Matt,
I don't know about the 2009 version of the IFC, but 2006, 903.4 requires
water-flow switch supervision, which I interpret to include the 1/2 alarm
line valve. I learned my lesson the hard way on this many years ago when I
got called on it by a fire marshal.
Jim
James L (Jim) Roberts,
Of
jim.robe...@fluor.com
Sent: Monday, December 06, 2010 10:18 AM
To: sprinklerforum@firesprinkler.org
Subject: Re: Tamper/Supervision of Alarm Line Valve
Matt,
I don't know about the 2009 version of the IFC, but 2006, 903.4 requires
water-flow switch supervision, which I interpret to include the 1/2
-
From: sprinklerforum-boun...@firesprinkler.org [mailto:sprinklerforum-
boun...@firesprinkler.org] On Behalf Of Pielow, Robert
Sent: Monday, December 06, 2010 10:47 AM
To: sprinklerforum@firesprinkler.org
Subject: RE: Tamper/Supervision of Alarm Line Valve
Read the exceptions to IFC
@firesprinkler.org
Subject: RE: Tamper/Supervision of Alarm Line Valve
Thanks folks.
Must have been in IFC that I saw it. I can find nothing corresponding in 1
or 101.
R/
Matt
Matthew J. Willis, CET
Automatic Fire Sprinklers
Norred Fire Systems L.L.C.
318-387-1134 Voice
318-816-1087 Mobile
318
: RE: Tamper/Supervision of Alarm Line Valve
Read the exceptions to IFC Section 903.4. You would normally lock or seal the
1/2 trim valves and not provide electronic supervision.
RJ Pielow, P.E.
-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum
, December 06, 2010 1:10 PM
To: sprinklerforum@firesprinkler.org
Subject: RE: Tamper/Supervision of Alarm Line Valve
I believe the locking exception in IFC IBC only applies to Dry,
Preaction Deluge systems. Wet systems still require electrical
supervision according to IFC IBC.
Exception:
Trim
: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Matthew J. Willis
Sent: Monday, December 06, 2010 2:24 PM
To: sprinklerforum@firesprinkler.org
Subject: RE: Tamper/Supervision of Alarm Line Valve
Thanks all. Maybe I wasn't completely crazy
[mailto:sprinklerforum-
boun...@firesprinkler.org] On Behalf Of craig.pr...@ch2m.com
Sent: Monday, December 06, 2010 1:45 PM
To: sprinklerforum@firesprinkler.org
Subject: RE: Tamper/Supervision of Alarm Line Valve
Was there no water flow switch on the system riser?
Craig L. Prahl, CET
Fire
-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Matthew J. Willis
Sent: Monday, December 06, 2010 2:47 PM
To: sprinklerforum@firesprinkler.org
Subject: RE: Tamper/Supervision of Alarm Line Valve
Yes, and it was isolated by the valve
...@firesprinkler.org] On Behalf Of
craig.pr...@ch2m.com
Sent: Monday, December 06, 2010 2:56 PM
To: sprinklerforum@firesprinkler.org
Subject: RE: Tamper/Supervision of Alarm Line Valve
So it wasn't directly on the riser it was on the trim piping.
Craig L. Prahl, CET
Fire Protection
CH2MHILL
Lockwood