Even the stamped TBC's are stronger than that. Check out the specs;

http://www.vikingcorp.com/sites/default/files/usrelated/tolco/fig65_66.pdf

 

Timothy W Goins
A & T Services

 

."Truly, truly, I say to you, unless one is born again he cannot see the
kingdom of God." Jn 3:3 NASB

 

Jesus answered, "Truly, truly, I say to you, unless one is born of water and
the Spirit he cannot enter into the kingdom of God. That which is born of
the flesh is flesh, and that which is born of the Spirit is spirit. Jn 3:5-6
NASB

 

Then I will sprinkle clean water on you, and you will be clean; I will
cleanse you from all your filthiness and from all your idols. Moreover, I
will give you a new heart and put a new spirit within you; and I will remove
the heart of stone from your flesh and give you a heart of flesh. Ezk
36:25-26 NASB

 

 

Reply to   <mailto:twgo...@outlook.com> mailto:twgo...@outlook.com

 

From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org]
On Behalf Of Mike Hairfield
Sent: Monday, November 12, 2018 7:09 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: Maximum Load for Top Beam C-Clamps

 

I have a structural Engineer stating that the maximum load for top beam
c-clamps is 50 lbs.

for 2 1/2" schedule-10 pipe for a building with bar joists spaced 5'-0" o.c.

 

His notes state that the maximum spacing would be 8'-6" o.c. for 2 1/2" pipe
and 2'-0" o.c.

for the 6" crossmains.

 

Have we as sprinkler contractors been designing systems inappropriately all
these years........LOL

 

Mike