RE: QUESTIONS NFPA 5000 AND OTHER RULES [EXTERNAL]

2017-03-28 Thread Prahl, Craig/GVL
You can access the NFPA Standards on-line for free by going to http://www.nfpa.org/codes-and-standards/resources/free-access Sorry but can't help with BS . Craig L. Prahl Fire Protection Group Lead/SME CH2M 200 Verdae Blvd. Greenville, SC 29607 Direct - 864.920.7540 Fax - 864.920.7129

RE: NFPA 20 4.7.7.2

2017-04-06 Thread Prahl, Craig/GVL
You can't use the PRV to relieve excess pressure under normal conditions due to an over designed pump. There can be unexpected times in a municipal supply where pressure spikes occur for various reasons. If your pump selection puts you close to the maximum system working pressure under normal

RE: NFPA 20 4.7.7.2

2017-04-06 Thread Prahl, Craig/GVL
Is the 140 psi total pressure or pump rating? The pressure relief valve comes into play if the combination of supply pressure and pump pressure exceeds the allowable system pressure, which for most cases is 175 psi. So if you had fluctuating supply pressures, during a higher than normal

RE: NFPA 20 4.7.7.2

2017-04-06 Thread Prahl, Craig/GVL
is 2210.4 , From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of Prahl, Craig/GVL Sent: April-06-17 4:52 PM To: sprinklerforum@lists.firesprinkler.org<mailto:sprinklerforum@lists.firesprinkler.org> Subject: RE: NFPA 20 4.7.7.2 You can't use the PRV to r

RE: Hood System - Question

2017-04-20 Thread Prahl, Craig/GVL
the original message. From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of Prahl, Craig/GVL Sent: Thursday, April 20, 2017 2:50 PM To: sprinklerforum@lists.firesprinkler.org<mailto:sprinklerforum@lists.firesprinkler.org> Subject: RE: Hood System - Questi

RE: Hood System - Question

2017-04-20 Thread Prahl, Craig/GVL
er by reply e-mail and destroy all copies of the original message. From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of Prahl, Craig/GVL Sent: Thursday, April 20, 2017 2:50 PM To: sprinklerforum@lists.firesprinkler.org<mailto:sprinklerforum@lists.firesprin

RE: Hood System - Question

2017-04-20 Thread Prahl, Craig/GVL
You say it's "approved and listed". If that is the case, why would it not be allowed? Do you have a link to this unit? Craig L. Prahl Fire Protection Group Lead/SME CH2M 200 Verdae Blvd. Greenville, SC 29607 Direct - 864.920.7540 Fax - 864.920.7129 CH2MHILL Extension 77540

RE: Hood System - Question

2017-04-20 Thread Prahl, Craig/GVL
inklerforum-boun...@lists.firesprinkler.org] On Behalf Of Prahl, Craig/GVL Sent: Thursday, April 20, 2017 2:28 PM To: sprinklerforum@lists.firesprinkler.org<mailto:sprinklerforum@lists.firesprinkler.org> Subject: RE: Hood System - Question You say it's "approved and listed". If that is the ca

RE: ESFR Sprinkler spacing

2017-04-19 Thread Prahl, Craig/GVL
There ya go. Now you're covered. Hopefully you got that in writing. Craig L. Prahl Fire Protection Group Lead/SME CH2M 200 Verdae Blvd. Greenville, SC 29607 Direct - 864.920.7540 Fax - 864.920.7129 CH2MHILL Extension 77540 craig.pr...@ch2m.com From: Sprinklerforum

RE: ESFR Sprinkler spacing

2017-04-19 Thread Prahl, Craig/GVL
iresprinkler.org>> on behalf of Prahl, Craig/GVL <craig.pr...@ch2m.com<mailto:craig.pr...@ch2m.com>> Sent: Wednesday, April 19, 2017 1:37 PM To: sprinklerforum@lists.firesprinkler.org<mailto:sprinklerforum@lists.firesprinkler.org> Subject: RE: ESFR Sprinkler spacing NFPA wo

RE: ESFR Sprinkler spacing

2017-04-19 Thread Prahl, Craig/GVL
NFPA would define the maximum allowable generic spacing but the vendor data sheet identifies the specific limitations of the sprinkler based on its UL or other tested listing. So if the vendor data says the maximum spacing is 10 ft and you install at 11 ft you’ve installed the product outside

RE: FM Global Electrical Room Fire Protection

2017-04-24 Thread Prahl, Craig/GVL
I have had fire code officials request removal of sprinklers or to disable sprinklers in electrical rooms in the past. But I digress. The old FMDS 2-8N used to call for sprinklers in electrical rooms with the same allowed omission text as NFPA 13. I’d get mixed responses out of various FM

RE: Revit Fire Protection Classes

2017-07-11 Thread Prahl, Craig/GVL
Fax 401-725-1583 Cell 508-277-3473 From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of Prahl, Craig/GVL Sent: Monday, June 26, 2017 5:44 PM To: sprinklerforum@lists.firesprinkler.org<mailto:sprinklerforum@lists.firesprinkler.org> Subject: RE: Revi

RE: Windshields

2017-07-12 Thread Prahl, Craig/GVL
s its attachments without reading or saving it in any manner. Thank you. On Wed, Jul 12, 2017 at 10:22 AM, Prahl, Craig/GVL <craig.pr...@ch2m.com<mailto:craig.pr...@ch2m.com>> wrote: Glass windshields as used for automobiles? Craig L. Prahl Fire Protection Group Lead/SME CH2M 200

RE: Windshields

2017-07-12 Thread Prahl, Craig/GVL
Glass windshields as used for automobiles? Craig L. Prahl Fire Protection Group Lead/SME CH2M 200 Verdae Blvd. Greenville, SC 29607 Direct - 864.920.7540 Fax - 864.920.7129 CH2MHILL Extension 77540 craig.pr...@ch2m.com From: Sprinklerforum

RE: Lithium Batteries

2017-07-18 Thread Prahl, Craig/GVL
FM 200 isn’t effective with this type of hazard. With lithium batteries being charged, overcharging or a defect can lead to a thermal run-away condition which causes the batteries to vent. When they do that, the gases being vented can ignite. The danger is that while a suppression gas might

RE: Lithium Batteries

2017-07-18 Thread Prahl, Craig/GVL
Yeah there’s lithium polymer (LiPo) and LiFe and others. That’s what makes our job so much fun! J The story about the testing was that it had to end due to limited funding. Burning up lithium batteries is expensive. Craig L. Prahl Fire Protection Group Lead/SME CH2M 200 Verdae Blvd.

RE: Sprinklers protecting openings

2017-07-20 Thread Prahl, Craig/GVL
There are some great details on opening protection in the FM Data sheet 1-23 Craig L. Prahl Fire Protection Group Lead/SME CH2M 200 Verdae Blvd. Greenville, SC 29607 Direct - 864.920.7540 Fax - 864.920.7129 CH2MHILL Extension 77540 craig.pr...@ch2m.com From: Sprinklerforum

RE: Parking Under MTA Tracks

2017-06-29 Thread Prahl, Craig/GVL
The fire was from construction materials stored under the bridge but the State DOT. The bridge has already been repaired and is back in service ahead of schedule. But it goes to show that storing combustibles below a non-protected “non-combustible” structure can still result in the failure

RE: Parking Under MTA Tracks

2017-06-29 Thread Prahl, Craig/GVL
A bridge or trestle doesn’t fall under any building code occupancy group since its use and purpose is very different than any occupied structure which is dealt with by the building and fire codes. Had this discussion with an AHJ. Craig L. Prahl Fire Protection Group Lead/SME CH2M 200 Verdae

RE: 22,500 gallon Underground water storage tank and pump

2017-07-05 Thread Prahl, Craig/GVL
...@lists.firesprinkler.org You can reach the person managing the list at sprinklerforum-ow...@lists.firesprinkler.org When replying, please edit your Subject line so it is more specific than "Re: Contents of Sprinklerforum digest..." Today's Topics: 1. RE: Parking Under MTA Tracks (Prahl,

RE: Heating cable and 1" wrap.

2017-08-07 Thread Prahl, Craig/GVL
I’d be highly surprised if anyone could guarantee 100% circulation in the system to prevent freezing. I wouldn’t put my name on it. But if presented with an unheated area I’d prefer to use Dry or preaction in lieu of heat tracing an entire wet system. That just doesn’t make sense. Craig L.

RE: Request for support

2017-05-09 Thread Prahl, Craig/GVL
Rachid, I would highly recommend you secure the assistance of an experienced fire protection design person or company. Fire protection design is not something you do just by opening a book and placing sprinklers in a room. Also, the software that is used for calculating sprinkler design is

RE: Pipe Height Above Ceiling

2017-06-26 Thread Prahl, Craig/GVL
8” absolute minimum but closer to 12” typically above the ceiling. It also depends on the lay-in light fixtures purchased and clearances required for removal. Craig L. Prahl Fire Protection Group Lead/SME CH2M 200 Verdae Blvd. Greenville, SC 29607 Direct - 864.920.7540 Fax - 864.920.7129

RE: Revit Fire Protection Classes

2017-06-26 Thread Prahl, Craig/GVL
There is no "fire protection design" for REVIT. We use it to do layouts but you are manually piping the system and locating sprinklers. Nothing is automated, you still have to manually input data into your calc program. It's a little bit clumsy to use, you have limited components with which

RE: Flammable & Combustible storage

2017-05-24 Thread Prahl, Craig/GVL
Read the Table again. 10ft and 15 ft are for “containers”, you stated you also had plastic IBCs so those heights don’t apply to IBCs. Go back to chapter 9 for definition of containers and other General requirements. An inadequate sprinkler system is the same as unsprinklered. An OH2 dry

RE: Flammable & Combustible storage

2017-05-24 Thread Prahl, Craig/GVL
Agreed, if a system is to be installed, it is to be installed per the applicable Standard and Code requirements. However one question is, what use or occupancy was the building originally designed for? It seems odd that an AHJ would require only an OH2 if he knew they were storing combustible

RE: Flammable & Combustible storage

2017-05-24 Thread Prahl, Craig/GVL
You need to also be referring to the applicable Fire and building Code for hazardous materials and flammable/combustible liquids. NFPA 30 is not the end-all of requirements. I’m not understanding what you mean by the “maximum allowable quantities have been met”. Are they at the maximum

RE: Steam Driven Fire Pumps

2017-05-24 Thread Prahl, Craig/GVL
Steam turbine driven pumps are in Chapter 13 of NFPA 20. Craig L. Prahl Fire Protection Group Lead/SME CH2M 200 Verdae Blvd. Greenville, SC 29607 Direct - 864.920.7540 Fax - 864.920.7129 CH2MHILL Extension 77540 craig.pr...@ch2m.com From: Sprinklerforum

RE: Grow Facilities

2017-05-31 Thread Prahl, Craig/GVL
Where does that note come from? The AHJ or owner or Engineer of Record? Either way that info should be provided by the Engineer of Record to the installing contractor to be included in submittals to the AHJ. I would certainly hope an Engineer is not dumping this off on the installing

RE: Heating cable and 1" wrap.

2017-06-13 Thread Prahl, Craig/GVL
an ESFR system without a pump from a 20" water main. What is the poor reliability aspect Concern? Art From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of Prahl, Craig/GVL Sent: Tuesday, June 13, 2017 5:17 PM To: sprinklerforum@lists.firesprinkler.org&l

RE: Heating cable and 1" wrap.

2017-06-13 Thread Prahl, Craig/GVL
What about using Single Interlock Preaction? You could use heat detection in lieu of smoke detection depending on environmental conditions. Heat tracing a complete system is a disaster waiting to happen IMHO. Also the Heat trace system must be electronically supervised to insure operability.

RE: Review Comments

2017-06-01 Thread Prahl, Craig/GVL
FM adherence is not a requirement unless you’re directed by the OWNER to adhere to FM recommendations. Just because FM publishes a Data Sheet doesn’t mean every portion will necessarily be followed. The specifications should explicitly state what is to be followed and to what degree as this

RE: HELP - Permanent Heat Source in Sprinkler Riser Rooms

2017-06-01 Thread Prahl, Craig/GVL
A unit heater with t'stat, or ducted heat into the room. Something that is fixed in place, not someone's bathroom portable heater plugged into an outlet in the riser room. Craig L. Prahl Fire Protection Group Lead/SME CH2M 200 Verdae Blvd. Greenville, SC  29607 Direct - 864.920.7540 Fax -

RE: Revit Fire Protection Classes

2017-06-27 Thread Prahl, Craig/GVL
http://www.mfpdesign.com https://www.facebook.com/pages/MFP-Design-LLC/92218417692 Send large files to us via: https://www.hightail.com/u/MFPDesign LinkedIn: https://www.linkedin.com/in/travismack From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of Prahl, Cra

RE: Revit Fire Protection Classes

2017-06-27 Thread Prahl, Craig/GVL
hightail.com/u/MFPDesign LinkedIn: https://www.linkedin.com/in/travismack From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of Prahl, Craig/GVL Sent: Monday, June 26, 2017 2:44 PM To: sprinklerforum@lists.firesprinkler.org<mailto:sprinklerforum@lists.firesprink

RE: Carbon Fiber Protection

2017-09-18 Thread Prahl, Craig/GVL
The raw fiber isn’t a class III, it won’t burn, actually burning it, the Carbonization process, “burns” the material. The spools on which the fiber is wound are actually more of a hazard (and not really much of one) than the fiber itself. The finished product shouldn’t be sensitive to water

RE: Liability Question

2017-09-18 Thread Prahl, Craig/GVL
I wouldn't waste my time or money arguing with him. It's hard to battle arrogance. He is the engineer of record and he stamps the design, he is responsible for it. Design it his way and keep good records of all conversations and documents. The piece of paper on the wall all too often means

RE: Flight Simulator Bldg

2017-09-20 Thread Prahl, Craig/GVL
Are these servo motor articulated or use hydraulic fluids? If there are no hydraulic fluids or other contributing hazards, the building may be able to classified as an F-2 occupancy and no sprinklers required. You might also investigate the possibility of a water mist or hybrid water mist

RE: Question for one of the smart ones...

2017-10-10 Thread Prahl, Craig/GVL
If they are standard IBC steel caged totes I would consider them stable. Craig L. Prahl Fire Protection Group Lead/SME CH2M 200 Verdae Blvd. Greenville, SC 29607 Direct - 864.920.7540 Fax - 864.920.7129 CH2MHILL Extension 77540 craig.pr...@ch2m.com From: Sprinklerforum

RE: Question for one of the smart ones...

2017-10-10 Thread Prahl, Craig/GVL
One thing to keep in mind, some manufacture’s recommendations do not permit full totes to be stacked more than 2-high. Empty may be different. Check with the Tote vendor on their stacking limitations. Craig L. Prahl Fire Protection Group Lead/SME CH2M 200 Verdae Blvd. Greenville, SC 29607

RE: Car Wash Station

2017-10-12 Thread Prahl, Craig/GVL
If the chemicals used could harm brass sprinklers, the cars stand no chance of survival. Plus the wash spray is typically focused more downward around the car than upward at the underside of the roof where the sprinklers reside. Craig L. Prahl Fire Protection Group Lead/SME CH2M 200 Verdae

RE: Car Wash Station

2017-10-12 Thread Prahl, Craig/GVL
- From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of Prahl, Craig/GVL Sent: Thursday, October 12, 2017 2:03 PM To: sprinklerforum@lists.firesprinkler.org Subject: RE: Car Wash Station If the chemicals used could harm brass sprinklers, the cars stand

RE: RE: Car Wash Station

2017-10-12 Thread Prahl, Craig/GVL
if that is really an issue or not, but I would probably use white poly heads. Cost difference is basically negligible. -Original Message- From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of Prahl, Craig/GVL Sent: Thursday, October 12, 2017 2:17 PM

RE: Standpipe question

2017-08-30 Thread Prahl, Craig/GVL
While all of that is true, there are times when you just cannot provide a wet standpipe such as in this case. However, from some discussions I’ve had, they would not charge into a fire until flow is established at the riser. Craig L. Prahl Fire Protection Group Lead/SME CH2M 200 Verdae Blvd.

RE: Paint Spray Operations

2017-08-30 Thread Prahl, Craig/GVL
>From past design discussions, this section assumes the area in which the >booths are installed is protected by an automatic sprinkler system and that >sublevel sprinklers are provided within the spray booths. The sublevel >sprinkler array in the booth(s) being provided with a control valve of

RE: Life Safety in Foam Systems

2017-09-26 Thread Prahl, Craig/GVL
If it is a simple NFPA 16 type foam-water system, expansion is a non-issue. AR-AFFF or AFFF are not intended to expand to fill a space, their expansion is very minimal as they are intended to blanket. Would you worry about someone drowning in the room if it were water-only sprinklers? If ALL

RE: Life Safety in Foam Systems

2017-09-26 Thread Prahl, Craig/GVL
1. Why are they asking for 7 heads in a 300 sq. ft. room? Does this include sub-level heads below obstructions? 2. Are you providing high expansion foam, only HEF will “fill a room”. 3. Foam-water systems are typically provided to protect areas subject to pool fires. The idea is to

RE: Parking under 13R system

2017-08-28 Thread Prahl, Craig/GVL
I can’t see stretching the definition of a carport to include a parking space located directly below an occupied space? It’s a parking garage level. I don’t think there’s anything fuzzy about what a carport would look like versus a parking deck/parking garage. Based on the Merriam Webster

RE: Clean Room Sprinkler Options

2017-10-18 Thread Prahl, Craig/GVL
fitting/escutcheon with a gasket to make a tight connection to the ceiling, so nothing could transfer from the concealed space into the clean room. Larry Keeping From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of Prahl, Craig/GVL Sent: October-17-17 4:17 PM

RE: Clean Room Sprinkler Options

2017-10-18 Thread Prahl, Craig/GVL
Same basic concept as the TYCO boot. Craig L. Prahl Fire Protection Group Lead/SME CH2M 200 Verdae Blvd. Greenville, SC 29607 Direct - 864.920.7540 Fax - 864.920.7129 CH2MHILL Extension 77540 craig.pr...@ch2m.com From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On

RE: Electric unit heaters

2017-10-17 Thread Prahl, Craig/GVL
What would be the fuel source? Nice warm space = squirrel nesting material? Craig L. Prahl Fire Protection Group Lead/SME CH2M 200 Verdae Blvd. Greenville, SC 29607 Direct - 864.920.7540 Fax - 864.920.7129 CH2MHILL Extension 77540 craig.pr...@ch2m.com From: Sprinklerforum

RE: Clean Room Sprinkler Options

2017-10-17 Thread Prahl, Craig/GVL
If you have a LH or OH criteria where the concealed heads can be used, one method that was approved by one of the big insurers for a similar installation used the TYCO DSB-2 dry sprinkler boot on the sprinkler drop. The boot was placed over the drop and sealed against the upper side of the

RE: Clean Room Sprinkler Options

2017-10-18 Thread Prahl, Craig/GVL
the top of the cup is required. On Wed, Oct 18, 2017 at 4:31 PM Prahl, Craig/GVL <craig.pr...@ch2m.com<mailto:craig.pr...@ch2m.com>> wrote: The cover is held on by solder tabs which melt and release the cover when the setpoint temperature of the cover plate is reached. You can a

RE: Clean Room Sprinkler Options

2017-10-18 Thread Prahl, Craig/GVL
with a gasket to make a tight connection to the ceiling, so nothing could transfer from the concealed space into the clean room. Larry Keeping From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of Prahl, Craig/GVL Sent: October-17-17 4:17 PM To: sprinkle

RE: Cartoned Expanded Group "A" Plastics

2017-12-12 Thread Prahl, Craig/GVL
When the NFPA Standards do not specifically address a particular situation, it is common to reach out to other recognized industry standards for guidance. FM Data Sheets often provide that info or you may find other Standards or Industry Practices/Guidelines that address a unique condition

RE: Informal Interps

2017-12-19 Thread Prahl, Craig/GVL
No one can be an expert in ALL things but one should be working to become an expert in MORE things. Craig L. Prahl Fire Protection Group Lead/SME CH2M 200 Verdae Blvd. Greenville, SC 29607 Direct - 864.920.7540 Fax - 864.920.7129 CH2MHILL Extension 77540 craig.pr...@ch2m.com From:

RE: St Louis Fire

2017-11-20 Thread Prahl, Craig/GVL
I'm always curious about what type of fire suppression system existed or if there even was one when an event such as this occurs. Glad there were no serious injuries. Craig L. Prahl Fire Protection Group Lead/SME CH2M 200 Verdae Blvd. Greenville, SC 29607 Direct - 864.920.7540 Fax -

1" grooved pipe and couplings and 2" and below grooved pipe

2017-11-20 Thread Prahl, Craig/GVL
I'm wondering what the consensus is amongst the group here on a couple issues as I look towards making some updates to our project specifications. #1, the use of 1" grooved pipe and fittings versus threaded. This would be using Sch. 40 pipe. I saw a presentation which if I were still a

RE: Fabric Ductwork - ESFR obstruction?

2017-11-14 Thread Prahl, Craig/GVL
...@lists.firesprinkler.org>] On Behalf Of Prahl, Craig/GVL Sent: Wednesday, November 08, 2017 4:29 PM To: sprinklerforum@lists.firesprinkler.org<mailto:sprinklerforum@lists.firesprinkler.org> Subject: RE: Fabric Ductwork - ESFR obstruction? Some of the fabric duct is designed not to co

RE: Fabric Ductwork - ESFR obstruction?

2017-11-08 Thread Prahl, Craig/GVL
Some of the fabric duct is designed not to collapse. I’m assuming this has been verified as not being that type? Craig L. Prahl Fire Protection Group Lead/SME CH2M 200 Verdae Blvd. Greenville, SC 29607 Direct - 864.920.7540 Fax - 864.920.7129 CH2MHILL Extension 77540 craig.pr...@ch2m.com

RE: compressor size

2017-11-08 Thread Prahl, Craig/GVL
General Air Products has a chart on their web page. Go to pg. 12 https://www.generalairproducts.com/media/files/GAP-fire-protection-air-compressors-brochure.pdf Craig L. Prahl Fire Protection Group Lead/SME CH2M 200 Verdae Blvd. Greenville, SC 29607 Direct - 864.920.7540 Fax - 864.920.7129

RE: High-Rise with Secondary Water Supply

2017-12-07 Thread Prahl, Craig/GVL
rs Saves Lives On Dec 6, 2017, at 1:47 PM, Prahl, Craig/GVL <craig.pr...@ch2m.com<mailto:craig.pr...@ch2m.com>> wrote: This section of pipe would not be a fire main, it would be part of the domestic water service, installed under the plumbing code by the plumber, not the sprinkler

RE: High-Rise with Secondary Water Supply

2017-12-07 Thread Prahl, Craig/GVL
://www.firesprinkler.org<http://www.firesprinkler.org/> Fire Sprinklers Saves Lives On Dec 6, 2017, at 1:47 PM, Prahl, Craig/GVL <craig.pr...@ch2m.com<mailto:craig.pr...@ch2m.com>> wrote: This section of pipe would not be a fire main, it would be part of the domestic water servic

RE: Nebraska Edition of NFPA 13

2017-12-11 Thread Prahl, Craig/GVL
When I doubt, make a call. It’s not that hard. If you can’t find the information on the State or local Fire Department, Code Enforcement or Building and Construction websites, make a call. Google the state or city and enter “fire codes” or “building codes”, then check several of the links

RE: High-Rise with Secondary Water Supply

2017-12-06 Thread Prahl, Craig/GVL
Why would you put a flow switch on the pump supply running through the building? I’m assuming this is from a potable source? If so, how is it any different than any other potable water service line running through the building? Why would he chances of this line leaking be any greater than

RE: High-Rise with Secondary Water Supply

2017-12-06 Thread Prahl, Craig/GVL
And that is the question. Why isn’t the BFP installed back at the origination of this 200 ft section as it comes out of the ground? Craig L. Prahl Fire Protection Group Lead/SME CH2M 200 Verdae Blvd. Greenville, SC 29607 Direct - 864.920.7540 Fax - 864.920.7129 CH2MHILL Extension 77540

RE: High-Rise with Secondary Water Supply

2017-12-06 Thread Prahl, Craig/GVL
Of Prahl, Craig/GVL Sent: Wednesday, December 06, 2017 2:55 PM To: sprinklerforum@lists.firesprinkler.org<mailto:sprinklerforum@lists.firesprinkler.org> Subject: RE: High-Rise with Secondary Water Supply Why would you put a flow switch on the pump supply running through the building? I’m as

RE: Underground Main

2017-10-25 Thread Prahl, Craig/GVL
There's nothing prohibiting you from flowing multiple hydrants. In some cases, you absolutely have to such as when you have large Fire Flow values. Ken's direction is spot on, it's an easy calculation. Use At times when we have had looped mains we have had to prove flow capabilities with

RE: Multiple Pumps

2017-12-20 Thread Prahl, Craig/GVL
You could use multiple pumps to achieve the desired flow rate but there would be no advantage in doing so. You would ultimately cost the owner more money in up-front installation costs as well as long term maintenance and inspection costs. I do a lot of large flow facilities where 8,000

RE: Multiple Pumps

2017-12-20 Thread Prahl, Craig/GVL
ail. Matt From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of Prahl, Craig/GVL Sent: Wednesday, December 20, 2017 7:34 AM To: sprinklerforum@lists.firesprinkler.org<mailto:sprinklerforum@lists.firesprinkler.org> Subject: RE: Multiple Pumps Y

RE: [EXTERNAL] Conveyor Protection

2018-05-14 Thread Prahl, Craig/GVL
Typically large material conveyors such as this are deluge systems but they can be wet or dry or preaction depending on the size, length and arrangement and value. Overland materials conveyors I've worked on were segmented into 100-200 ft sections based on whatever the water supply can handle

RE: [EXTERNAL] RE: Misc Rack Storage

2018-05-17 Thread Prahl, Craig/GVL
Not necessarily, you could use the provision of dissimilar adjacent hazards where you extend the more demanding design criteria 15 ft beyond the limit of that area per 12.3 (1) (2016 NFPA 13). Craig Prahl | Jacobs | Group Lead – Fire Protection | 864.676.5252 | craig.pr...@jacobs.com |

RE: Building Utility Tunnels

2018-05-16 Thread Prahl, Craig/GVL
What is the tunnel for? When you say utility, what kinds of systems conveying materials are being run through the tunnels? Either way, a utility tunnel typically won’t meet the whole definition of 8.15.1.2.2. Since it is accessible, it is really no different than a utility room or other

RE: Building Utility Tunnels

2018-05-16 Thread Prahl, Craig/GVL
Ye5iSi-kk=6qYbbLx8x0UrMujmEGNoh-2hzoFD2d1EB5d2sQF0_OI=fVkSvNDN5x6W9mHOTUUX54dzZ0wkHRmp6OiGSfxBruw=_mNdfyii3zW3l-_u4fN9EFiDWLqsS554JAfzsd3PbgU=> From: Sprinklerforum <sprinklerforum-boun...@lists.firesprinkler.org<mailto:sprinklerforum-boun...@lists.firesprinkler.org>> On Behalf Of Prahl, Craig/

RE: [EXTERNAL] Misc. Gas Storage

2018-05-16 Thread Prahl, Craig/GVL
Typically, propane tanks are stored in steel mesh cages not enclosed boxes. Same for the oxygen bottles. If these are in a flammable storage cabinet, then that’s another issue. NFPA 55, 6.10 provides design criteria guidance based on the type of gas. Overhead sprinklers are standard fare,

RE: [EXTERNAL] Ground Storage tank

2018-06-13 Thread Prahl, Craig/GVL
When sizing a water storage tank for fire protection do no forget the IFC code requirement for Fire Flow in section 507. It's an additional water supply requirement apart from sprinkler flow. This is especially critical if the municipal supply is not sufficient to meet the required flow rates

Heat detectors in fire pump house

2018-06-11 Thread Prahl, Craig/GVL
Had a question raised about whether or not there is a code or standard requirement for a heat detector in a standalone diesel fire pump house. I’ve hunted through just about every resource I’ve got and have not found any requirement on either heat or smoke detection. Have I missed something

RE: FM Mutual & ESFR Heads

2018-06-04 Thread Prahl, Craig/GVL
They don't use the term ESFR in their documentation. They do however describe the types of sprinklers such a Quick Response Suppression style storage sprinkler or similar jargon. Craig Prahl | Jacobs | Group Lead - Fire Protection | 864.676.5252 | craig.pr...@jacobs.com |

RE: [EXTERNAL] Information Technology Rooms

2018-06-05 Thread Prahl, Craig/GVL
The Standard says within itself that it is not the intent to apply this standard just because a computer is present. Obviously common sense and good engineering judgement should be applied when determining the applicability of the Standard. It's not a one-size-fits-all solution or guide.

RE: [EXTERNAL] RE: % open

2018-06-26 Thread Prahl, Craig/GVL
fpoint.com/v2/url?u=https-3A__www.hightail.com_u_MFPDesign=DwMFaQ=OgZOSER8c1RLeytEexU279Q2qk0jVwkrOdYe5iSi-kk=6qYbbLx8x0UrMujmEGNoh-2hzoFD2d1EB5d2sQF0_OI=EpLUAOR23O-8xVojIlUTgQxQLXZuulkZ__R8b-34160=K0gvUuMMKDClrXq8g0eSvguuW1CSjlfR33oOpm4FFV4=> Sent from my iPhone On Jun 26, 2018,

Real system pressures versus the calculations

2018-06-27 Thread Prahl, Craig/GVL
I have a system that was originally designed with a fire pump taking suction from an elevated municipal water tank. At some point in time the system source was changed from the tank to a municipal water supply. This change has resulted in the system pressures being well over 200-250 psi. So

RE: [EXTERNAL] RE: Real system pressures versus the calculations

2018-06-27 Thread Prahl, Craig/GVL
arious floor levels. Matt From: Sprinklerforum mailto:sprinklerforum-boun...@lists.firesprinkler.org>> On Behalf Of Prahl, Craig/GVL Sent: Wednesday, June 27, 2018 10:34 AM To: sprinklerforum@lists.firesprinkler.org<mailto:sprinklerforum@lists.firesprinkler.org> Subject: RE: [EXTERNA

RE: [EXTERNAL] RE: Real system pressures versus the calculations

2018-06-27 Thread Prahl, Craig/GVL
; On Behalf Of Prahl, Craig/GVL Sent: Wednesday, June 27, 2018 11:09 AM To: sprinklerforum@lists.firesprinkler.org<mailto:sprinklerforum@lists.firesprinkler.org> Subject: RE: [EXTERNAL] RE: Real system pressures versus the calculations Matt, the point is, that when the pump starts it int

RE: [EXTERNAL] RE: Real system pressures versus the calculations

2018-06-27 Thread Prahl, Craig/GVL
UrMujmEGNoh-2hzoFD2d1EB5d2sQF0_OI=TLFSl1U9Qj0s0yFLejZ21gAPh9nu1h7UpvICxkhX_dQ=kaKtfZQLNwhRlGJkqbhIKQMGXnFx83VbOLUlPhMK6FA=> “The bitterness of poor quality remains long after the sweetness of low price is forgotten.” From: Sprinklerforum mailto:sprinklerforum-boun...@lists.firesprinkler.org&g

RE: [EXTERNAL] Re: Real system pressures versus the calculations

2018-06-27 Thread Prahl, Craig/GVL
R67Hld0rY=EMtRTfazpYo9Jqx2Sw8CRcqLKHDKE_c9kkImir7w8dU=> Fire Sprinklers Saves Lives On Jun 27, 2018, at 8:21 AM, Prahl, Craig/GVL mailto:craig.pr...@ch2m.com>> wrote: I have a system that was originally designed with a fire pump taking suction from an elevated municipal water tank. At some point in time the system source

RE: [EXTERNAL] RE: % open

2018-06-25 Thread Prahl, Craig/GVL
8.15.14 doesn't apply to this application. That section is for grated "ceilings" installed below sprinklers. Trellis construction being open is similar to a pergola where there is no ceiling/roof. Being open, you can't trap heat or smoke as long as they don't plan to let plants grow on the

RE: [EXTERNAL] RE: % open

2018-06-25 Thread Prahl, Craig/GVL
Noh-2hzoFD2d1EB5d2sQF0_OI=GPz5cbJKDt5fO5kVrASI03foPAM1A7VWPJWXcqFI_qo=uE4TJL78cXsNlZL-atfB7HxpJ688ObFjrbV-cfbLixM=> Sent from my iPhone On Jun 25, 2018, at 8:24 AM, Prahl, Craig/GVL mailto:craig.pr...@ch2m.com>> wrote: 8.15.14 doesn’t apply to this application. That section is for grated “ce

RE: [EXTERNAL] RE: % open

2018-06-26 Thread Prahl, Craig/GVL
gt; Send large files to MFP Design via: https://www.hightail.com/u/MFPDesign<https://urldefense.proofpoint.com/v2/url?u=https-3A__www.hightail.com_u_MFPDesign=DwMFaQ=OgZOSER8c1RLeytEexU279Q2qk0jVwkrOdYe5iSi-kk=6qYbbLx8x0UrMujmEGNoh-2hzoFD2d1EB5d2sQF0_OI=ldfn84awZfQoxMvvMFaimdThYgKV-8RmhSM65xJt1_E=dWDdPsdpT1p-pakOnYfQtS7u

RE: powder coating ovens

2018-01-24 Thread Prahl, Craig/GVL
Verdae Blvd. Greenville, SC 29607 Direct - 864.920.7540 Fax - 864.920.7129 CH2MHILL Extension 77540 craig.pr...@ch2m.com From: Prahl, Craig/GVL Sent: Wednesday, January 24, 2018 2:48 PM To: sprinklerforum@lists.firesprinkler.org Subject: RE: powder coating ovens [EXTERNAL] Chapter 30 of the IFC

RE: Conveyors

2018-01-24 Thread Prahl, Craig/GVL
sprinkler.org<mailto:sprinklerforum-boun...@lists.firesprinkler.org>> on behalf of Prahl, Craig/GVL <craig.pr...@ch2m.com<mailto:craig.pr...@ch2m.com>> Sent: Wednesday, January 24, 2018 3:57 PM To: sprinklerforum@lists.firesprinkler.org<mailto:sprinklerforum@lists.firesprinkl

RE: Conveyors

2018-01-24 Thread Prahl, Craig/GVL
What is the actual spacing between the rollers? We have at times had to provide spray beneath conveyors since that is an area where debris could accumulate and often where drive units were located. Is this conveyor covered? I'm curious since you stated it was protected by ESFR which is a bit

RE: powder coating ovens

2018-01-24 Thread Prahl, Craig/GVL
Chapter 30 of the IFC deals with ovens/furnaces. First determine the Class of the oven based on its use. If your process falls into the definition of use for a Class A or Class B oven per Section 3006, internal fire protection is needed. Powder Coating curing ovens are often considered Class

RE: Conveyors

2018-01-24 Thread Prahl, Craig/GVL
inkler.org] On Behalf Of Prahl, Craig/GVL Sent: Wednesday, January 24, 2018 1:44 PM To: sprinklerforum@lists.firesprinkler.org<mailto:sprinklerforum@lists.firesprinkler.org> Subject: RE: Conveyors There are numerous occupancies with conveyors with numerously different cleanliness standa

RE: Conveyors

2018-01-24 Thread Prahl, Craig/GVL
There are numerous occupancies with conveyors with numerously different cleanliness standards and numerous different types of material being handled. Not every place fits into this nice neat tiny little box you describe. Craig L. Prahl Fire Protection Group Lead/SME JACOBS - CH2M 200 Verdae

RE: Conveyors

2018-01-24 Thread Prahl, Craig/GVL
02 PM To: sprinklerforum@lists.firesprinkler.org Subject: Re: Conveyors [EXTERNAL] nope From: Sprinklerforum <sprinklerforum-boun...@lists.firesprinkler.org<mailto:sprinklerforum-boun...@lists.firesprinkler.org>> on behalf of Prahl, Craig/GVL <craig.pr...@ch2m

RE: Rubber Tire Storage

2018-01-25 Thread Prahl, Craig/GVL
Tires are tires. Tires are not plastic milk jugs. Today's modern tires are a composition of numerous materials. Natural and synthetic rubbers are used in various proportions depending the tire use group. But regardless, synthetic rubber or not, the chemical characteristics, ignition and

RE: Rubber Tire Storage

2018-01-25 Thread Prahl, Craig/GVL
If you were dealing with purely synthetic rubber in slabs that would be a whole different story. But a slab of rubber is different than a tire. Craig L. Prahl Fire Protection Group Lead/SME JACOBS - CH2M 200 Verdae Blvd. Greenville, SC 29607 Direct - 864.920.7540 Fax - 864.920.7129 CH2MHILL

RE: Conveyors

2018-01-25 Thread Prahl, Craig/GVL
ode allows omission of sprinklers under conveyors yet? Mike From: Sprinklerforum <sprinklerforum-boun...@lists.firesprinkler.org<mailto:sprinklerforum-boun...@lists.firesprinkler.org>> on behalf of Prahl, Craig/GVL <craig.pr...@ch2m.com<mailto:cra

RE: Conveyors

2018-01-25 Thread Prahl, Craig/GVL
: Sprinklerforum <sprinklerforum-boun...@lists.firesprinkler.org<mailto:sprinklerforum-boun...@lists.firesprinkler.org>> on behalf of Prahl, Craig/GVL <craig.pr...@ch2m.com<mailto:craig.pr...@ch2m.com>> Sent: Wednesday, January 24, 2018 4:45 PM To: sprinklerforum