?url=https%3A%2F%2Fwww.linkedin.com%2Fin%2Ftravismack=02%7C01%7C%7C1121d49f9e6b4cf248f108d4df580e77%7C14e5497c16da42e69ffa77d19bafe511%7C0%7C0%7C636379016677342180=tT5E7LsZjSmyreKi4gDCa70EWN%2BZodi%2FhbeCbHNRijI%3D=0) > > > > > > > > “The bitterness of poor quality remains long after the sweetness of low pr

RE: 130 sq ft or 225 sq ft

2018-10-18 Thread MFP Design, LLC
%2FhbeCbHNRijI%3D=0> https://www.linkedin.com/in/travismack “The bitterness of poor quality remains long after the sweetness of low price is forgotten.” From: Sprinklerforum On Behalf Of Roland Huggins Sent: Thursday, October 18, 2018 1:20 PM To: sprinklerforum@lists.firesprinkler.org Subject: Re: 130

Re: 130 sq ft or 225 sq ft

2018-10-18 Thread Roland Huggins
The FPE kissed the pooch. The 2x6’s drive the boat so it’s combustible obstructed construction with members < 3 ft OC. Now if you put some insulation in the channels whereby the depth of the exposed member is less than 4 inches, then you get to merrily embrace the 225 sf As. Roland Roland

Re: 130 sq ft or 225 sq ft

2018-10-18 Thread Fpdcdesign
I’m with you at 130 Todd G Williams, PE Fire Protection Design/Consulting Stonington, CT 860-535-2080 (ofc) 860-553-3553 (fax) 860-608-4559 (cell) > > On Oct 18, 2018 at 4:06 PM, mailto:tm...@mfpdesign.com)> > wrote: > > >