/Concealed space access to sprinkler heads David, Interesting question. You hav

RE: Attic/Concealed space access to sprinkler heads

2019-08-15 Thread Scott Futrell via Sprinklerforum
David, Interesting question. You haven't provided enough information for a thorough answer. How big of an attic area? So you intend to mark the location of every upright sprinkler in the concealed space on the ceiling below? No one will ever paint that gypsum? Then cut access for NFPA 25

Re: Attic/Concealed space access to sprinkler heads

2019-08-15 Thread Ron Greenman via Sprinklerforum
Do note that NFPA 13 requires that the locations of low point drains be identified on the "General Information Sign" as well as the drain itself. Ron Greenman rongreen...@gmail.com 253.576.9700 The Universe is monstrously indifferent to the presence of man. -Werner Herzog, screenwriter, film

RE: Attic/Concealed space access to sprinkler heads

2019-08-15 Thread David Williams via Sprinklerforum
@lists.firesprinkler.org Cc: Bob Knight Subject: RE: Attic/Concealed space access to sprinkler heads NFPA 25 does not require the inspection of sprinklers in concealed spaces, so that should not be an issue. Thank you, Bob Knight, CET III Fire by Knight, LLC 208-318-3057 From: Sprinklerforum

RE: Attic/Concealed space access to sprinkler heads

2019-08-15 Thread Bob Knight via Sprinklerforum
NFPA 25 does not require the inspection of sprinklers in concealed spaces, so that should not be an issue. Thank you, Bob Knight, CET III Fire by Knight, LLC 208-318-3057 From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of David Williams via