Re: [WISPA] Preventing stupid outages

2012-03-20 Thread Scott Lambert
On Fri, Mar 16, 2012 at 09:04:35AM -0400, Troy Settle wrote:
 Ok, so to keep to code, we have a GFCI outlet for most of our towers.
 One of them tripped last night, causing me to have to put on some 80
 miles just to push a button (yes, it could have been much worse).

 Is there anything to prevent stupid outages like this from happening
 without violating code?

The tower at my house has gear plugged into the GFCI outlet nearby.
It seems to trip once every three or four months.

I've done some looking online for possible causes and the most
likely sounding explanation was that the equipment on the tower is
grounded to the tower and the tower ground system is not connected
to the electrical service ground.  

The AC panel is grounded to the electrical service ground rod on
the other end of the house.  I did not run the 80 feet of ground
wire to connect the tower ground system to the electrical service
ground rod.  I would have to break up some patio area to reach reach
the electrical service ground rod.

The postulation on the web forum was that in cases such as that,
there could be a very small difference in ground potential between
the two sets of grounds.  They suggested that the proper solution
would be to correctly connect the electrical service ground to the
tower ground.

Under certain circumstances the ground potential difference could
be increasing just enough to cause the GFCI to sense a fault.  The
last three times it happenned it was at around 8 AM which is about
when the tower end of the house gets fully bathed in the first
morning sunlight.  The service ground area is still fully shaded
for another 3 hours.  My best guess is that the temperature change
/ difference is causing ground potential variations.

I have a 3/4 inch copper, cold water, pipe running from one end of
the house to the other which I could use to connect the two ground
systems, but I haven't done the research to figure out if that is
safe.  The cold water pipe is plastic before it makes ground contact.
So, the pipe itself is not a good place to find an electrical ground.

-- 
Scott LambertKC5MLE   Unix SysAdmin
lamb...@lambertfam.org

___
Wireless mailing list
Wireless@wispa.org
http://lists.wispa.org/mailman/listinfo/wireless


Re: [WISPA] Preventing stupid outages

2012-03-20 Thread Jonathan Schmidt
Scott, I’m not quite so sure.



If current flows back through the ground rather than neutral, that will
trip the GFCI.  The ground is BAD as far as the GFCI is, so the dryer
can’t be a 3-wire.



The hypothetical situation was an Ungrounded hair dryer and plastic pipes
(which would have to be totally dry…no moisture).  Then, current flow
would be only back through neutral and, therefore, no pop.



With any other slight variance and it would pop…such as moisture from the
faucet to the water line along the surface of the tub.



. . . j o n a t h a n



  _

From: wireless-boun...@wispa.org [mailto:wireless-boun...@wispa.org] On
Behalf Of Scott Reed
Sent: Sunday, March 18, 2012 5:12 PM
To: WISPA General List
Subject: Re: [WISPA] Preventing stupid outages



GFCI works by comparing the current on the hot side and the neutral side.
If they are different by more than a very small amount, it trips.
Even the static discharge from walking across the carpet and touch a
protected device can create enough current on the neutral side to trip
some devices.

The water in the tub doesn't have to be ground if the hair dryer has a 3
wire cord.  There can be current through the water to the dryer's ground,
thus creating the imbalance needed to trip the device.

The last time I read the NEC, you can string outlets off a GFCI outlet, up
to a maximum of 4.  After that you need another GFCI.

On 3/17/2012 9:41 PM, Jonathan Schmidt wrote:

GFCIs…you can’t live with them and can’t live without them.



A real problem is that they wear out…something that isn’t well known.  Old
GFCIs may pop prematurely or fail to pop.  TEST THEM YEARLY!



About the hair dryer in the bathtub…assuming the water is ground, I can’t
imagine that exactly the same current from the “hot” side will 100% flow
back on the neutral because, if it isn’t, the thing will pop.



What am I missing about the bridge and the sensitivity?



I had my sister have all her old house sockets (at least the head of a
string) equipped with GFCIs.  I took a cheap tester to her house and
almost 50% of the AC sockets were wired wrong so they needed fixing, too.
Many had grounded outlets that had no ground, and ½ had the pins
backwards!  I guess the folks who sold them the house in 1985 did a
band-aid job.



If you have customers with older houses and old GFCIs supplying their
modem/router, you should encourage them to test and replace before calling
you.



Anyway, every time my sister had a thunderstorm, the office GFCI would
pop…probably because the computer was grounded through the cable router
and cable modem.  The socket was behind a very large, heavy bookcase.  I’m
proud of her, because, by the second time, she got a drill with a ¾” bit
and put a hole in the backboard to allow pushing the reset with a pencil
eraser.  Hence, my recommendation to have your customers understand this
since the GFCI that runs your service is the most likely to pop in a
thunderstorm.



. . . j o n a t h a n







  _

From: wireless-boun...@wispa.org [mailto:wireless-boun...@wispa.org] On
Behalf Of Blair Davis
Sent: Saturday, March 17, 2012 1:37 AM
To: WISPA General List
Subject: Re: [WISPA] Preventing stupid outages



GFCI's are to detect and prevent leakage currents.

They monitor the current in the hot and the neutral lines.

Ever stood barefoot on the ground and held a drill or saw and gotten
shocked?  A GFCI, working properly, will prevent that from killing you, or
even shocking you for more than a few mS

In properly working equipment, basic electrical theory shows that the
current in the hot line and current in the neutral lines must be equal.

If the currents are not equal, then current is 'leaking;' out of the
circuit.

The GFCI senses the imbalance and interrupts the circuit to stop the
leakage.

They are not perfect, though.

You can hook up an old 2 prong hair dryer and drop it in a bathtub full of
water without tripping the GFCI if you know how.

I was an electrician for the Navy for years...

I won't plug a tower into one.  Every time the lighting flashes for 30
miles around, they trip...



On 3/16/2012 11:45 AM, DJ Anderson wrote:

I thought GFCI's were to protect circuits from moisture mainly, AFAIK they
do not provide any type of protection for devices other than cutting the
circuit if it senses a ground fault.


DJ Anderson

Shelby Broadband






On Fri, Mar 16, 2012 at 11:38 AM, Ben West b...@gowasabi.net wrote:

To add to the anecdotal evidence against cheap GFCI outlets, I had to
remove one in a building when spontaneous trips started occurring randomly
(e.g. once every couple weeks) after an adjacent building received a
direct lightening strike.



For that matter, the GFCI contributed nothing to lightening protection,
still lost a bunch of equipment.



--
Ben West

http://gowasabi.net
b...@gowasabi.net




___
Wireless mailing list
Wireless@wispa.org
http://lists.wispa.org/mailman/listinfo/wireless

Re: [WISPA] Preventing stupid outages

2012-03-19 Thread Robert Kim App and Facebook Marketing
You'll need a solar powered battery pack if totally remote but instead of a
cell phone... you just need a 4g modem.

On Fri, Mar 16, 2012 at 10:40 PM, Victoria Proffer 
victo...@stlbroadband.com wrote:

 Is there a remote power strip that can be activated by a cell phone?

 ** **

 i.e. 

 strip  cell phone  pstn  my computer

 ** **

 Victoria Proffer

 314-974-5600

 **

-- 
Robert Q Kim
Event Marketing Company NYC and LA
http://www.youtube.com/watch?v=w-4z-ZwF5VA
2611 S Coast Highway
San Diego, CA 92007
310 598 1606
___
Wireless mailing list
Wireless@wispa.org
http://lists.wispa.org/mailman/listinfo/wireless


Re: [WISPA] Preventing stupid outages

2012-03-19 Thread Faisal Imtiaz
I have not seen those... but there are GMS Controlled Relays that can be 
used to turn things on and off..


We use  such devices...

Just google for 'GSM Remote Switch' or better yet search on Ebay for 
'gsm remote switch'


Regards.

Faisal Imtiaz
Snappy Internet  Telecom
7266 SW 48 Street
Miami, Fl 33155
Tel: 305 663 5518 x 232
Helpdesk: 305 663 5518 option 2 Email: supp...@snappydsl.net


On Fri, Mar 16, 2012 at 10:40 PM, Victoria Proffer 
victo...@stlbroadband.com mailto:victo...@stlbroadband.com wrote:


Is there a remote power strip that can be activated by a cell phone?

i.e.

strip  cell phone  pstn  my computer

Victoria Proffer

314-974-5600

--
Robert Q Kim
Event Marketing Company NYC and LA
http://www.youtube.com/watch?v=w-4z-ZwF5VA
2611 S Coast Highway
San Diego, CA 92007
310 598 1606


___
Wireless mailing list
Wireless@wispa.org
http://lists.wispa.org/mailman/listinfo/wireless
___
Wireless mailing list
Wireless@wispa.org
http://lists.wispa.org/mailman/listinfo/wireless


Re: [WISPA] Preventing stupid outages

2012-03-19 Thread Tom DeReggi
Troy,

Related to GFI We've removed all GFIs from our implemntations for this 
reason. We try to redesign our isntall plan to a way that code wont require the 
GFIs.

As far as Dragonwave versus Mikrotik, one rebooting and not the other. The 
Dragonwave draws more current than the Mikrotik to operate, so its not 
surprising, if a short brownout spike occurred that the power flowing was 
enough to keep the mikrotik running, but not the Dragonwave.

One way to help with that is to have a overspec'd UPS. Running a UPS at 44%, 
power storage capacity in its capacitor's will be less sufficient to cover for 
power drops, than if the UPS was run at a lower load.  Another way to deal with 
it is to modify the setup to a Dual realtime power feed situation, so better 
chance one of teh two systems will deliver power, before a switch to battery, 
or if a breaker trips on one of the power circuits.



 

Tom DeReggi
RapidDSL  Wireless, Inc
IntAirNet- Fixed Wireless Broadband


  - Original Message - 
  From: Troy Settle 
  To: 'WISPA General List' 
  Sent: Friday, March 16, 2012 4:48 PM
  Subject: Re: [WISPA] Preventing stupid outages


  Next stupid outage at a different site.

   

  Specs:

   

  Generac 8KW generator

  Automatic Transfer Switch

  APC 450 rack mount UPS

  Mikrotik RB1200

  Mikrotik RB435 (3x 802.11n sectors)

  Dragonwave Compact Horizon #1

  Dragonwave Compact Horizon #2

   

  (I don't know how many horses, chickens, goats, pigs, and other critters are 
onsite, but I don't think they're an issue).

   

  Total load on the UPS is at 44%, estimated run is 25 minutes (long enough for 
the generator and switch to do their thing).

   

  Radios grounded to the tower, tower grounded and bonded to the shack.  Shack 
has two rods (panel - Rod - Rod - Generator).

   

  Everything inside is bonded as well, including the drain wires on all the 
Cat-5.

   

  Yesterday, the Dragonwaves rebooted several times during the storm, but 
neither RB lost power even once.

   

  Any guesses?  I'm sleeping on it over the weekend, but probably need to get 
it figured out before too many more storms come over the mountains.

   

  Thanks,

   

  -Troy

   

   

   

  From: wireless-boun...@wispa.org [mailto:wireless-boun...@wispa.org] On 
Behalf Of Troy Settle
  Sent: Friday, March 16, 2012 9:05 AM
  To: wireless@wispa.org
  Subject: [WISPA] Preventing stupid outages

   

  Ok, so to keep to code, we have a GFCI outlet for most of our towers.  One of 
them tripped last night, causing me to have to put on some 80 miles just to 
push a button (yes, it could have been much worse).

   

  Is there anything to prevent stupid outages like this from happening without 
violating code?

   

  Thanks,

   

  -- 

Troy Settle, Network Administrator

The Wired Road Authority

1117 E. Stuart Dr.

Galax, VA 24333

(276) 238-0049 (office)

(276) 237-3890 (cell)

tset...@thewiredroad.net

   



--


  ___
  Wireless mailing list
  Wireless@wispa.org
  http://lists.wispa.org/mailman/listinfo/wireless
___
Wireless mailing list
Wireless@wispa.org
http://lists.wispa.org/mailman/listinfo/wireless


Re: [WISPA] Preventing stupid outages

2012-03-18 Thread Scott Reed
GFCI works by comparing the current on the hot side and the neutral 
side.  If they are different by more than a very small amount, it trips.
Even the static discharge from walking across the carpet and touch a 
protected device can create enough current on the neutral side to trip 
some devices.


The water in the tub doesn't have to be ground if the hair dryer has a 3 
wire cord.  There can be current through the water to the dryer's 
ground, thus creating the imbalance needed to trip the device.


The last time I read the NEC, you can string outlets off a GFCI outlet, 
up to a maximum of 4.  After that you need another GFCI.


On 3/17/2012 9:41 PM, Jonathan Schmidt wrote:


GFCIs...you can't live with them and can't live without them.

A real problem is that they wear out...something that isn't well 
known.  Old GFCIs may pop prematurely or fail to pop.  TEST THEM YEARLY!


About the hair dryer in the bathtub...assuming the water is ground, I 
can't imagine that exactly the same current from the hot side will 
100% flow back on the neutral because, if it isn't, the thing will pop.


What am I missing about the bridge and the sensitivity?

I had my sister have all her old house sockets (at least the head of a 
string) equipped with GFCIs.  I took a cheap tester to her house and 
almost 50% of the AC sockets were wired wrong so they needed fixing, 
too.  Many had grounded outlets that had no ground, and ½ had the pins 
backwards!  I guess the folks who sold them the house in 1985 did a 
band-aid job.


If you have customers with older houses and old GFCIs supplying their 
modem/router, you should encourage them to test and replace before 
calling you.


Anyway, every time my sister had a thunderstorm, the office GFCI would 
pop...probably because the computer was grounded through the cable 
router and cable modem.  The socket was behind a very large, heavy 
bookcase.  I'm proud of her, because, by the second time, she got a 
drill with a ¾ bit and put a hole in the backboard to allow pushing 
the reset with a pencil eraser.  Hence, my recommendation to have your 
customers understand this since the GFCI that runs your service is the 
most likely to pop in a thunderstorm.


. . . j o n a t h a n



*From:*wireless-boun...@wispa.org [mailto:wireless-boun...@wispa.org] 
*On Behalf Of *Blair Davis

*Sent:* Saturday, March 17, 2012 1:37 AM
*To:* WISPA General List
*Subject:* Re: [WISPA] Preventing stupid outages

GFCI's are to detect and prevent leakage currents.

They monitor the current in the hot and the neutral lines.

Ever stood barefoot on the ground and held a drill or saw and gotten 
shocked?  A GFCI, working properly, will prevent that from killing 
you, or even shocking you for more than a few mS


In properly working equipment, basic electrical theory shows that the 
current in the hot line and current in the neutral lines must be equal.


If the currents are not equal, then current is 'leaking;' out of the 
circuit.


The GFCI senses the imbalance and interrupts the circuit to stop the 
leakage.


They are not perfect, though.

You can hook up an old 2 prong hair dryer and drop it in a bathtub 
full of water without tripping the GFCI if you know how.


I was an electrician for the Navy for years...

I won't plug a tower into one.  Every time the lighting flashes for 30 
miles around, they trip...




On 3/16/2012 11:45 AM, DJ Anderson wrote:

I thought GFCI's were to protect circuits from moisture mainly, AFAIK 
they do not provide any type of protection for devices other than 
cutting the circuit if it senses a ground fault.


DJ Anderson

Shelby Broadband



On Fri, Mar 16, 2012 at 11:38 AM, Ben West b...@gowasabi.net 
mailto:b...@gowasabi.net wrote:


To add to the anecdotal evidence against cheap GFCI outlets, I had to 
remove one in a building when spontaneous trips started occurring 
randomly (e.g. once every couple weeks) after an adjacent building 
received a direct lightening strike.


For that matter, the GFCI contributed nothing to lightening 
protection, still lost a bunch of equipment.


--
Ben West

http://gowasabi.net
b...@gowasabi.net mailto:b...@gowasabi.net


___
Wireless mailing list
Wireless@wispa.org mailto:Wireless@wispa.org
http://lists.wispa.org/mailman/listinfo/wireless




___
Wireless mailing list
Wireless@wispa.org  mailto:Wireless@wispa.org
http://lists.wispa.org/mailman/listinfo/wireless



--
West Michigan  Wireless ISP
Allegan,Michigan49010
269-686-8648
  
A Division of:

Camp Communication Services, INC


___
Wireless mailing list
Wireless@wispa.org
http://lists.wispa.org/mailman/listinfo/wireless


No virus found in this message.
Checked by AVG - www.avg.com http://www.avg.com
Version: 2012.0.1913 / Virus Database: 2114/4876 - Release Date: 03/17/12

Re: [WISPA] Preventing stupid outages

2012-03-17 Thread Blair Davis

  
  
GFCI's are to detect and prevent leakage currents.

They monitor the current in the hot and the neutral lines.

Ever stood barefoot on the ground and held a drill or saw and gotten
shocked? A GFCI, working properly, will prevent that from killing
you, or even shocking you for more than a few mS

In properly working equipment, basic electrical theory shows that
the current in the hot line and current in the neutral lines must be
equal.

If the currents are not equal, then current is 'leaking;' out of the
circuit. 

The GFCI senses the imbalance and interrupts the circuit to stop the
leakage.

They are not perfect, though.

You can hook up an old 2 prong hair dryer and drop it in a bathtub
full of water without tripping the GFCI if you know how.

I was an electrician for the Navy for years...

I won't plug a tower into one. Every time the lighting flashes for
30 miles around, they trip...



On 3/16/2012 11:45 AM, DJ Anderson wrote:
I thought GFCI's wereto protect circuits from
  moisture mainly, AFAIK they do not provide any type of protection
  for devices other than cutting the circuit if it senses a ground
  fault.
  
  DJ Anderson

  Shelby Broadband



On Fri, Mar 16, 2012 at 11:38 AM, Ben
  West b...@gowasabi.net
  wrote:
  
To add to theanecdotal evidence against cheap GFCI outlets,
I had to remove one in a building when spontaneous trips
started occurring randomly (e.g. once every couple weeks)
after an adjacent building received a direct lightening
strike.

  

For that matter, the GFCI contributed nothing to
  lightening protection, still lost a bunch of equipment.
  
  
  -- 
  Ben West
  http://gowasabi.net
b...@gowasabi.net
  


___
Wireless mailing list
Wireless@wispa.org
http://lists.wispa.org/mailman/listinfo/wireless

  


  
  
  
  
  ___
Wireless mailing list
Wireless@wispa.org
http://lists.wispa.org/mailman/listinfo/wireless



-- 
West Michigan Wireless ISP
Allegan, Michigan  49010
269-686-8648

A Division of:
Camp Communication Services, INC

  

___
Wireless mailing list
Wireless@wispa.org
http://lists.wispa.org/mailman/listinfo/wireless


Re: [WISPA] Preventing stupid outages

2012-03-17 Thread Jonathan Schmidt
GFCIs…you can’t live with them and can’t live without them.



A real problem is that they wear out…something that isn’t well known.  Old
GFCIs may pop prematurely or fail to pop.  TEST THEM YEARLY!



About the hair dryer in the bathtub…assuming the water is ground, I can’t
imagine that exactly the same current from the “hot” side will 100% flow
back on the neutral because, if it isn’t, the thing will pop.



What am I missing about the bridge and the sensitivity?



I had my sister have all her old house sockets (at least the head of a
string) equipped with GFCIs.  I took a cheap tester to her house and
almost 50% of the AC sockets were wired wrong so they needed fixing, too.
Many had grounded outlets that had no ground, and ½ had the pins
backwards!  I guess the folks who sold them the house in 1985 did a
band-aid job.



If you have customers with older houses and old GFCIs supplying their
modem/router, you should encourage them to test and replace before calling
you.



Anyway, every time my sister had a thunderstorm, the office GFCI would
pop…probably because the computer was grounded through the cable router
and cable modem.  The socket was behind a very large, heavy bookcase.  I’m
proud of her, because, by the second time, she got a drill with a ¾” bit
and put a hole in the backboard to allow pushing the reset with a pencil
eraser.  Hence, my recommendation to have your customers understand this
since the GFCI that runs your service is the most likely to pop in a
thunderstorm.



. . . j o n a t h a n







  _

From: wireless-boun...@wispa.org [mailto:wireless-boun...@wispa.org] On
Behalf Of Blair Davis
Sent: Saturday, March 17, 2012 1:37 AM
To: WISPA General List
Subject: Re: [WISPA] Preventing stupid outages



GFCI's are to detect and prevent leakage currents.

They monitor the current in the hot and the neutral lines.

Ever stood barefoot on the ground and held a drill or saw and gotten
shocked?  A GFCI, working properly, will prevent that from killing you, or
even shocking you for more than a few mS

In properly working equipment, basic electrical theory shows that the
current in the hot line and current in the neutral lines must be equal.

If the currents are not equal, then current is 'leaking;' out of the
circuit.

The GFCI senses the imbalance and interrupts the circuit to stop the
leakage.

They are not perfect, though.

You can hook up an old 2 prong hair dryer and drop it in a bathtub full of
water without tripping the GFCI if you know how.

I was an electrician for the Navy for years...

I won't plug a tower into one.  Every time the lighting flashes for 30
miles around, they trip...



On 3/16/2012 11:45 AM, DJ Anderson wrote:

I thought GFCI's were to protect circuits from moisture mainly, AFAIK they
do not provide any type of protection for devices other than cutting the
circuit if it senses a ground fault.


DJ Anderson

Shelby Broadband





On Fri, Mar 16, 2012 at 11:38 AM, Ben West b...@gowasabi.net wrote:

To add to the anecdotal evidence against cheap GFCI outlets, I had to
remove one in a building when spontaneous trips started occurring randomly
(e.g. once every couple weeks) after an adjacent building received a
direct lightening strike.



For that matter, the GFCI contributed nothing to lightening protection,
still lost a bunch of equipment.



--
Ben West

http://gowasabi.net
b...@gowasabi.net




___
Wireless mailing list
Wireless@wispa.org
http://lists.wispa.org/mailman/listinfo/wireless








___
Wireless mailing list
Wireless@wispa.org
http://lists.wispa.org/mailman/listinfo/wireless





--
West Michigan Wireless ISP
Allegan, Michigan  49010
269-686-8648

A Division of:
Camp Communication Services, INC
___
Wireless mailing list
Wireless@wispa.org
http://lists.wispa.org/mailman/listinfo/wireless


Re: [WISPA] Preventing stupid outages

2012-03-17 Thread Blair Davis

  
  
Often, in homes with plastic pipes, the water in the tub is NOT
grounded!

On 3/17/2012 9:41 PM, Jonathan Schmidt wrote:

  
  
  

  

  
  
  
GFCIsyou
  cant live with them
  and cant live without them.

A real
  problem is that they wear outsomething
  that isnt well known. Old GFCIs may pop
  prematurely or fail to pop. TEST
  THEM YEARLY!

About the
  hair dryer in the bathtubassuming
  the water is ground, I cant imagine that exactly
  the same current from
  the hot side will 100% flow back on the neutral
  because, if it
  isnt, the thing will pop.

What am I
  missing about the bridge and the
  sensitivity?

I had my
  sister have all her old house
  sockets (at least the head of a string) equipped
  with GFCIs. I took a cheap
  tester to her house and almost 50% of the AC
  sockets were wired wrong so they
  needed fixing, too. Many had grounded outlets
  that had no ground, and  had
  the pins backwards! I guess the folks who sold
  them the house in 1985 did a
  band-aid job.

If you have
  customers with older houses
  and old GFCIs supplying their modem/router, you
  should encourage them to test
  and replace before calling you.

Anyway, every
  time my sister had a thunderstorm,
  the office GFCI would popprobably because the
  computer was grounded
  through the cable router and cable modem. The
  socket was behind a very large,
  heavy bookcase. Im proud of her, because, by the
  second time, she got a
  drill with a  bit and put a hole in the
  backboard to allow pushing the
  reset with a pencil eraser. Hence, my
  recommendation to have your customers
  understand this since the GFCI that runs your
  service is the most likely to pop
  in a thunderstorm.

. . . j o n a
  t h a n




  

  
  From: wireless-boun...@wispa.org
[mailto:wireless-boun...@wispa.org] On Behalf
Of Blair Davis
Sent:
Saturday, March 17, 2012
1:37 AM
To:
WISPA General List
Subject:
Re: [WISPA] Preventing
stupid outages


GFCI's
  are to detect and prevent leakage currents.
  
  They monitor the current in the hot and the
  neutral lines.
  
  Ever stood barefoot on the ground and held a drill
  or saw and gotten
  shocked? A GFCI, working properly, will prevent
  that from killing you, or
  even shocking you for more than a few mS
  
  In properly working equipment, basic electrical
  theory shows that the current
  in the hot line and current in the neutral lines
  must be equal.
  
  If the currents are not equal, then current is
  'leaking;' out of the
  circuit. 
  
  The GFCI senses the imbalance and interrupts the
  circuit to stop the leakage.
  
  They are not perfect, though.
  
  You can hook up an old 2 prong hair dryer and drop
  it in a bathtub full of
  water without tripping the GFCI if you know how

Re: [WISPA] Preventing stupid outages

2012-03-17 Thread Jonathan Schmidt
Oops…that tells you I’m an old F@#rt.

Thanks, Blair,…you’re right.  Hadn’t thought of that.

. . . j o n a t h a n



  _

From: wireless-boun...@wispa.org [mailto:wireless-boun...@wispa.org] On
Behalf Of Blair Davis
Sent: Saturday, March 17, 2012 9:08 PM
To: WISPA General List
Subject: Re: [WISPA] Preventing stupid outages



Often, in homes with plastic pipes, the water in the tub is NOT grounded!

On 3/17/2012 9:41 PM, Jonathan Schmidt wrote:

GFCIs…you can’t live with them and can’t live without them.



A real problem is that they wear out…something that isn’t well known.  Old
GFCIs may pop prematurely or fail to pop.  TEST THEM YEARLY!



About the hair dryer in the bathtub…assuming the water is ground, I can’t
imagine that exactly the same current from the “hot” side will 100% flow
back on the neutral because, if it isn’t, the thing will pop.



What am I missing about the bridge and the sensitivity?



I had my sister have all her old house sockets (at least the head of a
string) equipped with GFCIs.  I took a cheap tester to her house and
almost 50% of the AC sockets were wired wrong so they needed fixing, too.
Many had grounded outlets that had no ground, and ½ had the pins
backwards!  I guess the folks who sold them the house in 1985 did a
band-aid job.



If you have customers with older houses and old GFCIs supplying their
modem/router, you should encourage them to test and replace before calling
you.



Anyway, every time my sister had a thunderstorm, the office GFCI would
pop…probably because the computer was grounded through the cable router
and cable modem.  The socket was behind a very large, heavy bookcase.  I’m
proud of her, because, by the second time, she got a drill with a ¾” bit
and put a hole in the backboard to allow pushing the reset with a pencil
eraser.  Hence, my recommendation to have your customers understand this
since the GFCI that runs your service is the most likely to pop in a
thunderstorm.



. . . j o n a t h a n







  _

From: wireless-boun...@wispa.org [mailto:wireless-boun...@wispa.org] On
Behalf Of Blair Davis
Sent: Saturday, March 17, 2012 1:37 AM
To: WISPA General List
Subject: Re: [WISPA] Preventing stupid outages



GFCI's are to detect and prevent leakage currents.

They monitor the current in the hot and the neutral lines.

Ever stood barefoot on the ground and held a drill or saw and gotten
shocked?  A GFCI, working properly, will prevent that from killing you, or
even shocking you for more than a few mS

In properly working equipment, basic electrical theory shows that the
current in the hot line and current in the neutral lines must be equal.

If the currents are not equal, then current is 'leaking;' out of the
circuit.

The GFCI senses the imbalance and interrupts the circuit to stop the
leakage.

They are not perfect, though.

You can hook up an old 2 prong hair dryer and drop it in a bathtub full of
water without tripping the GFCI if you know how.

I was an electrician for the Navy for years...

I won't plug a tower into one.  Every time the lighting flashes for 30
miles around, they trip...



On 3/16/2012 11:45 AM, DJ Anderson wrote:

I thought GFCI's were to protect circuits from moisture mainly, AFAIK they
do not provide any type of protection for devices other than cutting the
circuit if it senses a ground fault.


DJ Anderson

Shelby Broadband






On Fri, Mar 16, 2012 at 11:38 AM, Ben West b...@gowasabi.net wrote:

To add to the anecdotal evidence against cheap GFCI outlets, I had to
remove one in a building when spontaneous trips started occurring randomly
(e.g. once every couple weeks) after an adjacent building received a
direct lightening strike.



For that matter, the GFCI contributed nothing to lightening protection,
still lost a bunch of equipment.



--
Ben West

http://gowasabi.net
b...@gowasabi.net




___
Wireless mailing list
Wireless@wispa.org
http://lists.wispa.org/mailman/listinfo/wireless







___
Wireless mailing list
Wireless@wispa.org
http://lists.wispa.org/mailman/listinfo/wireless






--
West Michigan Wireless ISP
Allegan, Michigan  49010
269-686-8648

A Division of:
Camp Communication Services, INC






___
Wireless mailing list
Wireless@wispa.org
http://lists.wispa.org/mailman/listinfo/wireless





--
West Michigan Wireless ISP
Allegan, Michigan  49010
269-686-8648

A Division of:
Camp Communication Services, INC
___
Wireless mailing list
Wireless@wispa.org
http://lists.wispa.org/mailman/listinfo/wireless


[WISPA] Preventing stupid outages

2012-03-16 Thread Troy Settle
Ok, so to keep to code, we have a GFCI outlet for most of our towers.  One
of them tripped last night, causing me to have to put on some 80 miles just
to push a button (yes, it could have been much worse).

 

Is there anything to prevent stupid outages like this from happening without
violating code?

 

Thanks,

 

-- 

  Troy Settle, Network Administrator

  The Wired Road Authority

  1117 E. Stuart Dr.

  Galax, VA 24333

  (276) 238-0049 (office)

  (276) 237-3890 (cell)

  tset...@thewiredroad.net

 

___
Wireless mailing list
Wireless@wispa.org
http://lists.wispa.org/mailman/listinfo/wireless


Re: [WISPA] Preventing stupid outages

2012-03-16 Thread Matt Hoppes
You have to have GFCI outlets indoors?  I've never heard of that 
regulation before.

A few thoughts come to mind:

* Battery backup with 2 or so hours of run time along with a remote page 
for a power outage.  Doesn't prevent you from having to dispatch but it 
keeps you from having an outage.

* Re-check code?  I don't understand why you need a GFCI outlet inside 
your shack.You don't have a sink or other water nearby.  I don't 
have GFCI outlets in my office.  Maybe I'm missing something here.

If you are mounting an outdoor NEMA box with your equipment and just 
plugging into a GFCI then maybe you can figure out some way to get a 
hardwire into the box rather than plugging into an outside GFCI?

On 3/16/12 9:04 AM, Troy Settle wrote:
 Ok, so to keep to code, we have a GFCI outlet for most of our towers.
 One of them tripped last night, causing me to have to put on some 80
 miles just to push a button (yes, it could have been much worse).

 Is there anything to prevent stupid outages like this from happening
 without violating code?

 Thanks,

 --

 Troy Settle, Network Administrator

 The Wired Road Authority

 1117 E. Stuart Dr.

 Galax, VA 24333

 (276) 238-0049 (office)

 (276) 237-3890 (cell)

 tset...@thewiredroad.net



 ___
 Wireless mailing list
 Wireless@wispa.org
 http://lists.wispa.org/mailman/listinfo/wireless
___
Wireless mailing list
Wireless@wispa.org
http://lists.wispa.org/mailman/listinfo/wireless


Re: [WISPA] Preventing stupid outages

2012-03-16 Thread Ryan Ghering
We don't use them at towers, but I have here at home auto resetting GFCI
outlets for my
Saltwater reef tank. Got them from Home Depot.. They reset automatically
after a few mins..

Ryan

On Fri, Mar 16, 2012 at 7:08 AM, Matt Hoppes mhop...@indigowireless.comwrote:

 You have to have GFCI outlets indoors?  I've never heard of that
 regulation before.

 A few thoughts come to mind:

 * Battery backup with 2 or so hours of run time along with a remote page
 for a power outage.  Doesn't prevent you from having to dispatch but it
 keeps you from having an outage.

 * Re-check code?  I don't understand why you need a GFCI outlet inside
 your shack.You don't have a sink or other water nearby.  I don't
 have GFCI outlets in my office.  Maybe I'm missing something here.

 If you are mounting an outdoor NEMA box with your equipment and just
 plugging into a GFCI then maybe you can figure out some way to get a
 hardwire into the box rather than plugging into an outside GFCI?

 On 3/16/12 9:04 AM, Troy Settle wrote:
  Ok, so to keep to code, we have a GFCI outlet for most of our towers.
  One of them tripped last night, causing me to have to put on some 80
  miles just to push a button (yes, it could have been much worse).
 
  Is there anything to prevent stupid outages like this from happening
  without violating code?
 
  Thanks,
 
  --
 
  Troy Settle, Network Administrator
 
  The Wired Road Authority
 
  1117 E. Stuart Dr.
 
  Galax, VA 24333
 
  (276) 238-0049 (office)
 
  (276) 237-3890 (cell)
 
  tset...@thewiredroad.net
 
 
 
  ___
  Wireless mailing list
  Wireless@wispa.org
  http://lists.wispa.org/mailman/listinfo/wireless
 ___
 Wireless mailing list
 Wireless@wispa.org
 http://lists.wispa.org/mailman/listinfo/wireless




-- 
Ryan Ghering
Network Operations - Plains.Net
Office: 970-848-0475 - Cell: 970-630-1879
___
Wireless mailing list
Wireless@wispa.org
http://lists.wispa.org/mailman/listinfo/wireless


Re: [WISPA] Preventing stupid outages

2012-03-16 Thread Victoria Proffer
Is there a remote power strip that can be activated by a cell phone?

 

i.e. 

strip  cell phone  pstn  my computer

 

Victoria Proffer

 http://www.stlwimax.com/ STLWiMAX, LLC

314-974-5600

 

From: wireless-boun...@wispa.org [mailto:wireless-boun...@wispa.org] On
Behalf Of Ryan Ghering
Sent: Friday, March 16, 2012 8:20 AM
To: WISPA General List
Subject: Re: [WISPA] Preventing stupid outages

 

We don't use them at towers, but I have here at home auto resetting GFCI
outlets for my 
Saltwater reef tank. Got them from Home Depot.. They reset automatically
after a few mins..

Ryan

On Fri, Mar 16, 2012 at 7:08 AM, Matt Hoppes mhop...@indigowireless.com
wrote:

You have to have GFCI outlets indoors?  I've never heard of that
regulation before.

A few thoughts come to mind:

* Battery backup with 2 or so hours of run time along with a remote page
for a power outage.  Doesn't prevent you from having to dispatch but it
keeps you from having an outage.

* Re-check code?  I don't understand why you need a GFCI outlet inside
your shack.You don't have a sink or other water nearby.  I don't
have GFCI outlets in my office.  Maybe I'm missing something here.

If you are mounting an outdoor NEMA box with your equipment and just
plugging into a GFCI then maybe you can figure out some way to get a
hardwire into the box rather than plugging into an outside GFCI?


On 3/16/12 9:04 AM, Troy Settle wrote:
 Ok, so to keep to code, we have a GFCI outlet for most of our towers.
 One of them tripped last night, causing me to have to put on some 80
 miles just to push a button (yes, it could have been much worse).

 Is there anything to prevent stupid outages like this from happening
 without violating code?

 Thanks,

 --

 Troy Settle, Network Administrator

 The Wired Road Authority

 1117 E. Stuart Dr.

 Galax, VA 24333

 (276) 238-0049 tel:%28276%29%20238-0049  (office)

 (276) 237-3890 tel:%28276%29%20237-3890  (cell)

 tset...@thewiredroad.net




 ___
 Wireless mailing list
 Wireless@wispa.org
 http://lists.wispa.org/mailman/listinfo/wireless
___
Wireless mailing list
Wireless@wispa.org
http://lists.wispa.org/mailman/listinfo/wireless




-- 
Ryan Ghering
Network Operations - Plains.Net
Office: 970-848-0475 - Cell: 970-630-1879

___
Wireless mailing list
Wireless@wispa.org
http://lists.wispa.org/mailman/listinfo/wireless


Re: [WISPA] Preventing stupid outages

2012-03-16 Thread Jay DeBoer

http://dataprobe.com/remote-reboot.html

I've used some of their older 'iboots' havent' used their phone devices.



On 3/16/2012 9:40, Victoria Proffer wrote:


Is there a remote power strip that can be activated by a cell phone?

i.e.

strip  cell phone  pstn  my computer

Victoria Proffer

STLWiMAX, LLC http://www.stlwimax.com/

314-974-5600

*From:*wireless-boun...@wispa.org [mailto:wireless-boun...@wispa.org] 
*On Behalf Of *Ryan Ghering

*Sent:* Friday, March 16, 2012 8:20 AM
*To:* WISPA General List
*Subject:* Re: [WISPA] Preventing stupid outages

We don't use them at towers, but I have here at home auto resetting 
GFCI outlets for my
Saltwater reef tank. Got them from Home Depot.. They reset 
automatically after a few mins..


Ryan

On Fri, Mar 16, 2012 at 7:08 AM, Matt Hoppes 
mhop...@indigowireless.com mailto:mhop...@indigowireless.com wrote:


You have to have GFCI outlets indoors?  I've never heard of that
regulation before.

A few thoughts come to mind:

* Battery backup with 2 or so hours of run time along with a remote page
for a power outage.  Doesn't prevent you from having to dispatch but it
keeps you from having an outage.

* Re-check code?  I don't understand why you need a GFCI outlet inside
your shack.You don't have a sink or other water nearby.  I don't
have GFCI outlets in my office.  Maybe I'm missing something here.

If you are mounting an outdoor NEMA box with your equipment and just
plugging into a GFCI then maybe you can figure out some way to get a
hardwire into the box rather than plugging into an outside GFCI?


On 3/16/12 9:04 AM, Troy Settle wrote:
 Ok, so to keep to code, we have a GFCI outlet for most of our towers.
 One of them tripped last night, causing me to have to put on some 80
 miles just to push a button (yes, it could have been much worse).

 Is there anything to prevent stupid outages like this from happening
 without violating code?

 Thanks,

 --

 Troy Settle, Network Administrator

 The Wired Road Authority

 1117 E. Stuart Dr.

 Galax, VA 24333

 (276) 238-0049 tel:%28276%29%20238-0049 (office)

 (276) 237-3890 tel:%28276%29%20237-3890 (cell)

 tset...@thewiredroad.net mailto:tset...@thewiredroad.net




 ___
 Wireless mailing list
 Wireless@wispa.org mailto:Wireless@wispa.org
 http://lists.wispa.org/mailman/listinfo/wireless
___
Wireless mailing list
Wireless@wispa.org mailto:Wireless@wispa.org
http://lists.wispa.org/mailman/listinfo/wireless




--
Ryan Ghering
Network Operations - Plains.Net
Office: 970-848-0475 - Cell: 970-630-1879



___
Wireless mailing list
Wireless@wispa.org
http://lists.wispa.org/mailman/listinfo/wireless


___
Wireless mailing list
Wireless@wispa.org
http://lists.wispa.org/mailman/listinfo/wireless


Re: [WISPA] Preventing stupid outages

2012-03-16 Thread Brian Webster
The remote reboot power strip does nothing for you if the GFCI outlet or
breaker has tripped, that needs to be reset unless it's an auto reset
device.

 

Thank You,

Brian Webster

www.wirelessmapping.com

www.Broadband-Mapping.com

 

From: wireless-boun...@wispa.org [mailto:wireless-boun...@wispa.org] On
Behalf Of Victoria Proffer
Sent: Friday, March 16, 2012 9:40 AM
To: 'WISPA General List'
Subject: Re: [WISPA] Preventing stupid outages

 

Is there a remote power strip that can be activated by a cell phone?

 

i.e. 

strip  cell phone  pstn  my computer

 

Victoria Proffer

STLWiMAX, LLC http://www.stlwimax.com/ 

314-974-5600

 

From: wireless-boun...@wispa.org [mailto:wireless-boun...@wispa.org] On
Behalf Of Ryan Ghering
Sent: Friday, March 16, 2012 8:20 AM
To: WISPA General List
Subject: Re: [WISPA] Preventing stupid outages

 

We don't use them at towers, but I have here at home auto resetting GFCI
outlets for my 
Saltwater reef tank. Got them from Home Depot.. They reset automatically
after a few mins..

Ryan

On Fri, Mar 16, 2012 at 7:08 AM, Matt Hoppes mhop...@indigowireless.com
wrote:

You have to have GFCI outlets indoors?  I've never heard of that
regulation before.

A few thoughts come to mind:

* Battery backup with 2 or so hours of run time along with a remote page
for a power outage.  Doesn't prevent you from having to dispatch but it
keeps you from having an outage.

* Re-check code?  I don't understand why you need a GFCI outlet inside
your shack.You don't have a sink or other water nearby.  I don't
have GFCI outlets in my office.  Maybe I'm missing something here.

If you are mounting an outdoor NEMA box with your equipment and just
plugging into a GFCI then maybe you can figure out some way to get a
hardwire into the box rather than plugging into an outside GFCI?


On 3/16/12 9:04 AM, Troy Settle wrote:
 Ok, so to keep to code, we have a GFCI outlet for most of our towers.
 One of them tripped last night, causing me to have to put on some 80
 miles just to push a button (yes, it could have been much worse).

 Is there anything to prevent stupid outages like this from happening
 without violating code?

 Thanks,

 --

 Troy Settle, Network Administrator

 The Wired Road Authority

 1117 E. Stuart Dr.

 Galax, VA 24333

 (276) 238-0049 tel:%28276%29%20238-0049  (office)

 (276) 237-3890 tel:%28276%29%20237-3890  (cell)

 tset...@thewiredroad.net




 ___
 Wireless mailing list
 Wireless@wispa.org
 http://lists.wispa.org/mailman/listinfo/wireless
___
Wireless mailing list
Wireless@wispa.org
http://lists.wispa.org/mailman/listinfo/wireless




-- 
Ryan Ghering
Network Operations - Plains.Net
Office: 970-848-0475 - Cell: 970-630-1879

___
Wireless mailing list
Wireless@wispa.org
http://lists.wispa.org/mailman/listinfo/wireless


Re: [WISPA] Preventing stupid outages

2012-03-16 Thread Victoria Proffer
Can you set it on an auto-ping?

 

Victoria Proffer

 http://www.stlwimax.com/ STLWiMAX, LLC

314-974-5600

 

From: Brian Webster [mailto:bwebs...@wirelessmapping.com] 
Sent: Friday, March 16, 2012 9:02 AM
To: victo...@stlbroadband.com; 'WISPA General List'
Subject: RE: [WISPA] Preventing stupid outages

 

The remote reboot power strip does nothing for you if the GFCI outlet or
breaker has tripped, that needs to be reset unless it's an auto reset
device.

 

Thank You,

Brian Webster

www.wirelessmapping.com

www.Broadband-Mapping.com

 

From: wireless-boun...@wispa.org [mailto:wireless-boun...@wispa.org] On
Behalf Of Victoria Proffer
Sent: Friday, March 16, 2012 9:40 AM
To: 'WISPA General List'
Subject: Re: [WISPA] Preventing stupid outages

 

Is there a remote power strip that can be activated by a cell phone?

 

i.e. 

strip  cell phone  pstn  my computer

 

Victoria Proffer

STLWiMAX, LLC http://www.stlwimax.com/ 

314-974-5600

 

From: wireless-boun...@wispa.org [mailto:wireless-boun...@wispa.org] On
Behalf Of Ryan Ghering
Sent: Friday, March 16, 2012 8:20 AM
To: WISPA General List
Subject: Re: [WISPA] Preventing stupid outages

 

We don't use them at towers, but I have here at home auto resetting GFCI
outlets for my 
Saltwater reef tank. Got them from Home Depot.. They reset automatically
after a few mins..

Ryan

On Fri, Mar 16, 2012 at 7:08 AM, Matt Hoppes mhop...@indigowireless.com
wrote:

You have to have GFCI outlets indoors?  I've never heard of that
regulation before.

A few thoughts come to mind:

* Battery backup with 2 or so hours of run time along with a remote page
for a power outage.  Doesn't prevent you from having to dispatch but it
keeps you from having an outage.

* Re-check code?  I don't understand why you need a GFCI outlet inside
your shack.You don't have a sink or other water nearby.  I don't
have GFCI outlets in my office.  Maybe I'm missing something here.

If you are mounting an outdoor NEMA box with your equipment and just
plugging into a GFCI then maybe you can figure out some way to get a
hardwire into the box rather than plugging into an outside GFCI?


On 3/16/12 9:04 AM, Troy Settle wrote:
 Ok, so to keep to code, we have a GFCI outlet for most of our towers.
 One of them tripped last night, causing me to have to put on some 80
 miles just to push a button (yes, it could have been much worse).

 Is there anything to prevent stupid outages like this from happening
 without violating code?

 Thanks,

 --

 Troy Settle, Network Administrator

 The Wired Road Authority

 1117 E. Stuart Dr.

 Galax, VA 24333

 (276) 238-0049 tel:%28276%29%20238-0049  (office)

 (276) 237-3890 tel:%28276%29%20237-3890  (cell)

 tset...@thewiredroad.net




 ___
 Wireless mailing list
 Wireless@wispa.org
 http://lists.wispa.org/mailman/listinfo/wireless
___
Wireless mailing list
Wireless@wispa.org
http://lists.wispa.org/mailman/listinfo/wireless




-- 
Ryan Ghering
Network Operations - Plains.Net
Office: 970-848-0475 - Cell: 970-630-1879

___
Wireless mailing list
Wireless@wispa.org
http://lists.wispa.org/mailman/listinfo/wireless


Re: [WISPA] Preventing stupid outages

2012-03-16 Thread Chuck Hogg
I don't think you understand.  A GFCI outlet is a mechanical device.  You
can't reboot it.

Regards,
Chuck


On Fri, Mar 16, 2012 at 10:19 AM, Victoria Proffer 
victo...@stlbroadband.com wrote:

 Can you set it on an auto-ping?

 ** **

 Victoria Proffer

 STLWiMAX, LLC http://www.stlwimax.com/

 314-974-5600

 ** **

 *From:* Brian Webster [mailto:bwebs...@wirelessmapping.com]
 *Sent:* Friday, March 16, 2012 9:02 AM
 *To:* victo...@stlbroadband.com; 'WISPA General List'
 *Subject:* RE: [WISPA] Preventing stupid outages

 ** **

 The remote reboot power strip does nothing for you if the GFCI outlet or
 breaker has tripped, that needs to be reset unless it’s an auto reset
 device.

 ** **

 Thank You,

 Brian Webster

 www.wirelessmapping.com

 www.Broadband-Mapping.com

 ** **

 *From:* wireless-boun...@wispa.org 
 [mailto:wireless-boun...@wispa.orgwireless-boun...@wispa.org]
 *On Behalf Of *Victoria Proffer
 *Sent:* Friday, March 16, 2012 9:40 AM
 *To:* 'WISPA General List'
 *Subject:* Re: [WISPA] Preventing stupid outages

 ** **

 Is there a remote power strip that can be activated by a cell phone?

 ** **

 i.e. 

 strip  cell phone  pstn  my computer

 ** **

 Victoria Proffer

 STLWiMAX, LLC http://www.stlwimax.com/

 314-974-5600

 ** **

 *From:* wireless-boun...@wispa.org [mailto:wireless-boun...@wispa.org] *On
 Behalf Of *Ryan Ghering
 *Sent:* Friday, March 16, 2012 8:20 AM
 *To:* WISPA General List
 *Subject:* Re: [WISPA] Preventing stupid outages

 ** **

 We don't use them at towers, but I have here at home auto resetting GFCI
 outlets for my
 Saltwater reef tank. Got them from Home Depot.. They reset automatically
 after a few mins..

 Ryan

 On Fri, Mar 16, 2012 at 7:08 AM, Matt Hoppes mhop...@indigowireless.com
 wrote:

 You have to have GFCI outlets indoors?  I've never heard of that
 regulation before.

 A few thoughts come to mind:

 * Battery backup with 2 or so hours of run time along with a remote page
 for a power outage.  Doesn't prevent you from having to dispatch but it
 keeps you from having an outage.

 * Re-check code?  I don't understand why you need a GFCI outlet inside
 your shack.You don't have a sink or other water nearby.  I don't
 have GFCI outlets in my office.  Maybe I'm missing something here.

 If you are mounting an outdoor NEMA box with your equipment and just
 plugging into a GFCI then maybe you can figure out some way to get a
 hardwire into the box rather than plugging into an outside GFCI?


 On 3/16/12 9:04 AM, Troy Settle wrote:
  Ok, so to keep to code, we have a GFCI outlet for most of our towers.
  One of them tripped last night, causing me to have to put on some 80
  miles just to push a button (yes, it could have been much worse).
 
  Is there anything to prevent stupid outages like this from happening
  without violating code?
 
  Thanks,
 
  --
 
  Troy Settle, Network Administrator
 
  The Wired Road Authority
 
  1117 E. Stuart Dr.
 
  Galax, VA 24333
 
  (276) 238-0049 (office)
 
  (276) 237-3890 (cell)
 
  tset...@thewiredroad.net
 
 
 

  ___
  Wireless mailing list
  Wireless@wispa.org
  http://lists.wispa.org/mailman/listinfo/wireless
 ___
 Wireless mailing list
 Wireless@wispa.org
 http://lists.wispa.org/mailman/listinfo/wireless




 --
 Ryan Ghering
 Network Operations - Plains.Net
 Office: 970-848-0475 - Cell: 970-630-1879

 ___
 Wireless mailing list
 Wireless@wispa.org
 http://lists.wispa.org/mailman/listinfo/wireless


___
Wireless mailing list
Wireless@wispa.org
http://lists.wispa.org/mailman/listinfo/wireless


Re: [WISPA] Preventing stupid outages

2012-03-16 Thread Josh Luthman
One of these

http://www.google.com/products/catalog?q=gfci+outletoe=utf-8rls=org.mozilla:en-US:officialclient=firefox-aum=1ie=UTF-8tbm=shopcid=16532274097447588363sa=Xei=Ik5jT6H-Nubk0QHnkZWZCAved=0CIoBEPICMAI

Where did you one that auto resets, Ryan?

Josh Luthman
Office: 937-552-2340
Direct: 937-552-2343
1100 Wayne St
Suite 1337
Troy, OH 45373



On Fri, Mar 16, 2012 at 10:23 AM, Chuck Hogg ch...@shelbybb.com wrote:
 I don't think you understand.  A GFCI outlet is a mechanical device.  You
 can't reboot it.

 Regards,
 Chuck



 On Fri, Mar 16, 2012 at 10:19 AM, Victoria Proffer
 victo...@stlbroadband.com wrote:

 Can you set it on an auto-ping?



 Victoria Proffer

 STLWiMAX, LLC

 314-974-5600



 From: Brian Webster [mailto:bwebs...@wirelessmapping.com]
 Sent: Friday, March 16, 2012 9:02 AM
 To: victo...@stlbroadband.com; 'WISPA General List'
 Subject: RE: [WISPA] Preventing stupid outages



 The remote reboot power strip does nothing for you if the GFCI outlet or
 breaker has tripped, that needs to be reset unless it’s an auto reset
 device.



 Thank You,

 Brian Webster

 www.wirelessmapping.com

 www.Broadband-Mapping.com



 From: wireless-boun...@wispa.org [mailto:wireless-boun...@wispa.org] On
 Behalf Of Victoria Proffer
 Sent: Friday, March 16, 2012 9:40 AM
 To: 'WISPA General List'
 Subject: Re: [WISPA] Preventing stupid outages



 Is there a remote power strip that can be activated by a cell phone?



 i.e.

 strip  cell phone  pstn  my computer



 Victoria Proffer

 STLWiMAX, LLC

 314-974-5600



 From: wireless-boun...@wispa.org [mailto:wireless-boun...@wispa.org] On
 Behalf Of Ryan Ghering
 Sent: Friday, March 16, 2012 8:20 AM
 To: WISPA General List
 Subject: Re: [WISPA] Preventing stupid outages



 We don't use them at towers, but I have here at home auto resetting GFCI
 outlets for my
 Saltwater reef tank. Got them from Home Depot.. They reset automatically
 after a few mins..

 Ryan

 On Fri, Mar 16, 2012 at 7:08 AM, Matt Hoppes mhop...@indigowireless.com
 wrote:

 You have to have GFCI outlets indoors?  I've never heard of that
 regulation before.

 A few thoughts come to mind:

 * Battery backup with 2 or so hours of run time along with a remote page
 for a power outage.  Doesn't prevent you from having to dispatch but it
 keeps you from having an outage.

 * Re-check code?  I don't understand why you need a GFCI outlet inside
 your shack.    You don't have a sink or other water nearby.  I don't
 have GFCI outlets in my office.  Maybe I'm missing something here.

 If you are mounting an outdoor NEMA box with your equipment and just
 plugging into a GFCI then maybe you can figure out some way to get a
 hardwire into the box rather than plugging into an outside GFCI?


 On 3/16/12 9:04 AM, Troy Settle wrote:
  Ok, so to keep to code, we have a GFCI outlet for most of our towers.
  One of them tripped last night, causing me to have to put on some 80
  miles just to push a button (yes, it could have been much worse).
 
  Is there anything to prevent stupid outages like this from happening
  without violating code?
 
  Thanks,
 
  --
 
  Troy Settle, Network Administrator
 
  The Wired Road Authority
 
  1117 E. Stuart Dr.
 
  Galax, VA 24333
 
  (276) 238-0049 (office)
 
  (276) 237-3890 (cell)
 
  tset...@thewiredroad.net
 
 
 

  ___
  Wireless mailing list
  Wireless@wispa.org
  http://lists.wispa.org/mailman/listinfo/wireless
 ___
 Wireless mailing list
 Wireless@wispa.org
 http://lists.wispa.org/mailman/listinfo/wireless




 --
 Ryan Ghering
 Network Operations - Plains.Net
 Office: 970-848-0475 - Cell: 970-630-1879


 ___
 Wireless mailing list
 Wireless@wispa.org
 http://lists.wispa.org/mailman/listinfo/wireless



 ___
 Wireless mailing list
 Wireless@wispa.org
 http://lists.wispa.org/mailman/listinfo/wireless

___
Wireless mailing list
Wireless@wispa.org
http://lists.wispa.org/mailman/listinfo/wireless


Re: [WISPA] Preventing stupid outages

2012-03-16 Thread Victoria Proffer
Oh, yeah ... I see, so than you have to reset the circuit, which requires a
flip.

 

Victoria Proffer

 http://www.stlwimax.com/ STLWiMAX, LLC

314-974-5600

 

From: Chuck Hogg [mailto:ch...@shelbybb.com] 
Sent: Friday, March 16, 2012 9:24 AM
To: victo...@stlbroadband.com; WISPA General List
Cc: bwebs...@wirelessmapping.com
Subject: Re: [WISPA] Preventing stupid outages

 

I don't think you understand.  A GFCI outlet is a mechanical device.  You
can't reboot it.


Regards,
Chuck



On Fri, Mar 16, 2012 at 10:19 AM, Victoria Proffer
victo...@stlbroadband.com wrote:

Can you set it on an auto-ping?

 

Victoria Proffer

STLWiMAX, LLC http://www.stlwimax.com/ 

314-974-5600

 

From: Brian Webster [mailto:bwebs...@wirelessmapping.com] 
Sent: Friday, March 16, 2012 9:02 AM
To: victo...@stlbroadband.com; 'WISPA General List'
Subject: RE: [WISPA] Preventing stupid outages

 

The remote reboot power strip does nothing for you if the GFCI outlet or
breaker has tripped, that needs to be reset unless it's an auto reset
device.

 

Thank You,

Brian Webster

www.wirelessmapping.com

www.Broadband-Mapping.com

 

From: wireless-boun...@wispa.org [mailto:wireless-boun...@wispa.org] On
Behalf Of Victoria Proffer
Sent: Friday, March 16, 2012 9:40 AM
To: 'WISPA General List'
Subject: Re: [WISPA] Preventing stupid outages

 

Is there a remote power strip that can be activated by a cell phone?

 

i.e. 

strip  cell phone  pstn  my computer

 

Victoria Proffer

STLWiMAX, LLC http://www.stlwimax.com/ 

314-974-5600

 

From: wireless-boun...@wispa.org [mailto:wireless-boun...@wispa.org] On
Behalf Of Ryan Ghering
Sent: Friday, March 16, 2012 8:20 AM
To: WISPA General List
Subject: Re: [WISPA] Preventing stupid outages

 

We don't use them at towers, but I have here at home auto resetting GFCI
outlets for my 
Saltwater reef tank. Got them from Home Depot.. They reset automatically
after a few mins..

Ryan

On Fri, Mar 16, 2012 at 7:08 AM, Matt Hoppes mhop...@indigowireless.com
wrote:

You have to have GFCI outlets indoors?  I've never heard of that
regulation before.

A few thoughts come to mind:

* Battery backup with 2 or so hours of run time along with a remote page
for a power outage.  Doesn't prevent you from having to dispatch but it
keeps you from having an outage.

* Re-check code?  I don't understand why you need a GFCI outlet inside
your shack.You don't have a sink or other water nearby.  I don't
have GFCI outlets in my office.  Maybe I'm missing something here.

If you are mounting an outdoor NEMA box with your equipment and just
plugging into a GFCI then maybe you can figure out some way to get a
hardwire into the box rather than plugging into an outside GFCI?


On 3/16/12 9:04 AM, Troy Settle wrote:
 Ok, so to keep to code, we have a GFCI outlet for most of our towers.
 One of them tripped last night, causing me to have to put on some 80
 miles just to push a button (yes, it could have been much worse).

 Is there anything to prevent stupid outages like this from happening
 without violating code?

 Thanks,

 --

 Troy Settle, Network Administrator

 The Wired Road Authority

 1117 E. Stuart Dr.

 Galax, VA 24333

 (276) 238-0049 tel:%28276%29%20238-0049  (office)

 (276) 237-3890 tel:%28276%29%20237-3890  (cell)

 tset...@thewiredroad.net




 ___
 Wireless mailing list
 Wireless@wispa.org
 http://lists.wispa.org/mailman/listinfo/wireless
___
Wireless mailing list
Wireless@wispa.org
http://lists.wispa.org/mailman/listinfo/wireless




-- 
Ryan Ghering
Network Operations - Plains.Net
Office: 970-848-0475 - Cell: 970-630-1879


___
Wireless mailing list
Wireless@wispa.org
http://lists.wispa.org/mailman/listinfo/wireless

 

___
Wireless mailing list
Wireless@wispa.org
http://lists.wispa.org/mailman/listinfo/wireless


Re: [WISPA] Preventing stupid outages

2012-03-16 Thread Marlon K. Schafer (509-982-2181)
Yeah.  Drop the GFCI.

If an inspector whines about it get his home phone and tell him he'll have to 
meet you at the site every time it goes down because the GFCI technology is so 
worthless.  It won't take but 2 trips and he'll beg you to take them out!

And if you think it's bad now.  Just wait till you have to put in arc fault 
breakers everywhere.  The whole house has to have them nowadays.  Can't even 
run a shop vac in my house if it's in one of the rooms with an arc fault.  Half 
my skill saws won't work etc.

Good ideas, both.  Rotten overly sensitive implementation.

The market for used arc faults will be huge sooner than later.  Every homeowner 
with a screw driver will pull them all out and put in normal breakers :-).

The NEC is getting to be worse than the dept. of ecology!

marlon

  - Original Message - 
  From: Troy Settle 
  To: wireless@wispa.org 
  Sent: Friday, March 16, 2012 6:04 AM
  Subject: [WISPA] Preventing stupid outages


  Ok, so to keep to code, we have a GFCI outlet for most of our towers.  One of 
them tripped last night, causing me to have to put on some 80 miles just to 
push a button (yes, it could have been much worse).

   

  Is there anything to prevent stupid outages like this from happening without 
violating code?

   

  Thanks,

   

  -- 

Troy Settle, Network Administrator

The Wired Road Authority

1117 E. Stuart Dr.

Galax, VA 24333

(276) 238-0049 (office)

(276) 237-3890 (cell)

tset...@thewiredroad.net

   



--


  ___
  Wireless mailing list
  Wireless@wispa.org
  http://lists.wispa.org/mailman/listinfo/wireless
___
Wireless mailing list
Wireless@wispa.org
http://lists.wispa.org/mailman/listinfo/wireless


Re: [WISPA] Preventing stupid outages

2012-03-16 Thread Marlon K. Schafer (509-982-2181)
I like the digital loggers products a LOT better than dataprobe.

Never had a DL unit start turning it's self off when it's not supposed to.  I 
have had that with an iboot.

marlon

  - Original Message - 
  From: Jay DeBoer 
  To: wireless@wispa.org 
  Sent: Friday, March 16, 2012 6:47 AM
  Subject: Re: [WISPA] Preventing stupid outages


  http://dataprobe.com/remote-reboot.html

  I've used some of their older 'iboots' havent' used their phone devices.



  On 3/16/2012 9:40, Victoria Proffer wrote: 
Is there a remote power strip that can be activated by a cell phone?



i.e. 

strip  cell phone  pstn  my computer



Victoria Proffer

STLWiMAX, LLC

314-974-5600



From: wireless-boun...@wispa.org [mailto:wireless-boun...@wispa.org] On 
Behalf Of Ryan Ghering
Sent: Friday, March 16, 2012 8:20 AM
To: WISPA General List
Subject: Re: [WISPA] Preventing stupid outages



We don't use them at towers, but I have here at home auto resetting GFCI 
outlets for my 
Saltwater reef tank. Got them from Home Depot.. They reset automatically 
after a few mins..

Ryan

On Fri, Mar 16, 2012 at 7:08 AM, Matt Hoppes mhop...@indigowireless.com 
wrote:

You have to have GFCI outlets indoors?  I've never heard of that
regulation before.

A few thoughts come to mind:

* Battery backup with 2 or so hours of run time along with a remote page
for a power outage.  Doesn't prevent you from having to dispatch but it
keeps you from having an outage.

* Re-check code?  I don't understand why you need a GFCI outlet inside
your shack.You don't have a sink or other water nearby.  I don't
have GFCI outlets in my office.  Maybe I'm missing something here.

If you are mounting an outdoor NEMA box with your equipment and just
plugging into a GFCI then maybe you can figure out some way to get a
hardwire into the box rather than plugging into an outside GFCI?


On 3/16/12 9:04 AM, Troy Settle wrote:
 Ok, so to keep to code, we have a GFCI outlet for most of our towers.
 One of them tripped last night, causing me to have to put on some 80
 miles just to push a button (yes, it could have been much worse).

 Is there anything to prevent stupid outages like this from happening
 without violating code?

 Thanks,

 --

 Troy Settle, Network Administrator

 The Wired Road Authority

 1117 E. Stuart Dr.

 Galax, VA 24333

 (276) 238-0049 (office)

 (276) 237-3890 (cell)

 tset...@thewiredroad.net




 ___
 Wireless mailing list
 Wireless@wispa.org
 http://lists.wispa.org/mailman/listinfo/wireless
___
Wireless mailing list
Wireless@wispa.org
http://lists.wispa.org/mailman/listinfo/wireless




-- 
Ryan Ghering
Network Operations - Plains.Net
Office: 970-848-0475 - Cell: 970-630-1879


 

___
Wireless mailing list
Wireless@wispa.org
http://lists.wispa.org/mailman/listinfo/wireless




--


  ___
  Wireless mailing list
  Wireless@wispa.org
  http://lists.wispa.org/mailman/listinfo/wireless
___
Wireless mailing list
Wireless@wispa.org
http://lists.wispa.org/mailman/listinfo/wireless


Re: [WISPA] Preventing stupid outages

2012-03-16 Thread Justin Wilson
But what happens if something shorts and it's traced down to the fact you
removed the GFCI.  I would not want to bet my business on it.  I would have
an outlet hardwired into a nema box.  That should satisfy code, but I would
check.

Justin

From:  Marlon K. Schafer (509-982-2181) o...@odessaoffice.com
Reply-To:  WISPA General List wireless@wispa.org
Date:  Fri, 16 Mar 2012 08:00:39 -0700
To:  WISPA General List wireless@wispa.org
Subject:  Re: [WISPA] Preventing stupid outages

 Yeah.  Drop the GFCI.
  
 If an inspector whines about it get his home phone and tell him he'll have to
 meet you at the site every time it goes down because the GFCI technology is so
 worthless.  It won't take but 2 trips and he'll beg you to take them out!
  
 And if you think it's bad now.  Just wait till you have to put in arc fault
 breakers everywhere.  The whole house has to have them nowadays.  Can't even
 run a shop vac in my house if it's in one of the rooms with an arc fault.
 Half my skill saws won't work etc.
  
 Good ideas, both.  Rotten overly sensitive implementation.
  
 The market for used arc faults will be huge sooner than later.  Every
 homeowner with a screw driver will pull them all out and put in normal
 breakers :-).
  
 The NEC is getting to be worse than the dept. of ecology!
  
 marlon
  
  
 - Original Message -
  
 From:  Troy  Settle mailto:tset...@thewiredroad.net
  
 To: wireless@wispa.org
  
 Sent: Friday, March 16, 2012 6:04 AM
  
 Subject: [WISPA] Preventing stupid  outages
  
 
  
  
 
 Ok, so to keep to code, we have a GFCI outlet for most of  our towers.  One
 of them tripped last night, causing me to have to put on  some 80 miles just
 to push a button (yes, it could have been much  worse).
  
  
  
 Is there anything to prevent stupid outages like this from  happening without
 violating code?
  
  
  
 Thanks,
  
  
  
 -- 
  
   Troy Settle, Network  Administrator
  
   The Wired Road Authority
  
   1117 E. Stuart Dr.
  
   Galax, VA 24333
  
   (276) 238-0049 (office)
  
   (276) 237-3890 (cell)
  
   tset...@thewiredroad.net
  
  
  
  
 
  
 
 ___
 Wireless mailing  list
 Wireless@wispa.org
 http://lists.wispa.org/mailman/listinfo/wireless
 ___ Wireless mailing list
 Wireless@wispa.org http://lists.wispa.org/mailman/listinfo/wireless


___
Wireless mailing list
Wireless@wispa.org
http://lists.wispa.org/mailman/listinfo/wireless


Re: [WISPA] Preventing stupid outages

2012-03-16 Thread Matt Hoppes
That's what breakers are for - shorts.
GFCIs are for quick blows for things like dropping something in 
water.   I still don't understand why it would be required in a tower 
building.

On 3/16/12 11:11 AM, Justin Wilson wrote:
 But what happens if something shorts and it's traced down to the fact
 you removed the GFCI. I would not want to bet my business on it. I would
 have an outlet hardwired into a nema box. That should satisfy code, but
 I would check.

 Justin

 From: Marlon K. Schafer (509-982-2181) o...@odessaoffice.com
 mailto:o...@odessaoffice.com
 Reply-To: WISPA General List wireless@wispa.org
 mailto:wireless@wispa.org
 Date: Fri, 16 Mar 2012 08:00:39 -0700
 To: WISPA General List wireless@wispa.org mailto:wireless@wispa.org
 Subject: Re: [WISPA] Preventing stupid outages

 Yeah. Drop the GFCI.
 If an inspector whines about it get his home phone and tell him
 he'll have to meet you at the site every time it goes down because
 the GFCI technology is so worthless. It won't take but 2 trips and
 he'll beg you to take them out!
 And if you think it's bad now. Just wait till you have to put in arc
 fault breakers everywhere. The whole house has to have them
 nowadays. Can't even run a shop vac in my house if it's in one of
 the rooms with an arc fault. Half my skill saws won't work etc.
 Good ideas, both. Rotten overly sensitive implementation.
 The market for used arc faults will be huge sooner than later. Every
 homeowner with a screw driver will pull them all out and put in
 normal breakers :-).
 The NEC is getting to be worse than the dept. of ecology!
 marlon

 - Original Message -
 *From:* Troy Settle mailto:tset...@thewiredroad.net
 *To:* wireless@wispa.org mailto:wireless@wispa.org
 *Sent:* Friday, March 16, 2012 6:04 AM
 *Subject:* [WISPA] Preventing stupid outages

 Ok, so to keep to code, we have a GFCI outlet for most of our
 towers. One of them tripped last night, causing me to have to
 put on some 80 miles just to push a button (yes, it could have
 been much worse).

 Is there anything to prevent stupid outages like this from
 happening without violating code?

 Thanks,

 --

 Troy Settle, Network Administrator

 The Wired Road Authority

 1117 E. Stuart Dr.

 Galax, VA 24333

 (276) 238-0049 (office)

 (276) 237-3890 (cell)

 tset...@thewiredroad.net mailto:tset...@thewiredroad.net

 
 

 ___
 Wireless mailing list
 Wireless@wispa.org mailto:Wireless@wispa.org
 http://lists.wispa.org/mailman/listinfo/wireless

 ___ Wireless mailing
 list Wireless@wispa.org mailto:Wireless@wispa.org
 http://lists.wispa.org/mailman/listinfo/wireless



 ___
 Wireless mailing list
 Wireless@wispa.org
 http://lists.wispa.org/mailman/listinfo/wireless
___
Wireless mailing list
Wireless@wispa.org
http://lists.wispa.org/mailman/listinfo/wireless


Re: [WISPA] Preventing stupid outages

2012-03-16 Thread Greg Ihnen
Just replace it. It's probably failing. They're a pain when they start failing 
but when you get a good one they're fine.

Greg

On Mar 16, 2012, at 8:34 AM, Troy Settle wrote:

 Ok, so to keep to code, we have a GFCI outlet for most of our towers.  One of 
 them tripped last night, causing me to have to put on some 80 miles just to 
 push a button (yes, it could have been much worse).
  
 Is there anything to prevent stupid outages like this from happening without 
 violating code?
  
 Thanks,
  
 --
   Troy Settle, Network Administrator
   The Wired Road Authority
   1117 E. Stuart Dr.
   Galax, VA 24333
   (276) 238-0049 (office)
   (276) 237-3890 (cell)
   tset...@thewiredroad.net
  

___
Wireless mailing list
Wireless@wispa.org
http://lists.wispa.org/mailman/listinfo/wireless


Re: [WISPA] Preventing stupid outages

2012-03-16 Thread Justin Wilson
My point was if Code actually requires it, which in this case it may 
not,
don't replace it because it's an inconvenience.  You are potentially
liable if something were to happen if you are the one who went against
code. Instead find a workaround.  If code doesn't require it, get an
inspector to sign off.

Justin

-Original Message-
From: Matt Hoppes mhop...@indigowireless.com
Date: Fri, 16 Mar 2012 11:27:40 -0400
To: WISPA General List wireless@wispa.org
Cc: Justin Wilson li...@mtin.net
Subject: Re: [WISPA] Preventing stupid outages

That's what breakers are for - shorts.
GFCIs are for quick blows for things like dropping something in
water.   I still don't understand why it would be required in a tower
building.

On 3/16/12 11:11 AM, Justin Wilson wrote:
 But what happens if something shorts and it's traced down to the fact
 you removed the GFCI. I would not want to bet my business on it. I would
 have an outlet hardwired into a nema box. That should satisfy code, but
 I would check.

 Justin

 From: Marlon K. Schafer (509-982-2181) o...@odessaoffice.com
 mailto:o...@odessaoffice.com
 Reply-To: WISPA General List wireless@wispa.org
 mailto:wireless@wispa.org
 Date: Fri, 16 Mar 2012 08:00:39 -0700
 To: WISPA General List wireless@wispa.org mailto:wireless@wispa.org
 Subject: Re: [WISPA] Preventing stupid outages

 Yeah. Drop the GFCI.
 If an inspector whines about it get his home phone and tell him
 he'll have to meet you at the site every time it goes down because
 the GFCI technology is so worthless. It won't take but 2 trips and
 he'll beg you to take them out!
 And if you think it's bad now. Just wait till you have to put in arc
 fault breakers everywhere. The whole house has to have them
 nowadays. Can't even run a shop vac in my house if it's in one of
 the rooms with an arc fault. Half my skill saws won't work etc.
 Good ideas, both. Rotten overly sensitive implementation.
 The market for used arc faults will be huge sooner than later. Every
 homeowner with a screw driver will pull them all out and put in
 normal breakers :-).
 The NEC is getting to be worse than the dept. of ecology!
 marlon

 - Original Message -
 *From:* Troy Settle mailto:tset...@thewiredroad.net
 *To:* wireless@wispa.org mailto:wireless@wispa.org
 *Sent:* Friday, March 16, 2012 6:04 AM
 *Subject:* [WISPA] Preventing stupid outages

 Ok, so to keep to code, we have a GFCI outlet for most of our
 towers. One of them tripped last night, causing me to have to
 put on some 80 miles just to push a button (yes, it could have
 been much worse).

 Is there anything to prevent stupid outages like this from
 happening without violating code?

 Thanks,

 --

 Troy Settle, Network Administrator

 The Wired Road Authority

 1117 E. Stuart Dr.

 Galax, VA 24333

 (276) 238-0049 (office)

 (276) 237-3890 (cell)

 tset...@thewiredroad.net mailto:tset...@thewiredroad.net

 


 ___
 Wireless mailing list
 Wireless@wispa.org mailto:Wireless@wispa.org
 http://lists.wispa.org/mailman/listinfo/wireless

 ___ Wireless mailing
 list Wireless@wispa.org mailto:Wireless@wispa.org
 http://lists.wispa.org/mailman/listinfo/wireless



 ___
 Wireless mailing list
 Wireless@wispa.org
 http://lists.wispa.org/mailman/listinfo/wireless



___
Wireless mailing list
Wireless@wispa.org
http://lists.wispa.org/mailman/listinfo/wireless


Re: [WISPA] Preventing stupid outages

2012-03-16 Thread Bret Clark

On 03/16/2012 11:27 AM, Matt Hoppes wrote:

That's what breakers are for - shorts.
GFCIs are for quick blows for things like dropping something in
water.   I still don't understand why it would be required in a tower
building.


I agree, there's  fuse panel, why the heck is a GFCI needed too at a 
tower site? Are you sure this is code? My guess is some inspector has 
completely misread the code and is applying house code to a tower site!
___
Wireless mailing list
Wireless@wispa.org
http://lists.wispa.org/mailman/listinfo/wireless


Re: [WISPA] Preventing stupid outages

2012-03-16 Thread Ben West
To add to the anecdotal evidence against cheap GFCI outlets, I had to
remove one in a building when spontaneous trips started occurring randomly
(e.g. once every couple weeks) after an adjacent building received a direct
lightening strike.

For that matter, the GFCI contributed nothing to lightening protection,
still lost a bunch of equipment.

-- 
Ben West
http://gowasabi.net
b...@gowasabi.net
___
Wireless mailing list
Wireless@wispa.org
http://lists.wispa.org/mailman/listinfo/wireless


Re: [WISPA] Preventing stupid outages

2012-03-16 Thread DJ Anderson
I thought GFCI's were to protect circuits from moisture mainly, AFAIK they
do not provide any type of protection for devices other than cutting the
circuit if it senses a ground fault.

DJ Anderson
Shelby Broadband



On Fri, Mar 16, 2012 at 11:38 AM, Ben West b...@gowasabi.net wrote:

 To add to the anecdotal evidence against cheap GFCI outlets, I had to
 remove one in a building when spontaneous trips started occurring randomly
 (e.g. once every couple weeks) after an adjacent building received a direct
 lightening strike.

 For that matter, the GFCI contributed nothing to lightening protection,
 still lost a bunch of equipment.

 --
 Ben West
 http://gowasabi.net
 b...@gowasabi.net


 ___
 Wireless mailing list
 Wireless@wispa.org
 http://lists.wispa.org/mailman/listinfo/wireless


___
Wireless mailing list
Wireless@wispa.org
http://lists.wispa.org/mailman/listinfo/wireless


Re: [WISPA] Preventing stupid outages

2012-03-16 Thread Ben West
This is true.  The GFCI outlet happened to already be in the building when
I installed equipment.  It turns out the GFCI outlet itself could have
benefited from lightening isolation.

On Fri, Mar 16, 2012 at 10:45 AM, DJ Anderson d...@shelbybb.com wrote:

 I thought GFCI's were to protect circuits from moisture mainly, AFAIK they
 do not provide any type of protection for devices other than cutting the
 circuit if it senses a ground fault.



-- 
Ben West
http://gowasabi.net
b...@gowasabi.net
___
Wireless mailing list
Wireless@wispa.org
http://lists.wispa.org/mailman/listinfo/wireless


Re: [WISPA] Preventing stupid outages

2012-03-16 Thread Troy Settle
Thanks Matt!

Yeah, the outlet itself is on a post next to the tower foundation and a
dropcord feeds into a NEMA box mounted on the tower (no shack).  We have a
few sites set up like this, and I think I'm going to hardwire everything
before we get much further into lightning season.

Since posting, I spoke with an electrician who has done some other work for
us, and he also suggested yanking the GFCI.

I don't know why this was installed this way.  I'm thinking that the
electrician who did the original work was thinking more residential than
industrial.  I'll leave the GFCI outlet in place as a convenience outlet to
provide the extra protection when we're out there working.


-Troy

 -Original Message-
 From: Matt Hoppes [mailto:mhop...@indigowireless.com]
 Sent: Friday, March 16, 2012 9:09 AM
 To: WISPA General List
 Cc: Troy Settle
 Subject: Re: [WISPA] Preventing stupid outages
 
 You have to have GFCI outlets indoors?  I've never heard of that
 regulation before.
 
 A few thoughts come to mind:
 
 * Battery backup with 2 or so hours of run time along with a remote page
 for a power outage.  Doesn't prevent you from having to dispatch but it
 keeps you from having an outage.
 
 * Re-check code?  I don't understand why you need a GFCI outlet inside
 your shack.You don't have a sink or other water nearby.  I don't
 have GFCI outlets in my office.  Maybe I'm missing something here.
 
 If you are mounting an outdoor NEMA box with your equipment and just
 plugging into a GFCI then maybe you can figure out some way to get a
 hardwire into the box rather than plugging into an outside GFCI?
 
 On 3/16/12 9:04 AM, Troy Settle wrote:
  Ok, so to keep to code, we have a GFCI outlet for most of our towers.
  One of them tripped last night, causing me to have to put on some 80
  miles just to push a button (yes, it could have been much worse).
 
  Is there anything to prevent stupid outages like this from happening
  without violating code?
 
  Thanks,
 
  --
 
  Troy Settle, Network Administrator
 
  The Wired Road Authority
 
  1117 E. Stuart Dr.
 
  Galax, VA 24333
 
  (276) 238-0049 (office)
 
  (276) 237-3890 (cell)
 
  tset...@thewiredroad.net
 
 
 
  ___
  Wireless mailing list
  Wireless@wispa.org
  http://lists.wispa.org/mailman/listinfo/wireless

___
Wireless mailing list
Wireless@wispa.org
http://lists.wispa.org/mailman/listinfo/wireless


Re: [WISPA] Preventing stupid outages

2012-03-16 Thread Jeromie Reeves
We put in a enclosure and that let us say it was 'indoors' and drop
the gfci requirement.

On Fri, Mar 16, 2012 at 6:04 AM, Troy Settle tset...@thewiredroad.net wrote:
 Ok, so to keep to code, we have a GFCI outlet for most of our towers.  One
 of them tripped last night, causing me to have to put on some 80 miles just
 to push a button (yes, it could have been much worse).



 Is there anything to prevent stupid outages like this from happening without
 violating code?



 Thanks,



 --

   Troy Settle, Network Administrator

   The Wired Road Authority

   1117 E. Stuart Dr.

   Galax, VA 24333

   (276) 238-0049 (office)

   (276) 237-3890 (cell)

   tset...@thewiredroad.net




 ___
 Wireless mailing list
 Wireless@wispa.org
 http://lists.wispa.org/mailman/listinfo/wireless

___
Wireless mailing list
Wireless@wispa.org
http://lists.wispa.org/mailman/listinfo/wireless


Re: [WISPA] Preventing stupid outages

2012-03-16 Thread Troy Settle
Next stupid outage at a different site.

 

Specs:

 

Generac 8KW generator

Automatic Transfer Switch

APC 450 rack mount UPS

Mikrotik RB1200

Mikrotik RB435 (3x 802.11n sectors)

Dragonwave Compact Horizon #1

Dragonwave Compact Horizon #2

 

(I don't know how many horses, chickens, goats, pigs, and other critters are
onsite, but I don't think they're an issue).

 

Total load on the UPS is at 44%, estimated run is 25 minutes (long enough
for the generator and switch to do their thing).

 

Radios grounded to the tower, tower grounded and bonded to the shack.  Shack
has two rods (panel - Rod - Rod - Generator).

 

Everything inside is bonded as well, including the drain wires on all the
Cat-5.

 

Yesterday, the Dragonwaves rebooted several times during the storm, but
neither RB lost power even once.

 

Any guesses?  I'm sleeping on it over the weekend, but probably need to get
it figured out before too many more storms come over the mountains.

 

Thanks,

 

-Troy

 

 

 

From: wireless-boun...@wispa.org [mailto:wireless-boun...@wispa.org] On
Behalf Of Troy Settle
Sent: Friday, March 16, 2012 9:05 AM
To: wireless@wispa.org
Subject: [WISPA] Preventing stupid outages

 

Ok, so to keep to code, we have a GFCI outlet for most of our towers.  One
of them tripped last night, causing me to have to put on some 80 miles just
to push a button (yes, it could have been much worse).

 

Is there anything to prevent stupid outages like this from happening without
violating code?

 

Thanks,

 

-- 

  Troy Settle, Network Administrator

  The Wired Road Authority

  1117 E. Stuart Dr.

  Galax, VA 24333

  (276) 238-0049 (office)

  (276) 237-3890 (cell)

  tset...@thewiredroad.net

 

___
Wireless mailing list
Wireless@wispa.org
http://lists.wispa.org/mailman/listinfo/wireless