This issue was addressed at the first revision on NFPA 13 regarding
noncombustible/limited-cpmbustible vestibules that contain no combustibles can
have the sprinkler omitted. This is certainly a reasonable allowance so has a
high likelihood of remaining through the second revision but you
Not that it helps you, but just an FYI. Minnesota now allows omission of
sprinklers in vestibules that meet certain criteria...
2015 MN Building Code
903.3.1.6.5 Vestibules.
Sprinkler protection is not required in vestibules that meet all of the
following conditions:
1. The vestibule is 225
Todd G Williams, PE Fire Protection Design/Consulting Stonington, CT
860-535-2080 (ofc) 860-608-4559 (cell)
via Newton Mail
[https://cloudmagic.com/k/d/mailapp?ct=ti=9.1.25=9.3.5=email_footer_2]
On Tue, Oct 18, 2016 at 7:24 PM, Brad Casterline
wrote:
but:
1) you still
but:
1) you still have your pride
2) those whom come after you will have an easier path, and,
3) those type of bully ahjs and inspectors change careers, becoming shoe
salesmen, etc.
On Oct 18, 2016 6:13 PM, "Travis Mack, SET" wrote:
> What is the cost of a dry pendent
What is the cost of a dry pendent installed? $100, $300??? How many man
hours is going to be spent by the contractor trying to fight against
it? Sometimes when you win, you still lose.
Travis Mack, SET
MFP Design, LLC
2508 E Lodgepole Drive
Gilbert, AZ 85298
480-505-9271
fax: 866-430-6107
That may be Travis, but it's more economical to tell the ahj where to put
it in this case.
b
On Oct 18, 2016 6:02 PM, "Travis Mack" wrote:
> We've had so many ahjs and inspectors require that it is just easier to
> put in.
>
> Travis Mack, SET
> MFP Design, LLC
> "Follow"
We've had so many ahjs and inspectors require that it is just easier to put in.
Travis Mack, SET
MFP Design, LLC
"Follow" us on Facebook:
https://www.facebook.com/pages/MFP-Design-LLC/92218417692
Send large files to MFP Design via:
https://www.hightail.com/u/MFPDesign
Sent from my iPhone
> On
Thats why i put the "?" after overhang.
How is it physically different?
We don't often sprinkler exterior floor areas.
Brad
On Oct 18, 2016 5:48 PM, "Travis Mack, SET" wrote:
> I have run into this many times. We always put a dry pendent in that area.
>
> Travis Mack, SET
This issue was addressed at the first revision regarding
noncombustible/limited-cpmbustible vestibules that contain no combustibles can
have the sprinkler omitted. This is certainly a reasonable allowance so has a
high likelihood of remaining through the second revision but you never know
I have run into this many times. We always put a dry pendent in that area.
Travis Mack, SET
MFP Design, LLC
2508 E Lodgepole Drive
Gilbert, AZ 85298
480-505-9271
fax: 866-430-6107
email:tm...@mfpdesign.com
http://www.mfpdesign.com
https://www.facebook.com/pages/MFP-Design-LLC/92218417692
Send
Not an overhang. The entry way juts into the warehouse so that the roof of the
building is still overhead fully protected and there is a 20ft gap then the
entry way. Since its cold in the winter here I would need to install a dry
pendant to protect the space below the entry ceiling. Just trying
Sounds like an exterior floor space with no fuel load to me. The 10 ft high
noncomb ceiling is an overhang?
I'm gonna scratch my head on 8.15.7.4 a while, but I don't think that's
your get out of Sprink free card here.
Brad
On Oct 18, 2016 7:38 AM, "Dewayne Martinez"
NFPA 13 (07ed)8.15.7.4
I have a warehouse that is 30ft tall with inset entryways with
non-combustible walls/doors on 3 sides and open on the 4 to the outside.
The entryway is about 10ft tall with a noncombustible ceiling. Would
8.15.7.4 (or any other rule) allow me to omit sprinkler protection