Re: SPRINKLERS INSIDE OVENS

2016-10-13 Thread rongreenman .
I was visualizing circuit board drying ovens but I see other ovens with
materials inside that could combust at this temperature. Tyco has a formula
for determine how long a dry pendent needs to be to keep from transferring
freezing temperatures to a wet supply. Perhaps that can be used to figure
the rate heat would dissipate from your drops and not be to high for your
system. If expansion is your only consideration then a PRV at the riser or
main drain will fix that. And finally put a control valve on the drops as
you will be replacing those heads often. If I recall, annually if links and
every five if bulbs.

On Thursday, October 13, 2016, <craig.pr...@ch2m.com> wrote:

> NFPA 86 dictates the types of ovens which require internal fire
> suppression.  There are all kinds of ovens other than just the type for
> cooking.
>
>
>
>
> *Craig L. Prahl*
> Fire Protection Group Lead/SME
> *CH2M*
> 200 Verdae Blvd.
> Greenville, SC  29607
> Direct - 864.920.7540
>
> Fax - 864.920.7129
>
> CH2MHILL Extension  77540
> craig.pr...@ch2m.com
> <javascript:_e(%7B%7D,'cvml','craig.pr...@ch2m.com');>
>
>
>
> *From:* Sprinklerforum [mailto:sprinklerforum-bounces@lists.firesprinkler.
> org
> <javascript:_e(%7B%7D,'cvml','sprinklerforum-boun...@lists.firesprinkler.org');>]
> *On Behalf Of *mphe...@aerofire.com
> <javascript:_e(%7B%7D,'cvml','mphe...@aerofire.com');>
> *Sent:* Wednesday, October 12, 2016 7:54 PM
> *To:* sprinklerforum@lists.firesprinkler.org
> <javascript:_e(%7B%7D,'cvml','sprinklerforum@lists.firesprinkler.org');>
> *Subject:* RE: SPRINKLERS INSIDE OVENS [EXTERNAL]
>
>
>
> I believe this question has been on the forum before and the question was
> WHY does one need to put sprinklers in an  oven, especially if the oven
> temperature is only 300 degrees.
>
> Wet, dry, or pre-action, the problems are 1) the pressure rating of the
> components at the operating temperature of the oven, and 2) what happens to
> 360 degree liquid water when you decompress it?
>
>
>
> Mark at Aero
>
> 602 820-7894
>
>
>
>
>
> *From:* Sprinklerforum [mailto:sprinklerforum-bounces@lists.firesprinkler.
> org
> <javascript:_e(%7B%7D,'cvml','sprinklerforum-boun...@lists.firesprinkler.org');>]
> *On Behalf Of *Cesar Lira
> *Sent:* Wednesday, October 12, 2016 3:28 PM
> *To:* sprinklerforum@lists.firesprinkler.org
> <javascript:_e(%7B%7D,'cvml','sprinklerforum@lists.firesprinkler.org');>
> *Subject:* SPRINKLERS INSIDE OVENS
>
>
>
> I have a worry,
>
> I need to install sprinklers inside an Oven that work at 300°F. I know
> that I need to use a sprinklers 360°F or high.
>
> But this system is tie to a same roof grid. And my concern is that what
> happen with the heat, in the water, it temperature could go up to roof grid
> system, or over pressurized my pipes system. What I need to do??..
>
> Or anyone have some recommendations??.
>
>
>
>
>
> Regards
>
> CLR
>


-- 
Sent from Gmail Mobile
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: SPRINKLERS INSIDE OVENS

2016-10-13 Thread Craig.Prahl
NFPA 86 dictates the types of ovens which require internal fire suppression.  
There are all kinds of ovens other than just the type for cooking.


Craig L. Prahl
Fire Protection Group Lead/SME
CH2M
200 Verdae Blvd.
Greenville, SC  29607
Direct - 864.920.7540
Fax - 864.920.7129
CH2MHILL Extension  77540
craig.pr...@ch2m.com


From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of mphe...@aerofire.com
Sent: Wednesday, October 12, 2016 7:54 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: SPRINKLERS INSIDE OVENS [EXTERNAL]

I believe this question has been on the forum before and the question was WHY 
does one need to put sprinklers in an  oven, especially if the oven temperature 
is only 300 degrees.
Wet, dry, or pre-action, the problems are 1) the pressure rating of the 
components at the operating temperature of the oven, and 2) what happens to 360 
degree liquid water when you decompress it?

Mark at Aero
602 820-7894


From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of Cesar Lira
Sent: Wednesday, October 12, 2016 3:28 PM
To: 
sprinklerforum@lists.firesprinkler.org<mailto:sprinklerforum@lists.firesprinkler.org>
Subject: SPRINKLERS INSIDE OVENS

I have a worry,
I need to install sprinklers inside an Oven that work at 300°F. I know that I 
need to use a sprinklers 360°F or high.
But this system is tie to a same roof grid. And my concern is that what happen 
with the heat, in the water, it temperature could go up to roof grid system, or 
over pressurized my pipes system. What I need to do??..
Or anyone have some recommendations??.


Regards
CLR
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: SPRINKLERS INSIDE OVENS

2016-10-12 Thread MPhelps
I believe this question has been on the forum before and the question was WHY 
does one need to put sprinklers in an  oven, especially if the oven temperature 
is only 300 degrees.
Wet, dry, or pre-action, the problems are 1) the pressure rating of the 
components at the operating temperature of the oven, and 2) what happens to 360 
degree liquid water when you decompress it?

Mark at Aero
602 820-7894


From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of Cesar Lira
Sent: Wednesday, October 12, 2016 3:28 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: SPRINKLERS INSIDE OVENS

I have a worry,
I need to install sprinklers inside an Oven that work at 300°F. I know that I 
need to use a sprinklers 360°F or high.
But this system is tie to a same roof grid. And my concern is that what happen 
with the heat, in the water, it temperature could go up to roof grid system, or 
over pressurized my pipes system. What I need to do??..
Or anyone have some recommendations??.


Regards
CLR
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


Re: SPRINKLERS INSIDE OVENS

2016-10-12 Thread Kenneth Berman
preaction systems are what I see for this


On Wed, Oct 12, 2016 at 5:28 PM, Cesar Lira  wrote:

> I have a worry,
>
> I need to install sprinklers inside an Oven that work at 300°F. I know
> that I need to use a sprinklers 360°F or high.
>
> But this system is tie to a same roof grid. And my concern is that what
> happen with the heat, in the water, it temperature could go up to roof grid
> system, or over pressurized my pipes system. What I need to do??..
>
> Or anyone have some recommendations??.
>
>
>
>
>
> Regards
>
> CLR
>