Change out what you believe are the most demanding 4 heads and do a bucket
test. Let’s know what happens.
Owen Evans
Sent from my iPhone
> On Mar 11, 2020, at 10:16 AM, Matt Grise via Sprinklerforum
> wrote:
>
>
> We are looking at an apartment complex that was built in the 2000-2001
> www.tomlinsonfire.com
>>
>>
>>
>> From: Sprinklerforum On
>> Behalf Of Matt Grise via Sprinklerforum
>> Sent: Wednesday, March 11, 2020 12:31 PM
>> To: sprinklerforum@lists.firesprinkler.org
>> Cc: Matt Grise
>> Subject: RE: low flow resi
412
>>
>> Fax: 316-202-2346
>>
>> Cell: 620-955-7293
>>
>> www.tomlinsonfire.com
>>
>>
>>
>> *From:* Sprinklerforum *On
>> Behalf Of *Matt Grise via Sprinklerforum
>> *Sent:* Wednesday, March 11, 2020 12:31 PM
>> *To:* spri
Cell: 620-955-7293
>
> www.tomlinsonfire.com
>
>
>
> *From:* Sprinklerforum *On
> Behalf Of *Matt Grise via Sprinklerforum
> *Sent:* Wednesday, March 11, 2020 12:31 PM
> *To:* sprinklerforum@lists.firesprinkler.org
> *Cc:* Matt Grise
> *Subject:* RE: low f
se via Sprinklerforum
Sent: Wednesday, March 11, 2020 12:31 PM
To: sprinklerforum@lists.firesprinkler.org
Cc: Matt Grise
Subject: RE: low flow residential head replacement
The current 3.0 pendent listing requires more gpm and psi to cover the same
area as the old Central head. If we swap out the old k3's for
documentation
addressing the change in listing demand?
Thanks!
Matt
From: Sprinklerforum On Behalf
Of Spencer Tomlinson via Sprinklerforum
Sent: Wednesday, March 11, 2020 12:25 PM
To: sprinklerforum@lists.firesprinkler.org
Cc: Spencer Tomlinson
Subject: RE: low flow residential head
w flow residential head replacement
We are looking at an apartment complex that was built in the 2000-2001 range
using Central low flow k3.0 pendent residential heads. The k3.0's were listed
for flow rates that are under .05gpm/sf for 13R applications before the .05
minimum was put into the standard
We are looking at an apartment complex that was built in the 2000-2001 range
using Central low flow k3.0 pendent residential heads. The k3.0's were listed
for flow rates that are under .05gpm/sf for 13R applications before the .05
minimum was put into the standard. Some of the sprinkler heads