@firesprinkler.org
Subject: Re: Stupid closet question...
Of course, I was only speaking of adopted codes. I'm not familiar with
all of the various code sets available for a jurisdiction to consider;
however, the prevalent code set in Texas is IFC. IFC references NFPA 13 and
13R specifically for its
@firesprinkler.org
Sent: Friday, October 05, 2012 8:24 AM
Subject: RE: Stupid closet question...
Based on NFPA 13, 2010 edition and NFPA 101, 2009 edition.
Annex D is not part of the enforceable section of NFPA 13, unless a
jurisdiction specifically adopts it (see section heading). In this case,
Annex D
cleaner
in...[chuckles under breath].
- Original Message - From: Johnson, Duane (NIH/OD/ORS) [C]
johnson...@mail.nih.gov
To: sprinklerforum@firesprinkler.**org sprinklerforum@firesprinkler.org
Sent: Friday, October 05, 2012 8:24 AM
Subject: RE: Stupid closet question...
Based
: Friday, October 05, 2012 7:25 AM
To: sprinklerforum@firesprinkler.org
Subject: RE: Stupid closet question...
Based on NFPA 13, 2010 edition and NFPA 101, 2009 edition.
Annex D is not part of the enforceable section of NFPA 13, unless a
jurisdiction specifically adopts it (see section heading
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Rod DiBona
Sent: Friday, October 05, 2012 12:04 PM
To: sprinklerforum@firesprinkler.org
Subject: RE: Stupid closet question...
Duane,
Thanks for the excellent analysis and clear delineation of the small yet
significant differences
: Friday, October 05, 2012 10:35 AM
To: sprinklerforum@firesprinkler.org
Subject: Re: Stupid closet question...
Excellent code analysis/decision tree formation Duane. And I still think we
need to work hard to put this idea of code versus standard, where the one
trumps the other because of a word
-
From: Ron Greenman rongreen...@gmail.com
To: sprinklerforum@firesprinkler.org
Sent: Thursday, September 27, 2012 6:26 PM
Subject: Re: Stupid closet question...
This is the conventional wisdom Curtis but I disagree. All model codes and
standards are simply books until adopted, no matter
I take this one step further. If 101 is adopted, it boils down to
which code requires the protection. If both, the most restrictive
applies. If the building code does not require protection but 101
does, then 101 is the driving code and their exception applies. If
neither require
I believe that the root of the confusion stems from semantics. NFPA 101 is
referred to as a code, where NFPA 13, 13R, etc., is referred to as a
standard. Many times, I have heard those of us in the business use the term
'code' interchangeably with the term 'standard'. This is technically
This is the conventional wisdom Curtis but I disagree. All model codes and
standards are simply books until adopted, no matter what they are called.
I'll use Washington as an example: The Revised Code of Washington (RCW)
stipulates there will be a building code. The Building Code itself derives
Does your state or jurisdiction formally adopt 101? (Most don't.). If 101
is equal to or supersedes the building code, you may be able to take it,
but remember that it's Annex material. Most AHJ's see it as code says to
sprinkler per 13, 13 says to sprinkler it, so sprinkler it.
Steve
CH Fire -
.
-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Steve
Leyton
Sent: Wednesday, September 26, 2012 4:35 PM
To: sprinklerforum@firesprinkler.org
Subject: Re: Stupid closet question...
Does your state or jurisdiction
: Stupid closet question...
Does your state or jurisdiction formally adopt 101? (Most don't.). If 101 is
equal to or supersedes the building code, you may be able to take it, but
remember that it's Annex material. Most AHJ's see it as code says to sprinkler
per 13, 13 says to sprinkler it, so
13 matches