Re: Hose Stream Demand Residential

2017-08-08 Thread Roland Huggins
Actually the A.7.2 explicitly states that for areas outside dwelling unit that 
must apply full 13 design factors, a hose stream is not required.


Roland Huggins, PE - Senior VP Engineering
American Fire Sprinkler Assn.
Dallas, TX
http://www.firesprinkler.org 

Fire Sprinklers Saves Lives




> On Aug 8, 2017, at 10:18 AM, Jay White  wrote:
> 
> Does NFPA 13R require a hose stream demand? Section A.7.2 of NFPA 13R only 
> reference a hose stream demand requirement of NFPA 13. The only additional 
> demand required in a calculation is the domestic demand if there is a common 
> domestic/fire main as referenced in section 9.6 of NFPA 13R.
>  
> Jay White
> Sales/Design Manager
> Dynamic Fire Protection
> 9771 Highway 25 South
> Starkville, MS 39759
> PH:   662-312-2426
> FAX: 662-324-1545
>  
>  
>  
> ___
> Sprinklerforum mailing list
> Sprinklerforum@lists.firesprinkler.org 
> 
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org 
> 
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


Re: Hose Stream Demand Residential

2017-08-08 Thread Tom Wellen
2016 ed.
A.7.2 It is only the intent of NFPA 13R to reference the sprinkler
discharge (flow and pressure), number of design sprinklers,
and position of sprinklers (distance from walls, ceilings,
and other sprinklers) requirements of NFPA 13. Other rules
from NFPA 13 such as sprinklering of combustible concealed
spaces, hose stream demand, and water supply duration are
not intended to be referenced by Section 7.2. It is also the
intent of Section 7.2 to apply to those systems or portions of
systems that are outside the dwelling unit but have been determined
to be considered residential, accessory, or incidental to
residential and within the scope of this standard.

Tom Wellen - AFSA

> On Aug 8, 2017, at 2:42 PM, Taylor Schumacher <tay...@sfsprinkler.com> wrote:
> 
> It used to be clear in 2002 but I have not been able to find it in more 
> recent editions.
>  
> NPFA 13R 2002 A.6.7.2
> It is only the intent of  NFPA 13R to reference the sprinkler discharge (flow 
> and pressure), number of design sprinklers and position of sprinklers 
> (distance from walls, ceilings, and other sprinklers) requirements of  NFPA 
> 13. Other rules from  NFPA 13 such as sprinklering of combustible concealed 
> spaces, hose stream demand and water supply duration are not intended to be 
> referenced by  6.7.2.
>  
>  
> Taylor Schumacher, CET
> Security Fire Sprinkler <http://www.j-berd.com/>
> P.O. BOX 7308 | St. Cloud, MN 56302-7308
> 3308 Southway Drive | St. Cloud, MN 56301
> Office: 320.656.0847 | tay...@sfsprinkler.com <mailto:tay...@sfsprinkler.com>
>  
> From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] 
> On Behalf Of Travis Mack; MFP Design, LLC
> Sent: Tuesday, August 08, 2017 1:28 PM
> To: sprinklerforum@lists.firesprinkler.org
> Subject: RE: Hose Stream Demand Residential
>  
> I’m going off of memory – which seems to be slipping as I age – but I don’t 
> believe NFPA 13R has a hose stream requirement.  However, be cautious of that 
> domestic demand.  Maybe I get conservative, but if I have a complex with 
> several buildings on a site water line, I add the domestic demand to the site 
> water loop.  That has been in excess of a hose allowance many times.
>  
> Travis Mack, SET
> MFP Design, LLC
> 3356 E Vallejo Ct
> Gilbert, AZ 85298
> 480-505-9271
> fax: 866-430-6107
> email:tm...@mfpdesign.com <mailto:email:tm...@mfpdesign.com>
>  
> http://www.mfpdesign.com <http://www.mfpdesign.com/>
> https://www.facebook.com/pages/MFP-Design-LLC/92218417692 
> <https://www.facebook.com/pages/MFP-Design-LLC/92218417692>
> Send large files to us via: https://www.hightail.com/u/MFPDesign 
> <https://www.hightail.com/u/MFPDesign>
> LinkedIn: https://www.linkedin.com/in/travismack 
> <https://www.linkedin.com/in/travismack>
>  
> **PLEASE NOTE NEW ADDRESS**
>  
> From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org 
> <mailto:sprinklerforum-boun...@lists.firesprinkler.org>] On Behalf Of Jay 
> White
> Sent: Tuesday, August 8, 2017 10:19 AM
> To: sprinklerforum@lists.firesprinkler.org 
> <mailto:sprinklerforum@lists.firesprinkler.org>
> Subject: Hose Stream Demand Residential
>  
> Does NFPA 13R require a hose stream demand? Section A.7.2 of NFPA 13R only 
> reference a hose stream demand requirement of NFPA 13. The only additional 
> demand required in a calculation is the domestic demand if there is a common 
> domestic/fire main as referenced in section 9.6 of NFPA 13R.
>  
> Jay White
> Sales/Design Manager
> Dynamic Fire Protection
> 9771 Highway 25 South
> Starkville, MS 39759
> PH:   662-312-2426
> FAX: 662-324-1545
>  
>  
>  
> ___
> Sprinklerforum mailing list
> Sprinklerforum@lists.firesprinkler.org
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: Hose Stream Demand Residential

2017-08-08 Thread Taylor Schumacher
It used to be clear in 2002 but I have not been able to find it in more recent 
editions.

NPFA 13R 2002 A.6.7.2
It is only the intent of  NFPA 13R to reference the sprinkler discharge (flow 
and pressure), number of design sprinklers and position of sprinklers (distance 
from walls, ceilings, and other sprinklers) requirements of  NFPA 13. Other 
rules from  NFPA 13 such as sprinklering of combustible concealed spaces, hose 
stream demand and water supply duration are not intended to be referenced by  
6.7.2.


Taylor Schumacher, CET
Security Fire Sprinkler<http://www.j-berd.com/>
P.O. BOX 7308 | St. Cloud, MN 56302-7308
3308 Southway Drive | St. Cloud, MN 56301
Office: 320.656.0847 | tay...@sfsprinkler.com<mailto:tay...@sfsprinkler.com>

From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of Travis Mack; MFP Design, LLC
Sent: Tuesday, August 08, 2017 1:28 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: Hose Stream Demand Residential

I'm going off of memory - which seems to be slipping as I age - but I don't 
believe NFPA 13R has a hose stream requirement.  However, be cautious of that 
domestic demand.  Maybe I get conservative, but if I have a complex with 
several buildings on a site water line, I add the domestic demand to the site 
water loop.  That has been in excess of a hose allowance many times.

Travis Mack, SET
MFP Design, LLC
3356 E Vallejo Ct
Gilbert, AZ 85298
480-505-9271
fax: 866-430-6107
email:tm...@mfpdesign.com<mailto:email:tm...@mfpdesign.com>

http://www.mfpdesign.com<http://www.mfpdesign.com/>
https://www.facebook.com/pages/MFP-Design-LLC/92218417692
Send large files to us via: https://www.hightail.com/u/MFPDesign
LinkedIn: https://www.linkedin.com/in/travismack

**PLEASE NOTE NEW ADDRESS**

From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of Jay White
Sent: Tuesday, August 8, 2017 10:19 AM
To: 
sprinklerforum@lists.firesprinkler.org<mailto:sprinklerforum@lists.firesprinkler.org>
Subject: Hose Stream Demand Residential

Does NFPA 13R require a hose stream demand? Section A.7.2 of NFPA 13R only 
reference a hose stream demand requirement of NFPA 13. The only additional 
demand required in a calculation is the domestic demand if there is a common 
domestic/fire main as referenced in section 9.6 of NFPA 13R.

Jay White
Sales/Design Manager
Dynamic Fire Protection
9771 Highway 25 South
Starkville, MS 39759
PH:   662-312-2426
FAX: 662-324-1545



___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: Hose Stream Demand Residential

2017-08-08 Thread Travis Mack; MFP Design, LLC
I'm going off of memory - which seems to be slipping as I age - but I don't
believe NFPA 13R has a hose stream requirement.  However, be cautious of
that domestic demand.  Maybe I get conservative, but if I have a complex
with several buildings on a site water line, I add the domestic demand to
the site water loop.  That has been in excess of a hose allowance many
times.

 

Travis Mack, SET

MFP Design, LLC

3356 E Vallejo Ct

Gilbert, AZ 85298

480-505-9271

fax: 866-430-6107

  email:tm...@mfpdesign.com

 

  http://www.mfpdesign.com

 
https://www.facebook.com/pages/MFP-Design-LLC/92218417692

Send large files to us via:  
https://www.hightail.com/u/MFPDesign 

LinkedIn:  
https://www.linkedin.com/in/travismack

 

**PLEASE NOTE NEW ADDRESS**

 

From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org]
On Behalf Of Jay White
Sent: Tuesday, August 8, 2017 10:19 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: Hose Stream Demand Residential

 

Does NFPA 13R require a hose stream demand? Section A.7.2 of NFPA 13R only
reference a hose stream demand requirement of NFPA 13. The only additional
demand required in a calculation is the domestic demand if there is a common
domestic/fire main as referenced in section 9.6 of NFPA 13R.

 

Jay White

Sales/Design Manager

Dynamic Fire Protection

9771 Highway 25 South

Starkville, MS 39759

PH:   662-312-2426

FAX: 662-324-1545

 

 

 

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org