Re: Stainless Steel pipe in sprinkler systems

2015-04-07 Thread bverhei
Did they say which stainless would be compatible? 304, 316, ... Bruce - Original Message - From: Mike Morey mo...@bmwc.com To: sprinklerforum@lists.firesprinkler.org Sent: Thursday, April 2, 2015 6:59:20 AM Subject: Stainless Steel pipe in sprinkler systems I'm sure this has

RE: Stainless Steel pipe in sprinkler systems

2015-04-03 Thread Thomas Watt
Why not grooved? Victaulic has SS couplings and mechanical tees. Just a thought... ___ Sprinklerforum mailing list Sprinklerforum@lists.firesprinkler.org http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

RE: Stainless Steel pipe in sprinkler systems

2015-04-02 Thread Art Tiroly
The problem may be joining pipe and outlets. What about copper? Art Tiroly ATCO Fire Protection/Tiroly 24400 Highland Rd CLE 44143 216-621-8899 216-570-7030 cell -Original Message- From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of Morey, Mike

Re: Stainless Steel pipe in sprinkler systems

2015-04-02 Thread Morey, Mike
...@lists.firesprinkler.org on behalf of Art Tiroly atir...@atcofirepro.com Sent: Thursday, April 02, 2015 11:53 AM To: sprinklerforum@lists.firesprinkler.org Subject: RE: Stainless Steel pipe in sprinkler systems The problem may be joining pipe and outlets. What about copper? Art Tiroly ATCO Fire

RE: Stainless Steel pipe in sprinkler systems

2015-04-02 Thread John Denhardt
Viking makes Stainless steel sprinklers. -Original Message- From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of Morey, Mike Sent: Thursday, April 02, 2015 1:39 PM To: sprinklerforum@lists.firesprinkler.org Subject: Re: Stainless Steel pipe

RE: stainless steel pipe fittings

2014-03-12 Thread Craig.Prahl
Yes there is SS pipe and fittings. The rod requirement is typical in Clean areas and food processing/handling areas to prevent accumulation of contaminants in the threads. This very common in cGMP environments having to comply with USDA and FDA requirements. You may also need SS sprinklers

RE: Stainless Steel Pipe

2012-10-29 Thread Dewayne Martinez
...@firesprinkler.org [mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Brad Casterline Sent: Friday, October 26, 2012 1:18 PM To: sprinklerforum@firesprinkler.org Subject: RE: Stainless Steel Pipe I know George, and it is not illegal! Several years ago I tried to reason out why the Corp

RE: Stainless Steel Pipe

2012-10-29 Thread George Church
: RE: Stainless Steel Pipe Brad, Could their reasoning be because with cut groove there isn't a bump in the pipe to potentially trap the small amount of water? I could see where they might think this would become a potential weak point corrosion issue later on. -Original Message- From

RE: Stainless Steel Pipe

2012-10-29 Thread Brad Casterline
@firesprinkler.org Subject: RE: Stainless Steel Pipe What the other Sornsin brother called mini-dams a decade ago on this Forum. Being from Fargo, ND, and growing up the son of a sprinkler contractor, I'll assume he understands a bit about dry systems. George L. Church, Jr., CET   Rowe Sprinkler Systems

Re: Stainless Steel Pipe

2012-10-26 Thread MPhelps
Yes Mark at Aero - Original Message - From: Brad Casterline [mailto:bcasterl...@fsc-inc.com] Sent: Friday, October 26, 2012 03:51 PM To: sprinklerforum@firesprinkler.org sprinklerforum@firesprinkler.org Subject: Stainless Steel Pipe Can S.S. pipe be grooved? 2, 2.5, 3, for foam

RE: Stainless Steel Pipe

2012-10-26 Thread Brad Casterline
Thanks Mark. Assuming stainless is like galvanized, it should be Cut Grooved only? -Original Message- From: mphe...@aerofire.com [mailto:mphe...@aerofire.com] Sent: Friday, October 26, 2012 11:00 AM To: sprinklerforum@firesprinkler.org Subject: Re: Stainless Steel Pipe Yes Mark at Aero

Re: Stainless Steel Pipe

2012-10-26 Thread MPhelps
@firesprinkler.org sprinklerforum@firesprinkler.org Subject: RE: Stainless Steel Pipe Thanks Mark. Assuming stainless is like galvanized, it should be Cut Grooved only? -Original Message- From: mphe...@aerofire.com [mailto:mphe...@aerofire.com] Sent: Friday, October 26, 2012 11:00 AM

RE: Stainless Steel Pipe

2012-10-26 Thread Brad Casterline
To: sprinklerforum@firesprinkler.org sprinklerforum@firesprinkler.org Subject: RE: Stainless Steel Pipe Thanks Mark. Assuming stainless is like galvanized, it should be Cut Grooved only? -Original Message- From: mphe...@aerofire.com [mailto:mphe...@aerofire.com] Sent: Friday, October 26, 2012 11:00 AM

RE: Stainless Steel Pipe

2012-10-26 Thread George Church
...@rowesprinkler.com -Original Message- From: sprinklerforum-boun...@firesprinkler.org [mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Brad Casterline Sent: Friday, October 26, 2012 1:20 PM To: sprinklerforum@firesprinkler.org Subject: RE: Stainless Steel Pipe Great

RE: Stainless Steel Pipe

2012-10-26 Thread Brad Casterline
Message- From: George Church [mailto:g...@rowesprinkler.com] Sent: Friday, October 26, 2012 1:07 PM To: sprinklerforum@firesprinkler.org Subject: RE: Stainless Steel Pipe There's a heckuva lot of roll grooved galv S10 installed in sprinkler systems. We have 7 miles of it in one freezer that comes