Re: [WISPA] Another Ubiquity question

2012-10-15 Thread Olufemi Adalemo
Thanks Greg,
I can see how putting load on just one part of the battery bank could cause
issues but this load is quite small compared to the total battery capacity.
I will be putting only 8w on two 150Ah 12v batteries (3600Wh total
capacity). It would take 400 hours to deplete the battery bank with this
load only, do you still think this will be a problem? If this will be a
problem I could have the load moved from one bank to the other at a
scheduled maintenance visit say twice a year. I really appreciate the
advice.

Regards,
- - -
*Olufemi Adalemo*
M: +234-803-5610040
M: +234-809-8610040
f...@adalemo.com




On Mon, Oct 15, 2012 at 8:19 PM, Greg Ihnen  wrote:

> My two cents: If you discharge part of your battery bank unevenly (pull
> off just half of your 24v bank to get 12v for some loads) you will have
> trouble with part of the bank getting over charged and part of the bank not
> getting charged enough. If you were charging the bank with an AC charger
> that charges each battery individually according to it's needs that
> wouldn't be a problem. But if you're charging the entire bank with a single
> device that charges the entire string in series like a 24v solar charger
> that is not a good way to go. You'd be better off with a 24v to 12v
> regulator.
>
> Greg
>
>
> On Mon, Oct 15, 2012 at 1:44 PM, Olufemi Adalemo wrote:
>
>> It just dawned on me that I may have been barking up the wrong tree
>> I only have the one NSM5 to connect, I could hook this up to the parallel
>> segment of my battery bank and get only 12v while the rest of the
>> installation that's connected in series gets 24v. Do you think this will
>> work? Don't really have to worry about the NSM5 running down the battery
>> cause load is low and the cable run is under 10m so the voltage drop from
>> 12v will be negligible
>>
>> So this is how it would be:
>> 24v solar panel connected to 24v charge controller with 4 x 12v batteries
>> connected in a 2x2 series/parallel array. cable connected to the parallel
>> segment of battery bank (theoretically giving 12v to the NSM5), rest of the
>> load connected to the charge controller at 24v
>>
>> What do you think?
>> - - -
>> *Olufemi Adalemo*
>> M: +234-803-5610040
>> M: +234-809-8610040
>> f...@adalemo.com
>>
>>
___
Wireless mailing list
Wireless@wispa.org
http://lists.wispa.org/mailman/listinfo/wireless


Re: [WISPA] Another Ubiquity question

2012-10-15 Thread Josh Luthman
Between the regulator and load.
On Oct 15, 2012 5:01 PM, "Jeromie Reeves"  wrote:

> Where did you put that diode? I have done this and at the low power
> that is needed they do not get noticeably warm at all.
>
> On Mon, Oct 15, 2012 at 1:38 PM, Josh Luthman
>  wrote:
> > I tried that method.  Diode got hotter than hell.  Burnt right through
> the
> > insulation I covered it with (and since it was bent the jacket came right
> > off).
> >
> > Josh Luthman
> > Office: 937-552-2340
> > Direct: 937-552-2343
> > 1100 Wayne St
> > Suite 1337
> > Troy, OH 45373
> >
> >
> > On Mon, Oct 15, 2012 at 4:22 PM, Jeromie Reeves 
> > wrote:
> >>
> >> Why not run the NSM5 on 24v? Just add a diode or two to the + side,
> >> the 1v drop on them will protect the NSM from
> >> the charge voltage of the bank. $2 fix
> >>
> >> On Mon, Oct 15, 2012 at 10:44 AM, Olufemi Adalemo 
> >> wrote:
> >> > It just dawned on me that I may have been barking up the wrong tree
> >> > I only have the one NSM5 to connect, I could hook this up to the
> >> > parallel
> >> > segment of my battery bank and get only 12v while the rest of the
> >> > installation that's connected in series gets 24v. Do you think this
> will
> >> > work? Don't really have to worry about the NSM5 running down the
> battery
> >> > cause load is low and the cable run is under 10m so the voltage drop
> >> > from
> >> > 12v will be negligible
> >> >
> >> > So this is how it would be:
> >> > 24v solar panel connected to 24v charge controller with 4 x 12v
> >> > batteries
> >> > connected in a 2x2 series/parallel array. cable connected to the
> >> > parallel
> >> > segment of battery bank (theoretically giving 12v to the NSM5), rest
> of
> >> > the
> >> > load connected to the charge controller at 24v
> >> >
> >> > What do you think?
> >> >
> >> > - - -
> >> > Olufemi Adalemo
> >> > M: +234-803-5610040
> >> > M: +234-809-8610040
> >> > f...@adalemo.com
> >> >
> >> >
> >> >
> >> >
> >> > On Fri, Oct 12, 2012 at 8:18 PM, Kristian Hoffmann <
> kh...@fire2wire.com>
> >> > wrote:
> >> >>
> >> >> Ya, it should be +24 on pins 4,5 and -24/comm on 7,8.  If it blew up
> >> >> then
> >> >> there was probably a short somewhere.
> >> >>
> >> >> -Kristian
> >> >>
> >> >>
> >> >> On 10/12/2012 11:11 AM, Olufemi Adalemo wrote:
> >> >>
> >> >> Ah ok, it is possible that the guys didn't get the polarity right
> >> >> I will check though they swear that they did
> >> >>
> >> >>
> >> >> - - -
> >> >> Olufemi Adalemo
> >> >> M: +234-803-5610040
> >> >> M: +234-809-8610040
> >> >> f...@adalemo.com
> >> >>
> >> >>
> >> >>
> >> >>
> >> >> On Fri, Oct 12, 2012 at 7:05 PM, Josh Luthman
> >> >>  wrote:
> >> >>>
> >> >>> What voltage were the batteries spitting out?  They charge at 27v
> but
> >> >>> without a charger put out much closer to 24v until they begin
> >> >>> discharging.
> >> >>> If it fried the radio I would first think that it was connected
> wrong,
> >> >>> not
> >> >>> that the voltage was too high.
> >> >>>
> >> >>> Josh Luthman
> >> >>> Office: 937-552-2340
> >> >>> Direct: 937-552-2343
> >> >>> 1100 Wayne St
> >> >>> Suite 1337
> >> >>> Troy, OH 45373
> >> >>>
> >> >>>
> >> >>> On Fri, Oct 12, 2012 at 2:02 PM, Olufemi Adalemo  >
> >> >>> wrote:
> >> 
> >>  What's your typical config for the NSM5?
> >>  Some of my guys just tried to power one off a 24v battery bank (no
> >>  charger connected just battery) and it fried good
> >> 
> >>  - - -
> >>  Olufemi Adalemo
> >>  M: +234-803-5610040
> >>  M: +234-809-8610040
> >>  f...@adalemo.com
> >> 
> >> 
> >> 
> >> 
> >>  On Fri, Oct 12, 2012 at 6:56 PM, Kristian Hoffmann
> >>  
> >>  wrote:
> >> >
> >> > We have MT and Ubnt equipment of all shapes and sizes running at
> >> > 27.6V.
> >> > The only problems we've had are a handful of freak RB411s that
> won't
> >> > power
> >> > on with >27V.  Most of the older ones wouldn't kick into
> overvoltage
> >> > protection until >28V, but we've come across a few odd balls.
> >> >
> >> > -Kristian
> >> >
> >> >
> >> > On 10/12/2012 10:44 AM, Josh Luthman wrote:
> >> >
> >> > Charger isn't going to spit out 24v for batteries that need
> charged,
> >> > it's usually 27v.
> >> >
> >> > I was under the impression they would simply lock up and you could
> >> > reboot, or maybe I'm just thinking of MT.
> >> >
> >> > Josh Luthman
> >> > Office: 937-552-2340
> >> > Direct: 937-552-2343
> >> > 1100 Wayne St
> >> > Suite 1337
> >> > Troy, OH 45373
> >> >
> >> >
> >> > On Fri, Oct 12, 2012 at 10:08 PM, Olufemi Adalemo
> >> > 
> >> > wrote:
> >> >>
> >> >> Aha, thanks
> >> >> That explains why I have a dead NSM5 on my desk
> >> >> I guess the charge controller is not very good at giving out 24v
> >> >> regulated power
> >> >>
> >> >> - - -
> >> >> Olufemi Adalemo
> >> >> M: +234-803-5610040

Re: [WISPA] Another Ubiquity question

2012-10-15 Thread Jeromie Reeves
Where did you put that diode? I have done this and at the low power
that is needed they do not get noticeably warm at all.

On Mon, Oct 15, 2012 at 1:38 PM, Josh Luthman
 wrote:
> I tried that method.  Diode got hotter than hell.  Burnt right through the
> insulation I covered it with (and since it was bent the jacket came right
> off).
>
> Josh Luthman
> Office: 937-552-2340
> Direct: 937-552-2343
> 1100 Wayne St
> Suite 1337
> Troy, OH 45373
>
>
> On Mon, Oct 15, 2012 at 4:22 PM, Jeromie Reeves 
> wrote:
>>
>> Why not run the NSM5 on 24v? Just add a diode or two to the + side,
>> the 1v drop on them will protect the NSM from
>> the charge voltage of the bank. $2 fix
>>
>> On Mon, Oct 15, 2012 at 10:44 AM, Olufemi Adalemo 
>> wrote:
>> > It just dawned on me that I may have been barking up the wrong tree
>> > I only have the one NSM5 to connect, I could hook this up to the
>> > parallel
>> > segment of my battery bank and get only 12v while the rest of the
>> > installation that's connected in series gets 24v. Do you think this will
>> > work? Don't really have to worry about the NSM5 running down the battery
>> > cause load is low and the cable run is under 10m so the voltage drop
>> > from
>> > 12v will be negligible
>> >
>> > So this is how it would be:
>> > 24v solar panel connected to 24v charge controller with 4 x 12v
>> > batteries
>> > connected in a 2x2 series/parallel array. cable connected to the
>> > parallel
>> > segment of battery bank (theoretically giving 12v to the NSM5), rest of
>> > the
>> > load connected to the charge controller at 24v
>> >
>> > What do you think?
>> >
>> > - - -
>> > Olufemi Adalemo
>> > M: +234-803-5610040
>> > M: +234-809-8610040
>> > f...@adalemo.com
>> >
>> >
>> >
>> >
>> > On Fri, Oct 12, 2012 at 8:18 PM, Kristian Hoffmann 
>> > wrote:
>> >>
>> >> Ya, it should be +24 on pins 4,5 and -24/comm on 7,8.  If it blew up
>> >> then
>> >> there was probably a short somewhere.
>> >>
>> >> -Kristian
>> >>
>> >>
>> >> On 10/12/2012 11:11 AM, Olufemi Adalemo wrote:
>> >>
>> >> Ah ok, it is possible that the guys didn't get the polarity right
>> >> I will check though they swear that they did
>> >>
>> >>
>> >> - - -
>> >> Olufemi Adalemo
>> >> M: +234-803-5610040
>> >> M: +234-809-8610040
>> >> f...@adalemo.com
>> >>
>> >>
>> >>
>> >>
>> >> On Fri, Oct 12, 2012 at 7:05 PM, Josh Luthman
>> >>  wrote:
>> >>>
>> >>> What voltage were the batteries spitting out?  They charge at 27v but
>> >>> without a charger put out much closer to 24v until they begin
>> >>> discharging.
>> >>> If it fried the radio I would first think that it was connected wrong,
>> >>> not
>> >>> that the voltage was too high.
>> >>>
>> >>> Josh Luthman
>> >>> Office: 937-552-2340
>> >>> Direct: 937-552-2343
>> >>> 1100 Wayne St
>> >>> Suite 1337
>> >>> Troy, OH 45373
>> >>>
>> >>>
>> >>> On Fri, Oct 12, 2012 at 2:02 PM, Olufemi Adalemo 
>> >>> wrote:
>> 
>>  What's your typical config for the NSM5?
>>  Some of my guys just tried to power one off a 24v battery bank (no
>>  charger connected just battery) and it fried good
>> 
>>  - - -
>>  Olufemi Adalemo
>>  M: +234-803-5610040
>>  M: +234-809-8610040
>>  f...@adalemo.com
>> 
>> 
>> 
>> 
>>  On Fri, Oct 12, 2012 at 6:56 PM, Kristian Hoffmann
>>  
>>  wrote:
>> >
>> > We have MT and Ubnt equipment of all shapes and sizes running at
>> > 27.6V.
>> > The only problems we've had are a handful of freak RB411s that won't
>> > power
>> > on with >27V.  Most of the older ones wouldn't kick into overvoltage
>> > protection until >28V, but we've come across a few odd balls.
>> >
>> > -Kristian
>> >
>> >
>> > On 10/12/2012 10:44 AM, Josh Luthman wrote:
>> >
>> > Charger isn't going to spit out 24v for batteries that need charged,
>> > it's usually 27v.
>> >
>> > I was under the impression they would simply lock up and you could
>> > reboot, or maybe I'm just thinking of MT.
>> >
>> > Josh Luthman
>> > Office: 937-552-2340
>> > Direct: 937-552-2343
>> > 1100 Wayne St
>> > Suite 1337
>> > Troy, OH 45373
>> >
>> >
>> > On Fri, Oct 12, 2012 at 10:08 PM, Olufemi Adalemo
>> > 
>> > wrote:
>> >>
>> >> Aha, thanks
>> >> That explains why I have a dead NSM5 on my desk
>> >> I guess the charge controller is not very good at giving out 24v
>> >> regulated power
>> >>
>> >> - - -
>> >> Olufemi Adalemo
>> >> M: +234-803-5610040
>> >> M: +234-809-8610040
>> >> f...@adalemo.com
>> >>
>> >>
>> >>
>> >>
>> >> On Fri, Oct 12, 2012 at 6:17 PM, Josh Luthman
>> >>  wrote:
>> >>>
>> >>> Yes you will.  The batteries will probably be around 27v which
>> >>> Ubnt
>> >>> won't like.  You'll need to clean the ~18-27v from the batteries
>> >>> to 24v.
>> >>>
>> >>> Josh Luthman
>> >>> Office: 937-552-2340
>> >>>

Re: [WISPA] Another Ubiquity question

2012-10-15 Thread Josh Luthman
Mine doesn't.  Only doing about 25 watts though.
On Oct 15, 2012 4:54 PM, "Faisal Imtiaz"  wrote:

>  hehe. well now you know why Rectifiers.. (large diodes) have
> heatsinks on them
>
> :)
>
> Faisal Imtiaz
> Snappy Internet & Telecom
> 7266 SW 48 Street
> Miami, Fl 33155
> Tel: 305 663 5518 x 232
> Helpdesk: 305 663 5518 option 2 Email: supp...@snappydsl.net
>
> On 10/15/2012 4:38 PM, Josh Luthman wrote:
>
> I tried that method.  Diode got hotter than hell.  Burnt right through the
> insulation I covered it with (and since it was bent the jacket came right
> off).
>
> Josh Luthman
> Office: 937-552-2340
> Direct: 937-552-2343
> 1100 Wayne St
> Suite 1337
> Troy, OH 45373
>
>
> On Mon, Oct 15, 2012 at 4:22 PM, Jeromie Reeves wrote:
>
>> Why not run the NSM5 on 24v? Just add a diode or two to the + side,
>> the 1v drop on them will protect the NSM from
>> the charge voltage of the bank. $2 fix
>>
>> On Mon, Oct 15, 2012 at 10:44 AM, Olufemi Adalemo 
>> wrote:
>> > It just dawned on me that I may have been barking up the wrong tree
>> > I only have the one NSM5 to connect, I could hook this up to the
>> parallel
>> > segment of my battery bank and get only 12v while the rest of the
>> > installation that's connected in series gets 24v. Do you think this will
>> > work? Don't really have to worry about the NSM5 running down the battery
>> > cause load is low and the cable run is under 10m so the voltage drop
>> from
>> > 12v will be negligible
>> >
>> > So this is how it would be:
>> > 24v solar panel connected to 24v charge controller with 4 x 12v
>> batteries
>> > connected in a 2x2 series/parallel array. cable connected to the
>> parallel
>> > segment of battery bank (theoretically giving 12v to the NSM5), rest of
>> the
>> > load connected to the charge controller at 24v
>> >
>> > What do you think?
>> >
>> > - - -
>> > Olufemi Adalemo
>> > M: +234-803-5610040
>> > M: +234-809-8610040
>> > f...@adalemo.com
>> >
>> >
>> >
>> >
>> > On Fri, Oct 12, 2012 at 8:18 PM, Kristian Hoffmann > >
>> > wrote:
>> >>
>> >> Ya, it should be +24 on pins 4,5 and -24/comm on 7,8.  If it blew up
>> then
>> >> there was probably a short somewhere.
>> >>
>> >> -Kristian
>> >>
>> >>
>> >> On 10/12/2012 11:11 AM, Olufemi Adalemo wrote:
>> >>
>> >> Ah ok, it is possible that the guys didn't get the polarity right
>> >> I will check though they swear that they did
>> >>
>> >>
>> >> - - -
>> >> Olufemi Adalemo
>> >> M: +234-803-5610040
>> >> M: +234-809-8610040
>> >> f...@adalemo.com
>> >>
>> >>
>> >>
>> >>
>> >> On Fri, Oct 12, 2012 at 7:05 PM, Josh Luthman
>> >>  wrote:
>> >>>
>> >>> What voltage were the batteries spitting out?  They charge at 27v but
>> >>> without a charger put out much closer to 24v until they begin
>> discharging.
>> >>> If it fried the radio I would first think that it was connected
>> wrong, not
>> >>> that the voltage was too high.
>> >>>
>> >>> Josh Luthman
>> >>> Office: 937-552-2340
>> >>> Direct: 937-552-2343
>> >>> 1100 Wayne St
>> >>> Suite 1337
>> >>> Troy, OH 45373
>> >>>
>> >>>
>> >>> On Fri, Oct 12, 2012 at 2:02 PM, Olufemi Adalemo 
>> >>> wrote:
>> 
>>  What's your typical config for the NSM5?
>>  Some of my guys just tried to power one off a 24v battery bank (no
>>  charger connected just battery) and it fried good
>> 
>>  - - -
>>  Olufemi Adalemo
>>  M: +234-803-5610040
>>  M: +234-809-8610040
>>  f...@adalemo.com
>> 
>> 
>> 
>> 
>>  On Fri, Oct 12, 2012 at 6:56 PM, Kristian Hoffmann <
>> kh...@fire2wire.com>
>>  wrote:
>> >
>> > We have MT and Ubnt equipment of all shapes and sizes running at
>> 27.6V.
>> > The only problems we've had are a handful of freak RB411s that
>> won't power
>> > on with >27V.  Most of the older ones wouldn't kick into overvoltage
>> > protection until >28V, but we've come across a few odd balls.
>> >
>> > -Kristian
>> >
>> >
>> > On 10/12/2012 10:44 AM, Josh Luthman wrote:
>> >
>> > Charger isn't going to spit out 24v for batteries that need charged,
>> > it's usually 27v.
>> >
>> > I was under the impression they would simply lock up and you could
>> > reboot, or maybe I'm just thinking of MT.
>> >
>> > Josh Luthman
>> > Office: 937-552-2340
>> > Direct: 937-552-2343
>> > 1100 Wayne St
>> > Suite 1337
>> > Troy, OH 45373
>> >
>> >
>> > On Fri, Oct 12, 2012 at 10:08 PM, Olufemi Adalemo <
>> adal...@gmail.com>
>> > wrote:
>> >>
>> >> Aha, thanks
>> >> That explains why I have a dead NSM5 on my desk
>> >> I guess the charge controller is not very good at giving out 24v
>> >> regulated power
>> >>
>> >> - - -
>> >> Olufemi Adalemo
>> >> M: +234-803-5610040
>> >> M: +234-809-8610040
>> >> f...@adalemo.com
>> >>
>> >>
>> >>
>> >>
>> >> On Fri, Oct 12, 2012 at 6:17 PM, Josh Luthman
>> >>  wrote:
>> >>>
>> >>> Yes you 

Re: [WISPA] Another Ubiquity question

2012-10-15 Thread Faisal Imtiaz
hehe. well now you know why Rectifiers.. (large diodes) have 
heatsinks on them


:)

Faisal Imtiaz
Snappy Internet & Telecom
7266 SW 48 Street
Miami, Fl 33155
Tel: 305 663 5518 x 232
Helpdesk: 305 663 5518 option 2 Email: supp...@snappydsl.net

On 10/15/2012 4:38 PM, Josh Luthman wrote:
I tried that method.  Diode got hotter than hell.  Burnt right through 
the insulation I covered it with (and since it was bent the jacket 
came right off).


Josh Luthman
Office: 937-552-2340 
Direct: 937-552-2343 
1100 Wayne St
Suite 1337
Troy, OH 45373


On Mon, Oct 15, 2012 at 4:22 PM, Jeromie Reeves > wrote:


Why not run the NSM5 on 24v? Just add a diode or two to the + side,
the 1v drop on them will protect the NSM from
the charge voltage of the bank. $2 fix

On Mon, Oct 15, 2012 at 10:44 AM, Olufemi Adalemo
mailto:adal...@gmail.com>> wrote:
> It just dawned on me that I may have been barking up the wrong tree
> I only have the one NSM5 to connect, I could hook this up to the
parallel
> segment of my battery bank and get only 12v while the rest of the
> installation that's connected in series gets 24v. Do you think
this will
> work? Don't really have to worry about the NSM5 running down the
battery
> cause load is low and the cable run is under 10m so the voltage
drop from
> 12v will be negligible
>
> So this is how it would be:
> 24v solar panel connected to 24v charge controller with 4 x 12v
batteries
> connected in a 2x2 series/parallel array. cable connected to the
parallel
> segment of battery bank (theoretically giving 12v to the NSM5),
rest of the
> load connected to the charge controller at 24v
>
> What do you think?
>
> - - -
> Olufemi Adalemo
> M: +234-803-5610040 
> M: +234-809-8610040 
> f...@adalemo.com 
>
>
>
>
> On Fri, Oct 12, 2012 at 8:18 PM, Kristian Hoffmann
mailto:kh...@fire2wire.com>>
> wrote:
>>
>> Ya, it should be +24 on pins 4,5 and -24/comm on 7,8.  If it
blew up then
>> there was probably a short somewhere.
>>
>> -Kristian
>>
>>
>> On 10/12/2012 11:11 AM, Olufemi Adalemo wrote:
>>
>> Ah ok, it is possible that the guys didn't get the polarity right
>> I will check though they swear that they did
>>
>>
>> - - -
>> Olufemi Adalemo
>> M: +234-803-5610040 
>> M: +234-809-8610040 
>> f...@adalemo.com 
>>
>>
>>
>>
>> On Fri, Oct 12, 2012 at 7:05 PM, Josh Luthman
>> mailto:j...@imaginenetworksllc.com>> wrote:
>>>
>>> What voltage were the batteries spitting out?  They charge at
27v but
>>> without a charger put out much closer to 24v until they begin
discharging.
>>> If it fried the radio I would first think that it was
connected wrong, not
>>> that the voltage was too high.
>>>
>>> Josh Luthman
>>> Office: 937-552-2340 
>>> Direct: 937-552-2343 
>>> 1100 Wayne St
>>> Suite 1337
>>> Troy, OH 45373
>>>
>>>
>>> On Fri, Oct 12, 2012 at 2:02 PM, Olufemi Adalemo
mailto:adal...@gmail.com>>
>>> wrote:

 What's your typical config for the NSM5?
 Some of my guys just tried to power one off a 24v battery
bank (no
 charger connected just battery) and it fried good

 - - -
 Olufemi Adalemo
 M: +234-803-5610040 
 M: +234-809-8610040 
 f...@adalemo.com 




 On Fri, Oct 12, 2012 at 6:56 PM, Kristian Hoffmann
mailto:kh...@fire2wire.com>>
 wrote:
>
> We have MT and Ubnt equipment of all shapes and sizes
running at 27.6V.
> The only problems we've had are a handful of freak RB411s
that won't power
> on with >27V.  Most of the older ones wouldn't kick into
overvoltage
> protection until >28V, but we've come across a few odd balls.
>
> -Kristian
>
>
> On 10/12/2012 10:44 AM, Josh Luthman wrote:
>
> Charger isn't going to spit out 24v for batteries that need
charged,
> it's usually 27v.
>
> I was under the impression they would simply lock up and you
could
> reboot, or maybe I'm just thinking of MT.
>
> Josh Luthman
> Office: 937-552-2340 
> Direct: 937-552-2343 
> 1100 Wayne St
> Suite 1337
> Troy, OH 45373
>
>
> On Fri, Oct 12, 2012 at 10:08 PM, Olufemi Adalemo
mailto:adal...@gmail.com>>
> wrote:
>>
>> Aha, thanks
>> That explains why I have a dead NSM5 on my desk
>> I guess the charge controller is not very good at giving
out 24v
>> regulated power
>

Re: [WISPA] Another Ubiquity question

2012-10-15 Thread Josh Luthman
I tried that method.  Diode got hotter than hell.  Burnt right through the
insulation I covered it with (and since it was bent the jacket came right
off).

Josh Luthman
Office: 937-552-2340
Direct: 937-552-2343
1100 Wayne St
Suite 1337
Troy, OH 45373


On Mon, Oct 15, 2012 at 4:22 PM, Jeromie Reeves wrote:

> Why not run the NSM5 on 24v? Just add a diode or two to the + side,
> the 1v drop on them will protect the NSM from
> the charge voltage of the bank. $2 fix
>
> On Mon, Oct 15, 2012 at 10:44 AM, Olufemi Adalemo 
> wrote:
> > It just dawned on me that I may have been barking up the wrong tree
> > I only have the one NSM5 to connect, I could hook this up to the parallel
> > segment of my battery bank and get only 12v while the rest of the
> > installation that's connected in series gets 24v. Do you think this will
> > work? Don't really have to worry about the NSM5 running down the battery
> > cause load is low and the cable run is under 10m so the voltage drop from
> > 12v will be negligible
> >
> > So this is how it would be:
> > 24v solar panel connected to 24v charge controller with 4 x 12v batteries
> > connected in a 2x2 series/parallel array. cable connected to the parallel
> > segment of battery bank (theoretically giving 12v to the NSM5), rest of
> the
> > load connected to the charge controller at 24v
> >
> > What do you think?
> >
> > - - -
> > Olufemi Adalemo
> > M: +234-803-5610040
> > M: +234-809-8610040
> > f...@adalemo.com
> >
> >
> >
> >
> > On Fri, Oct 12, 2012 at 8:18 PM, Kristian Hoffmann 
> > wrote:
> >>
> >> Ya, it should be +24 on pins 4,5 and -24/comm on 7,8.  If it blew up
> then
> >> there was probably a short somewhere.
> >>
> >> -Kristian
> >>
> >>
> >> On 10/12/2012 11:11 AM, Olufemi Adalemo wrote:
> >>
> >> Ah ok, it is possible that the guys didn't get the polarity right
> >> I will check though they swear that they did
> >>
> >>
> >> - - -
> >> Olufemi Adalemo
> >> M: +234-803-5610040
> >> M: +234-809-8610040
> >> f...@adalemo.com
> >>
> >>
> >>
> >>
> >> On Fri, Oct 12, 2012 at 7:05 PM, Josh Luthman
> >>  wrote:
> >>>
> >>> What voltage were the batteries spitting out?  They charge at 27v but
> >>> without a charger put out much closer to 24v until they begin
> discharging.
> >>> If it fried the radio I would first think that it was connected wrong,
> not
> >>> that the voltage was too high.
> >>>
> >>> Josh Luthman
> >>> Office: 937-552-2340
> >>> Direct: 937-552-2343
> >>> 1100 Wayne St
> >>> Suite 1337
> >>> Troy, OH 45373
> >>>
> >>>
> >>> On Fri, Oct 12, 2012 at 2:02 PM, Olufemi Adalemo 
> >>> wrote:
> 
>  What's your typical config for the NSM5?
>  Some of my guys just tried to power one off a 24v battery bank (no
>  charger connected just battery) and it fried good
> 
>  - - -
>  Olufemi Adalemo
>  M: +234-803-5610040
>  M: +234-809-8610040
>  f...@adalemo.com
> 
> 
> 
> 
>  On Fri, Oct 12, 2012 at 6:56 PM, Kristian Hoffmann <
> kh...@fire2wire.com>
>  wrote:
> >
> > We have MT and Ubnt equipment of all shapes and sizes running at
> 27.6V.
> > The only problems we've had are a handful of freak RB411s that won't
> power
> > on with >27V.  Most of the older ones wouldn't kick into overvoltage
> > protection until >28V, but we've come across a few odd balls.
> >
> > -Kristian
> >
> >
> > On 10/12/2012 10:44 AM, Josh Luthman wrote:
> >
> > Charger isn't going to spit out 24v for batteries that need charged,
> > it's usually 27v.
> >
> > I was under the impression they would simply lock up and you could
> > reboot, or maybe I'm just thinking of MT.
> >
> > Josh Luthman
> > Office: 937-552-2340
> > Direct: 937-552-2343
> > 1100 Wayne St
> > Suite 1337
> > Troy, OH 45373
> >
> >
> > On Fri, Oct 12, 2012 at 10:08 PM, Olufemi Adalemo  >
> > wrote:
> >>
> >> Aha, thanks
> >> That explains why I have a dead NSM5 on my desk
> >> I guess the charge controller is not very good at giving out 24v
> >> regulated power
> >>
> >> - - -
> >> Olufemi Adalemo
> >> M: +234-803-5610040
> >> M: +234-809-8610040
> >> f...@adalemo.com
> >>
> >>
> >>
> >>
> >> On Fri, Oct 12, 2012 at 6:17 PM, Josh Luthman
> >>  wrote:
> >>>
> >>> Yes you will.  The batteries will probably be around 27v which Ubnt
> >>> won't like.  You'll need to clean the ~18-27v from the batteries
> to 24v.
> >>>
> >>> Josh Luthman
> >>> Office: 937-552-2340
> >>> Direct: 937-552-2343
> >>> 1100 Wayne St
> >>> Suite 1337
> >>> Troy, OH 45373
> >>>
> >>>
> >>> On Fri, Oct 12, 2012 at 1:14 PM, Olufemi Adalemo <
> adal...@gmail.com>
> >>> wrote:
> 
>  Need help,
>  I'm looking to deploy a UBNT NSM5 powered by a 24v solar supply.
>  Does anyone have experience with this? The data sheet shows that
> it
> >

Re: [WISPA] Another Ubiquity question

2012-10-15 Thread Jeromie Reeves
Why not run the NSM5 on 24v? Just add a diode or two to the + side,
the 1v drop on them will protect the NSM from
the charge voltage of the bank. $2 fix

On Mon, Oct 15, 2012 at 10:44 AM, Olufemi Adalemo  wrote:
> It just dawned on me that I may have been barking up the wrong tree
> I only have the one NSM5 to connect, I could hook this up to the parallel
> segment of my battery bank and get only 12v while the rest of the
> installation that's connected in series gets 24v. Do you think this will
> work? Don't really have to worry about the NSM5 running down the battery
> cause load is low and the cable run is under 10m so the voltage drop from
> 12v will be negligible
>
> So this is how it would be:
> 24v solar panel connected to 24v charge controller with 4 x 12v batteries
> connected in a 2x2 series/parallel array. cable connected to the parallel
> segment of battery bank (theoretically giving 12v to the NSM5), rest of the
> load connected to the charge controller at 24v
>
> What do you think?
>
> - - -
> Olufemi Adalemo
> M: +234-803-5610040
> M: +234-809-8610040
> f...@adalemo.com
>
>
>
>
> On Fri, Oct 12, 2012 at 8:18 PM, Kristian Hoffmann 
> wrote:
>>
>> Ya, it should be +24 on pins 4,5 and -24/comm on 7,8.  If it blew up then
>> there was probably a short somewhere.
>>
>> -Kristian
>>
>>
>> On 10/12/2012 11:11 AM, Olufemi Adalemo wrote:
>>
>> Ah ok, it is possible that the guys didn't get the polarity right
>> I will check though they swear that they did
>>
>>
>> - - -
>> Olufemi Adalemo
>> M: +234-803-5610040
>> M: +234-809-8610040
>> f...@adalemo.com
>>
>>
>>
>>
>> On Fri, Oct 12, 2012 at 7:05 PM, Josh Luthman
>>  wrote:
>>>
>>> What voltage were the batteries spitting out?  They charge at 27v but
>>> without a charger put out much closer to 24v until they begin discharging.
>>> If it fried the radio I would first think that it was connected wrong, not
>>> that the voltage was too high.
>>>
>>> Josh Luthman
>>> Office: 937-552-2340
>>> Direct: 937-552-2343
>>> 1100 Wayne St
>>> Suite 1337
>>> Troy, OH 45373
>>>
>>>
>>> On Fri, Oct 12, 2012 at 2:02 PM, Olufemi Adalemo 
>>> wrote:

 What's your typical config for the NSM5?
 Some of my guys just tried to power one off a 24v battery bank (no
 charger connected just battery) and it fried good

 - - -
 Olufemi Adalemo
 M: +234-803-5610040
 M: +234-809-8610040
 f...@adalemo.com




 On Fri, Oct 12, 2012 at 6:56 PM, Kristian Hoffmann 
 wrote:
>
> We have MT and Ubnt equipment of all shapes and sizes running at 27.6V.
> The only problems we've had are a handful of freak RB411s that won't power
> on with >27V.  Most of the older ones wouldn't kick into overvoltage
> protection until >28V, but we've come across a few odd balls.
>
> -Kristian
>
>
> On 10/12/2012 10:44 AM, Josh Luthman wrote:
>
> Charger isn't going to spit out 24v for batteries that need charged,
> it's usually 27v.
>
> I was under the impression they would simply lock up and you could
> reboot, or maybe I'm just thinking of MT.
>
> Josh Luthman
> Office: 937-552-2340
> Direct: 937-552-2343
> 1100 Wayne St
> Suite 1337
> Troy, OH 45373
>
>
> On Fri, Oct 12, 2012 at 10:08 PM, Olufemi Adalemo 
> wrote:
>>
>> Aha, thanks
>> That explains why I have a dead NSM5 on my desk
>> I guess the charge controller is not very good at giving out 24v
>> regulated power
>>
>> - - -
>> Olufemi Adalemo
>> M: +234-803-5610040
>> M: +234-809-8610040
>> f...@adalemo.com
>>
>>
>>
>>
>> On Fri, Oct 12, 2012 at 6:17 PM, Josh Luthman
>>  wrote:
>>>
>>> Yes you will.  The batteries will probably be around 27v which Ubnt
>>> won't like.  You'll need to clean the ~18-27v from the batteries to 24v.
>>>
>>> Josh Luthman
>>> Office: 937-552-2340
>>> Direct: 937-552-2343
>>> 1100 Wayne St
>>> Suite 1337
>>> Troy, OH 45373
>>>
>>>
>>> On Fri, Oct 12, 2012 at 1:14 PM, Olufemi Adalemo 
>>> wrote:

 Need help,
 I'm looking to deploy a UBNT NSM5 powered by a 24v solar supply.
 Does anyone have experience with this? The data sheet shows that it
 requires a 24v supply however the POE injector supplied is 15v, do I 
 need a
 DC to DC converter?

 Best regards,
 - - -
 Olufemi Adalemo
 M: +234-803-5610040
 M: +234-809-8610040
 f...@adalemo.com



 ___
 Wireless mailing list
 Wireless@wispa.org
 http://lists.wispa.org/mailman/listinfo/wireless

>>>
>>>
>>> ___
>>> Wireless mailing list
>>> Wireless@wispa.org
>>> http://lists.wispa.org/mailman/listinfo/wireless
>

Re: [WISPA] Another Ubiquity question

2012-10-15 Thread Greg Ihnen
I have a PS2 wired to the 12 starting battery of a generator which starts
and stops a few times a day with no issues. The PS2 doesn't even reset when
the gen starts and the battery pulls down to around 8~9 volts while the
starter is cranking. When the gen runs the batt voltage goes to ~14.6.

Greg

On Mon, Oct 15, 2012 at 1:50 PM, Josh Luthman
wrote:

> ~12v should be OK by specs, but I've never heard of anyone doing such a
> "low" voltage to a Ubnt device.  Not sure if no ones tried it or it just
> ended quickly in failure.
>
> Just be aware that 24v and 12v batteries have a higher voltage for
> charging.
>
> Josh Luthman
> Office: 937-552-2340
> Direct: 937-552-2343
> 1100 Wayne St
> Suite 1337
> Troy, OH 45373
>
>
> On Mon, Oct 15, 2012 at 1:44 PM, Olufemi Adalemo wrote:
>
>> It just dawned on me that I may have been barking up the wrong tree
>> I only have the one NSM5 to connect, I could hook this up to the parallel
>> segment of my battery bank and get only 12v while the rest of the
>> installation that's connected in series gets 24v. Do you think this will
>> work? Don't really have to worry about the NSM5 running down the battery
>> cause load is low and the cable run is under 10m so the voltage drop from
>> 12v will be negligible
>>
>> So this is how it would be:
>> 24v solar panel connected to 24v charge controller with 4 x 12v batteries
>> connected in a 2x2 series/parallel array. cable connected to the parallel
>> segment of battery bank (theoretically giving 12v to the NSM5), rest of the
>> load connected to the charge controller at 24v
>>
>> What do you think?
>>
>> - - -
>> *Olufemi Adalemo*
>> M: +234-803-5610040
>> M: +234-809-8610040
>> f...@adalemo.com
>>
>>
>>
>>
>> On Fri, Oct 12, 2012 at 8:18 PM, Kristian Hoffmann 
>> wrote:
>>
>>>  Ya, it should be +24 on pins 4,5 and -24/comm on 7,8.  If it blew up
>>> then there was probably a short somewhere.
>>>
>>> -Kristian
>>>
>>>
>>> On 10/12/2012 11:11 AM, Olufemi Adalemo wrote:
>>>
>>> Ah ok, it is possible that the guys didn't get the polarity right
>>> I will check though they swear that they did
>>>
>>>
>>>   - - -
>>> *Olufemi Adalemo*
>>>  M: +234-803-5610040
>>> M: +234-809-8610040
>>>  f...@adalemo.com
>>>
>>>
>>>
>>>
>>> On Fri, Oct 12, 2012 at 7:05 PM, Josh Luthman <
>>> j...@imaginenetworksllc.com> wrote:
>>>
 What voltage were the batteries spitting out?  They charge at 27v but
 without a charger put out much closer to 24v until they begin discharging.
  If it fried the radio I would first think that it was connected wrong, not
 that the voltage was too high.

 Josh Luthman
 Office: 937-552-2340
 Direct: 937-552-2343
 1100 Wayne St
 Suite 1337
 Troy, OH 45373


   On Fri, Oct 12, 2012 at 2:02 PM, Olufemi Adalemo 
 wrote:

> What's your typical config for the NSM5?
> Some of my guys just tried to power one off a 24v battery bank (no
> charger connected just battery) and it fried good
>
>   - - -
> *Olufemi Adalemo*
>  M: +234-803-5610040
> M: +234-809-8610040
>  f...@adalemo.com
>
>
>
>
>   On Fri, Oct 12, 2012 at 6:56 PM, Kristian Hoffmann <
> kh...@fire2wire.com> wrote:
>
>>  We have MT and Ubnt equipment of all shapes and sizes running at
>> 27.6V.  The only problems we've had are a handful of freak RB411s that
>> won't power on with >27V.  Most of the older ones wouldn't kick into
>> overvoltage protection until >28V, but we've come across a few odd balls.
>>
>> -Kristian
>>
>>
>> On 10/12/2012 10:44 AM, Josh Luthman wrote:
>>
>> Charger isn't going to spit out 24v for batteries that need charged,
>> it's usually 27v.
>>
>>  I was under the impression they would simply lock up and you could
>> reboot, or maybe I'm just thinking of MT.
>>
>> Josh Luthman
>> Office: 937-552-2340
>> Direct: 937-552-2343
>> 1100 Wayne St
>> Suite 1337
>> Troy, OH 45373
>>
>>
>> On Fri, Oct 12, 2012 at 10:08 PM, Olufemi Adalemo 
>> wrote:
>>
>>> Aha, thanks
>>> That explains why I have a dead NSM5 on my desk
>>> I guess the charge controller is not very good at giving out 24v
>>> regulated power
>>>
>>>   - - -
>>> *Olufemi Adalemo*
>>>  M: +234-803-5610040
>>> M: +234-809-8610040
>>>  f...@adalemo.com
>>>
>>>
>>>
>>>
>>>   On Fri, Oct 12, 2012 at 6:17 PM, Josh Luthman <
>>> j...@imaginenetworksllc.com> wrote:
>>>
 Yes you will.  The batteries will probably be around 27v which Ubnt
 won't like.  You'll need to clean the ~18-27v from the batteries to 
 24v.

 Josh Luthman
 Office: 937-552-2340
 Direct: 937-552-2343
 1100 Wayne St
 Suite 1337
 Troy, OH 45373


  On Fri, Oct 12, 2012 at 1:14 PM, Olufemi Adalemo <
 adal...@gmail.com> wrote:
>>>

Re: [WISPA] Another Ubiquity question

2012-10-15 Thread Greg Ihnen
My two cents: If you discharge part of your battery bank unevenly (pull off
just half of your 24v bank to get 12v for some loads) you will have trouble
with part of the bank getting over charged and part of the bank not getting
charged enough. If you were charging the bank with an AC charger that
charges each battery individually according to it's needs that wouldn't be
a problem. But if you're charging the entire bank with a single device that
charges the entire string in series like a 24v solar charger that is not a
good way to go. You'd be better off with a 24v to 12v regulator.

Greg

On Mon, Oct 15, 2012 at 1:44 PM, Olufemi Adalemo  wrote:

> It just dawned on me that I may have been barking up the wrong tree
> I only have the one NSM5 to connect, I could hook this up to the parallel
> segment of my battery bank and get only 12v while the rest of the
> installation that's connected in series gets 24v. Do you think this will
> work? Don't really have to worry about the NSM5 running down the battery
> cause load is low and the cable run is under 10m so the voltage drop from
> 12v will be negligible
>
> So this is how it would be:
> 24v solar panel connected to 24v charge controller with 4 x 12v batteries
> connected in a 2x2 series/parallel array. cable connected to the parallel
> segment of battery bank (theoretically giving 12v to the NSM5), rest of the
> load connected to the charge controller at 24v
>
> What do you think?
> - - -
> *Olufemi Adalemo*
> M: +234-803-5610040
> M: +234-809-8610040
> f...@adalemo.com
>
>
>
>
> On Fri, Oct 12, 2012 at 8:18 PM, Kristian Hoffmann wrote:
>
>>  Ya, it should be +24 on pins 4,5 and -24/comm on 7,8.  If it blew up
>> then there was probably a short somewhere.
>>
>> -Kristian
>>
>>
>> On 10/12/2012 11:11 AM, Olufemi Adalemo wrote:
>>
>> Ah ok, it is possible that the guys didn't get the polarity right
>> I will check though they swear that they did
>>
>>
>>   - - -
>> *Olufemi Adalemo*
>>  M: +234-803-5610040
>> M: +234-809-8610040
>>  f...@adalemo.com
>>
>>
>>
>>
>> On Fri, Oct 12, 2012 at 7:05 PM, Josh Luthman <
>> j...@imaginenetworksllc.com> wrote:
>>
>>> What voltage were the batteries spitting out?  They charge at 27v but
>>> without a charger put out much closer to 24v until they begin discharging.
>>>  If it fried the radio I would first think that it was connected wrong, not
>>> that the voltage was too high.
>>>
>>> Josh Luthman
>>> Office: 937-552-2340
>>> Direct: 937-552-2343
>>> 1100 Wayne St
>>> Suite 1337
>>> Troy, OH 45373
>>>
>>>
>>>   On Fri, Oct 12, 2012 at 2:02 PM, Olufemi Adalemo wrote:
>>>
 What's your typical config for the NSM5?
 Some of my guys just tried to power one off a 24v battery bank (no
 charger connected just battery) and it fried good

   - - -
 *Olufemi Adalemo*
  M: +234-803-5610040
 M: +234-809-8610040
  f...@adalemo.com




   On Fri, Oct 12, 2012 at 6:56 PM, Kristian Hoffmann <
 kh...@fire2wire.com> wrote:

>  We have MT and Ubnt equipment of all shapes and sizes running at
> 27.6V.  The only problems we've had are a handful of freak RB411s that
> won't power on with >27V.  Most of the older ones wouldn't kick into
> overvoltage protection until >28V, but we've come across a few odd balls.
>
> -Kristian
>
>
> On 10/12/2012 10:44 AM, Josh Luthman wrote:
>
> Charger isn't going to spit out 24v for batteries that need charged,
> it's usually 27v.
>
>  I was under the impression they would simply lock up and you could
> reboot, or maybe I'm just thinking of MT.
>
> Josh Luthman
> Office: 937-552-2340
> Direct: 937-552-2343
> 1100 Wayne St
> Suite 1337
> Troy, OH 45373
>
>
> On Fri, Oct 12, 2012 at 10:08 PM, Olufemi Adalemo 
> wrote:
>
>> Aha, thanks
>> That explains why I have a dead NSM5 on my desk
>> I guess the charge controller is not very good at giving out 24v
>> regulated power
>>
>>   - - -
>> *Olufemi Adalemo*
>>  M: +234-803-5610040
>> M: +234-809-8610040
>>  f...@adalemo.com
>>
>>
>>
>>
>>   On Fri, Oct 12, 2012 at 6:17 PM, Josh Luthman <
>> j...@imaginenetworksllc.com> wrote:
>>
>>> Yes you will.  The batteries will probably be around 27v which Ubnt
>>> won't like.  You'll need to clean the ~18-27v from the batteries to 24v.
>>>
>>> Josh Luthman
>>> Office: 937-552-2340
>>> Direct: 937-552-2343
>>> 1100 Wayne St
>>> Suite 1337
>>> Troy, OH 45373
>>>
>>>
>>>  On Fri, Oct 12, 2012 at 1:14 PM, Olufemi Adalemo >> > wrote:
>>>
  Need help,
 I'm looking to deploy a UBNT NSM5 powered by a 24v solar supply.
 Does anyone have experience with this? The data sheet shows that it
 requires a 24v supply however the POE injector supplied is 15v, do I 
 need a
 DC to DC converter?


Re: [WISPA] Another Ubiquity question

2012-10-15 Thread Eric Roth
I have done this at home with a Pico M2HP. My setup has two 60w 12v solar
panels connected to a charge controller with 2 12v 55AH AGM batteries in
parallel. The Pico is connected to the load output of the charge
controller with a DC input POE injector that I bought from Amazon for
about $10.

 

The setup works pretty good and I've had my first true test of the battery
bank this past month. Its rained here every day for the last three weeks.

 

--Eric Roth

Network Engineer

Webjogger Internet Services

(845) 757-4000

www.webjogger.net

 

 

From: wireless-boun...@wispa.org [mailto:wireless-boun...@wispa.org] On
Behalf Of Josh Luthman
Sent: Monday, October 15, 2012 1:51 PM
To: WISPA General List
Subject: Re: [WISPA] Another Ubiquity question

 

~12v should be OK by specs, but I've never heard of anyone doing such a
"low" voltage to a Ubnt device.  Not sure if no ones tried it or it just
ended quickly in failure.

 

Just be aware that 24v and 12v batteries have a higher voltage for
charging.


Josh Luthman
Office: 937-552-2340
Direct: 937-552-2343
1100 Wayne St
Suite 1337
Troy, OH 45373



On Mon, Oct 15, 2012 at 1:44 PM, Olufemi Adalemo 
wrote:

It just dawned on me that I may have been barking up the wrong tree

I only have the one NSM5 to connect, I could hook this up to the parallel
segment of my battery bank and get only 12v while the rest of the
installation that's connected in series gets 24v. Do you think this will
work? Don't really have to worry about the NSM5 running down the battery
cause load is low and the cable run is under 10m so the voltage drop from
12v will be negligible

 

So this is how it would be:

24v solar panel connected to 24v charge controller with 4 x 12v batteries
connected in a 2x2 series/parallel array. cable connected to the parallel
segment of battery bank (theoretically giving 12v to the NSM5), rest of
the load connected to the charge controller at 24v

 

What do you think?




- - -

Olufemi Adalemo

M: +234-803-5610040  

M: +234-809-8610040  

f...@adalemo.com

 





On Fri, Oct 12, 2012 at 8:18 PM, Kristian Hoffmann 
wrote:

Ya, it should be +24 on pins 4,5 and -24/comm on 7,8.  If it blew up then
there was probably a short somewhere.

-Kristian

 

On 10/12/2012 11:11 AM, Olufemi Adalemo wrote:

Ah ok, it is possible that the guys didn't get the polarity right 

I will check though they swear that they did

 




- - -

Olufemi Adalemo

M: +234-803-5610040  

M: +234-809-8610040  

f...@adalemo.com

 





On Fri, Oct 12, 2012 at 7:05 PM, Josh Luthman
 wrote:

What voltage were the batteries spitting out?  They charge at 27v but
without a charger put out much closer to 24v until they begin discharging.
If it fried the radio I would first think that it was connected wrong, not
that the voltage was too high. 


Josh Luthman
Office: 937-552-2340
Direct: 937-552-2343
1100 Wayne St
Suite 1337
Troy, OH 45373



On Fri, Oct 12, 2012 at 2:02 PM, Olufemi Adalemo 
wrote:

What's your typical config for the NSM5? 

Some of my guys just tried to power one off a 24v battery bank (no charger
connected just battery) and it fried good




- - -

Olufemi Adalemo

M: +234-803-5610040  

M: +234-809-8610040  

f...@adalemo.com

 





On Fri, Oct 12, 2012 at 6:56 PM, Kristian Hoffmann 
wrote:

We have MT and Ubnt equipment of all shapes and sizes running at 27.6V.
The only problems we've had are a handful of freak RB411s that won't power
on with >27V.  Most of the older ones wouldn't kick into overvoltage
protection until >28V, but we've come across a few odd balls.

-Kristian 

 

On 10/12/2012 10:44 AM, Josh Luthman wrote:

Charger isn't going to spit out 24v for batteries that need charged, it's
usually 27v. 

 

I was under the impression they would simply lock up and you could reboot,
or maybe I'm just thinking of MT.


Josh Luthman
Office: 937-552-2340
Direct: 937-552-2343
1100 Wayne St
Suite 1337
Troy, OH 45373



On Fri, Oct 12, 2012 at 10:08 PM, Olufemi Adalemo 
wrote:

Aha, thanks 

That explains why I have a dead NSM5 on my desk

I guess the charge controller is not very good at giving out 24v regulated
power




- - -

Olufemi Adalemo

M: +234-803-5610040  

M: +234-809-8610040  

f...@adalemo.com

 





On Fri, Oct 12, 2012 at 6:17 PM, Josh Luthman
 wrote:

Yes you will.  The batteries will probably be around 27v which Ubnt won't
like.  You'll need to clean the ~18-27v from the batteries to 24v. 


Josh Luthman
Office: 937-552-2340
Direct: 937-552-2343
1100 Wayne St
Suite 1337
Troy, OH 45373



On Fri, Oct 12, 2012 at 1:14 PM, Olufemi Adalemo 
wrote:

Need help, 

I'm looking to deploy a UBNT NSM5 powered by a 24v solar supply. 

Does anyone have experience with this? The data sheet shows that it
requires a 24v supply however the POE injector supplied is 15v, do I need
a DC to DC converter?

 

Best regards,


- - -

Olufemi Adalemo

M: +234-803-5610040  

M: +234-809-8610040  

f...@adalemo.com

 

 

 

___
Wireless mai

Re: [WISPA] Another Ubiquity question

2012-10-15 Thread aajayiobe
I've had installations like this. Its best to move the radio periodically if 
you are draining the batteries.



Akinlolu C. Ajayi-Obe
+234(0)8023258027

-Original Message-
From: Olufemi Adalemo 
Sender: wireless-boun...@wispa.org
Date: Mon, 15 Oct 2012 18:44:26 
To: WISPA General List
Reply-To: WISPA General List 
Subject: Re: [WISPA] Another Ubiquity question

___
Wireless mailing list
Wireless@wispa.org
http://lists.wispa.org/mailman/listinfo/wireless


___
Wireless mailing list
Wireless@wispa.org
http://lists.wispa.org/mailman/listinfo/wireless


Re: [WISPA] Another Ubiquity question

2012-10-15 Thread Josh Luthman
~12v should be OK by specs, but I've never heard of anyone doing such a
"low" voltage to a Ubnt device.  Not sure if no ones tried it or it just
ended quickly in failure.

Just be aware that 24v and 12v batteries have a higher voltage for charging.

Josh Luthman
Office: 937-552-2340
Direct: 937-552-2343
1100 Wayne St
Suite 1337
Troy, OH 45373


On Mon, Oct 15, 2012 at 1:44 PM, Olufemi Adalemo  wrote:

> It just dawned on me that I may have been barking up the wrong tree
> I only have the one NSM5 to connect, I could hook this up to the parallel
> segment of my battery bank and get only 12v while the rest of the
> installation that's connected in series gets 24v. Do you think this will
> work? Don't really have to worry about the NSM5 running down the battery
> cause load is low and the cable run is under 10m so the voltage drop from
> 12v will be negligible
>
> So this is how it would be:
> 24v solar panel connected to 24v charge controller with 4 x 12v batteries
> connected in a 2x2 series/parallel array. cable connected to the parallel
> segment of battery bank (theoretically giving 12v to the NSM5), rest of the
> load connected to the charge controller at 24v
>
> What do you think?
>
> - - -
> *Olufemi Adalemo*
> M: +234-803-5610040
> M: +234-809-8610040
> f...@adalemo.com
>
>
>
>
> On Fri, Oct 12, 2012 at 8:18 PM, Kristian Hoffmann wrote:
>
>>  Ya, it should be +24 on pins 4,5 and -24/comm on 7,8.  If it blew up
>> then there was probably a short somewhere.
>>
>> -Kristian
>>
>>
>> On 10/12/2012 11:11 AM, Olufemi Adalemo wrote:
>>
>> Ah ok, it is possible that the guys didn't get the polarity right
>> I will check though they swear that they did
>>
>>
>>   - - -
>> *Olufemi Adalemo*
>>  M: +234-803-5610040
>> M: +234-809-8610040
>>  f...@adalemo.com
>>
>>
>>
>>
>> On Fri, Oct 12, 2012 at 7:05 PM, Josh Luthman <
>> j...@imaginenetworksllc.com> wrote:
>>
>>> What voltage were the batteries spitting out?  They charge at 27v but
>>> without a charger put out much closer to 24v until they begin discharging.
>>>  If it fried the radio I would first think that it was connected wrong, not
>>> that the voltage was too high.
>>>
>>> Josh Luthman
>>> Office: 937-552-2340
>>> Direct: 937-552-2343
>>> 1100 Wayne St
>>> Suite 1337
>>> Troy, OH 45373
>>>
>>>
>>>   On Fri, Oct 12, 2012 at 2:02 PM, Olufemi Adalemo wrote:
>>>
 What's your typical config for the NSM5?
 Some of my guys just tried to power one off a 24v battery bank (no
 charger connected just battery) and it fried good

   - - -
 *Olufemi Adalemo*
  M: +234-803-5610040
 M: +234-809-8610040
  f...@adalemo.com




   On Fri, Oct 12, 2012 at 6:56 PM, Kristian Hoffmann <
 kh...@fire2wire.com> wrote:

>  We have MT and Ubnt equipment of all shapes and sizes running at
> 27.6V.  The only problems we've had are a handful of freak RB411s that
> won't power on with >27V.  Most of the older ones wouldn't kick into
> overvoltage protection until >28V, but we've come across a few odd balls.
>
> -Kristian
>
>
> On 10/12/2012 10:44 AM, Josh Luthman wrote:
>
> Charger isn't going to spit out 24v for batteries that need charged,
> it's usually 27v.
>
>  I was under the impression they would simply lock up and you could
> reboot, or maybe I'm just thinking of MT.
>
> Josh Luthman
> Office: 937-552-2340
> Direct: 937-552-2343
> 1100 Wayne St
> Suite 1337
> Troy, OH 45373
>
>
> On Fri, Oct 12, 2012 at 10:08 PM, Olufemi Adalemo 
> wrote:
>
>> Aha, thanks
>> That explains why I have a dead NSM5 on my desk
>> I guess the charge controller is not very good at giving out 24v
>> regulated power
>>
>>   - - -
>> *Olufemi Adalemo*
>>  M: +234-803-5610040
>> M: +234-809-8610040
>>  f...@adalemo.com
>>
>>
>>
>>
>>   On Fri, Oct 12, 2012 at 6:17 PM, Josh Luthman <
>> j...@imaginenetworksllc.com> wrote:
>>
>>> Yes you will.  The batteries will probably be around 27v which Ubnt
>>> won't like.  You'll need to clean the ~18-27v from the batteries to 24v.
>>>
>>> Josh Luthman
>>> Office: 937-552-2340
>>> Direct: 937-552-2343
>>> 1100 Wayne St
>>> Suite 1337
>>> Troy, OH 45373
>>>
>>>
>>>  On Fri, Oct 12, 2012 at 1:14 PM, Olufemi Adalemo >> > wrote:
>>>
  Need help,
 I'm looking to deploy a UBNT NSM5 powered by a 24v solar supply.
 Does anyone have experience with this? The data sheet shows that it
 requires a 24v supply however the POE injector supplied is 15v, do I 
 need a
 DC to DC converter?

  Best regards,
   - - -
 *Olufemi Adalemo*
  M: +234-803-5610040
 M: +234-809-8610040
  f...@adalemo.com



  ___
 Wir

Re: [WISPA] Another Ubiquity question

2012-10-15 Thread Olufemi Adalemo
It just dawned on me that I may have been barking up the wrong tree
I only have the one NSM5 to connect, I could hook this up to the parallel
segment of my battery bank and get only 12v while the rest of the
installation that's connected in series gets 24v. Do you think this will
work? Don't really have to worry about the NSM5 running down the battery
cause load is low and the cable run is under 10m so the voltage drop from
12v will be negligible

So this is how it would be:
24v solar panel connected to 24v charge controller with 4 x 12v batteries
connected in a 2x2 series/parallel array. cable connected to the parallel
segment of battery bank (theoretically giving 12v to the NSM5), rest of the
load connected to the charge controller at 24v

What do you think?
- - -
*Olufemi Adalemo*
M: +234-803-5610040
M: +234-809-8610040
f...@adalemo.com




On Fri, Oct 12, 2012 at 8:18 PM, Kristian Hoffmann wrote:

>  Ya, it should be +24 on pins 4,5 and -24/comm on 7,8.  If it blew up then
> there was probably a short somewhere.
>
> -Kristian
>
>
> On 10/12/2012 11:11 AM, Olufemi Adalemo wrote:
>
> Ah ok, it is possible that the guys didn't get the polarity right
> I will check though they swear that they did
>
>
>   - - -
> *Olufemi Adalemo*
>  M: +234-803-5610040
> M: +234-809-8610040
>  f...@adalemo.com
>
>
>
>
> On Fri, Oct 12, 2012 at 7:05 PM, Josh Luthman  > wrote:
>
>> What voltage were the batteries spitting out?  They charge at 27v but
>> without a charger put out much closer to 24v until they begin discharging.
>>  If it fried the radio I would first think that it was connected wrong, not
>> that the voltage was too high.
>>
>> Josh Luthman
>> Office: 937-552-2340
>> Direct: 937-552-2343
>> 1100 Wayne St
>> Suite 1337
>> Troy, OH 45373
>>
>>
>>   On Fri, Oct 12, 2012 at 2:02 PM, Olufemi Adalemo wrote:
>>
>>> What's your typical config for the NSM5?
>>> Some of my guys just tried to power one off a 24v battery bank (no
>>> charger connected just battery) and it fried good
>>>
>>>   - - -
>>> *Olufemi Adalemo*
>>>  M: +234-803-5610040
>>> M: +234-809-8610040
>>>  f...@adalemo.com
>>>
>>>
>>>
>>>
>>>   On Fri, Oct 12, 2012 at 6:56 PM, Kristian Hoffmann <
>>> kh...@fire2wire.com> wrote:
>>>
  We have MT and Ubnt equipment of all shapes and sizes running at
 27.6V.  The only problems we've had are a handful of freak RB411s that
 won't power on with >27V.  Most of the older ones wouldn't kick into
 overvoltage protection until >28V, but we've come across a few odd balls.

 -Kristian


 On 10/12/2012 10:44 AM, Josh Luthman wrote:

 Charger isn't going to spit out 24v for batteries that need charged,
 it's usually 27v.

  I was under the impression they would simply lock up and you could
 reboot, or maybe I'm just thinking of MT.

 Josh Luthman
 Office: 937-552-2340
 Direct: 937-552-2343
 1100 Wayne St
 Suite 1337
 Troy, OH 45373


 On Fri, Oct 12, 2012 at 10:08 PM, Olufemi Adalemo wrote:

> Aha, thanks
> That explains why I have a dead NSM5 on my desk
> I guess the charge controller is not very good at giving out 24v
> regulated power
>
>   - - -
> *Olufemi Adalemo*
>  M: +234-803-5610040
> M: +234-809-8610040
>  f...@adalemo.com
>
>
>
>
>   On Fri, Oct 12, 2012 at 6:17 PM, Josh Luthman <
> j...@imaginenetworksllc.com> wrote:
>
>> Yes you will.  The batteries will probably be around 27v which Ubnt
>> won't like.  You'll need to clean the ~18-27v from the batteries to 24v.
>>
>> Josh Luthman
>> Office: 937-552-2340
>> Direct: 937-552-2343
>> 1100 Wayne St
>> Suite 1337
>> Troy, OH 45373
>>
>>
>>  On Fri, Oct 12, 2012 at 1:14 PM, Olufemi Adalemo 
>> wrote:
>>
>>>  Need help,
>>> I'm looking to deploy a UBNT NSM5 powered by a 24v solar supply.
>>> Does anyone have experience with this? The data sheet shows that it
>>> requires a 24v supply however the POE injector supplied is 15v, do I 
>>> need a
>>> DC to DC converter?
>>>
>>>  Best regards,
>>>   - - -
>>> *Olufemi Adalemo*
>>>  M: +234-803-5610040
>>> M: +234-809-8610040
>>>  f...@adalemo.com
>>>
>>>
>>>
>>>  ___
>>> Wireless mailing list
>>> Wireless@wispa.org
>>> http://lists.wispa.org/mailman/listinfo/wireless
>>>
>>>
>>
>> ___
>> Wireless mailing list
>> Wireless@wispa.org
>> http://lists.wispa.org/mailman/listinfo/wireless
>>
>>
>
> ___
> Wireless mailing list
> Wireless@wispa.org
> http://lists.wispa.org/mailman/listinfo/wireless
>
>


 ___
 Wireless mailing 
 listWireless@wispa.orghttp://lists.wispa.o