Single lead in.
I do you mean a single tap at the main? At some point I’d expect a ‘T’.
I assume separate meters are required. The water agencies want you to
individually pay, so you’ll use less. Isn’t this the norm nationally?
Best.
Bruce Verhei
> On Feb 9, 2018, at 12:08, Parsley
st savings in building
>materials pays for the added sprinklers in the typical 2-car garage.
>
>[Steve Signature (3)]
>
>From: Sprinklerforum
>[mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of
>John Irwin
>Sent: Friday, February 9, 2018 1:23 PM
>To: sprinklerforum@lis
If Florida code is going to call a garage for a duplex an S2 occupancy, do
you then have to design to OH1 and a 1-hour duration? And Bruce's question
too?
Ron Greenman
rongreen...@gmail.com
253.576.9700
The Universe is monstrously indifferent to the presence of man. -Werner
Herzog,
@lists.firesprinkler.org
Subject: Re: Abuse of 13D?
More information :
Code analysis says the residential area are R-2 and the Parking level is S-2.
The Florida Building Code seems to indicate S-2 as a public parking garage and
when enclosed (which this is) requires protection. Additionally S occupencies
located below
Ken, your first point - yes, but on your second point, the closets don't
have to be exterior - I'm referencing the first exemption 'closets in
garages' and not the second 'closets on exterior balconies.' I think the
point is that if you don't have to sprinkler garages then you likewise
wouldn't
Why R-2?
Bruce
> On Feb 9, 2018, at 12:22, John Irwin wrote:
>
> More information :
>
> Code analysis says the residential area are R-2 and the Parking level is S-2.
> The Florida Building Code seems to indicate S-2 as a public parking garage
> and when enclosed
More information :
Code analysis says the residential area are R-2 and the Parking level is S-2.
The Florida Building Code seems to indicate S-2 as a public parking garage and
when enclosed (which this is) requires protection. Additionally S occupencies
located below any other type of occupied
I'm not sure the reference to 8.3.8 would apply.
First, John mentioned he was working with the 2010 edition of 13D. That
edition doesn't contain this language.
Second, if John were working with the '16 edition then 8.3.8 would not
apply in my opinion as the "storage areas" are not exterior,
John, why don't we take this in pieces to see how it shakes out.
* "This is the garage level of a two family home."
o By the title of the standard, "Standard for the Installation of
Sprinkler Systems in One- and Two- Family Dwellings and
Manufactured Homes" it would seem at
If it's a 13D system then:
13D 8.3.8Sprinklers shall not be required in closets in garages and
exterior closets (regardless of size) located on exterior balconies,
exterior breezeways/corridors, or accessed from outdoors where the closet
does not have doors or unprotected penetrations directly
I’m referencing the 2013 Edition of 13D.
1.2.2 A sprinkler system shall be designed and installed in accordance with
this standard to prevent flashover (total involvement) in the room of the fire
origin, where sprinklered, and to improve the chance for occupants to escape or
be evacuated.
This is pretty cut and dry here in Nor Cal. We have to sprinkler garages for
most of our homes due to local AHJ requirements.
Even if you sprinkler the garage, still seems like 13D to me.
Paul B. Cetani
Exec. Vice President
Nor Cal Fire, Inc.
16840 Joleen Way, Bldg A
Morgan Hill, CA 95037
T