RE: NYC Standpipe

2017-10-24 Thread Mike Stossel
uesday, October 24, 2017 5:42 PM To: sprinklerforum@lists.firesprinkler.org Subject: Re: NYC Standpipe Mike, Using the 4” on the lower height areas is correct. I have done this in the past without issue from the FDNY or NYC DOB. Regards, Wayne T. Cordiner, Jr. 917-426-5844 fpdrawi...@gmail.com<mailt

Re: NYC Standpipe

2017-10-24 Thread Wayne Cordiner
Mike, Using the 4” on the lower height areas is correct. I have done this in the past without issue from the FDNY or NYC DOB. Regards, Wayne T. Cordiner, Jr. 917-426-5844 fpdrawi...@gmail.com > On Oct 24, 2017, at 17:09, Kyle.Montgomery wrote: > > I would think

RE: NYC Standpipe

2017-10-24 Thread Kyle . Montgomery
I would think 4" would be allowable for the shorter standpipes, but I've never worked in NYC so my thoughts probably aren't worth much. You are going to run calcs to prove that 4" would work hydraulically, right? Kyle Montgomery [cid:image001.gif@01CAA0CE.8D8066F0] Aero Automatic Sprinkler Co.

RE: NYC Standpipe

2017-10-24 Thread Tom Duross
I would think the height would state size so 4" and 6". I do believe NYFD has their own FDV flow requirements, 230 gpm at 80 psi (if I remember right). TD From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of Mike Stossel Sent: Tuesday, October 24, 2017