Then should public street hydrants need BFP installed?
Arthur Tiroly
ATCO Fire Protection Design
Tiroly and Associates
24400 Highland Rd rm 25, CLE 44143
216-621-8899
216-570-7030 Cell
WWW.ATCOfirepro.com
-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
Not sure how yours looks but it is extra hazard - .40/. There is also the
exhaust to deal with.
Just did one with the exhaust was in tunnels in the floor,
with down draft air flow and filters also in the floor.
It all worked out well.
Arthur Tiroly
ATCO Fire Protection Design
Tiroly and
Congrats to George Church who made the cover of the FPC mag.
He is the Person of the Year with 3-1/2 pages inside.
Good luck George.
Arthur Tiroly
ATCO Fire Protection Design
Tiroly and Associates
24400 Highland Rd rm 25, CLE 44143
216-621-8899
216-570-7030 Cell
WWW.ATCOfirepro.com
-
Considering the amount of rubber and plastic parts, oil, solvents and
aerosol sprays and paint, I think it should be higher. I think in spots it
is more than a class 4 commodity.
Arthur Tiroly
ATCO Fire Protection Design
Tiroly and Associates
24400 Highland Rd rm 25, CLE 44143
216-621-8899
Look at table 12.12.1.2(a), 2010. The minimum density is .60 from 8ft to 20
ft. The .45 is only good to 8 ft. Unless the pile sizes are small and well
spaced I think you are looking at 8-10 ft max height. The orifice size at
11.2 and above is not the most important factor. The density controls
I think this is the elevator shaft enclosure that is a fire rated assembly
like a stair tower.
Arthur Tiroly
ATCO Fire Protection Design
Tiroly and Associates
24400 Highland Rd rm 25, CLE 44143
216-621-8899
216-570-7030 Cell
WWW.ATCOfirepro.com
-Original Message-
From:
At 30 gpm the sprinkler required is K=5.6.
In 2010 16.3.4.3.1 says 30 gpm so a K=8 sprinkler can be used at 15 psi.
Arthur Tiroly
ATCO Fire Protection Design
Tiroly and Associates
24400 Highland Rd rm 25, CLE 44143
216-621-8899
216-570-7030 Cell
WWW.ATCOfirepro.com
-Original Message-
Are their any videos of the test and procedure documents of how the test was
set up? AF systems have been around for a very long time and only recently
has there been any questions about flash fires of AF/water mix going thru a
sprinkler.
Arthur Tiroly
ATCO Fire Protection Design
Tiroly and
Bidding on a repair to a dry standpipe system with underground supply that
leaked below floor of an apartment building.
Running the pipe through the hall way to 4 standpipes is particularly
difficult.
An option is to run galvanized pipe on the flat concrete roof to connect all
4 risers to one
From old time experience there may be obstructions at the dry inspector's
test valve or other that is obstructing the flow of air. From insurance
inspector days anything over 3 minutes needs further investigation. I would
have called 15 minutes a failure in the 60's and 70's.
Arthur Tiroly
ATCO
How do you plan to drain the system full of water to reset the DPV?
Arthur Tiroly
ATCO Fire Protection Design
Tiroly and Associates
24400 Highland Rd rm 25, CLE 44143
216-621-8899
216-570-7030 Cell
WWW.ATCOfirepro.com
-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
There are stiffening beams attached to the bottom of 28 bar joist about 6
wide. Sect 8.12.5.3.1 allows 1 ft wide obstruction below the ESFR head 1 ft
away but no mention of the distance below. His seems to be an excessive
obstruction unless it was 3 ft below he deflector or is this not an
These beams are 25 ft long starting at the outside wall and parallel to the
2 branch lines. It seems line 1 ft and 2 ft wide row of lights or ducts
would be serious obstructions.
Arthur Tiroly
ATCO Fire Protection Design
Tiroly and Associates
24400 Highland Rd rm 25, CLE 44143
216-621-8899
What is the orifice size or K factor of the old heads? What area of coverage
per sprinkler? Pendent or sidewall? Is this a 13R system? You should be able
to match the K or orifice size and not be trouble.
Arthur Tiroly
ATCO Fire Protection Design
Tiroly and Associates
24400 Highland Rd rm 25,
Vertical turbine pumps take suction from open ponds and lakes with 1/2 mesh
screen.
Silt and other vegetation is common. Pendent heads on return bends are
required. Inspections and flushing will be required.
Particulates will settle to the bottom of the tanks. How to remove excess.
I don't know
I agree with the 165*F heads under grating maybe even QR heads.
With open grating will these sprinklers ever go off or will the heat blow
right through the deck up to the roof. Seems we need something to trap the
heat. What's the thought on this
Arthur Tiroly
ATCO Fire Protection Design
Tiroly
See section 11.3 Residential in 2010 NFPA 13. Residential areas and adjacent
corridors are allowed by NFPA 13 by calculating just 4 sprinklers with a .10
density or with residential flows whichever is greater
Arthur Tiroly
ATCO Fire Protection Design
Tiroly and Associates
24400 Highland Rd
May I suggest that you consider a diesel driver with a right angle gear
drive for the VT pump. This is an approved method and likely less costly.
Arthur Tiroly
ATCO Fire Protection Design
Tiroly and Associates
24400 Highland Rd rm 25, CLE 44143
216-621-8899
216-570-7030 Cell
WWW.ATCOfirepro.com
As a former HPR inspector I ask a lot questions. I get everything I need to
determine the hazards in a facility. I get criticized for asking too many
questions but I need to know what the protection requirements for the
hazardous areas. I am not a contractor but I work for contractors architects
Storage is the problem.
Finished bottled beer storage in cartons stacking?
Bags of grain storage and raw material for the process unless it is outside
storage bins.
Arthur Tiroly
ATCO Fire Protection Design
Tiroly and Associates
24400 Highland Rd rm 25, CLE 44143
216-621-8899
216-570-7030 Cell
Isn't 300 psi a high temp steam rating?
Cold water may be even more than 300 psi.
Arthur Tiroly
ATCO Fire Protection Design
Tiroly and Associates
24400 Highland Rd rm 25, CLE 44143
216-621-8899
216-570-7030 Cell
WWW.ATCOfirepro.com
-Original Message-
From:
I need some history on warehouse protection requirements.
When was high piled storage protection with hydraulic calculations required?
That was covered in NFPA 231 back then.
The problem is a 22 ft high building with a 1975 - 130 SF pipe schedule
system and a 45 psi water supply for class 3 and
...@lists.firesprinkler.org
[mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of Art
Tiroly
Sent: Monday, May 13, 2013 12:33 PM
To: sprinklerfo...@firesprinkler.org
Subject: RE: Warehouse protection
I need some history on warehouse protection requirements.
When was high piled storage protection
The building will never be used for high piled storage right?
Arthur Tiroly
ATCO Fire Protection Design
Tiroly and Associates
24400 Highland Rd rm 25, CLE 44143
216-621-8899
216-570-7030 Cell
WWW.ATCOfirepro.com
-Original Message-
From: sprinklerforum-boun...@lists.firesprinkler.org
A foam/water system could reduce the water supply required. I had very good
success with Compressed air foam. This greatly reduced water supply
required.
Arthur Tiroly
ATCO Fire Protection Design
Tiroly and Associates
24400 Highland Rd rm 25, CLE 44143
216-621-8899
216-570-7030 Cell
spec. Which manufacturer would I look at
for the system that you have used.
On Mon, May 13, 2013 at 2:39 PM, Art Tiroly atir...@atcofirepro.com wrote:
A foam/water system could reduce the water supply required. I had very
good success with Compressed air foam. This greatly reduced water
A 4 pipe 40 long with a shutoff valve should flow 1500 gpm and provide a
smooth flow to pitot.
Arthur Tiroly
ATCO Fire Protection Design
Tiroly and Associates
24400 Highland Rd rm 25, CLE 44143
216-621-8899
216-570-7030 Cell
WWW.ATCOfirepro.com
-Original Message-
From:
Are you testing the water supply and gpm/psi? If you flow 500 gpm at the
remote you can flow 250 or 500 through any outlet even on the 1st floor.
IMHO
Arthur Tiroly
ATCO Fire Protection Design
Tiroly and Associates
24400 Highland Rd rm 25, CLE 44143
216-621-8899
216-570-7030 Cell
Highland Rd rm 25, CLE 44143
216-621-8899
216-570-7030 Cell
WWW.ATCOfirepro.com
-Original Message-
From: sprinklerforum-boun...@lists.firesprinkler.org
[mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of Art
Tiroly
Sent: Tuesday, May 21, 2013 4:50 PM
To: sprinklerforum
I have a Model 38B Automatic Sprinkler 1/2 SSU head. I cant find the
date.
165*F is on the solder link. 38-600 is on the deflector.
I know it has a date somewhere. It is about 40 years old
Arthur Tiroly
ATCO Fire Protection Design
Tiroly and Associates
24400 Highland Rd rm 25, CLE 44143
-inc.com
-Original Message-
From: sprinklerforum-boun...@lists.firesprinkler.org
[mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of Art
Tiroly
Sent: Friday, May 24, 2013 2:30 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: Can't find a date
I have a Model 38B
I enjoyed his many emails over time. I was at a Ford car show in Carlisle PA
last year. I asked George to come visit our picnic dinner hour that weekend.
He came with his TR6 to watch some of our antics. It was great to meet with
him to talk shop and cars. He will be dearly missed.
Arthur
An owner wants us to cover sprinklers with a bag or dust cover to keep the
sprinklers from becoming loaded with dust.
They say the dust is noncombustible due to chemical additives in the mix.
Is this allowed?
If not how does he keep them clean?
Arthur Tiroly
ATCO Fire Protection Design
www.lakelandgov.net Working together to achieve
an exceptional quality of life
-Original Message-
From: sprinklerforum-boun...@lists.firesprinkler.org
[mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of Art
Tiroly
Sent: Friday, July 12, 2013 2:31 PM
To: sprinklerfo
plastic) will not interfere with the head opening under a fire condition.
Layers and layers of crap, on the heads or on the bags, will.
On Fri, Jul 12, 2013 at 12:19 PM, Art Tiroly
atir...@atcofirepro.comwrote:
That section applies to paint booths. Would a bag cover be acceptable
in a larger open
The problem is not the OH2 retail sales floor. Check out the expected
storage areas with the plastics, Styrofoam, aerosols and high piled rack
storage that will require storage protection.
Arthur Tiroly
ATCO Fire Protection Design
Tiroly and Associates
24400 Highland Rd rm 25, CLE 44143
1. This reduction depends on ceiling height and varies.
2. This is based on spacing over 200 SF per head and extended coverage
spacing.
Arthur Tiroly
ATCO Fire Protection Design
Tiroly and Associates
24400 Highland Rd rm 25, CLE 44143
216-621-8899
216-570-7030 Cell
WWW.ATCOfirepro.com
Why not use the residential rules in 13?
Arthur Tiroly
ATCO Fire Protection Design
Tiroly and Associates
24400 Highland Rd rm 25, CLE 44143
216-621-8899
216-570-7030 Cell
WWW.ATCOfirepro.com
-Original Message-
From: sprinklerforum-boun...@lists.firesprinkler.org
Cesar,
Viking Sprinkler has several extended coverage concealed sprinklers with
several orifice sizes. K= 5.6, 8.0 and 11.2 are available. You need to
determine the required density for the occupancy to prepare hydraulic
calculations for your project.
Art Tiroly
ATCO fire protection design
Check the TYCO attic sprinkler info again. With sloped roof in a wood truss
attic you can cover the 40-60ft wide attic with BB sprinklers at the peak
only spaced 6ft apart. They are available in K= 5.6 and 8.0 with just one
row at the peak. Attic Sprinklers are expensive but very efficient
It is up to the water company regarding backflow requirements.
Art Tiroly
ATCO Fire Protec
-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Ed Kramer
Sent: Thursday, March 11, 2010 11:23 AM
A disconnect and breaker will also disable the power to the A/C unless
locked in ON position. Low air alarm will provide the backup if not too
late.
Art
-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Greg
One concern I have is for dry pipe and preaction systems. The in-rush to
fill the system will have a short term high velocity flow that will pick up
any debris in the fire line and move it into the riser. Should that be added
to the flushing proceedure or is it a special case that that does not
George,
Is this in PA? PA has been behind code wise for years. Ohio has had nursing
home requirements for over 30 years and High rise and assistaant living for
15-20 years. Now that PA has new codes life safety should get better.
-Original Message-
From:
I have done this a few times. After the dry system piping had rusted out
this was suggested to the owner to reduce the maintenance problems with dry
sprinklers in attics. I have only know of one problem ie: when PG was
refilled in a system with CPVC piping.
Art
Tiroly and Associates
I usually end up calculating 4 sprinklers in the hall since that becomes the
largest room. What do others do?
-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Richardson, R
Sent: Friday, May 28, 2010 2:39 PM
Is this tank dedicated for fire protection? Why would you assume it is
empty? Then the water is only available for 1 minute while you empty the
riser pipe. Calculate friction loss through riser pipe down and through
sprinkler riser with an assumed flow entering the tank discharge pipe.
Eleveation
Called Potter yesterday. List price is over $1400 for the supervised unit
with the catch can. Viking has one- also very expensive. The device looks
pretty simple why so expensive? Reliability?
-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
A high temp. solder must be used - silver solder or other high temp solder
not 95-5.
Art
-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Travis Mack,
SET
Sent: Monday, June 28, 2010 12:07 PM
To:
The Ohio IBC has allowed and encourages the use of residential sprinklers in
I occupancies. We have used the residential rules in 13 with 4 head calc
areas for many years. But attics etc are required for 100% sprinkler
coverage due to NFPA 13 requirements per IBC for the I occupancy.
ART
ATCO
It is hard to visualize this to maintain reliability. Pond grass can be a
big problem. Then you need access to pump screens. I would not be in favor
of it do to reliability and maintenance.
Art
-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
to the
requirements of the new occupancy?
If it is a calculated OH2 system does that need to be brought up to the
requirements of the hazard due to the change in occupancy?
Art Tiroly/AFSA
ATCO Fire Protection
-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
Water supply is weak 63/500/20. Single 6andpipe riser in a round building.
500 gpm at 125 psi.
We are asking for a city water supply improvenent.
Arthur Tiroly
ATCO Fire Protection Design
Tiroly and Associates
216-621-8899
216-570-7030 Cell
WWW.ATCOfirepro.com
A 1.75 smooth bore nozzle has a K = 88.67. Your nozzle may be different.
Art
-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Jamie.seidl
Sent: Thursday, September 16, 2010 9:43 AM
To:
When AF is above 50% it is a combustible liquid below 50% it is not easily
ignited. Break it up, in a fine spray from sprinkler and there is no
surprise that the spray is explosive. If we cant control the industry to not
use high concentrations of AF then we must find a different method. Properly
Architect calls with a small addition to an existing 3500 SF, R4 assisted
living building. He says all we have to protect is the new addition and
some connecting rooms by the fire official. R4 only requires a 13D systems
per IBC with only 8 patients.
I want at least a 13R system and 100%
to 4 stories) can be a 13- D but
the same function in a one story building with less than 16 does not have
this explicit exception. It's an easy argument to apply it but is a call by
the AHJ.
Roland
On Sep 23, 2010, at 9:07 AM, Art Tiroly wrote:
Architect calls with a small addition to an existing
Two things could apply here. See chapter 24. See figure A.24.6 Sprinkler
system- general information and the Hydraulic Design information sign. There
is also a occupancy inforamtion sheet that I could not find quickly. These
describe what the owner intends for the building use and occupancy.
Art
As I understand it, the examinee will be allowed to take NFPA 13, 14 and 20.
No note books, calculators or loose paper. This is subject to change.
Arthur Tiroly
ATCO Fire Protection Design
Tiroly and Associates
216-621-8899
216-570-7030 Cell
WWW.ATCOfirepro.com
-Original Message-
From:
All questions are based on NFPA documents not like the old test. There are
some safety questions from OSHA handbook for level 2
Arthur Tiroly
ATCO Fire Protection Design
Tiroly and Associates
216-621-8899
216-570-7030 Cell
WWW.ATCOfirepro.com
-Original Message-
From:
Soon the element testing program will not be available. The new test is
comprehensive pass fail system. Check the NICET website for availability -
coming soon.
Arthur Tiroly
ATCO Fire Protection Design
Tiroly and Associates
216-621-8899
216-570-7030 Cell
WWW.ATCOfirepro.com
-Original
By increasing pipe sizes with velocity you are in effect increasing the
density since the required pressure is likely far below the available water
pressure. The industry rules for hydraulic calculations are pretty
conservative if the correct density has been established for the occupancy.
If I understand this correctly, are you creating a loop feed for the
hydraulics? You need check valves and control valves at both ends.
I don't think you need a standard AF loop beyond the RPZBFP. You do need to
control pressure but in a different way.
Arthur Tiroly
ATCO Fire Protection Design
Ron,
I recently tried to find IDOD pipe supplier. IDOD gave the process to a
European Co. that stole the process, never paid for it. It is no longer
available in the US. Sad!
Arthur Tiroly
ATCO Fire Protection Design
Tiroly and Associates
216-621-8899
216-570-7030 Cell
WWW.ATCOfirepro.com
Solder joints allowed only in wet systems. Dry systems require high
temperature brazed joints. The pre-action will require brazing.
Arthur Tiroly
ATCO Fire Protection Design
Tiroly and Associates
216-621-8899
216-570-7030 Cell
WWW.ATCOfirepro.com
-Original Message-
From:
I beg to differ with you. The high density spray pattern may be small but
the total spray area is much larger. After investigating a fire opened 4
ESFR sprinklers, the total spray pattern had a radius of over 10ft per
sprinkler that wet boxes in a very large area over 30' x 30' from 4
sprinklers.
Designing an auto paint booth with 3 booth areas. Airflow is down draft
with filters in the floor in a shallow 1'-6 deep pit. A typical pit is 8'x
23'. What type sprinklers will cover this shallow space? We don't have the
18 minimum space. Would pendent heads in the upright position be better
And when ice forms there will be no sprinkler flow even though the pipe may
not burst.
Arthur Tiroly
ATCO Fire Protection Design
Tiroly and Associates
216-621-8899
216-570-7030 Cell
WWW.ATCOfirepro.com http://www.atcofirepro.com/
_
From: sprinklerforum-boun...@firesprinkler.org
The booths are fully enclosed and adequately protected with .40/
ex.HAZ.GP2.. The area outside the booth only requires protection for the
surrounding occupancy. Ask the right questions about the building occupancy
to determine the requirements.
Arthur Tiroly
ATCO Fire Protection Design
Tiroly
From my experience the hydrant gage and the pitot gage read about the same
with pitots of 20-40 psi.
Arthur Tiroly
ATCO Fire Protection Design
Tiroly and Associates
216-621-8899
216-570-7030 Cell
WWW.ATCOfirepro.com
-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
I am working on a proposed trash recycling plant. Automobile trash from a
hammer mill type crusher arrives in large dump trucks. All steel has been
removed by magnets. This is mostly auto waste with a variety of
combustibles: plastic, rubber, foam seats, carpeting, door panels, fiber
board,
There is a nice detail at Tyco attic sprinklers that may help.
They reference the insulation.
SEE: http://www.tyco-fire.com/TD_TFP/TFP/TFP610_05_2008.pdf
Arthur Tiroly
ATCO Fire Protection Design
Tiroly and Associates
216-621-8899
216-570-7030 Cell
WWW.ATCOfirepro.com
-Original
Can you point to anything in NFPA that will allow this design application?
Arthur Tiroly
ATCO Fire Protection Design
Tiroly and Associates
24400 Highland Rd Rm 25, CLE 44143
216-621-8899
216-570-7030 Cell
WWW.ATCOfirepro.com
-Original Message-
From:
Check for definitions in your building code for dwelling units. You still
may be required to do closets, bathrooms and attics of course. Also follow
the guidelines in NFPA 13. These bedroom wings are usually residential areas
contrary to what the AHJ is saying. You may need to calculate .10
903.2.5 says it only applies to I-1 therefore a full 13 system is required
for I-2 IMHO.
Arthur Tiroly
ATCO Fire Protection Design
-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Johnson,
Duane (NIH/OD/ORS)
Science - One Sprinkler at a Time
-Original Message-
From: Art Tiroly [mailto:atir...@atcofirepro.com]
Sent: Tuesday, November 01, 2011 12:29 PM
To: sprinklerforum@firesprinkler.org
Subject: RE: Residential Sprinkler in I-2
903.2.5 says it only applies to I-1 therefore a full 13 system
If possible flow through the by-pass and the test header wide open. You
should get close to the required flow. Also max flow should not have to
exceed 150% of pump rated capacity.
Arthur Tiroly
ATCO Fire Protection Design
Tiroly and Associates
-Original Message-
From:
All systems will receive high pressure air. The reset system will be getting
more but all systems will receive some air in the process. The air
compressor will likely be
the same as the lowest air pressure being filled due to compressor rate and
not 90 psi.
Arthur Tiroly
ATCO Fire Protection
Your last question can be determined by hydraulic calculation. If you need
4000 gpm flowing then calculate the flow and pressure drop through 12 or
larger pipe. Check velocity and psi drop.
Arthur Tiroly
ATCO Fire Protection Design
Tiroly and Associates
24400 Highland Rd rm 25, CLE 44143
If the materials are known and the protection requirements are clear in NFPA
standards I would be comfortable designing and specifying the system. I do
have a different background than most NICET designers but I'm not a PE just
M SFPE and HPR guy.
Arthur Tiroly
ATCO Fire Protection Design
Does your state allow an ordinance to require more than the state code?
Is it possible to appeal to your state building department.
I would place the call to the state level. I have had a local ordinance
overturned in Ohio by an over zealous local city.
Arthur Tiroly
ATCO Fire Protection
Is black pipe OK above a CT Scan room.
I know MRI room res non ferrous pipe.
Arthur Tiroly
ATCO Fire Protection Design
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
What type nozzles are you using? When there is a deflector, the deflector
absorbs some of the reaction and helps to neutralize it. The arm over's will
torque from the reaction. What are the nozzle pressures you are expecting?
Arthur Tiroly
ATCO Fire Protection Design
Tiroly and Associates
24400
Does this surge in pressure occur during testing pumps or 2 drains or is it
a gradual build up likely due to the increase in water temperature in the
sprinkler system? Grid system are prone to psi increases due to temp
changes. Reducing the air pockets just makes it worse. Relief valves should
If there is a large amount of rubber ad plastic then this could be a
plastics storage hazard.
Then OH2 may not be adequate.
Arthur Tiroly
ATCO Fire Protection Design
Tiroly and Associates
24400 Highland Rd rm 25, CLE 44143
216-621-8899
216-570-7030 Cell
WWW.ATCOfirepro.com
-Original
Liquor and nail polish in small bottles is class 4 in table A5634 in the
handbook. Looks like 4 to me.
Arthur Tiroly
ATCO Fire Protection Design
Tiroly and Associates
24400 Highland Rd rm 25, CLE 44143
216-621-8899
216-570-7030 Cell
WWW.ATCOfirepro.com
-Original Message-
From:
Tony,
The problem is usually with a city water booster pump. City water is
deficient. A 1000 gpm pump is required. City pressure drops below 20 psi at
1100 gpm. You won't get 1500 gpm but it is OK.
Arthur Tiroly
ATCO Fire Protection Design
Tiroly and Associates
24400 Highland Rd rm 25, CLE
One more comment: You still need the flowing pressure OR a pitot psi or at
least a residual psi at the test header. If the BFP is becomes restricted
the pressures are necessary to determine the next step. Without psi and flow
the K has no meaning except to have a basis for the device when in new
Google Pillow Tanks
-Original Message-
From: sprinklerforum-boun...@lists.firesprinkler.org
[mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of Todd
Williams
Sent: Friday, September 13, 2013 12:01 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: Fabric suction
Can you go back to the OEM?
.
Art Tiroly
ATCO Fire Protection/Tiroly
24400 Highland Rd CLE 44143
216-621-8899
216-570-7030 cell
-Original Message-
From: sprinklerforum-boun...@lists.firesprinkler.org
[mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of Todd -
Work
Sent
Can there be a design issue in question with hydraulic calculation method or
head types that does not provide life safety.
Standard response sprinklers versus the required quick response heads would
be an issue.
Art Tiroly
ATCO Fire Protection/Tiroly
24400 Highland Rd CLE 44143
216-621-8899
216
is not
meant for storage. I have done many sprinkler assessments over the years and
designed the necessary hydraulic upgrade to the system. This is a building
code issue. There needs to be a mandatory assessment when the tenant change
occurs and at 3-5 years intervals thereafter per NFPA 25.
Art
It is not required for 3000 sf area calc. See item 4 (d) under 11.2.3.1.4.
Art Tiroly
ATCO Fire Protection
-Original Message-
From: sprinklerforum-boun...@lists.firesprinkler.org
[mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of Will
Crisler
Sent: Wednesday, February
See Fig 16.2.1.3.2B. With in-rack sprinklers and adjusting with fig
16.2.1.3.4.1 to 60% of 20 Ft. required.
OR Is this miscellaneous stge or a rack warehouse?
Art Tiroly
ATCO Fire Protection/Tiroly
24400 Highland Rd CLE 44143
216-621-8899
216-570-7030 cell
-Original Message-
From
shelves.
Bill Menster
WFM Consulting Inc.
- Original Message -
From: Art Tiroly atir...@atcofirepro.com
To: sprinklerforum@lists.firesprinkler.org
Sent: Friday, March 14, 2014 2:35:44 PM
Subject: RE: Solid Shelf Rack Storage Ceiling Density?
See Fig 16.2.1.3.2B. With in-rack
Is this really solid shelves? Or are there open longitudinal and transverse
flue spaces at the rack uprights?
Art
-Original Message-
From: sprinklerforum-boun...@lists.firesprinkler.org
[mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of
wmens...@comcast.net
Sent:
I could see a lot of stress on the valve when it is nearly closed
restricting the flow but not when it is fully open.
Art Tiroly
ATCO Fire Protection
-Original Message-
From: sprinklerforum-boun...@lists.firesprinkler.org
[mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf
The pipe going through the wall must be restrained and anchored to the wall
or floor penetration. Link seal is a water seal.
Art Tiroly
ATCO Fire Protection/Tiroly
24400 Highland Rd CLE 44143
216-621-8899
216-570-7030 cell
-Original Message-
From: Sprinklerforum [mailto:sprinklerforum
Is the powdered product combustible? Likely yes. Then It is likely class 3
.
Powder may be explosion hazard like flour or grain dust.
ART
ATCO Fire
-Original Message-
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org]
On Behalf Of Jay Stough
Sent: Wednesday,
Think about what this does to the hydraulics and turbulent flow through the
reduced orifice with over 100 gpm per head.
Art Tiroly
ATCO Fire Protection
-Original Message-
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On
Behalf Of Stafford, Susan
Sent