I'd agree.
Maybe this strategy would work; a veteran FM field engineer looking at a round
duct and the possible need for dropping a sprinkler under it:
Is the building going to burn down because of it, or the lack of it?
Since this particular duct was a short run above a corridor between Truckers
Tough to make the min 18 clearance to storage as well
At 10:11 AM 6/22/2012, you wrote:
I'd agree.
Maybe this strategy would work; a veteran FM field engineer looking at a round
duct and the possible need for dropping a sprinkler under it:
Is the building going to burn down because of it, or
: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of George Church
Sent: Friday, June 22, 2012 7:11 AM
To: sprinklerforum@firesprinkler.org
Subject: RE: Heads Under Duct
I'd agree.
Maybe this strategy would work; a veteran FM field engineer looking
: RE: Heads Under Duct
I'd agree.
Maybe this strategy would work; a veteran FM field engineer looking at a round
duct and the possible need for dropping a sprinkler under it:
Is the building going to burn down because of it, or the lack of it?
Since this particular duct was a short run above
-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Todd Williams
Sent: Friday, June 22, 2012 7:32 AM
To: sprinklerforum@firesprinkler.org
Subject: RE: Heads Under Duct
Only if they are over 48 wide. Same
Yes, they are. Two-sided open top containers: inside and outside.
Have a nice weekend!
Frans Stoop
At 14:46 22-6-2012 +, you wrote:
So ducts over 48 wide could not be stored in multiple row racks
with the duct running from front to back of the rack?
What about ducts stored standing on
Strictly speaking it is, although you could have ten of these with a one
inch gap between each and not need to if the widest width were 47.
On Tue, Jun 19, 2012 at 5:13 AM, Brian Harris bhar...@bvssystemsinc.comwrote:
I have an engineer requesting I put a head under a reducer that is located
-boun...@firesprinkler.org] On Behalf Of Ron Greenman
Sent: Tuesday, June 19, 2012 10:44 AM
To: sprinklerforum@firesprinkler.org
Subject: Re: Heads Under Duct
Strictly speaking it is, although you could have ten of these with a one inch
gap between each and not need to if the widest width were 47
...@ch2m.com
Sent: Tuesday, June 19, 2012 10:56 AM
To: sprinklerforum@firesprinkler.org
Subject: RE: Heads Under Duct
You didn't state the length of this 48x32 reducer.
But if providing a sprinkler below creates an issue, ask for the HVAC
contractor to just flash from the duct to the floor so
, CET
BVS Systems Inc.
bvssytemsinc.com
-Original Message-
From: sprinklerforum-boun...@firesprinkler.org [mailto:
sprinklerforum-boun...@firesprinkler.org] On Behalf Of
craig.pr...@ch2m.com
Sent: Tuesday, June 19, 2012 10:56 AM
To: sprinklerforum@firesprinkler.org
Subject: RE: Heads