Re: NFPA 13 prior to 1969 edition

2018-04-06 Thread bcasterline
Thanks Scott. Yes, that does help zero in on when it went from open to  
closed sprinklers.
I've recently modeled activation with and without a draft stop for  
3,6,9,12,15, and 18 inch deflector distance, for 135F, 155F, 175F, and  
200F Sprinklers 9" from edge of opening splitting the difference of 6  
to 12.
I remember seeing the detail when open sprk deluge was required I just  
can't recall if there was draft stop or not.


Brad.

Quoting Scott Futrell :


Seems like a fun research project Brad for a Friday afternoon.



From the 1955 edition,

621: Open sprinklers may be used to protect special hazards, for  
protection against exposures, or in other special locations.


777 (c): Where vertical openings are not protected by standard  
enclosures, sprinklers should be so placed as to fully cover them.  
This necessitates placing sprinklers close to such openings at each  
floor level.




I don't see anything else. Maybe narrows it down to 1955-1969.

Scott



Office: (763) 425-1001 x 2

Cell: (612) 759-5556



-Original Message-
From: Sprinklerforum  
[mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of  
bcasterl...@fsc-inc.com

Sent: Friday, April 06, 2018 12:15 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: NFPA 13 prior to 1969 edition



Does anyone have access to 13 where the water curtain detail still  
required open sprinklers (deluge)?


I'm curious if the draft stop is required.

Besides smoke protecting the opening it occurred to me the other day  
the draft stop would help form a 'wall of water' by blocking ~9 gpm,  
making it drop straight down, and thereby providing a density of  
greater than 1 gpm/sf around the perimiter.




Thanks,

Brad



___

Sprinklerforum mailing list

Sprinklerforum@lists.firesprinkler.org

http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org




___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: NFPA 13 prior to 1969 edition

2018-04-06 Thread Scott Futrell
Seems like a fun research project Brad for a Friday afternoon.



>From the 1955 edition,

621: Open sprinklers may be used to protect special hazards, for protection 
against exposures, or in other special locations.

777 (c): Where vertical openings are not protected by standard enclosures, 
sprinklers should be so placed as to fully cover them. This necessitates 
placing sprinklers close to such openings at each floor level.



I don't see anything else. Maybe narrows it down to 1955-1969.

Scott



Office: (763) 425-1001 x 2

Cell: (612) 759-5556



-Original Message-
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of bcasterl...@fsc-inc.com
Sent: Friday, April 06, 2018 12:15 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: NFPA 13 prior to 1969 edition



Does anyone have access to 13 where the water curtain detail still required 
open sprinklers (deluge)?

I'm curious if the draft stop is required.

Besides smoke protecting the opening it occurred to me the other day the draft 
stop would help form a 'wall of water' by blocking ~9 gpm, making it drop 
straight down, and thereby providing a density of greater than 1 gpm/sf around 
the perimiter.



Thanks,

Brad