: 1/15/20 10:51 AM (GMT-06:00)
To: sprinklerforum@lists.firesprinkler.org
Cc: Michael Goodis , "'Travis Mack, SET, CFPS, CWBSP, RME-G'"
Subject: RE: [EXTERNAL] Pipe adjacent to duct
Bim modeling, that’s funny. Never seen it work yet…. Only thing its been god
for is (your duct is in t
ce-+(706?entry=gmail=g>)
> 790-3473*
>
> *Cell- (706) 220-8822*
>
> *Fax: (706) 738-2119*
>
>
>
>
>
>
>
> *From:* Sprinklerforum *On
> Behalf Of *Travis Mack, SET, CFPS, CWBSP, RME-G via Sprinklerforum
> *Sent:* Wednesday, January 15, 2020 11:44 AM
2020 8:54 AM
To: sprinklerforum@lists.firesprinkler.org
Cc: Travis Mack, SET, CFPS, CWBSP, RME-G
Subject: RE: [EXTERNAL] Pipe adjacent to duct
Well, when I’ve gotten that “it’s in the code” response from an AHJ and I am
pretty certain it is not, I respectfully request them to please prov
, CWBSP, RME-G'
Subject: RE: [EXTERNAL] Pipe adjacent to duct
Bim modeling, that’s funny. Never seen it work yet…. Only thing its been god
for is (your duct is in the way, we see you cant move, the model is wrong, let
now reroute due to the conflict, oh and wait, its not a CO because
ehalf
Of Bob Knight via Sprinklerforum
Sent: Wednesday, January 15, 2020 10:02 AM
To: sprinklerforum@lists.firesprinkler.org
Cc: Bob Knight
Subject: RE: Pipe adjacent to duct
Travis,
The only thing I can think of is where there is to be a 2” clearance to
structural that isn’t supportin
[mailto:sprinklerforum-boun...@lists.firesprinkler.org] On
Behalf Of Travis Mack via Sprinklerforum
Sent: Wednesday, January 15, 2020 6:54 AM
To:
Cc: Travis Mack
Subject: Pipe adjacent to duct
We have a project where the fire inspector is stating that the fire sprinkler
main is too close
Subject: RE: [EXTERNAL] Pipe adjacent to duct
Exactly. It’s all up in the air. It was a BIM job and not an issue with
anyone during coordination. Now it’s all up in the air installed and seems to
be an issue. You can’t win some days. Plus, it shouldn’t be an issue at all,
but now it is.
) 738-2119
From: Sprinklerforum On Behalf
Of Travis Mack, SET, CFPS, CWBSP, RME-G via Sprinklerforum
Sent: Wednesday, January 15, 2020 11:44 AM
To: sprinklerforum@lists.firesprinkler.org
Cc: Travis Mack, SET, CFPS, CWBSP, RME-G
Subject: RE: [EXTERNAL] Pipe adjacent to duct
Exactly
annon ; Matthew J Willis
; jdenha...@stricklandfire.com
Subject: RE: [EXTERNAL] Pipe adjacent to duct
Well it’s only a click of the mouse and it’s moved, so what’s your problem?
Craig Prahl | Jacobs | Group Lead/SME – Fire Protection | 864.676.5252 |
<mailto:craig.pr...@jacobs.com> cr
ville, South Carolina 29606
From: Sprinklerforum On Behalf
Of Travis Mack via Sprinklerforum
Sent: Wednesday, January 15, 2020 11:34 AM
To: sprinklerforum@lists.firesprinkler.org
Cc: Travis Mack ; jdenha...@stricklandfire.com; Matthew J
Willis ; David Bohannon
Subject: Re: [EXTERNAL] Pipe adjacent
AM, Matthew J Willis via Sprinklerforum
> wrote:
>
>
> Hahahahaha
>
>
>
>
> From: David Bohannon
> Sent: Wednesday, January 15, 2020 9:21 AM
> To: sprinklerforum@lists.firesprinkler.org
> Cc: Matthew J Willis ; jdenha...@stricklandfire.com
> Sub
Hahahahaha
From: David Bohannon
Sent: Wednesday, January 15, 2020 9:21 AM
To: sprinklerforum@lists.firesprinkler.org
Cc: Matthew J Willis ; jdenha...@stricklandfire.com
Subject: RE: [EXTERNAL] Pipe adjacent to duct
Just a question. If the duct is to close to the fire main why wouldn’t
- Mobile
From: Sprinklerforum On Behalf
Of Matthew J Willis via Sprinklerforum
Sent: Wednesday, January 15, 2020 10:00 AM
To: sprinklerforum@lists.firesprinkler.org
Cc: Matthew J Willis
Subject: RE: [EXTERNAL] Pipe adjacent to duct
Educate him.
Use your charm.
R/
Matt
Sprinklerforum
Sent: Wednesday, January 15, 2020 10:00 AM
To: sprinklerforum@lists.firesprinkler.org
Cc: Matthew J Willis
Subject: RE: [EXTERNAL] Pipe adjacent to duct
Educate him.
Use your charm.
R/
Matt
From: Sprinklerforum
mailto:sprinklerforum-boun...@lists.firesprinkler.org>>
On Behalf Of
Educate him.
Use your charm.
R/
Matt
From: Sprinklerforum On Behalf
Of Travis Mack via Sprinklerforum
Sent: Wednesday, January 15, 2020 7:16 AM
To: sprinklerforum@lists.firesprinkler.org
Cc: Travis Mack ; Prahl, Craig/GVL
Subject: Re: [EXTERNAL] Pipe adjacent to duct
No seismic
.5252 |
> craig.pr...@jacobs.com | www.jacobs.com
> 1041 East Butler Road Greenville, South Carolina 29606
>
> From: Sprinklerforum On
> Behalf Of Travis Mack via Sprinklerforum
> Sent: Wednesday, January 15, 2020 8:54 AM
> To:
>
> Cc: Travis Mack
> Subject: [EXTERNA
lto:sprinklerforum@lists.firesprinkler.org>>
mailto:sprinklerforum@lists.firesprinkler.org>>
Cc: Travis Mack mailto:tm...@mfpdesign.com>>
Subject: [EXTERNAL] Pipe adjacent to duct
We have a project where the fire inspector is stating that the fire sprinkler
main is too cl
Sprinklerforum
Sent: Wednesday, January 15, 2020 7:54 AM
To:
Cc: Travis Mack
Subject: Pipe adjacent to duct
We have a project where the fire inspector is stating that the fire sprinkler
main is too close to ductwork. There is a 6” main that is about 1/2” from the
ductwork.
Of course
We have a project where the fire inspector is stating that the fire sprinkler
main is too close to ductwork. There is a 6” main that is about 1/2” from the
ductwork.
Of course, the inspectors response is “it’s in the code book” when asking for a
reference that mandates clearance to hvac