RE: RPZ for a dedicated private underground fire mains having fire hydrants

2012-06-07 Thread Art Tiroly
Then should public street hydrants need BFP installed? Arthur Tiroly ATCO Fire Protection Design Tiroly and Associates 24400 Highland Rd rm 25, CLE 44143 216-621-8899 216-570-7030 Cell WWW.ATCOfirepro.com -Original Message- From: sprinklerforum-boun...@firesprinkler.org

RE: Paint Booth Convertible

2012-08-09 Thread Art Tiroly
Not sure how yours looks but it is extra hazard - .40/. There is also the exhaust to deal with. Just did one with the exhaust was in tunnels in the floor, with down draft air flow and filters also in the floor. It all worked out well. Arthur Tiroly ATCO Fire Protection Design Tiroly and

RE: FPC Celebrity

2012-08-09 Thread Art Tiroly
Congrats to George Church who made the cover of the FPC mag. He is the Person of the Year with 3-1/2 pages inside. Good luck George. Arthur Tiroly ATCO Fire Protection Design Tiroly and Associates 24400 Highland Rd rm 25, CLE 44143 216-621-8899 216-570-7030 Cell WWW.ATCOfirepro.com -

RE: solid shelves in auto parts stores

2012-08-16 Thread Art Tiroly
Considering the amount of rubber and plastic parts, oil, solvents and aerosol sprays and paint, I think it should be higher. I think in spots it is more than a class 4 commodity. Arthur Tiroly ATCO Fire Protection Design Tiroly and Associates 24400 Highland Rd rm 25, CLE 44143 216-621-8899

RE: Idle wood pallets NFPA 13, 12.12.1.2(a) 2010 Ed

2012-08-27 Thread Art Tiroly
Look at table 12.12.1.2(a), 2010. The minimum density is .60 from 8ft to 20 ft. The .45 is only good to 8 ft. Unless the pile sizes are small and well spaced I think you are looking at 8-10 ft max height. The orifice size at 11.2 and above is not the most important factor. The density controls

RE: 8.14.5.2 (2002 edt.)

2012-08-27 Thread Art Tiroly
I think this is the elevator shaft enclosure that is a fire rated assembly like a stair tower. Arthur Tiroly ATCO Fire Protection Design Tiroly and Associates 24400 Highland Rd rm 25, CLE 44143 216-621-8899 216-570-7030 Cell WWW.ATCOfirepro.com -Original Message- From:

RE: In-rack sprinkler K-factors

2012-08-28 Thread Art Tiroly
At 30 gpm the sprinkler required is K=5.6. In 2010 16.3.4.3.1 says 30 gpm so a K=8 sprinkler can be used at 15 psi. Arthur Tiroly ATCO Fire Protection Design Tiroly and Associates 24400 Highland Rd rm 25, CLE 44143 216-621-8899 216-570-7030 Cell WWW.ATCOfirepro.com -Original Message-

RE: Antifreeze Update

2012-08-28 Thread Art Tiroly
Are their any videos of the test and procedure documents of how the test was set up? AF systems have been around for a very long time and only recently has there been any questions about flash fires of AF/water mix going thru a sprinkler. Arthur Tiroly ATCO Fire Protection Design Tiroly and

RE: Roof piping system

2012-10-03 Thread Art Tiroly
Bidding on a repair to a dry standpipe system with underground supply that leaked below floor of an apartment building. Running the pipe through the hall way to 4 standpipes is particularly difficult. An option is to run galvanized pipe on the flat concrete roof to connect all 4 risers to one

RE: trip time per nfpa 25

2012-10-24 Thread Art Tiroly
From old time experience there may be obstructions at the dry inspector's test valve or other that is obstructing the flow of air. From insurance inspector days anything over 3 minutes needs further investigation. I would have called 15 minutes a failure in the 60's and 70's. Arthur Tiroly ATCO

RE: Auxiliary Dry Pipe Question

2012-12-28 Thread Art Tiroly
How do you plan to drain the system full of water to reset the DPV? Arthur Tiroly ATCO Fire Protection Design Tiroly and Associates 24400 Highland Rd rm 25, CLE 44143 216-621-8899 216-570-7030 Cell WWW.ATCOfirepro.com -Original Message- From: sprinklerforum-boun...@firesprinkler.org

RE: Obstruction below ESFR's

2013-01-08 Thread Art Tiroly
There are stiffening beams attached to the bottom of 28 bar joist about 6 wide. Sect 8.12.5.3.1 allows 1 ft wide obstruction below the ESFR head 1 ft away but no mention of the distance below. His seems to be an excessive obstruction unless it was 3 ft below he deflector or is this not an

RE: Obstruction below ESFR's

2013-01-08 Thread Art Tiroly
These beams are 25 ft long starting at the outside wall and parallel to the 2 branch lines. It seems line 1 ft and 2 ft wide row of lights or ducts would be serious obstructions. Arthur Tiroly ATCO Fire Protection Design Tiroly and Associates 24400 Highland Rd rm 25, CLE 44143 216-621-8899

RE: Pre-.05 density heads: What heads can be used as a replacement ?

2013-01-09 Thread Art Tiroly
What is the orifice size or K factor of the old heads? What area of coverage per sprinkler? Pendent or sidewall? Is this a 13R system? You should be able to match the K or orifice size and not be trouble. Arthur Tiroly ATCO Fire Protection Design Tiroly and Associates 24400 Highland Rd rm 25,

RE: Water filtration specifications

2013-01-11 Thread Art Tiroly
Vertical turbine pumps take suction from open ponds and lakes with 1/2 mesh screen. Silt and other vegetation is common. Pendent heads on return bends are required. Inspections and flushing will be required. Particulates will settle to the bottom of the tanks. How to remove excess. I don't know

RE: Sprinklers below open grated decks

2013-01-25 Thread Art Tiroly
I agree with the 165*F heads under grating maybe even QR heads. With open grating will these sprinklers ever go off or will the heat blow right through the deck up to the roof. Seems we need something to trap the heat. What's the thought on this Arthur Tiroly ATCO Fire Protection Design Tiroly

RE: hydraulic design approaches

2013-03-19 Thread Art Tiroly
See section 11.3 Residential in 2010 NFPA 13. Residential areas and adjacent corridors are allowed by NFPA 13 by calculating just 4 sprinklers with a .10 density or with residential flows whichever is greater Arthur Tiroly ATCO Fire Protection Design Tiroly and Associates 24400 Highland Rd

RE: generator as primary supply

2013-04-09 Thread Art Tiroly
May I suggest that you consider a diesel driver with a right angle gear drive for the VT pump. This is an approved method and likely less costly. Arthur Tiroly ATCO Fire Protection Design Tiroly and Associates 24400 Highland Rd rm 25, CLE 44143 216-621-8899 216-570-7030 Cell WWW.ATCOfirepro.com

RE: West, TX explosion

2013-04-26 Thread Art Tiroly
As a former HPR inspector I ask a lot questions. I get everything I need to determine the hazards in a facility. I get criticized for asking too many questions but I need to know what the protection requirements for the hazardous areas. I am not a contractor but I work for contractors architects

RE: Brewery Occupancy Clasification

2013-04-26 Thread Art Tiroly
Storage is the problem. Finished bottled beer storage in cartons stacking? Bags of grain storage and raw material for the process unless it is outside storage bins. Arthur Tiroly ATCO Fire Protection Design Tiroly and Associates 24400 Highland Rd rm 25, CLE 44143 216-621-8899 216-570-7030 Cell

RE: Listed 400psi weld-o-lets

2013-05-07 Thread Art Tiroly
Isn't 300 psi a high temp steam rating? Cold water may be even more than 300 psi. Arthur Tiroly ATCO Fire Protection Design Tiroly and Associates 24400 Highland Rd rm 25, CLE 44143 216-621-8899 216-570-7030 Cell WWW.ATCOfirepro.com -Original Message- From:

RE: Warehouse protection

2013-05-13 Thread Art Tiroly
I need some history on warehouse protection requirements. When was high piled storage protection with hydraulic calculations required? That was covered in NFPA 231 back then. The problem is a 22 ft high building with a 1975 - 130 SF pipe schedule system and a 45 psi water supply for class 3 and

RE: Warehouse protection

2013-05-13 Thread Art Tiroly
...@lists.firesprinkler.org [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of Art Tiroly Sent: Monday, May 13, 2013 12:33 PM To: sprinklerfo...@firesprinkler.org Subject: RE: Warehouse protection I need some history on warehouse protection requirements. When was high piled storage protection

RE: Sizing tanks with hydrants?

2013-05-13 Thread Art Tiroly
The building will never be used for high piled storage right? Arthur Tiroly ATCO Fire Protection Design Tiroly and Associates 24400 Highland Rd rm 25, CLE 44143 216-621-8899 216-570-7030 Cell WWW.ATCOfirepro.com -Original Message- From: sprinklerforum-boun...@lists.firesprinkler.org

RE: Extra Hazard storage

2013-05-13 Thread Art Tiroly
A foam/water system could reduce the water supply required. I had very good success with Compressed air foam. This greatly reduced water supply required. Arthur Tiroly ATCO Fire Protection Design Tiroly and Associates 24400 Highland Rd rm 25, CLE 44143 216-621-8899 216-570-7030 Cell

RE: Extra Hazard storage

2013-05-13 Thread Art Tiroly
spec. Which manufacturer would I look at for the system that you have used. On Mon, May 13, 2013 at 2:39 PM, Art Tiroly atir...@atcofirepro.com wrote: A foam/water system could reduce the water supply required. I had very good success with Compressed air foam. This greatly reduced water

RE: Forward Flow Testing of BFP's

2013-05-13 Thread Art Tiroly
A 4 pipe 40 long with a shutoff valve should flow 1500 gpm and provide a smooth flow to pitot. Arthur Tiroly ATCO Fire Protection Design Tiroly and Associates 24400 Highland Rd rm 25, CLE 44143 216-621-8899 216-570-7030 Cell WWW.ATCOfirepro.com -Original Message- From:

RE: Standpipe Testing!!!!

2013-05-21 Thread Art Tiroly
Are you testing the water supply and gpm/psi? If you flow 500 gpm at the remote you can flow 250 or 500 through any outlet even on the 1st floor. IMHO Arthur Tiroly ATCO Fire Protection Design Tiroly and Associates 24400 Highland Rd rm 25, CLE 44143 216-621-8899 216-570-7030 Cell

RE: Standpipe Testing!!!!

2013-05-21 Thread Art Tiroly
Highland Rd rm 25, CLE 44143 216-621-8899 216-570-7030 Cell WWW.ATCOfirepro.com -Original Message- From: sprinklerforum-boun...@lists.firesprinkler.org [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of Art Tiroly Sent: Tuesday, May 21, 2013 4:50 PM To: sprinklerforum

RE: Can't find a date

2013-05-24 Thread Art Tiroly
I have a Model 38B Automatic Sprinkler 1/2 SSU head. I cant find the date. 165*F is on the solder link. 38-600 is on the deflector. I know it has a date somewhere. It is about 40 years old Arthur Tiroly ATCO Fire Protection Design Tiroly and Associates 24400 Highland Rd rm 25, CLE 44143

RE: Can't find a date

2013-05-24 Thread Art Tiroly
-inc.com -Original Message- From: sprinklerforum-boun...@lists.firesprinkler.org [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of Art Tiroly Sent: Friday, May 24, 2013 2:30 PM To: sprinklerforum@lists.firesprinkler.org Subject: RE: Can't find a date I have a Model 38B

RE: George L. Church, Jr.

2013-06-27 Thread Art Tiroly
I enjoyed his many emails over time. I was at a Ford car show in Carlisle PA last year. I asked George to come visit our picnic dinner hour that weekend. He came with his TR6 to watch some of our antics. It was great to meet with him to talk shop and cars. He will be dearly missed. Arthur

RE: Sprinkler dust cover

2013-07-12 Thread Art Tiroly
An owner wants us to cover sprinklers with a bag or dust cover to keep the sprinklers from becoming loaded with dust. They say the dust is noncombustible due to chemical additives in the mix. Is this allowed? If not how does he keep them clean? Arthur Tiroly ATCO Fire Protection Design

RE: Sprinkler dust cover

2013-07-12 Thread Art Tiroly
www.lakelandgov.net Working together to achieve an exceptional quality of life -Original Message- From: sprinklerforum-boun...@lists.firesprinkler.org [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of Art Tiroly Sent: Friday, July 12, 2013 2:31 PM To: sprinklerfo

RE: Sprinkler dust cover

2013-07-12 Thread Art Tiroly
plastic) will not interfere with the head opening under a fire condition. Layers and layers of crap, on the heads or on the bags, will. On Fri, Jul 12, 2013 at 12:19 PM, Art Tiroly atir...@atcofirepro.comwrote: That section applies to paint booths. Would a bag cover be acceptable in a larger open

RE: Hazard classification

2013-07-24 Thread Art Tiroly
The problem is not the OH2 retail sales floor. Check out the expected storage areas with the plastics, Styrofoam, aerosols and high piled rack storage that will require storage protection. Arthur Tiroly ATCO Fire Protection Design Tiroly and Associates 24400 Highland Rd rm 25, CLE 44143

RE: Minimum number of operating sprinklers

2013-08-07 Thread Art Tiroly
1. This reduction depends on ceiling height and varies. 2. This is based on spacing over 200 SF per head and extended coverage spacing. Arthur Tiroly ATCO Fire Protection Design Tiroly and Associates 24400 Highland Rd rm 25, CLE 44143 216-621-8899 216-570-7030 Cell WWW.ATCOfirepro.com

RE: 13 13R

2013-08-12 Thread Art Tiroly
Why not use the residential rules in 13? Arthur Tiroly ATCO Fire Protection Design Tiroly and Associates 24400 Highland Rd rm 25, CLE 44143 216-621-8899 216-570-7030 Cell WWW.ATCOfirepro.com -Original Message- From: sprinklerforum-boun...@lists.firesprinkler.org

RE: Ordinary risk sprinklers ?

2010-02-17 Thread Art Tiroly
Cesar, Viking Sprinkler has several extended coverage concealed sprinklers with several orifice sizes. K= 5.6, 8.0 and 11.2 are available. You need to determine the required density for the occupancy to prepare hydraulic calculations for your project. Art Tiroly ATCO fire protection design

RE: Attics and Tyco AP sprinklers

2010-02-22 Thread Art Tiroly
Check the TYCO attic sprinkler info again. With sloped roof in a wood truss attic you can cover the 40-60ft wide attic with BB sprinklers at the peak only spaced 6ft apart. They are available in K= 5.6 and 8.0 with just one row at the peak. Attic Sprinklers are expensive but very efficient

RE: Backflow protection on antifreeze system

2010-03-11 Thread Art Tiroly
It is up to the water company regarding backflow requirements. Art Tiroly ATCO Fire Protec -Original Message- From: sprinklerforum-boun...@firesprinkler.org [mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Ed Kramer Sent: Thursday, March 11, 2010 11:23 AM

RE: Hard wired air compressors

2010-03-18 Thread Art Tiroly
A disconnect and breaker will also disable the power to the A/C unless locked in ON position. Low air alarm will provide the backup if not too late. Art -Original Message- From: sprinklerforum-boun...@firesprinkler.org [mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Greg

RE: Underground flushing velocities

2010-04-02 Thread Art Tiroly
One concern I have is for dry pipe and preaction systems. The in-rush to fill the system will have a short term high velocity flow that will pick up any debris in the fire line and move it into the riser. Should that be added to the flushing proceedure or is it a special case that that does not

RE: NFPA #13 changes/additions

2010-04-29 Thread Art Tiroly
George, Is this in PA? PA has been behind code wise for years. Ohio has had nursing home requirements for over 30 years and High rise and assistaant living for 15-20 years. Now that PA has new codes life safety should get better. -Original Message- From:

RE: Anti-Freeze Systems

2010-05-20 Thread Art Tiroly
I have done this a few times. After the dry system piping had rusted out this was suggested to the owner to reduce the maintenance problems with dry sprinklers in attics. I have only know of one problem ie: when PG was refilled in a system with CPVC piping. Art Tiroly and Associates

RE: How Many Heads to calc for 13D 13R

2010-05-28 Thread Art Tiroly
I usually end up calculating 4 sprinklers in the hall since that becomes the largest room. What do others do? -Original Message- From: sprinklerforum-boun...@firesprinkler.org [mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Richardson, R Sent: Friday, May 28, 2010 2:39 PM

RE: Gravity Tanks

2010-06-17 Thread Art Tiroly
Is this tank dedicated for fire protection? Why would you assume it is empty? Then the water is only available for 1 minute while you empty the riser pipe. Calculate friction loss through riser pipe down and through sprinkler riser with an assumed flow entering the tank discharge pipe. Eleveation

RE: Automatic air release

2010-06-24 Thread Art Tiroly
Called Potter yesterday. List price is over $1400 for the supervised unit with the catch can. Viking has one- also very expensive. The device looks pretty simple why so expensive? Reliability? -Original Message- From: sprinklerforum-boun...@firesprinkler.org

RE: Copper Tube in a Dry System??

2010-06-28 Thread Art Tiroly
A high temp. solder must be used - silver solder or other high temp solder not 95-5. Art -Original Message- From: sprinklerforum-boun...@firesprinkler.org [mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Travis Mack, SET Sent: Monday, June 28, 2010 12:07 PM To:

RE: Question regarding NFPA 13 vs. NFPA 13R

2010-07-07 Thread Art Tiroly
The Ohio IBC has allowed and encourages the use of residential sprinklers in I occupancies. We have used the residential rules in 13 with 4 head calc areas for many years. But attics etc are required for 100% sprinkler coverage due to NFPA 13 requirements per IBC for the I occupancy. ART ATCO

RE: VT pump suction

2010-07-16 Thread Art Tiroly
It is hard to visualize this to maintain reliability. Pond grass can be a big problem. Then you need access to pump screens. I would not be in favor of it do to reliability and maintenance. Art -Original Message- From: sprinklerforum-boun...@firesprinkler.org

RE: pipe schedule and storage

2010-08-11 Thread Art Tiroly
to the requirements of the new occupancy? If it is a calculated OH2 system does that need to be brought up to the requirements of the hazard due to the change in occupancy? Art Tiroly/AFSA ATCO Fire Protection -Original Message- From: sprinklerforum-boun...@firesprinkler.org

RE: High rise retrofit standpipe

2010-08-31 Thread Art Tiroly
Water supply is weak 63/500/20. Single 6andpipe riser in a round building. 500 gpm at 125 psi. We are asking for a city water supply improvenent. Arthur Tiroly ATCO Fire Protection Design Tiroly and Associates 216-621-8899 216-570-7030 Cell WWW.ATCOfirepro.com

RE: Monitor nozzle

2010-09-16 Thread Art Tiroly
A 1.75 smooth bore nozzle has a K = 88.67. Your nozzle may be different. Art -Original Message- From: sprinklerforum-boun...@firesprinkler.org [mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Jamie.seidl Sent: Thursday, September 16, 2010 9:43 AM To:

RE: Anti Freeze for commercial

2010-09-22 Thread Art Tiroly
When AF is above 50% it is a combustible liquid below 50% it is not easily ignited. Break it up, in a fine spray from sprinkler and there is no surprise that the spray is explosive. If we cant control the industry to not use high concentrations of AF then we must find a different method. Properly

RE: Assisted living partial sprinkler?

2010-09-23 Thread Art Tiroly
Architect calls with a small addition to an existing 3500 SF, R4 assisted living building. He says all we have to protect is the new addition and some connecting rooms by the fire official. R4 only requires a 13D systems per IBC with only 8 patients. I want at least a 13R system and 100%

RE: Assisted living partial sprinkler?

2010-09-23 Thread Art Tiroly
to 4 stories) can be a 13- D but the same function in a one story building with less than 16 does not have this explicit exception. It's an easy argument to apply it but is a call by the AHJ. Roland On Sep 23, 2010, at 9:07 AM, Art Tiroly wrote: Architect calls with a small addition to an existing

RE: PA LI - UCC Sprinkler Design Data Sheet

2010-09-30 Thread Art Tiroly
Two things could apply here. See chapter 24. See figure A.24.6 Sprinkler system- general information and the Hydraulic Design information sign. There is also a occupancy inforamtion sheet that I could not find quickly. These describe what the owner intends for the building use and occupancy. Art

RE: Physical Science :)

2010-11-04 Thread Art Tiroly
As I understand it, the examinee will be allowed to take NFPA 13, 14 and 20. No note books, calculators or loose paper. This is subject to change. Arthur Tiroly ATCO Fire Protection Design Tiroly and Associates 216-621-8899 216-570-7030 Cell WWW.ATCOfirepro.com -Original Message- From:

RE: Physical Science :)

2010-11-04 Thread Art Tiroly
All questions are based on NFPA documents not like the old test. There are some safety questions from OSHA handbook for level 2 Arthur Tiroly ATCO Fire Protection Design Tiroly and Associates 216-621-8899 216-570-7030 Cell WWW.ATCOfirepro.com -Original Message- From:

RE: NICET III

2010-12-08 Thread Art Tiroly
Soon the element testing program will not be available. The new test is comprehensive pass fail system. Check the NICET website for availability - coming soon. Arthur Tiroly ATCO Fire Protection Design Tiroly and Associates 216-621-8899 216-570-7030 Cell WWW.ATCOfirepro.com -Original

RE: USACE Velocity

2010-12-28 Thread Art Tiroly
By increasing pipe sizes with velocity you are in effect increasing the density since the required pressure is likely far below the available water pressure. The industry rules for hydraulic calculations are pretty conservative if the correct density has been established for the occupancy.

RE: antifreeze system with 2 connection points

2011-01-04 Thread Art Tiroly
If I understand this correctly, are you creating a loop feed for the hydraulics? You need check valves and control valves at both ends. I don't think you need a standard AF loop beyond the RPZBFP. You do need to control pressure but in a different way. Arthur Tiroly ATCO Fire Protection Design

RE: Butterfly vs. Gate valves: corrosion

2011-02-01 Thread Art Tiroly
Ron, I recently tried to find IDOD pipe supplier. IDOD gave the process to a European Co. that stole the process, never paid for it. It is no longer available in the US. Sad! Arthur Tiroly ATCO Fire Protection Design Tiroly and Associates 216-621-8899 216-570-7030 Cell WWW.ATCOfirepro.com

RE: Soldered vs Brazed Joints

2011-02-07 Thread Art Tiroly
Solder joints allowed only in wet systems. Dry systems require high temperature brazed joints. The pre-action will require brazing. Arthur Tiroly ATCO Fire Protection Design Tiroly and Associates 216-621-8899 216-570-7030 Cell WWW.ATCOfirepro.com -Original Message- From:

RE: ESFR

2011-02-24 Thread Art Tiroly
I beg to differ with you. The high density spray pattern may be small but the total spray area is much larger. After investigating a fire opened 4 ESFR sprinklers, the total spray pattern had a radius of over 10ft per sprinkler that wet boxes in a very large area over 30' x 30' from 4 sprinklers.

RE: Down draft paint booth pits

2011-02-25 Thread Art Tiroly
Designing an auto paint booth with 3 booth areas. Airflow is down draft with filters in the floor in a shallow 1'-6 deep pit. A typical pit is 8'x 23'. What type sprinklers will cover this shallow space? We don't have the 18 minimum space. Would pendent heads in the upright position be better

RE: antifreeze solutions

2011-03-18 Thread Art Tiroly
And when ice forms there will be no sprinkler flow even though the pipe may not burst. Arthur Tiroly ATCO Fire Protection Design Tiroly and Associates 216-621-8899 216-570-7030 Cell WWW.ATCOfirepro.com http://www.atcofirepro.com/ _ From: sprinklerforum-boun...@firesprinkler.org

RE: Sprinklers above Paint Booths

2011-03-19 Thread Art Tiroly
The booths are fully enclosed and adequately protected with .40/ ex.HAZ.GP2.. The area outside the booth only requires protection for the surrounding occupancy. Ask the right questions about the building occupancy to determine the requirements. Arthur Tiroly ATCO Fire Protection Design Tiroly

RE: Convert pitot to actual residual??

2011-07-22 Thread Art Tiroly
From my experience the hydrant gage and the pitot gage read about the same with pitots of 20-40 psi. Arthur Tiroly ATCO Fire Protection Design Tiroly and Associates 216-621-8899 216-570-7030 Cell WWW.ATCOfirepro.com -Original Message- From: sprinklerforum-boun...@firesprinkler.org

RE: Trash Recycling plant

2011-08-24 Thread Art Tiroly
I am working on a proposed trash recycling plant. Automobile trash from a hammer mill type crusher arrives in large dump trucks. All steel has been removed by magnets. This is mostly auto waste with a variety of combustibles: plastic, rubber, foam seats, carpeting, door panels, fiber board,

RE: Attic Protection Measured from Insulation at Eaves?

2011-09-13 Thread Art Tiroly
There is a nice detail at Tyco attic sprinklers that may help. They reference the insulation. SEE: http://www.tyco-fire.com/TD_TFP/TFP/TFP610_05_2008.pdf Arthur Tiroly ATCO Fire Protection Design Tiroly and Associates 216-621-8899 216-570-7030 Cell WWW.ATCOfirepro.com -Original

RE: Top Spray Deluge nozzle

2011-10-12 Thread Art Tiroly
Can you point to anything in NFPA that will allow this design application? Arthur Tiroly ATCO Fire Protection Design Tiroly and Associates 24400 Highland Rd Rm 25, CLE 44143 216-621-8899 216-570-7030 Cell WWW.ATCOfirepro.com -Original Message- From:

RE: Residential Sprinkler in I-2

2011-10-31 Thread Art Tiroly
Check for definitions in your building code for dwelling units. You still may be required to do closets, bathrooms and attics of course. Also follow the guidelines in NFPA 13. These bedroom wings are usually residential areas contrary to what the AHJ is saying. You may need to calculate .10

RE: Residential Sprinkler in I-2

2011-11-01 Thread Art Tiroly
903.2.5 says it only applies to I-1 therefore a full 13 system is required for I-2 IMHO. Arthur Tiroly ATCO Fire Protection Design -Original Message- From: sprinklerforum-boun...@firesprinkler.org [mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Johnson, Duane (NIH/OD/ORS)

RE: Residential Sprinkler in I-2

2011-11-01 Thread Art Tiroly
Science - One Sprinkler at a Time -Original Message- From: Art Tiroly [mailto:atir...@atcofirepro.com] Sent: Tuesday, November 01, 2011 12:29 PM To: sprinklerforum@firesprinkler.org Subject: RE: Residential Sprinkler in I-2 903.2.5 says it only applies to I-1 therefore a full 13 system

RE: fire pump suction piping - flushing

2011-11-18 Thread Art Tiroly
If possible flow through the by-pass and the test header wide open. You should get close to the required flow. Also max flow should not have to exceed 150% of pump rated capacity. Arthur Tiroly ATCO Fire Protection Design Tiroly and Associates -Original Message- From:

RE: Multiple Dry Systems Air Maintenance

2011-11-29 Thread Art Tiroly
All systems will receive high pressure air. The reset system will be getting more but all systems will receive some air in the process. The air compressor will likely be the same as the lowest air pressure being filled due to compressor rate and not 90 psi. Arthur Tiroly ATCO Fire Protection

RE: Simultaneous Pump Operation

2011-12-06 Thread Art Tiroly
Your last question can be determined by hydraulic calculation. If you need 4000 gpm flowing then calculate the flow and pressure drop through 12 or larger pipe. Check velocity and psi drop. Arthur Tiroly ATCO Fire Protection Design Tiroly and Associates 24400 Highland Rd rm 25, CLE 44143

RE: Good one for a Friday

2011-12-09 Thread Art Tiroly
If the materials are known and the protection requirements are clear in NFPA standards I would be comfortable designing and specifying the system. I do have a different background than most NICET designers but I'm not a PE just M SFPE and HPR guy. Arthur Tiroly ATCO Fire Protection Design

RE: IBC - building separations

2011-12-16 Thread Art Tiroly
Does your state allow an ordinance to require more than the state code? Is it possible to appeal to your state building department. I would place the call to the state level. I have had a local ordinance overturned in Ohio by an over zealous local city. Arthur Tiroly ATCO Fire Protection

RE: CT Scan room.

2012-01-04 Thread Art Tiroly
Is black pipe OK above a CT Scan room. I know MRI room res non ferrous pipe. Arthur Tiroly ATCO Fire Protection Design ___ Sprinklerforum mailing list Sprinklerforum@firesprinkler.org

RE: NFPA 15 - Nozzle Reaction

2012-01-09 Thread Art Tiroly
What type nozzles are you using? When there is a deflector, the deflector absorbs some of the reaction and helps to neutralize it. The arm over's will torque from the reaction. What are the nozzle pressures you are expecting? Arthur Tiroly ATCO Fire Protection Design Tiroly and Associates 24400

RE: Excessive pressure hydraulic ram effect

2012-03-27 Thread Art Tiroly
Does this surge in pressure occur during testing pumps or 2 drains or is it a gradual build up likely due to the increase in water temperature in the sprinkler system? Grid system are prone to psi increases due to temp changes. Reducing the air pockets just makes it worse. Relief valves should

RE: OH1 vs OH2

2012-03-28 Thread Art Tiroly
If there is a large amount of rubber ad plastic then this could be a plastics storage hazard. Then OH2 may not be adequate. Arthur Tiroly ATCO Fire Protection Design Tiroly and Associates 24400 Highland Rd rm 25, CLE 44143 216-621-8899 216-570-7030 Cell WWW.ATCOfirepro.com -Original

RE: Commodity classification

2012-03-29 Thread Art Tiroly
Liquor and nail polish in small bottles is class 4 in table A5634 in the handbook. Looks like 4 to me. Arthur Tiroly ATCO Fire Protection Design Tiroly and Associates 24400 Highland Rd rm 25, CLE 44143 216-621-8899 216-570-7030 Cell WWW.ATCOfirepro.com -Original Message- From:

RE: Fire Pump suction

2012-03-30 Thread Art Tiroly
Tony, The problem is usually with a city water booster pump. City water is deficient. A 1000 gpm pump is required. City pressure drops below 20 psi at 1100 gpm. You won't get 1500 gpm but it is OK. Arthur Tiroly ATCO Fire Protection Design Tiroly and Associates 24400 Highland Rd rm 25, CLE

RE: k -- WHAT?

2012-04-16 Thread Art Tiroly
One more comment: You still need the flowing pressure OR a pitot psi or at least a residual psi at the test header. If the BFP is becomes restricted the pressures are necessary to determine the next step. Without psi and flow the K has no meaning except to have a basis for the device when in new

RE: Fabric suction tanks

2013-09-13 Thread Art Tiroly
Google Pillow Tanks -Original Message- From: sprinklerforum-boun...@lists.firesprinkler.org [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of Todd Williams Sent: Friday, September 13, 2013 12:01 PM To: sprinklerforum@lists.firesprinkler.org Subject: Fabric suction

RE: Fabric suction tanks

2013-09-13 Thread Art Tiroly
Can you go back to the OEM? . Art Tiroly ATCO Fire Protection/Tiroly 24400 Highland Rd CLE 44143 216-621-8899 216-570-7030 cell -Original Message- From: sprinklerforum-boun...@lists.firesprinkler.org [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of Todd - Work Sent

RE: Life Safety or Property Protection

2013-09-27 Thread Art Tiroly
Can there be a design issue in question with hydraulic calculation method or head types that does not provide life safety. Standard response sprinklers versus the required quick response heads would be an issue. Art Tiroly ATCO Fire Protection/Tiroly 24400 Highland Rd CLE 44143 216-621-8899 216

RE: NFPA25 scope

2013-11-06 Thread Art Tiroly
is not meant for storage. I have done many sprinkler assessments over the years and designed the necessary hydraulic upgrade to the system. This is a building code issue. There needs to be a mandatory assessment when the tenant change occurs and at 3-5 years intervals thereafter per NFPA 25. Art

RE: 3,000 sq ft minimum design area rule...

2014-02-05 Thread Art Tiroly
It is not required for 3000 sf area calc. See item 4 (d) under 11.2.3.1.4. Art Tiroly ATCO Fire Protection -Original Message- From: sprinklerforum-boun...@lists.firesprinkler.org [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of Will Crisler Sent: Wednesday, February

RE: Solid Shelf Rack Storage Ceiling Density?

2014-03-14 Thread Art Tiroly
See Fig 16.2.1.3.2B. With in-rack sprinklers and adjusting with fig 16.2.1.3.4.1 to 60% of 20 Ft. required. OR Is this miscellaneous stge or a rack warehouse? Art Tiroly ATCO Fire Protection/Tiroly 24400 Highland Rd CLE 44143 216-621-8899 216-570-7030 cell -Original Message- From

RE: Solid Shelf Rack Storage Ceiling Density?

2014-03-14 Thread Art Tiroly
shelves. Bill Menster WFM Consulting Inc. - Original Message - From: Art Tiroly atir...@atcofirepro.com To: sprinklerforum@lists.firesprinkler.org Sent: Friday, March 14, 2014 2:35:44 PM Subject: RE: Solid Shelf Rack Storage Ceiling Density? See Fig 16.2.1.3.2B. With in-rack

RE: Solid Shelf Rack Storage Ceiling Density?

2014-03-17 Thread Art Tiroly
Is this really solid shelves? Or are there open longitudinal and transverse flue spaces at the rack uprights? Art -Original Message- From: sprinklerforum-boun...@lists.firesprinkler.org [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of wmens...@comcast.net Sent:

RE: Valve Velocities

2014-04-16 Thread Art Tiroly
I could see a lot of stress on the valve when it is nearly closed restricting the flow but not when it is fully open. Art Tiroly ATCO Fire Protection -Original Message- From: sprinklerforum-boun...@lists.firesprinkler.org [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf

RE: UG Restraint

2014-07-28 Thread Art Tiroly
The pipe going through the wall must be restrained and anchored to the wall or floor penetration. Link seal is a water seal. Art Tiroly ATCO Fire Protection/Tiroly 24400 Highland Rd CLE 44143 216-621-8899 216-570-7030 cell -Original Message- From: Sprinklerforum [mailto:sprinklerforum

RE: Commodity classification

2014-09-10 Thread Art Tiroly
Is the powdered product combustible? Likely yes. Then It is likely class 3 . Powder may be explosion hazard like flour or grain dust. ART ATCO Fire -Original Message- From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of Jay Stough Sent: Wednesday,

RE: 3/4 Outlets

2014-10-06 Thread Art Tiroly
Think about what this does to the hydraulics and turbulent flow through the reduced orifice with over 100 gpm per head. Art Tiroly ATCO Fire Protection -Original Message- From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of Stafford, Susan Sent