RE: [EXTERNAL] standpipes

2017-08-09 Thread Ed . Tambini
Do a calc to see if it becomes the more demanding valve? From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of Rocci Cetani 3 Sent: Wednesday, August 09, 2017 8:24 AM To: sprinklerforum@lists.firesprinkler.org Subject: [EXTERNAL] standpipes I have a situation

RE: Building Expansion Joints in NON-seismic Areas

2017-08-09 Thread Mark Phillips
There is a informal interpretation on the AFSA website from 2010 I have used it before The answer is nothing is required Search for Expansion under the question contains box From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of Kyle.Montgomery Sent:

RE: Building Expansion Joints in NON-seismic Areas

2017-08-09 Thread Steve Leyton
In structural terms and by definition, an expansion joint is not a seismic joint. HOWEVER, they come in different flavors and may be subject to differential movement. Because we're in the heart of seismic country, we have to deal with seismic joints and bracing and flexibility and clearance

Building Expansion Joints in NON-seismic Areas

2017-08-09 Thread Kyle . Montgomery
The only reference to expansion joints I can find in NFPA 13 is within section 9.3 "Protection of piping WHERE SUBJECT TO EARTHQUAKES". So, if I'm not in an area that is subject to earthquakes, can I ignore the building expansion joints? Usually I still add a flexible coupling just to be safe,

RE: standpipes

2017-08-09 Thread Rocci Cetani 3
Thanks Steve Rocci Cetani III, CET Senior Designer Water-Based Fire Protections Systems Layout, Nicet Level III Northern California Fire Protection Services Inc. 16840 Joleen Way Bldg. A Morgan Hill, CA 93037 P-(408) 776-1580 EXT.111 F-(408) 776-1590

RE: standpipes

2017-08-09 Thread Steve Leyton
By definition, a "Branch Line" is piping that connects a single hose connection to a standpipe. Per NFPA 14, §7.6.3, branch piping shall be based on the hydraulic criteria of §7.8 but not smaller than 2½". Since you're at the base of a standpipe and not near the presumed remote area, I'd say

Wall penetrations

2017-08-09 Thread Gary Stites
Hello Forumites! I'm penetrating some walls with listed thinwall pipe (Eddy Flow). All of the firestop details from Hilti or 3M say the penetrant shall be "Sch.10 or heavier". Is their a detail for listed thinwall? Do I have to upsize to Sch.10 at the wall to penetrate it? Thanks guys... --

RE: [EXTERNAL] Re: Wall penetrations

2017-08-09 Thread Mark . Phelps
Just my perception maybe, but a water filled pipe would be much less likely to fail when subjected to fire , regardless of the wall thickness, than a dry (Empty)pipe. Mark at Aero From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of Gary Stites Sent:

Re: Wall penetrations

2017-08-09 Thread Gary Stites
Not any one in particular... they all say "Sch.10 or heavier". I'm just looking for a way to penetrate with thinner wall pipe. On Wed, Aug 9, 2017 at 2:36 PM, Matt Grise wrote: > What hilti product are you looking at? > > > > Matt > > > > > > *From:* Sprinklerforum

RE: [EXTERNAL] Re: Wall penetrations

2017-08-09 Thread Mark . Phelps
Matt, is the system wet pipe, dry or pre-action? Mark at Aero From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of Gary Stites Sent: Wednesday, August 09, 2017 2:45 PM To: sprinklerforum@lists.firesprinkler.org Subject: [EXTERNAL] Re: Wall penetrations Not

Re: [EXTERNAL] Re: Wall penetrations

2017-08-09 Thread Gary Stites
It's a wet system, but why would that matter? On Wed, Aug 9, 2017 at 2:48 PM, Mark.Phelps wrote: > Matt, is the system wet pipe, dry or pre-action? > > > > Mark at Aero > > > > *From:* Sprinklerforum [mailto:sprinklerforum-bounces@lists.firesprinkler. > org] *On Behalf Of

RE: Wall penetrations

2017-08-09 Thread Matt Grise
What hilti product are you looking at? Matt From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of Gary Stites Sent: Wednesday, August 09, 2017 4:18 PM To: sprinklerforum@lists.firesprinkler.org Subject: Wall penetrations Hello Forumites! I'm penetrating

Re: Quick-Response Sprinklers in Storage/Extra Hazard

2017-08-09 Thread bcasterline
Quoting bcasterl...@fsc-inc.com: Make that 46% increase. If we started with 2500 and reduced to 2000 for using 286F (SR) because of the reasoning, "fewer heads would go off", we would have to go the other direction for QR. 2500x1.3=3250. I did a quick activation comparison with 286F SR

Attic Sprinkler Temps

2017-08-09 Thread Dwight Havens
I'll back Travis up.   Northern US, probably not nearly that hot.  Spent a little time in my attic in Phoenix.  Preferably not in the summer, but 140F to 150 F was typical that time of year. Dwight HavensCity of Phoenix Fire Prevention-Retired___

standpipes

2017-08-09 Thread Rocci Cetani 3
I have a situation where my 6" standpipe is coming into stairwell @ 16' AFF can I drop down 11' (to get to my max 5 AFF) with 2.5" to feed the hose valve on the 1st floor or does it need to drop down 6" with a 2.5" outlet? Thanks in advance Mr. Leyton for your assistance J Rocci