RE: Back Up Fire Pump

2021-09-14 Thread BRUCE VERHEI via Sprinklerforum
Apologies. I meant to note that theses were originally my comments. bv > On 09/14/2021 2:27 PM BRUCE VERHEI via Sprinklerforum > wrote: > > > This is cut and past of partial comments from discussion on another forum, > originating from an NFSA post. > > What is missing from this excerpt is

RE: Back Up Fire Pump

2021-09-14 Thread BRUCE VERHEI via Sprinklerforum
This is cut and past of partial comments from discussion on another forum, originating from an NFSA post. What is missing from this excerpt is pressure rating of the hose. At acceptance and annually FD’s test hose at 250 psi. You are quickly going to lose persuasion ability with your fire plan

RE: Back Up Fire Pump

2021-09-14 Thread John Irwin via Sprinklerforum
otten." - Benjamin Franklin -Original Message- From: Steve Leyton Sent: Tuesday, September 14, 2021 12:24 PM To: sprinklerforum@lists.firesprinkler.org Cc: John Irwin Subject: RE: Back Up Fire Pump By my reckoning, you need about 300 PSI at the ground level to pump 100 PSI to the ro

RE: Back Up Fire Pump

2021-09-14 Thread Steve Leyton via Sprinklerforum
By my reckoning, you need about 300 PSI at the ground level to pump 100 PSI to the roof of what I'll call a 385' tall standpipe system (35x11). Bottom line: Can the responding FD pump 750 or 1,000 GPM at 300 psi? Most muni departments can, but that might be at the limit of what they can

RE: Back Up Fire Pump

2021-09-14 Thread Matt Grise via Sprinklerforum
@lists.firesprinkler.org Cc: Spencer Tomlinson ; John Irwin Subject: RE: Back Up Fire Pump Might come from the requirements of IFC Section 914, etcpending height. Just another place to look anyway. Spencer Tomlinson, PE Owner, Fire Protection Engineer Ph:  316-202-6412 Fax: 316-202-2346 Cell: 620-955-7293

RE: Back Up Fire Pump

2021-09-14 Thread Spencer Tomlinson via Sprinklerforum
Might come from the requirements of IFC Section 914, etcpending height. Just another place to look anyway. Spencer Tomlinson, PE Owner, Fire Protection Engineer Ph:  316-202-6412 Fax: 316-202-2346 Cell: 620-955-7293 -Original Message- From: Sprinklerforum On Behalf Of John