Re: [WISPA] Direct Lightning Strikes

2009-08-08 Thread Gary Garrett
Yes, we use DC ground antennas.
I am going to move the ground wire from the XR2 to the case instead of
the Board standoff screw.
Someone said the RB411 has a weird ground arrangement and that may be
part of it. I have not been grounding the case either.
Sounds like I need to act like the satellite guys. They ground
everything no matter how far up the building the wire has to run.




Tom Sharples wrote:
 We used to see occasional loss of RX sensitivity from lightning on our older 
 installs, but not since we started using DC grounded antennas. Are you using 
 those (e.g. ARCs), or separate lightning protection on the XR2's?
 




WISPA Wants You! Join today!
http://signup.wispa.org/

 
WISPA Wireless List: wireless@wispa.org

Subscribe/Unsubscribe:
http://lists.wispa.org/mailman/listinfo/wireless

Archives: http://lists.wispa.org/pipermail/wireless/


Re: [WISPA] Direct Lightning Strikes

2009-08-07 Thread Gary Garrett
Seems to me it is ethernet cable picking up EMP. I seem to lose a lot of 
Netgear routers lately. Seems to go right through the POE and gets the 
WAN port.  Also Transmit side of XR2's. Always see receive side 
degrading after mid path lightning strikes even a mile away.
Trango ethernet survives. Once we got a direct Tower strike and 
everything on the tower was shot, the only survivor was the top antenna 
a Trango 900 EXT. that was the only one with non-shielded cat 5.
Go figure.





Scottie Arnett wrote:
 Whats the majority think the equipment damage from lightning comes 
 from...electric surge or coupling on the Ethernet



WISPA Wants You! Join today!
http://signup.wispa.org/

 
WISPA Wireless List: wireless@wispa.org

Subscribe/Unsubscribe:
http://lists.wispa.org/mailman/listinfo/wireless

Archives: http://lists.wispa.org/pipermail/wireless/


Re: [WISPA] Direct Lightning Strikes

2009-08-07 Thread David Hulsebus
We ground our Heliax at 75 ft increments down the tower but have never 
done it with shielded CAT5.

I've seen a few notes about soldering the drain to the connector and it 
may work well but I recall being told by an engineer, from I think 
Erico, as we discussed attachment of our copper wire back to clamps for 
our tower not to solder them to the ground lugs because the temperature 
would rise during a lightning strike causing the solder to overheat 
effectively loosing ground potential of the tower.

Thoughts?

Dave Hulsebus
Portative Technologies, LLC

Chuck Hogg wrote:
 I have attached a photo of what we do with our Cat5 cabling.  Soldered
 end and then heat shrink wrapped with the glue inside.  I'm starting to
 wonder if we should ground out every 50 ft on the Cat5 side.

 It's what we watched Nextel do to their RF cabling.  One other thing I
 found when looking at their cabling, they are draining the ground to
 multiple places along the path down the tower.  The cable is cut open,
 grounded out, then it is cold-shrinked back together.  I found the
 shrink wrap used on Tessco's site, granted it is not made for Ethernet.

 Regards,
 Chuck Hogg
 Shelby Broadband
 502-722-9292
 ch...@shelbybb.com
 http://www.shelbybb.com


 -Original Message-
 From: wireless-boun...@wispa.org [mailto:wireless-boun...@wispa.org] On
 Behalf Of Gary Garrett
 Sent: Friday, August 07, 2009 2:34 PM
 To: sarn...@info-ed.com; WISPA General List
 Subject: Re: [WISPA] Direct Lightning Strikes

 Seems to me it is ethernet cable picking up EMP. I seem to lose a lot of

 Netgear routers lately. Seems to go right through the POE and gets the 
 WAN port.  Also Transmit side of XR2's. Always see receive side 
 degrading after mid path lightning strikes even a mile away.
 Trango ethernet survives. Once we got a direct Tower strike and 
 everything on the tower was shot, the only survivor was the top antenna 
 a Trango 900 EXT. that was the only one with non-shielded cat 5.
 Go figure.





 Scottie Arnett wrote:
   
 Whats the majority think the equipment damage from lightning comes
 
 from...electric surge or coupling on the Ethernet


 
 
 WISPA Wants You! Join today!
 http://signup.wispa.org/
 
 
  
 WISPA Wireless List: wireless@wispa.org

 Subscribe/Unsubscribe:
 http://lists.wispa.org/mailman/listinfo/wireless

 Archives: http://lists.wispa.org/pipermail/wireless/
   

 

 



 
 WISPA Wants You! Join today!
 http://signup.wispa.org/
 
  
 WISPA Wireless List: wireless@wispa.org

 Subscribe/Unsubscribe:
 http://lists.wispa.org/mailman/listinfo/wireless

 Archives: http://lists.wispa.org/pipermail/wireless/



WISPA Wants You! Join today!
http://signup.wispa.org/

 
WISPA Wireless List: wireless@wispa.org

Subscribe/Unsubscribe:
http://lists.wispa.org/mailman/listinfo/wireless

Archives: http://lists.wispa.org/pipermail/wireless/


Re: [WISPA] Direct Lightning Strikes

2009-08-07 Thread Leon D. Zetekoff, NCE

* Gary Garrett wrote, On 8/7/2009 2:34 PM:
Seems to me it is ethernet cable picking up EMP. I seem to lose a lot of 
Netgear routers lately. Seems to go right through the POE and gets the 
WAN port.  Also Transmit side of XR2's. Always see receive side 
degrading after mid path lightning strikes even a mile away.
Trango ethernet survives. Once we got a direct Tower strike and 
everything on the tower was shot, the only survivor was the top antenna 
a Trango 900 EXT. that was the only one with non-shielded cat 5.

Go figure.
  
One of the things I remember is like some have said not have a ground 
loop. Also, usually one side of the cable should be grounded.


WHen I lived in South Florida and hada  35' tower for my ham and tv 
stuff, I put in a Joslyn (sp) surge suppressor in the electrical panel 
across the AC feed coming in and put in some GFI breakers for that 
stuff. I also had some GFI outlets running the equipment. Luckily never 
had a problem as South Florida has lots of lightning.


Leon
No virus found in this outgoing message.
Checked by AVG - www.avg.com
Version: 8.5.406 / Virus Database: 270.13.46/2288 - Release Date: 08/07/09 
13:13:00



WISPA Wants You! Join today!
http://signup.wispa.org/

 
WISPA Wireless List: wireless@wispa.org

Subscribe/Unsubscribe:
http://lists.wispa.org/mailman/listinfo/wireless

Archives: http://lists.wispa.org/pipermail/wireless/

Re: [WISPA] Direct Lightning Strikes

2009-08-06 Thread RickG
Every RF guy I know ways the lightning dissipators work.
These are nice: http://www.lawrencebehr.net/international/lightmas.php
-RickG

On Wed, Aug 5, 2009 at 11:38 AM, Marlon K. Schafero...@odessaoffice.com wrote:
 Nextel spends tens or hundreds of thousands per device.

 Our stuff is cheaper than cheap.

 Get off of the TOP of the tower.  Polyphaser has a great lightning white
 paper.  If you can be 10' below the top you'll be much more protected.

 Also, I've had good luck lately with ferrite beads.

 And ground everything.  Ground it again.  and again and again.

 You might also want to consider adding a static dissipater on the top of the
 tower to help keep the lightning away in the first place.
 http://www.affordable-solar.com/gs-1.brush.lightning.dissipator.htm
 http://www.eriinc.com/products/btss/CA21831A_10.pdf

 I think Hutton carries something too.
 marlon

 - Original Message -
 From: Chuck Hogg ch...@shelbybb.com
 To: WISPA General List wireless@wispa.org
 Sent: Wednesday, August 05, 2009 7:31 AM
 Subject: [WISPA] Direct Lightning Strikes


 Has anyone been able to withstand a direct lightning strike? We had a
 tower get hit last night, and some of our equipment lost Ethernet ports
 (RB/433AH), and we lost 3 canopy APs, but that is all (considering what
 is all up there only 2/3rds was blown).  Our Trango AP survived and a
 RB/433AH survived.  Even Nextel had their guys out there, but they just
 had to reset alarms it appears as nothing was fried on their end.  I
 wish I had to just reset alarms.



 So tell me, what do you do ? I'm tired of dumping a few grand during big
 lightning storms.



 I do the basics, Ethernet surge suppression up top and on the bottom,
 Polyphasers, ground out to the ground bars, ground out the cat5 cable,
 and no omni's.



 Regards,

 Chuck Hogg

 Shelby Broadband
 502-722-9292
 ch...@shelbybb.com

 http://www.shelbybb.com





 
 WISPA Wants You! Join today!
 http://signup.wispa.org/
 

 WISPA Wireless List: wireless@wispa.org

 Subscribe/Unsubscribe:
 http://lists.wispa.org/mailman/listinfo/wireless

 Archives: http://lists.wispa.org/pipermail/wireless/



 
 WISPA Wants You! Join today!
 http://signup.wispa.org/
 

 WISPA Wireless List: wireless@wispa.org

 Subscribe/Unsubscribe:
 http://lists.wispa.org/mailman/listinfo/wireless

 Archives: http://lists.wispa.org/pipermail/wireless/




WISPA Wants You! Join today!
http://signup.wispa.org/

 
WISPA Wireless List: wireless@wispa.org

Subscribe/Unsubscribe:
http://lists.wispa.org/mailman/listinfo/wireless

Archives: http://lists.wispa.org/pipermail/wireless/


Re: [WISPA] Direct Lightning Strikes

2009-08-06 Thread David Hulsebus
Don't feel too left Chuck out we lost a tower site in the same storm. 
Second time in seven years a total loss. Both times we've lost our gear 
it has come via the electrical side. Our tower gets hit by a strike or 
two almost every storm and we never have issues. This time it literaly 
blew the entrance panel off the side of the building and outlets off the 
walls of the building. Cracked one of the APC batterty units, every 
ethernet surge suppressor and every grounded POE injectors were blown 
apart. Interesting that our four coax arrestors were okay, but the gear 
was cooked.  Most of the cat5 ends included.  Had spare gear on the 
tower plugged in at the radios but dangling in the building, we fired it 
up and were in operation within a few minutes.  Took another 16 hours to 
get all of the damage cleaned up.

We have on that site forty-five 3/4 ground rods in two concentric 
circles around the tower and building none more than eight feet apart; 
all interconnected with #2 bare stranded wire and cad welded. Inside the 
building - a halo ring and 3 1/2 copper strapping, the list goes on and 
on for what we have done to minimize issues. We spent nearly 5K on 
grounding and still lost it all.

We are moving to total battery power next week. I am looking for 
something I can use to isolate a smart charger from the power company 
when we see storms in the area, I expect we will have enough battery for 
a minimum 3 days runtime. Some type of relay that we can control 
remotely I would guess.

If it makes you feel any better Verizon Wireless took total loses on 
four towers between Cincinnati and Louisville Tuesday as well.

Dave Hulsebus
Portative Technologies, LLC

Chuck Hogg wrote:
 Has anyone been able to withstand a direct lightning strike? We had a
 tower get hit last night, and some of our equipment lost Ethernet ports
 (RB/433AH), and we lost 3 canopy APs, but that is all (considering what
 is all up there only 2/3rds was blown).  Our Trango AP survived and a
 RB/433AH survived.  Even Nextel had their guys out there, but they just
 had to reset alarms it appears as nothing was fried on their end.  I
 wish I had to just reset alarms.

  

 So tell me, what do you do ? I'm tired of dumping a few grand during big
 lightning storms.

  

 I do the basics, Ethernet surge suppression up top and on the bottom,
 Polyphasers, ground out to the ground bars, ground out the cat5 cable,
 and no omni's.

  

 Regards,

 Chuck Hogg

 Shelby Broadband
 502-722-9292
 ch...@shelbybb.com

 http://www.shelbybb.com

  



 
 WISPA Wants You! Join today!
 http://signup.wispa.org/
 
  
 WISPA Wireless List: wireless@wispa.org

 Subscribe/Unsubscribe:
 http://lists.wispa.org/mailman/listinfo/wireless

 Archives: http://lists.wispa.org/pipermail/wireless/
   



WISPA Wants You! Join today!
http://signup.wispa.org/

 
WISPA Wireless List: wireless@wispa.org

Subscribe/Unsubscribe:
http://lists.wispa.org/mailman/listinfo/wireless

Archives: http://lists.wispa.org/pipermail/wireless/


Re: [WISPA] Direct Lightning Strikes

2009-08-06 Thread ccrum
Since it sounds like this came in on the AC, how about a surge protector
on incoming AC line? We've had sites where the power company's grounding
is so bad we've lost power supply surge protectors in just about every
storm that comes through the area...until we put surge protection at the
breaker box. Now all is good.

Cameron

 Don't feel too left Chuck out we lost a tower site in the same storm.
 Second time in seven years a total loss. Both times we've lost our gear
 it has come via the electrical side. Our tower gets hit by a strike or
 two almost every storm and we never have issues. This time it literaly
 blew the entrance panel off the side of the building and outlets off the
 walls of the building. Cracked one of the APC batterty units, every
 ethernet surge suppressor and every grounded POE injectors were blown
 apart. Interesting that our four coax arrestors were okay, but the gear
 was cooked.  Most of the cat5 ends included.  Had spare gear on the
 tower plugged in at the radios but dangling in the building, we fired it
 up and were in operation within a few minutes.  Took another 16 hours to
 get all of the damage cleaned up.

 We have on that site forty-five 3/4 ground rods in two concentric
 circles around the tower and building none more than eight feet apart;
 all interconnected with #2 bare stranded wire and cad welded. Inside the
 building - a halo ring and 3 1/2 copper strapping, the list goes on and
 on for what we have done to minimize issues. We spent nearly 5K on
 grounding and still lost it all.

 We are moving to total battery power next week. I am looking for
 something I can use to isolate a smart charger from the power company
 when we see storms in the area, I expect we will have enough battery for
 a minimum 3 days runtime. Some type of relay that we can control
 remotely I would guess.

 If it makes you feel any better Verizon Wireless took total loses on
 four towers between Cincinnati and Louisville Tuesday as well.

 Dave Hulsebus
 Portative Technologies, LLC

 Chuck Hogg wrote:
 Has anyone been able to withstand a direct lightning strike? We had a
 tower get hit last night, and some of our equipment lost Ethernet ports
 (RB/433AH), and we lost 3 canopy APs, but that is all (considering what
 is all up there only 2/3rds was blown).  Our Trango AP survived and a
 RB/433AH survived.  Even Nextel had their guys out there, but they just
 had to reset alarms it appears as nothing was fried on their end.  I
 wish I had to just reset alarms.



 So tell me, what do you do ? I'm tired of dumping a few grand during big
 lightning storms.



 I do the basics, Ethernet surge suppression up top and on the bottom,
 Polyphasers, ground out to the ground bars, ground out the cat5 cable,
 and no omni's.



 Regards,

 Chuck Hogg

 Shelby Broadband
 502-722-9292
 ch...@shelbybb.com

 http://www.shelbybb.com





 
 WISPA Wants You! Join today!
 http://signup.wispa.org/
 

 WISPA Wireless List: wireless@wispa.org

 Subscribe/Unsubscribe:
 http://lists.wispa.org/mailman/listinfo/wireless

 Archives: http://lists.wispa.org/pipermail/wireless/



 
 WISPA Wants You! Join today!
 http://signup.wispa.org/
 

 WISPA Wireless List: wireless@wispa.org

 Subscribe/Unsubscribe:
 http://lists.wispa.org/mailman/listinfo/wireless

 Archives: http://lists.wispa.org/pipermail/wireless/






WISPA Wants You! Join today!
http://signup.wispa.org/

 
WISPA Wireless List: wireless@wispa.org

Subscribe/Unsubscribe:
http://lists.wispa.org/mailman/listinfo/wireless

Archives: http://lists.wispa.org/pipermail/wireless/


Re: [WISPA] Direct Lightning Strikes

2009-08-06 Thread David Hulsebus
I looked at a Transtector unit a few weeks ago. It's an isolation 
transformer that sits outdoors between the entrance panel and our 
internal electrical system. It was roughly $1K for the unit. Kind of 
wish I would have bought it now. We are the end of the line on the power 
grid and have 1-3 days of outages multiple times a year, that's the real 
reason for the battery solution; that and we are tired of generators.

Your right though. Most cell and radio towers I visit have just that, an 
isolation transformer at the entrance panel.

Thanks, Dave

cc...@dot11net.com wrote:
 Since it sounds like this came in on the AC, how about a surge protector
 on incoming AC line? We've had sites where the power company's grounding
 is so bad we've lost power supply surge protectors in just about every
 storm that comes through the area...until we put surge protection at the
 breaker box. Now all is good.

 Cameron

   
 Don't feel too left Chuck out we lost a tower site in the same storm.
 Second time in seven years a total loss. Both times we've lost our gear
 it has come via the electrical side. Our tower gets hit by a strike or
 two almost every storm and we never have issues. This time it literaly
 blew the entrance panel off the side of the building and outlets off the
 walls of the building. Cracked one of the APC batterty units, every
 ethernet surge suppressor and every grounded POE injectors were blown
 apart. Interesting that our four coax arrestors were okay, but the gear
 was cooked.  Most of the cat5 ends included.  Had spare gear on the
 tower plugged in at the radios but dangling in the building, we fired it
 up and were in operation within a few minutes.  Took another 16 hours to
 get all of the damage cleaned up.

 We have on that site forty-five 3/4 ground rods in two concentric
 circles around the tower and building none more than eight feet apart;
 all interconnected with #2 bare stranded wire and cad welded. Inside the
 building - a halo ring and 3 1/2 copper strapping, the list goes on and
 on for what we have done to minimize issues. We spent nearly 5K on
 grounding and still lost it all.

 We are moving to total battery power next week. I am looking for
 something I can use to isolate a smart charger from the power company
 when we see storms in the area, I expect we will have enough battery for
 a minimum 3 days runtime. Some type of relay that we can control
 remotely I would guess.

 If it makes you feel any better Verizon Wireless took total loses on
 four towers between Cincinnati and Louisville Tuesday as well.

 Dave Hulsebus
 Portative Technologies, LLC

 Chuck Hogg wrote:
 
 Has anyone been able to withstand a direct lightning strike? We had a
 tower get hit last night, and some of our equipment lost Ethernet ports
 (RB/433AH), and we lost 3 canopy APs, but that is all (considering what
 is all up there only 2/3rds was blown).  Our Trango AP survived and a
 RB/433AH survived.  Even Nextel had their guys out there, but they just
 had to reset alarms it appears as nothing was fried on their end.  I
 wish I had to just reset alarms.



 So tell me, what do you do ? I'm tired of dumping a few grand during big
 lightning storms.



 I do the basics, Ethernet surge suppression up top and on the bottom,
 Polyphasers, ground out to the ground bars, ground out the cat5 cable,
 and no omni's.



 Regards,

 Chuck Hogg

 Shelby Broadband
 502-722-9292
 ch...@shelbybb.com

 http://www.shelbybb.com





 
 WISPA Wants You! Join today!
 http://signup.wispa.org/
 

 WISPA Wireless List: wireless@wispa.org

 Subscribe/Unsubscribe:
 http://lists.wispa.org/mailman/listinfo/wireless

 Archives: http://lists.wispa.org/pipermail/wireless/

   
 
 WISPA Wants You! Join today!
 http://signup.wispa.org/
 

 WISPA Wireless List: wireless@wispa.org

 Subscribe/Unsubscribe:
 http://lists.wispa.org/mailman/listinfo/wireless

 Archives: http://lists.wispa.org/pipermail/wireless/

 




 
 WISPA Wants You! Join today!
 http://signup.wispa.org/
 
  
 WISPA Wireless List: wireless@wispa.org

 Subscribe/Unsubscribe:
 http://lists.wispa.org/mailman/listinfo/wireless

 Archives: http://lists.wispa.org/pipermail/wireless/
   



WISPA Wants You! Join today!
http://signup.wispa.org/

 
WISPA Wireless List: wireless@wispa.org

Subscribe/Unsubscribe:

Re: [WISPA] Direct Lightning Strikes

2009-08-06 Thread os10rules
An isolation transformer without any protection probably wouldn't  
offer much as the higher frequency components of the transient would  
probably pass the transformer through capacitive coupling between the  
windings. I'm sure the Transtector has some type of protection/ 
clamping. That price range ($1k) is where the stuff that actually  
works starts.

The series style AC protectors are best as they have some inductance  
the incoming power has to flow through and the higher frequency  
components of the transient create a high enough voltage to trigger  
the protectors before the transient is seen by the equipment. The  
parallel style protectors subject your equipment to the same voltage  
required to trigger the protection.

As per the Polyphaser white paper and other sources it is possible to  
pick a strike size you want to survive and engineer for that  
successfully (grounding system, single point entry for all I/O's and  
protectors on all I/O's, etc.) which becomes even more complicated  
when you have IDU/ODU systems since you're trying to keep all I/O's  
and grounds more or less at the same potential during the strike and  
give it somewhere to go (ground).

Greg

On Aug 6, 2009, at 10:39 AM, David Hulsebus wrote:

 I looked at a Transtector unit a few weeks ago. It's an isolation
 transformer that sits outdoors between the entrance panel and our
 internal electrical system. It was roughly $1K for the unit. Kind of
 wish I would have bought it now. We are the end of the line on the  
 power
 grid and have 1-3 days of outages multiple times a year, that's the  
 real
 reason for the battery solution; that and we are tired of generators.

 Your right though. Most cell and radio towers I visit have just  
 that, an
 isolation transformer at the entrance panel.

 Thanks, Dave

 cc...@dot11net.com wrote:
 Since it sounds like this came in on the AC, how about a surge  
 protector
 on incoming AC line? We've had sites where the power company's  
 grounding
 is so bad we've lost power supply surge protectors in just about  
 every
 storm that comes through the area...until we put surge protection  
 at the
 breaker box. Now all is good.

 Cameron


 Don't feel too left Chuck out we lost a tower site in the same  
 storm.
 Second time in seven years a total loss. Both times we've lost our  
 gear
 it has come via the electrical side. Our tower gets hit by a  
 strike or
 two almost every storm and we never have issues. This time it  
 literaly
 blew the entrance panel off the side of the building and outlets  
 off the
 walls of the building. Cracked one of the APC batterty units, every
 ethernet surge suppressor and every grounded POE injectors were  
 blown
 apart. Interesting that our four coax arrestors were okay, but the  
 gear
 was cooked.  Most of the cat5 ends included.  Had spare gear on the
 tower plugged in at the radios but dangling in the building, we  
 fired it
 up and were in operation within a few minutes.  Took another 16  
 hours to
 get all of the damage cleaned up.

 We have on that site forty-five 3/4 ground rods in two concentric
 circles around the tower and building none more than eight feet  
 apart;
 all interconnected with #2 bare stranded wire and cad welded.  
 Inside the
 building - a halo ring and 3 1/2 copper strapping, the list goes  
 on and
 on for what we have done to minimize issues. We spent nearly 5K on
 grounding and still lost it all.

 We are moving to total battery power next week. I am looking for
 something I can use to isolate a smart charger from the power  
 company
 when we see storms in the area, I expect we will have enough  
 battery for
 a minimum 3 days runtime. Some type of relay that we can control
 remotely I would guess.

 If it makes you feel any better Verizon Wireless took total loses on
 four towers between Cincinnati and Louisville Tuesday as well.

 Dave Hulsebus
 Portative Technologies, LLC

 Chuck Hogg wrote:

 Has anyone been able to withstand a direct lightning strike? We  
 had a
 tower get hit last night, and some of our equipment lost Ethernet  
 ports
 (RB/433AH), and we lost 3 canopy APs, but that is all  
 (considering what
 is all up there only 2/3rds was blown).  Our Trango AP survived  
 and a
 RB/433AH survived.  Even Nextel had their guys out there, but  
 they just
 had to reset alarms it appears as nothing was fried on their  
 end.  I
 wish I had to just reset alarms.



 So tell me, what do you do ? I'm tired of dumping a few grand  
 during big
 lightning storms.



 I do the basics, Ethernet surge suppression up top and on the  
 bottom,
 Polyphasers, ground out to the ground bars, ground out the cat5  
 cable,
 and no omni's.



 Regards,

 Chuck Hogg

 Shelby Broadband
 502-722-9292
 ch...@shelbybb.com

 http://www.shelbybb.com





 
 WISPA Wants You! Join today!
 http://signup.wispa.org/
 

Re: [WISPA] Direct Lightning Strikes

2009-08-06 Thread Marco Coelho
I did a lot of lightning protection for composite aircraft.  After
initial losses on my towers, here's our basic system:

1.  All ethernet cables inside or out must be shielded.  Ethernet is a
high impedance signal that lightning can couple into easily.  We also
prefer gel filled cables for outdoor work.  water proof non-filled
cables aren't.  Each end of these cable shields must be terminated to
ground.

1.a  Surge protection at entrance to NOC for all CAT5 / Coax.
Polyphaser rocks for RF.  Again, all of this must go to the ground
ring with #2 copper.  Between antennas at the top and any RF gear at
top, polyphaser again.  Keep it out of the radio.

2.  Ground ring around tower and NOC.  We are in clay, so we have
about 100 8 ft ground rods interconnected with #2 sold tinned copper
via cadweld.  Stingers come off these rings for equipment in the NOC,
and to each leg of the tower.

3.  Up the tower, 2 #2 stranded conductors. One end tied to the ring
at the bottom, the other to solid tinned copper ground plates at each
boom elevation.  Each boom grounded to the plate via cad weld.  Ground
rod at top of tower grounded to same plate.  Lightning dissapaters
grounded to same plate.

4.  Tower legs, booms, and other bolted together structure is not a
proper ground.

4.a  Water towers (metal) are usually very well bonded.  They make
good ground interconnects since they are welded.

5.  Large whole building surge protection at utility power entrance.
This must tie to the same ring.

6.  UPS everything or DC power everything.

7.  Small prayer when storms come seems to help!

That said, I've seen a direct strike  hit with so much energy that it
blew a 1 foot whole through the foundation!

Marco



WISPA Wants You! Join today!
http://signup.wispa.org/

 
WISPA Wireless List: wireless@wispa.org

Subscribe/Unsubscribe:
http://lists.wispa.org/mailman/listinfo/wireless

Archives: http://lists.wispa.org/pipermail/wireless/


Re: [WISPA] Direct Lightning Strikes

2009-08-06 Thread Scottie Arnett
Whats the majority think the equipment damage from lightning comes 
from...electric surge or coupling on the Ethernet? Will running on battery or 
solar lessen your chances of equipment damage that much more that it is worth 
the cost? I am in the same boat as these guys and have one location hit 5 times 
in the last two years that caused major damage(talking SMOKED AP's), more than 
that if you just include power supplies and switches.

I was thinking of grounding the crap out of this location, but it looks like 
David did that and it did not help much.

Scottie

-- Original Message --
From: David Hulsebus cont...@portative.net
Reply-To: WISPA General List wireless@wispa.org
Date:  Thu, 06 Aug 2009 11:09:58 -0400

I looked at a Transtector unit a few weeks ago. It's an isolation 
transformer that sits outdoors between the entrance panel and our 
internal electrical system. It was roughly $1K for the unit. Kind of 
wish I would have bought it now. We are the end of the line on the power 
grid and have 1-3 days of outages multiple times a year, that's the real 
reason for the battery solution; that and we are tired of generators.

Your right though. Most cell and radio towers I visit have just that, an 
isolation transformer at the entrance panel.

Thanks, Dave

cc...@dot11net.com wrote:
 Since it sounds like this came in on the AC, how about a surge protector
 on incoming AC line? We've had sites where the power company's grounding
 is so bad we've lost power supply surge protectors in just about every
 storm that comes through the area...until we put surge protection at the
 breaker box. Now all is good.

 Cameron

   
 Don't feel too left Chuck out we lost a tower site in the same storm.
 Second time in seven years a total loss. Both times we've lost our gear
 it has come via the electrical side. Our tower gets hit by a strike or
 two almost every storm and we never have issues. This time it literaly
 blew the entrance panel off the side of the building and outlets off the
 walls of the building. Cracked one of the APC batterty units, every
 ethernet surge suppressor and every grounded POE injectors were blown
 apart. Interesting that our four coax arrestors were okay, but the gear
 was cooked.  Most of the cat5 ends included.  Had spare gear on the
 tower plugged in at the radios but dangling in the building, we fired it
 up and were in operation within a few minutes.  Took another 16 hours to
 get all of the damage cleaned up.

 We have on that site forty-five 3/4 ground rods in two concentric
 circles around the tower and building none more than eight feet apart;
 all interconnected with #2 bare stranded wire and cad welded. Inside the
 building - a halo ring and 3 1/2 copper strapping, the list goes on and
 on for what we have done to minimize issues. We spent nearly 5K on
 grounding and still lost it all.

 We are moving to total battery power next week. I am looking for
 something I can use to isolate a smart charger from the power company
 when we see storms in the area, I expect we will have enough battery for
 a minimum 3 days runtime. Some type of relay that we can control
 remotely I would guess.

 If it makes you feel any better Verizon Wireless took total loses on
 four towers between Cincinnati and Louisville Tuesday as well.

 Dave Hulsebus
 Portative Technologies, LLC

 Chuck Hogg wrote:
 
 Has anyone been able to withstand a direct lightning strike? We had a
 tower get hit last night, and some of our equipment lost Ethernet ports
 (RB/433AH), and we lost 3 canopy APs, but that is all (considering what
 is all up there only 2/3rds was blown).  Our Trango AP survived and a
 RB/433AH survived.  Even Nextel had their guys out there, but they just
 had to reset alarms it appears as nothing was fried on their end.  I
 wish I had to just reset alarms.



 So tell me, what do you do ? I'm tired of dumping a few grand during big
 lightning storms.



 I do the basics, Ethernet surge suppression up top and on the bottom,
 Polyphasers, ground out to the ground bars, ground out the cat5 cable,
 and no omni's.



 Regards,

 Chuck Hogg

 Shelby Broadband
 502-722-9292
 ch...@shelbybb.com

 http://www.shelbybb.com





 
 WISPA Wants You! Join today!
 http://signup.wispa.org/
 

 WISPA Wireless List: wireless@wispa.org

 Subscribe/Unsubscribe:
 http://lists.wispa.org/mailman/listinfo/wireless

 Archives: http://lists.wispa.org/pipermail/wireless/

   
 
 WISPA Wants You! Join today!
 http://signup.wispa.org/
 

 WISPA Wireless List: wireless@wispa.org

 Subscribe/Unsubscribe:
 http://lists.wispa.org/mailman/listinfo/wireless

 Archives: 

Re: [WISPA] Direct Lightning Strikes

2009-08-06 Thread Josh Luthman
Every time I've had lightning damage my UPS is uneffected.  APC and
no-name brands.

On 8/6/09, Scottie Arnett sarn...@info-ed.com wrote:
 Whats the majority think the equipment damage from lightning comes
 from...electric surge or coupling on the Ethernet? Will running on battery
 or solar lessen your chances of equipment damage that much more that it is
 worth the cost? I am in the same boat as these guys and have one location
 hit 5 times in the last two years that caused major damage(talking SMOKED
 AP's), more than that if you just include power supplies and switches.

 I was thinking of grounding the crap out of this location, but it looks like
 David did that and it did not help much.

 Scottie

 -- Original Message --
 From: David Hulsebus cont...@portative.net
 Reply-To: WISPA General List wireless@wispa.org
 Date:  Thu, 06 Aug 2009 11:09:58 -0400

I looked at a Transtector unit a few weeks ago. It's an isolation
transformer that sits outdoors between the entrance panel and our
internal electrical system. It was roughly $1K for the unit. Kind of
wish I would have bought it now. We are the end of the line on the power
grid and have 1-3 days of outages multiple times a year, that's the real
reason for the battery solution; that and we are tired of generators.

Your right though. Most cell and radio towers I visit have just that, an
isolation transformer at the entrance panel.

Thanks, Dave

cc...@dot11net.com wrote:
 Since it sounds like this came in on the AC, how about a surge protector
 on incoming AC line? We've had sites where the power company's grounding
 is so bad we've lost power supply surge protectors in just about every
 storm that comes through the area...until we put surge protection at the
 breaker box. Now all is good.

 Cameron


 Don't feel too left Chuck out we lost a tower site in the same storm.
 Second time in seven years a total loss. Both times we've lost our gear
 it has come via the electrical side. Our tower gets hit by a strike or
 two almost every storm and we never have issues. This time it literaly
 blew the entrance panel off the side of the building and outlets off the
 walls of the building. Cracked one of the APC batterty units, every
 ethernet surge suppressor and every grounded POE injectors were blown
 apart. Interesting that our four coax arrestors were okay, but the gear
 was cooked.  Most of the cat5 ends included.  Had spare gear on the
 tower plugged in at the radios but dangling in the building, we fired it
 up and were in operation within a few minutes.  Took another 16 hours to
 get all of the damage cleaned up.

 We have on that site forty-five 3/4 ground rods in two concentric
 circles around the tower and building none more than eight feet apart;
 all interconnected with #2 bare stranded wire and cad welded. Inside the
 building - a halo ring and 3 1/2 copper strapping, the list goes on and
 on for what we have done to minimize issues. We spent nearly 5K on
 grounding and still lost it all.

 We are moving to total battery power next week. I am looking for
 something I can use to isolate a smart charger from the power company
 when we see storms in the area, I expect we will have enough battery for
 a minimum 3 days runtime. Some type of relay that we can control
 remotely I would guess.

 If it makes you feel any better Verizon Wireless took total loses on
 four towers between Cincinnati and Louisville Tuesday as well.

 Dave Hulsebus
 Portative Technologies, LLC

 Chuck Hogg wrote:

 Has anyone been able to withstand a direct lightning strike? We had a
 tower get hit last night, and some of our equipment lost Ethernet ports
 (RB/433AH), and we lost 3 canopy APs, but that is all (considering what
 is all up there only 2/3rds was blown).  Our Trango AP survived and a
 RB/433AH survived.  Even Nextel had their guys out there, but they just
 had to reset alarms it appears as nothing was fried on their end.  I
 wish I had to just reset alarms.



 So tell me, what do you do ? I'm tired of dumping a few grand during
 big
 lightning storms.



 I do the basics, Ethernet surge suppression up top and on the bottom,
 Polyphasers, ground out to the ground bars, ground out the cat5 cable,
 and no omni's.



 Regards,

 Chuck Hogg

 Shelby Broadband
 502-722-9292
 ch...@shelbybb.com

 http://www.shelbybb.com





 
 WISPA Wants You! Join today!
 http://signup.wispa.org/
 

 WISPA Wireless List: wireless@wispa.org

 Subscribe/Unsubscribe:
 http://lists.wispa.org/mailman/listinfo/wireless

 Archives: http://lists.wispa.org/pipermail/wireless/


 
 WISPA Wants You! Join today!
 http://signup.wispa.org/
 

 

Re: [WISPA] Direct Lightning Strikes

2009-08-06 Thread Bob Knight
We have four solar locations, two of which have operated for over five 
years without any lightning damage. At least one of them is in a 
location and with a mast that I'd consider to be a prime target.

The one that really nailed us was a nearby building strike - it 
destroyed an antenna and the associated AP. Did not take out any of the 
associated ethernet stuff. We may have just gotten lucky, but we've 
since taken care to put in place professional-grade (the guy has done 
stuff at Los Alamos National Lab and we are---I work there---real heavy 
into lightning protection and high energy safety) protection.

Given what I just said, no doubt two of those APs will get taken out in 
the next couple of weeks :)...lightning is nothing if not capricious and 
deadly.

FWIW.

Bob


Scottie Arnett wrote:
 Whats the majority think the equipment damage from lightning comes 
 from...electric surge or coupling on the Ethernet? Will running on battery or 
 solar lessen your chances of equipment damage that much more that it is worth 
 the cost? I am in the same boat as these guys and have one location hit 5 
 times in the last two years that caused major damage(talking SMOKED AP's), 
 more than that if you just include power supplies and switches.
 
 I was thinking of grounding the crap out of this location, but it looks like 
 David did that and it did not help much.
 
 Scottie
 
 -- Original Message --
 From: David Hulsebus cont...@portative.net
 Reply-To: WISPA General List wireless@wispa.org
 Date:  Thu, 06 Aug 2009 11:09:58 -0400
 
 I looked at a Transtector unit a few weeks ago. It's an isolation 
 transformer that sits outdoors between the entrance panel and our 
 internal electrical system. It was roughly $1K for the unit. Kind of 
 wish I would have bought it now. We are the end of the line on the power 
 grid and have 1-3 days of outages multiple times a year, that's the real 
 reason for the battery solution; that and we are tired of generators.

 Your right though. Most cell and radio towers I visit have just that, an 
 isolation transformer at the entrance panel.

 Thanks, Dave

 cc...@dot11net.com wrote:
 Since it sounds like this came in on the AC, how about a surge protector
 on incoming AC line? We've had sites where the power company's grounding
 is so bad we've lost power supply surge protectors in just about every
 storm that comes through the area...until we put surge protection at the
 breaker box. Now all is good.

 Cameron

   
 Don't feel too left Chuck out we lost a tower site in the same storm.
 Second time in seven years a total loss. Both times we've lost our gear
 it has come via the electrical side. Our tower gets hit by a strike or
 two almost every storm and we never have issues. This time it literaly
 blew the entrance panel off the side of the building and outlets off the
 walls of the building. Cracked one of the APC batterty units, every
 ethernet surge suppressor and every grounded POE injectors were blown
 apart. Interesting that our four coax arrestors were okay, but the gear
 was cooked.  Most of the cat5 ends included.  Had spare gear on the
 tower plugged in at the radios but dangling in the building, we fired it
 up and were in operation within a few minutes.  Took another 16 hours to
 get all of the damage cleaned up.

 We have on that site forty-five 3/4 ground rods in two concentric
 circles around the tower and building none more than eight feet apart;
 all interconnected with #2 bare stranded wire and cad welded. Inside the
 building - a halo ring and 3 1/2 copper strapping, the list goes on and
 on for what we have done to minimize issues. We spent nearly 5K on
 grounding and still lost it all.

 We are moving to total battery power next week. I am looking for
 something I can use to isolate a smart charger from the power company
 when we see storms in the area, I expect we will have enough battery for
 a minimum 3 days runtime. Some type of relay that we can control
 remotely I would guess.

 If it makes you feel any better Verizon Wireless took total loses on
 four towers between Cincinnati and Louisville Tuesday as well.

 Dave Hulsebus
 Portative Technologies, LLC

 Chuck Hogg wrote:
 
 Has anyone been able to withstand a direct lightning strike? We had a
 tower get hit last night, and some of our equipment lost Ethernet ports
 (RB/433AH), and we lost 3 canopy APs, but that is all (considering what
 is all up there only 2/3rds was blown).  Our Trango AP survived and a
 RB/433AH survived.  Even Nextel had their guys out there, but they just
 had to reset alarms it appears as nothing was fried on their end.  I
 wish I had to just reset alarms.



 So tell me, what do you do ? I'm tired of dumping a few grand during big
 lightning storms.



 I do the basics, Ethernet surge suppression up top and on the bottom,
 Polyphasers, ground out to the ground bars, ground out the cat5 cable,
 and no omni's.



 Regards,

 Chuck Hogg


Re: [WISPA] Direct Lightning Strikes

2009-08-06 Thread Eje Gustafsson
Sounds like your ground potential between tower ground and electrical ground
might is not optimal. 
Make sure that the tower ground is also correctly and properly grounded to
the electrical ground. 
Seems your electronic might be shunt between the two grounds so each time
tower get a hit your equipment gets fried. 

/ Eje

-Original Message-
From: wireless-boun...@wispa.org [mailto:wireless-boun...@wispa.org] On
Behalf Of Scottie Arnett
Sent: Thursday, August 06, 2009 9:03 PM
To: WISPA General List
Subject: Re: [WISPA] Direct Lightning Strikes

Whats the majority think the equipment damage from lightning comes
from...electric surge or coupling on the Ethernet? Will running on battery
or solar lessen your chances of equipment damage that much more that it is
worth the cost? I am in the same boat as these guys and have one location
hit 5 times in the last two years that caused major damage(talking SMOKED
AP's), more than that if you just include power supplies and switches.

I was thinking of grounding the crap out of this location, but it looks like
David did that and it did not help much.

Scottie

-- Original Message --
From: David Hulsebus cont...@portative.net
Reply-To: WISPA General List wireless@wispa.org
Date:  Thu, 06 Aug 2009 11:09:58 -0400

I looked at a Transtector unit a few weeks ago. It's an isolation 
transformer that sits outdoors between the entrance panel and our 
internal electrical system. It was roughly $1K for the unit. Kind of 
wish I would have bought it now. We are the end of the line on the power 
grid and have 1-3 days of outages multiple times a year, that's the real 
reason for the battery solution; that and we are tired of generators.

Your right though. Most cell and radio towers I visit have just that, an 
isolation transformer at the entrance panel.

Thanks, Dave

cc...@dot11net.com wrote:
 Since it sounds like this came in on the AC, how about a surge protector
 on incoming AC line? We've had sites where the power company's grounding
 is so bad we've lost power supply surge protectors in just about every
 storm that comes through the area...until we put surge protection at the
 breaker box. Now all is good.

 Cameron

   
 Don't feel too left Chuck out we lost a tower site in the same storm.
 Second time in seven years a total loss. Both times we've lost our gear
 it has come via the electrical side. Our tower gets hit by a strike or
 two almost every storm and we never have issues. This time it literaly
 blew the entrance panel off the side of the building and outlets off the
 walls of the building. Cracked one of the APC batterty units, every
 ethernet surge suppressor and every grounded POE injectors were blown
 apart. Interesting that our four coax arrestors were okay, but the gear
 was cooked.  Most of the cat5 ends included.  Had spare gear on the
 tower plugged in at the radios but dangling in the building, we fired it
 up and were in operation within a few minutes.  Took another 16 hours to
 get all of the damage cleaned up.

 We have on that site forty-five 3/4 ground rods in two concentric
 circles around the tower and building none more than eight feet apart;
 all interconnected with #2 bare stranded wire and cad welded. Inside the
 building - a halo ring and 3 1/2 copper strapping, the list goes on and
 on for what we have done to minimize issues. We spent nearly 5K on
 grounding and still lost it all.

 We are moving to total battery power next week. I am looking for
 something I can use to isolate a smart charger from the power company
 when we see storms in the area, I expect we will have enough battery for
 a minimum 3 days runtime. Some type of relay that we can control
 remotely I would guess.

 If it makes you feel any better Verizon Wireless took total loses on
 four towers between Cincinnati and Louisville Tuesday as well.

 Dave Hulsebus
 Portative Technologies, LLC

 Chuck Hogg wrote:
 
 Has anyone been able to withstand a direct lightning strike? We had a
 tower get hit last night, and some of our equipment lost Ethernet ports
 (RB/433AH), and we lost 3 canopy APs, but that is all (considering what
 is all up there only 2/3rds was blown).  Our Trango AP survived and a
 RB/433AH survived.  Even Nextel had their guys out there, but they just
 had to reset alarms it appears as nothing was fried on their end.  I
 wish I had to just reset alarms.



 So tell me, what do you do ? I'm tired of dumping a few grand during
big
 lightning storms.



 I do the basics, Ethernet surge suppression up top and on the bottom,
 Polyphasers, ground out to the ground bars, ground out the cat5 cable,
 and no omni's.



 Regards,

 Chuck Hogg

 Shelby Broadband
 502-722-9292
 ch...@shelbybb.com

 http://www.shelbybb.com








 WISPA Wants You! Join today!
 http://signup.wispa.org

Re: [WISPA] Direct Lightning Strikes

2009-08-06 Thread Scottie Arnett
Where are you located?

4.a  Water towers (metal) are usually very well bonded.  They make
good ground interconnects since they are welded.

This is an almost exact case of my problem location. It is on top of a 66' 
water tower that is on a very high elevation for our area. Not the highest 
spot, but close. I have found NO ground what-so-ever on this tank. I asked the 
water dept. about this tank and they said it was not grounded because they did 
not have any equipment on it. They also said it was setting on about 4 ft. of 
sand, soaked in oil to keep the bottom of the tank from rusting. They would not 
let us install an electrical entrance close, so we had to bury conduit with 
ethernet run through it about 100' from the base of the tank to the electrical 
pole where all our equipment is installed.

On the first hit, we had Moto's SS surges installed bonded to the electrical 
ground. Did not help. After our first hit, we grounded all our metal conduit 
that the cat5 runs through from top of the tank to bottom with ground rods at 
the bottom of the tank. Did not help.

We tried floating grounds, did not help.

Our next step is to get excessive. We are going to ground the tank ourselves, 
connect the tank to the electrical ground to rule out ground loops, install 
Polyphaser surge on all equipment, and ground at top and bottom of the tank on 
all cat5. Do you guys think this will work?

Scottie 

-- Original Message --
From: Marco Coelho coelh...@gmail.com
Reply-To: WISPA General List wireless@wispa.org
Date:  Thu, 6 Aug 2009 14:45:05 -0500

I did a lot of lightning protection for composite aircraft.  After
initial losses on my towers, here's our basic system:

1.  All ethernet cables inside or out must be shielded.  Ethernet is a
high impedance signal that lightning can couple into easily.  We also
prefer gel filled cables for outdoor work.  water proof non-filled
cables aren't.  Each end of these cable shields must be terminated to
ground.

1.a  Surge protection at entrance to NOC for all CAT5 / Coax.
Polyphaser rocks for RF.  Again, all of this must go to the ground
ring with #2 copper.  Between antennas at the top and any RF gear at
top, polyphaser again.  Keep it out of the radio.

2.  Ground ring around tower and NOC.  We are in clay, so we have
about 100 8 ft ground rods interconnected with #2 sold tinned copper
via cadweld.  Stingers come off these rings for equipment in the NOC,
and to each leg of the tower.

3.  Up the tower, 2 #2 stranded conductors. One end tied to the ring
at the bottom, the other to solid tinned copper ground plates at each
boom elevation.  Each boom grounded to the plate via cad weld.  Ground
rod at top of tower grounded to same plate.  Lightning dissapaters
grounded to same plate.

4.  Tower legs, booms, and other bolted together structure is not a
proper ground.

4.a  Water towers (metal) are usually very well bonded.  They make
good ground interconnects since they are welded.

5.  Large whole building surge protection at utility power entrance.
This must tie to the same ring.

6.  UPS everything or DC power everything.

7.  Small prayer when storms come seems to help!

That said, I've seen a direct strike  hit with so much energy that it
blew a 1 foot whole through the foundation!

Marco



WISPA Wants You! Join today!
http://signup.wispa.org/

 
WISPA Wireless List: wireless@wispa.org

Subscribe/Unsubscribe:
http://lists.wispa.org/mailman/listinfo/wireless

Archives: http://lists.wispa.org/pipermail/wireless/
---
[This E-mail scanned for viruses by Declude Virus]



Wireless High Speed Broadband service from Info-Ed, Inc. as low as $30.00/mth.
Check out www.info-ed.com/wireless.html for information.



WISPA Wants You! Join today!
http://signup.wispa.org/

 
WISPA Wireless List: wireless@wispa.org

Subscribe/Unsubscribe:
http://lists.wispa.org/mailman/listinfo/wireless

Archives: http://lists.wispa.org/pipermail/wireless/


Re: [WISPA] Direct Lightning Strikes

2009-08-06 Thread Scott Piehn
We are in Midwest, not a high stick area, so take this for what it's worth.

Electrical.
ISObar 2 outlet sure plugged into outlet
Tripplite DUAL CONVERSION battery plugged into ISObar.  This converts from 
ac to dc, and back to ac.  It cleans the power
digital loggers reboot board for outlet control - not pertinent to 
lightening protection, but useful

Ethernets
All new towers and any retrofits, shielded cable with shielded ends on both 
sides.
all Ethernets bundled into a PVC conduit.  Yes you have to plan ahead for 
any expansion.
Very Important - KEEP THE PVC OFF THE LEG. - attach the pvc to the face.

#2 ground in building attached to halo
Ethernets attached to this ground. - In my opinion if the Ethernet shield 
isn't attached to a ground, it is about worthless
#2 running up tower attaching to all antennas, etc - if problems continue


Scott Piehn
- Original Message - 
From: Scottie Arnett sarn...@info-ed.com
To: WISPA General List wireless@wispa.org
Sent: Thursday, August 06, 2009 9:02 PM
Subject: Re: [WISPA] Direct Lightning Strikes


 Whats the majority think the equipment damage from lightning comes 
 from...electric surge or coupling on the Ethernet? Will running on battery 
 or solar lessen your chances of equipment damage that much more that it is 
 worth the cost? I am in the same boat as these guys and have one location 
 hit 5 times in the last two years that caused major damage(talking SMOKED 
 AP's), more than that if you just include power supplies and switches.

 I was thinking of grounding the crap out of this location, but it looks 
 like David did that and it did not help much.

 Scottie

 -- Original Message --
 From: David Hulsebus cont...@portative.net
 Reply-To: WISPA General List wireless@wispa.org
 Date:  Thu, 06 Aug 2009 11:09:58 -0400

I looked at a Transtector unit a few weeks ago. It's an isolation
transformer that sits outdoors between the entrance panel and our
internal electrical system. It was roughly $1K for the unit. Kind of
wish I would have bought it now. We are the end of the line on the power
grid and have 1-3 days of outages multiple times a year, that's the real
reason for the battery solution; that and we are tired of generators.

Your right though. Most cell and radio towers I visit have just that, an
isolation transformer at the entrance panel.

Thanks, Dave

cc...@dot11net.com wrote:
 Since it sounds like this came in on the AC, how about a surge protector
 on incoming AC line? We've had sites where the power company's grounding
 is so bad we've lost power supply surge protectors in just about every
 storm that comes through the area...until we put surge protection at the
 breaker box. Now all is good.

 Cameron


 Don't feel too left Chuck out we lost a tower site in the same storm.
 Second time in seven years a total loss. Both times we've lost our gear
 it has come via the electrical side. Our tower gets hit by a strike or
 two almost every storm and we never have issues. This time it literaly
 blew the entrance panel off the side of the building and outlets off 
 the
 walls of the building. Cracked one of the APC batterty units, every
 ethernet surge suppressor and every grounded POE injectors were blown
 apart. Interesting that our four coax arrestors were okay, but the gear
 was cooked.  Most of the cat5 ends included.  Had spare gear on the
 tower plugged in at the radios but dangling in the building, we fired 
 it
 up and were in operation within a few minutes.  Took another 16 hours 
 to
 get all of the damage cleaned up.

 We have on that site forty-five 3/4 ground rods in two concentric
 circles around the tower and building none more than eight feet apart;
 all interconnected with #2 bare stranded wire and cad welded. Inside 
 the
 building - a halo ring and 3 1/2 copper strapping, the list goes on 
 and
 on for what we have done to minimize issues. We spent nearly 5K on
 grounding and still lost it all.

 We are moving to total battery power next week. I am looking for
 something I can use to isolate a smart charger from the power company
 when we see storms in the area, I expect we will have enough battery 
 for
 a minimum 3 days runtime. Some type of relay that we can control
 remotely I would guess.

 If it makes you feel any better Verizon Wireless took total loses on
 four towers between Cincinnati and Louisville Tuesday as well.

 Dave Hulsebus
 Portative Technologies, LLC

 Chuck Hogg wrote:

 Has anyone been able to withstand a direct lightning strike? We had a
 tower get hit last night, and some of our equipment lost Ethernet 
 ports
 (RB/433AH), and we lost 3 canopy APs, but that is all (considering 
 what
 is all up there only 2/3rds was blown).  Our Trango AP survived and a
 RB/433AH survived.  Even Nextel had their guys out there, but they 
 just
 had to reset alarms it appears as nothing was fried on their end.  I
 wish I had

[WISPA] Direct Lightning Strikes

2009-08-05 Thread Chuck Hogg
Has anyone been able to withstand a direct lightning strike? We had a
tower get hit last night, and some of our equipment lost Ethernet ports
(RB/433AH), and we lost 3 canopy APs, but that is all (considering what
is all up there only 2/3rds was blown).  Our Trango AP survived and a
RB/433AH survived.  Even Nextel had their guys out there, but they just
had to reset alarms it appears as nothing was fried on their end.  I
wish I had to just reset alarms.

 

So tell me, what do you do ? I'm tired of dumping a few grand during big
lightning storms.

 

I do the basics, Ethernet surge suppression up top and on the bottom,
Polyphasers, ground out to the ground bars, ground out the cat5 cable,
and no omni's.

 

Regards,

Chuck Hogg

Shelby Broadband
502-722-9292
ch...@shelbybb.com

http://www.shelbybb.com

 




WISPA Wants You! Join today!
http://signup.wispa.org/

 
WISPA Wireless List: wireless@wispa.org

Subscribe/Unsubscribe:
http://lists.wispa.org/mailman/listinfo/wireless

Archives: http://lists.wispa.org/pipermail/wireless/


Re: [WISPA] Direct Lightning Strikes

2009-08-05 Thread Josh Luthman
On the Motorola list someone said that by using shielded connectors/cable
and soldering the drain wire on both ends they haven't lost anything to
lightning in Colorado OR Costa Rica (per him via NOAA the two of three worst
areas for lightning in North America).

Might just want to pull up that archive and read through the discussion.

Josh Luthman
Office: 937-552-2340
Direct: 937-552-2343
1100 Wayne St
Suite 1337
Troy, OH 45373

When you have eliminated the impossible, that which remains, however
improbable, must be the truth.
--- Sir Arthur Conan Doyle


On Wed, Aug 5, 2009 at 10:31 AM, Chuck Hogg ch...@shelbybb.com wrote:

 Has anyone been able to withstand a direct lightning strike? We had a
 tower get hit last night, and some of our equipment lost Ethernet ports
 (RB/433AH), and we lost 3 canopy APs, but that is all (considering what
 is all up there only 2/3rds was blown).  Our Trango AP survived and a
 RB/433AH survived.  Even Nextel had their guys out there, but they just
 had to reset alarms it appears as nothing was fried on their end.  I
 wish I had to just reset alarms.



 So tell me, what do you do ? I'm tired of dumping a few grand during big
 lightning storms.



 I do the basics, Ethernet surge suppression up top and on the bottom,
 Polyphasers, ground out to the ground bars, ground out the cat5 cable,
 and no omni's.



 Regards,

 Chuck Hogg

 Shelby Broadband
 502-722-9292
 ch...@shelbybb.com

 http://www.shelbybb.com






 
 WISPA Wants You! Join today!
 http://signup.wispa.org/

 

 WISPA Wireless List: wireless@wispa.org

 Subscribe/Unsubscribe:
 http://lists.wispa.org/mailman/listinfo/wireless

 Archives: http://lists.wispa.org/pipermail/wireless/




WISPA Wants You! Join today!
http://signup.wispa.org/

 
WISPA Wireless List: wireless@wispa.org

Subscribe/Unsubscribe:
http://lists.wispa.org/mailman/listinfo/wireless

Archives: http://lists.wispa.org/pipermail/wireless/


Re: [WISPA] Direct Lightning Strikes

2009-08-05 Thread Marlon K. Schafer
Nextel spends tens or hundreds of thousands per device.

Our stuff is cheaper than cheap.

Get off of the TOP of the tower.  Polyphaser has a great lightning white 
paper.  If you can be 10' below the top you'll be much more protected.

Also, I've had good luck lately with ferrite beads.

And ground everything.  Ground it again.  and again and again.

You might also want to consider adding a static dissipater on the top of the 
tower to help keep the lightning away in the first place.
http://www.affordable-solar.com/gs-1.brush.lightning.dissipator.htm
http://www.eriinc.com/products/btss/CA21831A_10.pdf

I think Hutton carries something too.
marlon

- Original Message - 
From: Chuck Hogg ch...@shelbybb.com
To: WISPA General List wireless@wispa.org
Sent: Wednesday, August 05, 2009 7:31 AM
Subject: [WISPA] Direct Lightning Strikes


 Has anyone been able to withstand a direct lightning strike? We had a
 tower get hit last night, and some of our equipment lost Ethernet ports
 (RB/433AH), and we lost 3 canopy APs, but that is all (considering what
 is all up there only 2/3rds was blown).  Our Trango AP survived and a
 RB/433AH survived.  Even Nextel had their guys out there, but they just
 had to reset alarms it appears as nothing was fried on their end.  I
 wish I had to just reset alarms.



 So tell me, what do you do ? I'm tired of dumping a few grand during big
 lightning storms.



 I do the basics, Ethernet surge suppression up top and on the bottom,
 Polyphasers, ground out to the ground bars, ground out the cat5 cable,
 and no omni's.



 Regards,

 Chuck Hogg

 Shelby Broadband
 502-722-9292
 ch...@shelbybb.com

 http://www.shelbybb.com





 
 WISPA Wants You! Join today!
 http://signup.wispa.org/
 

 WISPA Wireless List: wireless@wispa.org

 Subscribe/Unsubscribe:
 http://lists.wispa.org/mailman/listinfo/wireless

 Archives: http://lists.wispa.org/pipermail/wireless/ 




WISPA Wants You! Join today!
http://signup.wispa.org/

 
WISPA Wireless List: wireless@wispa.org

Subscribe/Unsubscribe:
http://lists.wispa.org/mailman/listinfo/wireless

Archives: http://lists.wispa.org/pipermail/wireless/


Re: [WISPA] Direct Lightning Strikes

2009-08-05 Thread jp
We've added a 2/0 (I think) insulated copper wire from the tower top rod 
to the grounding at the bottom. This has helped a great deal at the two 
towers we've done it at. The current will go mostly through this instead 
of mostly on the tower framework (or your shielding). It was about 
$3/foot, and a similar amount for installation labor.

The cell phone guys usually also run their own heavy duty ground down 
their cable management ladder next to their coaxes, probably for similar 
purposes.

We can't do this everywhere for various reasons, and we've lost a lot of 
money on lighting damage in July.

On Wed, Aug 05, 2009 at 10:31:42AM -0400, Chuck Hogg wrote:
 Has anyone been able to withstand a direct lightning strike? We had a
 tower get hit last night, and some of our equipment lost Ethernet ports
 (RB/433AH), and we lost 3 canopy APs, but that is all (considering what
 is all up there only 2/3rds was blown).  Our Trango AP survived and a
 RB/433AH survived.  Even Nextel had their guys out there, but they just
 had to reset alarms it appears as nothing was fried on their end.  I
 wish I had to just reset alarms.
 
  
 
 So tell me, what do you do ? I'm tired of dumping a few grand during big
 lightning storms.
 
  
 
 I do the basics, Ethernet surge suppression up top and on the bottom,
 Polyphasers, ground out to the ground bars, ground out the cat5 cable,
 and no omni's.
 
  
 
 Regards,
 
 Chuck Hogg
 
 Shelby Broadband
 502-722-9292
 ch...@shelbybb.com
 
 http://www.shelbybb.com
 
  
 
 
 
 
 WISPA Wants You! Join today!
 http://signup.wispa.org/
 
  
 WISPA Wireless List: wireless@wispa.org
 
 Subscribe/Unsubscribe:
 http://lists.wispa.org/mailman/listinfo/wireless
 
 Archives: http://lists.wispa.org/pipermail/wireless/

-- 
/*
Jason Philbrook   |   Midcoast Internet Solutions - Wireless and DSL
KB1IOJ|   Broadband Internet Access, Dialup, and Hosting 
 http://f64.nu/   |   for Midcoast Mainehttp://www.midcoast.com/
*/



WISPA Wants You! Join today!
http://signup.wispa.org/

 
WISPA Wireless List: wireless@wispa.org

Subscribe/Unsubscribe:
http://lists.wispa.org/mailman/listinfo/wireless

Archives: http://lists.wispa.org/pipermail/wireless/


Re: [WISPA] Direct Lightning Strikes

2009-08-05 Thread Scott Reed
We did something similar on a tower where we had a PacWireless SO24-xx 
antenna at the top.  Ran a piece of 10AWG up so it stuck up about 1 foot 
above the antenna.  Never took a lightning hit.  Can't say so much for 
the wind, though.  Blew the cover off one day.

jp wrote:
 We've added a 2/0 (I think) insulated copper wire from the tower top rod 
 to the grounding at the bottom. This has helped a great deal at the two 
 towers we've done it at. The current will go mostly through this instead 
 of mostly on the tower framework (or your shielding). It was about 
 $3/foot, and a similar amount for installation labor.

 The cell phone guys usually also run their own heavy duty ground down 
 their cable management ladder next to their coaxes, probably for similar 
 purposes.

 We can't do this everywhere for various reasons, and we've lost a lot of 
 money on lighting damage in July.

 On Wed, Aug 05, 2009 at 10:31:42AM -0400, Chuck Hogg wrote:
   
 Has anyone been able to withstand a direct lightning strike? We had a
 tower get hit last night, and some of our equipment lost Ethernet ports
 (RB/433AH), and we lost 3 canopy APs, but that is all (considering what
 is all up there only 2/3rds was blown).  Our Trango AP survived and a
 RB/433AH survived.  Even Nextel had their guys out there, but they just
 had to reset alarms it appears as nothing was fried on their end.  I
 wish I had to just reset alarms.

  

 So tell me, what do you do ? I'm tired of dumping a few grand during big
 lightning storms.

  

 I do the basics, Ethernet surge suppression up top and on the bottom,
 Polyphasers, ground out to the ground bars, ground out the cat5 cable,
 and no omni's.

  

 Regards,

 Chuck Hogg

 Shelby Broadband
 502-722-9292
 ch...@shelbybb.com

 http://www.shelbybb.com

  



 
 WISPA Wants You! Join today!
 http://signup.wispa.org/
 
  
 WISPA Wireless List: wireless@wispa.org

 Subscribe/Unsubscribe:
 http://lists.wispa.org/mailman/listinfo/wireless

 Archives: http://lists.wispa.org/pipermail/wireless/
 

   
 


 No virus found in this incoming message.
 Checked by AVG - www.avg.com 
 Version: 8.5.392 / Virus Database: 270.13.44/2283 - Release Date: 08/05/09 
 05:57:00

   

-- 
Scott Reed
Sr. Systems Engineer
GAB Midwest
1-800-363-1544 x4000
Cell: 260-273-7239




WISPA Wants You! Join today!
http://signup.wispa.org/

 
WISPA Wireless List: wireless@wispa.org

Subscribe/Unsubscribe:
http://lists.wispa.org/mailman/listinfo/wireless

Archives: http://lists.wispa.org/pipermail/wireless/