Do a calc to see if it becomes the more demanding valve?
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On
Behalf Of Rocci Cetani 3
Sent: Wednesday, August 09, 2017 8:24 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: [EXTERNAL] standpipes
I have a situation
There is a informal interpretation on the AFSA website from 2010 I have used it
before
The answer is nothing is required
Search for Expansion under the question contains box
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On
Behalf Of Kyle.Montgomery
Sent:
In structural terms and by definition, an expansion joint is not a seismic
joint. HOWEVER, they come in different flavors and may be subject to
differential movement. Because we're in the heart of seismic country, we have
to deal with seismic joints and bracing and flexibility and clearance
The only reference to expansion joints I can find in NFPA 13 is within section
9.3 "Protection of piping WHERE SUBJECT TO EARTHQUAKES". So, if I'm not in an
area that is subject to earthquakes, can I ignore the building expansion joints?
Usually I still add a flexible coupling just to be safe,
Thanks Steve
Rocci Cetani III, CET
Senior Designer
Water-Based Fire Protections Systems Layout, Nicet Level III
Northern California Fire Protection Services Inc.
16840 Joleen Way Bldg. A
Morgan Hill, CA 93037
P-(408) 776-1580 EXT.111
F-(408) 776-1590
By definition, a "Branch Line" is piping that connects a single hose connection
to a standpipe. Per NFPA 14, §7.6.3, branch piping shall be based on the
hydraulic criteria of §7.8 but not smaller than 2½". Since you're at the base
of a standpipe and not near the presumed remote area, I'd say
Hello Forumites!
I'm penetrating some walls with listed thinwall pipe (Eddy Flow). All of
the firestop details from Hilti or 3M say the penetrant shall be "Sch.10 or
heavier". Is their a detail for listed thinwall? Do I have to upsize to
Sch.10 at the wall to penetrate it?
Thanks guys...
--
Just my perception maybe, but a water filled pipe would be much less likely to
fail when subjected to fire , regardless of the wall thickness, than a dry
(Empty)pipe.
Mark at Aero
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On
Behalf Of Gary Stites
Sent:
Not any one in particular... they all say "Sch.10 or heavier". I'm just
looking for a way to penetrate with thinner wall pipe.
On Wed, Aug 9, 2017 at 2:36 PM, Matt Grise wrote:
> What hilti product are you looking at?
>
>
>
> Matt
>
>
>
>
>
> *From:* Sprinklerforum
Matt, is the system wet pipe, dry or pre-action?
Mark at Aero
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On
Behalf Of Gary Stites
Sent: Wednesday, August 09, 2017 2:45 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: [EXTERNAL] Re: Wall penetrations
Not
It's a wet system, but why would that matter?
On Wed, Aug 9, 2017 at 2:48 PM, Mark.Phelps wrote:
> Matt, is the system wet pipe, dry or pre-action?
>
>
>
> Mark at Aero
>
>
>
> *From:* Sprinklerforum [mailto:sprinklerforum-bounces@lists.firesprinkler.
> org] *On Behalf Of
What hilti product are you looking at?
Matt
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On
Behalf Of Gary Stites
Sent: Wednesday, August 09, 2017 4:18 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: Wall penetrations
Hello Forumites!
I'm penetrating
Quoting bcasterl...@fsc-inc.com:
Make that 46% increase.
If we started with 2500 and reduced to 2000 for using 286F (SR)
because of the reasoning, "fewer heads would go off", we would have to
go the other direction for QR. 2500x1.3=3250.
I did a quick activation comparison with 286F SR
I'll back Travis up. Northern US, probably not nearly that hot. Spent a
little time in my attic in Phoenix. Preferably not in the summer, but 140F to
150 F was typical that time of year.
Dwight HavensCity of Phoenix Fire Prevention-Retired___
I have a situation where my 6" standpipe is coming into stairwell @ 16' AFF
can I drop down 11' (to get to my max 5 AFF) with 2.5" to feed the hose
valve on the 1st floor or does it need to drop down 6" with a 2.5" outlet?
Thanks in advance Mr. Leyton for your assistance J
Rocci