Re: rod orientation installed below sloped roof decks

2009-02-12 Thread Ron Greenman
2 > > > > > > "Roland Huggins" > inkler.org> sprinklerforum@firesprinkler.org > Sent by: cc > sprinklerforum-bo > un...@firespri

Re: rod orientation installed below sloped roof decks

2009-02-12 Thread rahe . loftin
Sent by: cc sprinklerforum-bo un...@firesprinkl Subject er.org Re: rod orientation insta

Re: rod orientation installed below sloped roof decks

2009-02-12 Thread Roland Huggins
That translates to rods shall be perpendicular to the pipe, clarified in the 2007 edition. This is one of those rare situations where the 2002 ed Sprinkler Handbook got it wrong. Roland On Feb 11, 2009, at 2:17 PM, Thom McMahon wrote: 9.1.2.3* Hanger rods shall be installed so that latera

RE: rod orientation installed below sloped roof decks

2009-02-11 Thread Thom McMahon
9.1.2.3* Hanger rods shall be installed so that lateral gravity loads are not induced on the rods. Thom McMahon, SET Firetech, Inc. 2560 Copper Ridge Dr P.O. Box 882136 Steamboat Springs, CO 80488 Tel: 970-879-7952 Fax: 970-879-7926 ___ Sprinklerfo

Re: rod orientation installed below sloped roof decks

2009-02-11 Thread rahe . loftin
Hang the rod vertically, just as the good book says and use a clevis hanger. Rahe Loftin - Original Message - From: "Ryan Hinson" [rhin...@fireconstructionservices.com] Sent: 02/11/2009 03:54 PM CST To: sprinklerforum@firesprinkler.org Subject: rod orientation installed be

rod orientation installed below sloped roof decks

2009-02-11 Thread Ryan Hinson
Does anyone out there know of the/a specific code requirement of the rod supporting X-mains or branchlines oriented perpendicular to the slope of the roof or ceiling? I seem to recall a requirement that these hangers must be in a vertical orientation to prevent gravity from “pulling the pipe down