RE: Townhome - Common Areas

2021-01-27 Thread Steve Leyton via Sprinklerforum
If there are common areas then there's an HOA, right?   At least there would 
have to be in CA due to state Dept. of Real Estate reg's.Perhaps not in the 
sales contract, but possibly in the CC for the HOA?

SL

-Original Message-
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of Ron Greenman via Sprinklerforum
Sent: Wednesday, January 27, 2021 1:44 PM
To: sprinklerforum@lists.firesprinkler.org
Cc: Ron Greenman 
Subject: Re: Townhome - Common Areas

A clause in the sales contract that that owner of the adjacent unit is 
responsible, or that all owners that use that common area are equally 
responsible as in the maintenance assessments associated with HOAs. This is my 
opinion for a solution way out of the purview of the sprinkler contractor, and 
not being a lawyer I may be suggesting something that can't be done in a 
contract, but just a thought for legally assigning responsibility that could be 
explored.

On Wed, Jan 27, 2021 at 10:41 AM Steve Leyton via Sprinklerforum < 
sprinklerforum@lists.firesprinkler.org> wrote:

> I get it, but the "fee simple unit" extends beyond the fee simple unit 
> so...
>
> SL
>
> -Original Message-
> From: John Irwin [mailto:jir...@quickresponsefl.com]
> Sent: Wednesday, January 27, 2021 10:33 AM
> To: Steve Leyton ; Kyle.Montgomery < 
> kmontgom...@aerofire.com>; sprinklerforum@lists.firesprinkler.org
> Subject: RE: Townhome - Common Areas
>
> And if some random person breaks a sprinkler inside the mail room, 
> who's responsible for the repair? This is my issue with having 
> sprinklers outside the fee simple unit.
>
> John Irwin
> Director of Construction
> Quick Response Fire Protection
> Cell: 727-282-9243
>
>
> "The bitterness of poor quality remains long after the sweetness of 
> low price is forgotten." - Benjamin Franklin
>
> -Original Message-
> From: Steve Leyton 
> Sent: Wednesday, January 27, 2021 1:31 PM
> To: Kyle.Montgomery ; 
> sprinklerforum@lists.firesprinkler.org
> Cc: John Irwin 
> Subject: RE: Townhome - Common Areas
>
> Yes.  You have living space associated with a particular unit over the 
> subject utility occupancy, so I would protect it with the system from 
> that particular unit.
>
> Steve L.
>
> -Original Message-
> From: Kyle.Montgomery [mailto:kmontgom...@aerofire.com]
> Sent: Wednesday, January 27, 2021 9:26 AM
> To: sprinklerforum@lists.firesprinkler.org
> Cc: Steve Leyton ; John Irwin < 
> jir...@quickresponsefl.com>
> Subject: RE: Townhome - Common Areas
>
> Are you saying to just extend the system from the adjacent home into 
> that area to protect it? As opposed to providing another lead-in? Is 
> that an option?
>
> -Kyle M
>
> -Original Message-
> From: Sprinklerforum  
> On Behalf Of Steve Leyton via Sprinklerforum
> Sent: Wednesday, January 27, 2021 8:45 AM
> To: sprinklerforum@lists.firesprinkler.org
> Cc: Steve Leyton ; John Irwin < 
> jir...@quickresponsefl.com>
> Subject: [EXTERNAL] RE: Townhome - Common Areas
>
> That last part made it easy for me to firm a quick opinion. If you 
> have living space over a utility space like a garage or trash 
> enclosure, I would say that accessory structure becomes a part of the 
> dwelling unit associated
> with that terrace or patio space.   Protect the trash enclosure as you
> would a garage. If you are in a state or jurisdiction that doesn't 
> require protection of garages per the exception in13D, then protect as 
> for a garage in 13R.
>
>
> Steve Leyton
>
> (Sent from my smartphone; please excuse typos and voice-to-text
> corruptions.)
>
>
>
>  Original message 
> From: John Irwin via Sprinklerforum <
> sprinklerforum@lists.firesprinkler.org>
> Date: 1/27/21 6:48 AM (GMT-08:00)
> To: sprinklerforum@lists.firesprinkler.org
> Cc: John Irwin 
> Subject: Townhome - Common Areas
>
> We're protecting (4) rows of townhomes per NFPA 13D. Between buildings 
> are small common areas such as trash storage (132sqft) and mail room 
> (260sqft).  Providing protection in these rooms would come at an 
> additional expense because the units being protected are fee simple 
> and each has it's own lead-in. Adding sprinklers to these small common 
> rooms would require additional lead ins, meters, light hazard and 
> combustible concealed protection. Do these rooms need to be protected?
>
> As an added twist, the townhomes that immediately abut these rooms 
> have exterior terraces on the ROOFs of these rooms. Is this a factor?
>
>
>
> John Irwin
> Quick Response Fire Protection
>
>
> "The bitterness of poor quality 

Re: Townhome - Common Areas

2021-01-27 Thread Ron Greenman via Sprinklerforum
A clause in the sales contract that that owner of the adjacent unit is
responsible, or that all owners that use that common area are equally
responsible as in the maintenance assessments associated with HOAs. This is
my opinion for a solution way out of the purview of the sprinkler
contractor, and not being a lawyer I may be suggesting something that can't
be done in a contract, but just a thought for legally
assigning responsibility that could be explored.

On Wed, Jan 27, 2021 at 10:41 AM Steve Leyton via Sprinklerforum <
sprinklerforum@lists.firesprinkler.org> wrote:

> I get it, but the "fee simple unit" extends beyond the fee simple unit
> so...
>
> SL
>
> -Original Message-
> From: John Irwin [mailto:jir...@quickresponsefl.com]
> Sent: Wednesday, January 27, 2021 10:33 AM
> To: Steve Leyton ; Kyle.Montgomery <
> kmontgom...@aerofire.com>; sprinklerforum@lists.firesprinkler.org
> Subject: RE: Townhome - Common Areas
>
> And if some random person breaks a sprinkler inside the mail room, who's
> responsible for the repair? This is my issue with having sprinklers outside
> the fee simple unit.
>
> John Irwin
> Director of Construction
> Quick Response Fire Protection
> Cell: 727-282-9243
>
>
> "The bitterness of poor quality remains long after the sweetness of low
> price is forgotten." - Benjamin Franklin
>
> -Original Message-
> From: Steve Leyton 
> Sent: Wednesday, January 27, 2021 1:31 PM
> To: Kyle.Montgomery ;
> sprinklerforum@lists.firesprinkler.org
> Cc: John Irwin 
> Subject: RE: Townhome - Common Areas
>
> Yes.  You have living space associated with a particular unit over the
> subject utility occupancy, so I would protect it with the system from that
> particular unit.
>
> Steve L.
>
> -Original Message-
> From: Kyle.Montgomery [mailto:kmontgom...@aerofire.com]
> Sent: Wednesday, January 27, 2021 9:26 AM
> To: sprinklerforum@lists.firesprinkler.org
> Cc: Steve Leyton ; John Irwin <
> jir...@quickresponsefl.com>
> Subject: RE: Townhome - Common Areas
>
> Are you saying to just extend the system from the adjacent home into that
> area to protect it? As opposed to providing another lead-in? Is that an
> option?
>
> -Kyle M
>
> -Original Message-
> From: Sprinklerforum  On
> Behalf Of Steve Leyton via Sprinklerforum
> Sent: Wednesday, January 27, 2021 8:45 AM
> To: sprinklerforum@lists.firesprinkler.org
> Cc: Steve Leyton ; John Irwin <
> jir...@quickresponsefl.com>
> Subject: [EXTERNAL] RE: Townhome - Common Areas
>
> That last part made it easy for me to firm a quick opinion. If you have
> living space over a utility space like a garage or trash enclosure, I would
> say that accessory structure becomes a part of the dwelling unit associated
> with that terrace or patio space.   Protect the trash enclosure as you
> would a garage. If you are in a state or jurisdiction that doesn't require
> protection of garages per the exception in13D, then protect as for a garage
> in 13R.
>
>
> Steve Leyton
>
> (Sent from my smartphone; please excuse typos and voice-to-text
> corruptions.)
>
>
>
>  Original message 
> From: John Irwin via Sprinklerforum <
> sprinklerforum@lists.firesprinkler.org>
> Date: 1/27/21 6:48 AM (GMT-08:00)
> To: sprinklerforum@lists.firesprinkler.org
> Cc: John Irwin 
> Subject: Townhome - Common Areas
>
> We're protecting (4) rows of townhomes per NFPA 13D. Between buildings are
> small common areas such as trash storage (132sqft) and mail room
> (260sqft).  Providing protection in these rooms would come at an additional
> expense because the units being protected are fee simple and each has it's
> own lead-in. Adding sprinklers to these small common rooms would require
> additional lead ins, meters, light hazard and combustible concealed
> protection. Do these rooms need to be protected?
>
> As an added twist, the townhomes that immediately abut these rooms have
> exterior terraces on the ROOFs of these rooms. Is this a factor?
>
>
>
> John Irwin
> Quick Response Fire Protection
>
>
> "The bitterness of poor quality remains long after the sweetness of low
> price is forgotten." - Benjamin Franklin
>
> ___
> Sprinklerforum mailing list
> Sprinklerforum@lists.firesprinkler.org
>
> https://urldefense.proofpoint.com/v2/url?u=http-3A__lists.firesprinkler.org_listinfo.cgi_sprinklerforum-2Dfiresprinkler.org=DwICAg=wn3mZQLIuInh2ClcJ0_DIA=Z_2A85VL7AQzoqudh6uOyS3bn8etxB7nLN8OBJwQd9A=faLC6Gr2aXcLulFYub3ZQSbhFvUDwniBMdSL2deInFQ=HfI4Lqejjh6B80Gz6TCV8T5UsQAvWcPuFsupz6bJO14=
> 

RE: Townhome - Common Areas

2021-01-27 Thread Steve Leyton via Sprinklerforum
I get it, but the "fee simple unit" extends beyond the fee simple unit so...

SL

-Original Message-
From: John Irwin [mailto:jir...@quickresponsefl.com] 
Sent: Wednesday, January 27, 2021 10:33 AM
To: Steve Leyton ; Kyle.Montgomery 
; sprinklerforum@lists.firesprinkler.org
Subject: RE: Townhome - Common Areas

And if some random person breaks a sprinkler inside the mail room, who's 
responsible for the repair? This is my issue with having sprinklers outside the 
fee simple unit.

John Irwin
Director of Construction
Quick Response Fire Protection
Cell: 727-282-9243


"The bitterness of poor quality remains long after the sweetness of low price 
is forgotten." - Benjamin Franklin

-Original Message-
From: Steve Leyton  
Sent: Wednesday, January 27, 2021 1:31 PM
To: Kyle.Montgomery ; 
sprinklerforum@lists.firesprinkler.org
Cc: John Irwin 
Subject: RE: Townhome - Common Areas

Yes.  You have living space associated with a particular unit over the subject 
utility occupancy, so I would protect it with the system from that particular 
unit.

Steve L.

-Original Message-
From: Kyle.Montgomery [mailto:kmontgom...@aerofire.com] 
Sent: Wednesday, January 27, 2021 9:26 AM
To: sprinklerforum@lists.firesprinkler.org
Cc: Steve Leyton ; John Irwin 

Subject: RE: Townhome - Common Areas

Are you saying to just extend the system from the adjacent home into that area 
to protect it? As opposed to providing another lead-in? Is that an option?

-Kyle M

-Original Message-
From: Sprinklerforum  On Behalf 
Of Steve Leyton via Sprinklerforum
Sent: Wednesday, January 27, 2021 8:45 AM
To: sprinklerforum@lists.firesprinkler.org
Cc: Steve Leyton ; John Irwin 

Subject: [EXTERNAL] RE: Townhome - Common Areas

That last part made it easy for me to firm a quick opinion. If you have living 
space over a utility space like a garage or trash enclosure, I would say that 
accessory structure becomes a part of the dwelling unit associated with that 
terrace or patio space.   Protect the trash enclosure as you would a garage. If 
you are in a state or jurisdiction that doesn't require protection of garages 
per the exception in13D, then protect as for a garage in 13R.


Steve Leyton

(Sent from my smartphone; please excuse typos and voice-to-text corruptions.)



 Original message 
From: John Irwin via Sprinklerforum 
Date: 1/27/21 6:48 AM (GMT-08:00)
To: sprinklerforum@lists.firesprinkler.org
Cc: John Irwin 
Subject: Townhome - Common Areas

We're protecting (4) rows of townhomes per NFPA 13D. Between buildings are 
small common areas such as trash storage (132sqft) and mail room (260sqft).  
Providing protection in these rooms would come at an additional expense because 
the units being protected are fee simple and each has it's own lead-in. Adding 
sprinklers to these small common rooms would require additional lead ins, 
meters, light hazard and combustible concealed protection. Do these rooms need 
to be protected?

As an added twist, the townhomes that immediately abut these rooms have 
exterior terraces on the ROOFs of these rooms. Is this a factor?



John Irwin
Quick Response Fire Protection


"The bitterness of poor quality remains long after the sweetness of low price 
is forgotten." - Benjamin Franklin

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
https://urldefense.proofpoint.com/v2/url?u=http-3A__lists.firesprinkler.org_listinfo.cgi_sprinklerforum-2Dfiresprinkler.org=DwICAg=wn3mZQLIuInh2ClcJ0_DIA=Z_2A85VL7AQzoqudh6uOyS3bn8etxB7nLN8OBJwQd9A=faLC6Gr2aXcLulFYub3ZQSbhFvUDwniBMdSL2deInFQ=HfI4Lqejjh6B80Gz6TCV8T5UsQAvWcPuFsupz6bJO14=
 
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
https://urldefense.proofpoint.com/v2/url?u=http-3A__lists.firesprinkler.org_listinfo.cgi_sprinklerforum-2Dfiresprinkler.org=DwICAg=wn3mZQLIuInh2ClcJ0_DIA=Z_2A85VL7AQzoqudh6uOyS3bn8etxB7nLN8OBJwQd9A=faLC6Gr2aXcLulFYub3ZQSbhFvUDwniBMdSL2deInFQ=HfI4Lqejjh6B80Gz6TCV8T5UsQAvWcPuFsupz6bJO14=
 
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: Townhome - Common Areas

2021-01-27 Thread Steve Leyton via Sprinklerforum
Yes.  You have living space associated with a particular unit over the subject 
utility occupancy, so I would protect it with the system from that particular 
unit.

Steve L.

-Original Message-
From: Kyle.Montgomery [mailto:kmontgom...@aerofire.com] 
Sent: Wednesday, January 27, 2021 9:26 AM
To: sprinklerforum@lists.firesprinkler.org
Cc: Steve Leyton ; John Irwin 

Subject: RE: Townhome - Common Areas

Are you saying to just extend the system from the adjacent home into that area 
to protect it? As opposed to providing another lead-in? Is that an option?

-Kyle M

-Original Message-
From: Sprinklerforum  On Behalf 
Of Steve Leyton via Sprinklerforum
Sent: Wednesday, January 27, 2021 8:45 AM
To: sprinklerforum@lists.firesprinkler.org
Cc: Steve Leyton ; John Irwin 

Subject: [EXTERNAL] RE: Townhome - Common Areas

That last part made it easy for me to firm a quick opinion. If you have living 
space over a utility space like a garage or trash enclosure, I would say that 
accessory structure becomes a part of the dwelling unit associated with that 
terrace or patio space.   Protect the trash enclosure as you would a garage. If 
you are in a state or jurisdiction that doesn't require protection of garages 
per the exception in13D, then protect as for a garage in 13R.


Steve Leyton

(Sent from my smartphone; please excuse typos and voice-to-text corruptions.)



 Original message 
From: John Irwin via Sprinklerforum 
Date: 1/27/21 6:48 AM (GMT-08:00)
To: sprinklerforum@lists.firesprinkler.org
Cc: John Irwin 
Subject: Townhome - Common Areas

We're protecting (4) rows of townhomes per NFPA 13D. Between buildings are 
small common areas such as trash storage (132sqft) and mail room (260sqft).  
Providing protection in these rooms would come at an additional expense because 
the units being protected are fee simple and each has it's own lead-in. Adding 
sprinklers to these small common rooms would require additional lead ins, 
meters, light hazard and combustible concealed protection. Do these rooms need 
to be protected?

As an added twist, the townhomes that immediately abut these rooms have 
exterior terraces on the ROOFs of these rooms. Is this a factor?



John Irwin
Quick Response Fire Protection


"The bitterness of poor quality remains long after the sweetness of low price 
is forgotten." - Benjamin Franklin

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
https://urldefense.proofpoint.com/v2/url?u=http-3A__lists.firesprinkler.org_listinfo.cgi_sprinklerforum-2Dfiresprinkler.org=DwICAg=wn3mZQLIuInh2ClcJ0_DIA=Z_2A85VL7AQzoqudh6uOyS3bn8etxB7nLN8OBJwQd9A=faLC6Gr2aXcLulFYub3ZQSbhFvUDwniBMdSL2deInFQ=HfI4Lqejjh6B80Gz6TCV8T5UsQAvWcPuFsupz6bJO14=
 
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
https://urldefense.proofpoint.com/v2/url?u=http-3A__lists.firesprinkler.org_listinfo.cgi_sprinklerforum-2Dfiresprinkler.org=DwICAg=wn3mZQLIuInh2ClcJ0_DIA=Z_2A85VL7AQzoqudh6uOyS3bn8etxB7nLN8OBJwQd9A=faLC6Gr2aXcLulFYub3ZQSbhFvUDwniBMdSL2deInFQ=HfI4Lqejjh6B80Gz6TCV8T5UsQAvWcPuFsupz6bJO14=
 
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: Townhome - Common Areas

2021-01-27 Thread Kyle.Montgomery via Sprinklerforum
Are you saying to just extend the system from the adjacent home into that area 
to protect it? As opposed to providing another lead-in? Is that an option?

-Kyle M

-Original Message-
From: Sprinklerforum  On Behalf 
Of Steve Leyton via Sprinklerforum
Sent: Wednesday, January 27, 2021 8:45 AM
To: sprinklerforum@lists.firesprinkler.org
Cc: Steve Leyton ; John Irwin 

Subject: [EXTERNAL] RE: Townhome - Common Areas

That last part made it easy for me to firm a quick opinion. If you have living 
space over a utility space like a garage or trash enclosure, I would say that 
accessory structure becomes a part of the dwelling unit associated with that 
terrace or patio space.   Protect the trash enclosure as you would a garage. If 
you are in a state or jurisdiction that doesn't require protection of garages 
per the exception in13D, then protect as for a garage in 13R.


Steve Leyton

(Sent from my smartphone; please excuse typos and voice-to-text corruptions.)



 Original message 
From: John Irwin via Sprinklerforum 
Date: 1/27/21 6:48 AM (GMT-08:00)
To: sprinklerforum@lists.firesprinkler.org
Cc: John Irwin 
Subject: Townhome - Common Areas

We're protecting (4) rows of townhomes per NFPA 13D. Between buildings are 
small common areas such as trash storage (132sqft) and mail room (260sqft).  
Providing protection in these rooms would come at an additional expense because 
the units being protected are fee simple and each has it's own lead-in. Adding 
sprinklers to these small common rooms would require additional lead ins, 
meters, light hazard and combustible concealed protection. Do these rooms need 
to be protected?

As an added twist, the townhomes that immediately abut these rooms have 
exterior terraces on the ROOFs of these rooms. Is this a factor?



John Irwin
Quick Response Fire Protection


"The bitterness of poor quality remains long after the sweetness of low price 
is forgotten." - Benjamin Franklin

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
https://urldefense.proofpoint.com/v2/url?u=http-3A__lists.firesprinkler.org_listinfo.cgi_sprinklerforum-2Dfiresprinkler.org=DwICAg=wn3mZQLIuInh2ClcJ0_DIA=Z_2A85VL7AQzoqudh6uOyS3bn8etxB7nLN8OBJwQd9A=faLC6Gr2aXcLulFYub3ZQSbhFvUDwniBMdSL2deInFQ=HfI4Lqejjh6B80Gz6TCV8T5UsQAvWcPuFsupz6bJO14=
 
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
https://urldefense.proofpoint.com/v2/url?u=http-3A__lists.firesprinkler.org_listinfo.cgi_sprinklerforum-2Dfiresprinkler.org=DwICAg=wn3mZQLIuInh2ClcJ0_DIA=Z_2A85VL7AQzoqudh6uOyS3bn8etxB7nLN8OBJwQd9A=faLC6Gr2aXcLulFYub3ZQSbhFvUDwniBMdSL2deInFQ=HfI4Lqejjh6B80Gz6TCV8T5UsQAvWcPuFsupz6bJO14=
 
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: Townhome - Common Areas

2021-01-27 Thread Steve Leyton via Sprinklerforum
That last part made it easy for me to firm a quick opinion. If you have living 
space over a utility space like a garage or trash enclosure, I would say that 
accessory structure becomes a part of the dwelling unit associated with that 
terrace or patio space.   Protect the trash enclosure as you would a garage. If 
you are in a state or jurisdiction that doesn't require protection of garages 
per the exception in13D, then protect as for a garage in 13R.


Steve Leyton

(Sent from my smartphone; please excuse typos and voice-to-text corruptions.)



 Original message 
From: John Irwin via Sprinklerforum 
Date: 1/27/21 6:48 AM (GMT-08:00)
To: sprinklerforum@lists.firesprinkler.org
Cc: John Irwin 
Subject: Townhome - Common Areas

We're protecting (4) rows of townhomes per NFPA 13D. Between buildings are 
small common areas such as trash storage (132sqft) and mail room (260sqft).  
Providing protection in these rooms would come at an additional expense because 
the units being protected are fee simple and each has it's own lead-in. Adding 
sprinklers to these small common rooms would require additional lead ins, 
meters, light hazard and combustible concealed protection. Do these rooms need 
to be protected?

As an added twist, the townhomes that immediately abut these rooms have 
exterior terraces on the ROOFs of these rooms. Is this a factor?



John Irwin
Quick Response Fire Protection


"The bitterness of poor quality remains long after the sweetness of low price 
is forgotten." - Benjamin Franklin

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org